Jay,

I researched this years ago, so I have no specific figures for you such as pullout strength, only the general lesson that I learned. The pullout strength of Tek and similar self-tapping screws is surprisingly high, especially in the larger diameters, such as #14, which equates to 1/4" as I recall. As long as the purlin into which you're drilling and threading is of sufficient thickness to resist deforming and tearout (your 3/16" should be sufficient), the screw will not tear out under more-than-normal wind loading.

You should be able to find actual values via online research, as I did.

Allan

On 10/17/2020 8:11 AM, Jay wrote:
What do people recommend for a metal roof ( with flat sections, not 
corrugated)on 3/16” thick x 2” wide C channel for attaching L feet

Self taping fasteners would be the easiest. Doing a nut and bolt would be 
possible but quite time consuming.
A machine self taping bolt and then adding a nut would be a lot easier than nut 
and bolt.

But that is my question. Is a self taping screw enough or does it need to be 
bolted?

Jay
Peltz power
--

*Allan Sindelar*
[email protected] <mailto:[email protected]>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to