Since the Flexnet on port 3 was active and could be seen on the Mate, thus
I moved the slave on port 2 to port 3 and moved the FlexNet from port 3 to
port 4. No change. I did try another OB factory green cable to no avail.

Christopher

On Thu, Jun 25, 2020 at 4:25 PM Jerry Shafer <[email protected]>
wrote:

> Chris
> Did you skip over and plug in to port 3 with the slave, swap the cord,
> Jerry
>
> On Thu, Jun 25, 2020, 12:54 PM Chris Schaefer <[email protected]>
> wrote:
>
>> The system is critical to a farm watering operation so I wasn't able to
>> shut it down to try and swap the port 1 inverter with the port 2 inverter.
>> As for changing the power save settings, that is what alerted me to the
>> issue. Under no circumstance can you see a port 2 via the Mate. That's what
>> had me looking at the hub itself and that's when I noticed that the LED on
>> port 2 wasn't lighting up as the hub scrolled/polled by.
>>
>> Christopher
>>
>> On Thu, Jun 25, 2020 at 3:37 PM William Miller <[email protected]>
>> wrote:
>>
>>> Christopher;
>>>
>>>
>>>
>>> Just spit-balling here:  is the secondary inverter asleep (hate the
>>> master/slave terminology…)?  Try changing power save settings to make sure
>>> the secondary is awake and see if that changes the situation.  Seems
>>> unlikely this will solve the problem, but it may provide some kind of clue.
>>>
>>>
>>>
>>> Also, did you try swapping primary and secondary?  Run with secondary
>>> alone as primary?
>>>
>>>
>>>
>>> William Miller
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:[email protected]] *On
>>> Behalf Of *Chris Schaefer
>>> *Sent:* Thursday, June 25, 2020 10:35 AM
>>> *To:* RE-wrenches
>>> *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @
>>> Mate3s
>>>
>>>
>>>
>>> G'Day All,
>>>
>>>
>>>
>>> So I started up a system recently with two Radian 8048A's. The master is
>>> connected to port 1 and the slave connected to port 2 with the FlexNet at
>>> port 3. There are no OB charge controllers in the system. When the hub is
>>> polling (led's scrolling) nothing shows up for the slave at port 2. It's
>>> like the slave inverter doesn't exist. So I moved the slave and flexnet
>>> down to port 3 and 4. No change in the polling. I swapped out comm (factory
>>> green) cables. Again no change. Looking at the control board of the slave
>>> there is only one green led on which is located at the upper right-hand
>>> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
>>> the inverter. Of course since there is no polling at the hub there is no
>>> way to view port 2 to view the slave at the Mate.
>>>
>>>
>>>
>>> Now the only thing that I didn't do was to try and use the manual
>>> on/off  switch-jumper to start the slave. But in the past regardless of the
>>> inverter being on or off it would still show up on the hub. This is  a new
>>> one and I'm looking for some direction here.
>>>
>>>
>>>
>>> Thanks,
>>>
>>> Christopher-
>>>
>>> Chris Schaefer’s
>>> <http://www.solarandwindfx.com>
>>>
>>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>>> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
>>> <http://www.solarandwindfx.com> ~ E-mail: **[email protected]
>>> <[email protected]>*
>>>
>>> Thomas Jefferson, the author of our great Constitution, once said,
>>> "democracy" will cease to exist when you take away from those who are
>>> willing to work and give to those who would not."
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>
>> --
>>
>> Chris Schaefer’s
>> <http:www.solarandwindfx.com>
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>> <http://www.solarandwindfx.com> ~ E-mail: [email protected]
>> <[email protected]>*
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s
<http:www.solarandwindfx.com>

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: [email protected]
<[email protected]>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to