The notes in the NEC 2020 Handbook for article 706 clearly state that 706 only covers ESS which is an assembly of components, and that the total assembly must be listed under UL 9540.

Further it states: "/A group of separate components that includes storage batteries, that is provided with support systems (racks), charge controllers, and inverters, and that does NOT have an overall listing as an ESS is a storage battery system and as such is subject to the requirements of article 480"/

and just in case someone says the notes don't matter, 706.5 says: "/Energy Storage systems shall be listed"/.

So, since I have never used an actual listed ESS, I'm back to 480. Specifically, 480.7 (A) says we need a disconnect for batteries over 60 vdc (48v should be exempt) and then 480.7(B) says houses need to have an outside disconnect for the batteries labeled "Emergency Disconnect".

So here's the real question:   Does 480.7(A) exempt us from 480.7(B)?

Ray Walters
Remote Solar
303 505-8760

On 3/9/19 8:08 PM, Brian Mehalic wrote:
Hi Glenn, I don't completely agree with your interpretation of ESS systems and the application of Article 706.  Yes, an ESS /could/ provide 120/240 VAC (e.g. the Powerwall), but the figures in Article 690 show three different configurations where the output of the ESS is not AC, and where the ESS disconnect comes before any power electronics (like a multimode inverter, as shown in the AC and DC coupled systems) or loads (as shown in the stand-alone system). Are those ESS connected to other systems which utilize stored energy to provide AC power? Yes, but the key is "connected to other systems" - in many cases the ESS only provides DC.  In fact the definition of ESS clearly states this - it /can/ have AC or DC output, and it /may/ include power electronics (but may not).

My understanding is that the 60 volt limit (which is obviously problematic in a world where 48 VDC batteries and ESS are very common) was inserted in order to exempt other devices that store energy (such as UPS, or battery backup in fire alarms/exit signage/etc.) from the 706 requirements.

Cheers,

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com <http://www.seisolarpros.com>



On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt <[email protected] <mailto:[email protected]>> wrote:

    Hi Ray,

    This is a conversation I have had some time ago with a number of
    my fellow inspectors and code experts. When the 2017 NEC came out,
    I agreed with Mike Holt and Bill Brooks' assessment that the new
    article was poorly written and did not apply to most systems being
    installed today. After much discussion through my Cadmus network
    of authorities, it emerged that indeed 706 apples to the typical
    residential systems.
    So Energy Storage Systems (ESS) are the point of article 706, and
    I believe that the key point is that the SYSTEM is generating AC
    voltage of 120VAC or 240VAC, making the system fall under article 706.

    Batteries themselves are minimally covered by NEC 480, NFPA 1, and
    the IFC as applicable locally.
    So, the bottom line is that the new article does cover the work we
    do when systems provide or interface with 120VAC or above (making
    the system operation exceeding the 60V AC trigger).

    My initial problem was believing that the article applied to a
    component (the battery bank), and not the system (all components
    taken together as a generator/storage system). It is an easy
    misunderstanding to make.

    Hope this helps!

    -Glenn Burt

    -----Original Message-----
    From: RE-wrenches <[email protected]
    <mailto:[email protected]>> On Behalf Of Ray
    Sent: Saturday, March 09, 2019 12:41 PM
    To: RE-wrenches <[email protected]
    <mailto:[email protected]>>
    Cc: Bill Brooks <[email protected]
    <mailto:[email protected]>>; Bill Brooks <[email protected]
    <mailto:[email protected]>>
    Subject: [RE-wrenches] NEC for Batteries < 60v ??

    Hi Everyone;

    I'm updating all my verbage on plansets, and I just realized that
    the newly created article 706 covering Energy Storage Systems is
    only for Over 60 VDC (706.1)  Also article 480 for batteries only
    requires disconnecting means over 60 VDC ?! (480.7).   I'm not
    about to not have a disconnect, so now that NEC pulled battery
    systems out of 690,  where do we go for guidance on normal battery
    systems: 12, 24, 48 VDC?

    Overall, I welcome most of the changes in NEC 2017, like
    separating off grid systems into articles 706, and 710, but it
    seems us off grid installers need some more clarification.

    Thanks,

    --
    Ray Walters
    Remote Solar
    303 505-8760

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to