I've used Blue Planet, so I guess I have used an actual UL listed ESS, even though they don't include the charge controller or inverter.  I knew they were UL, but I double checked and it is the UL 9540 standard mentioned in 706. So in this case, we could ignore 480, but are held to 706.  Regardless of 480 or 706, both are possibly requiring the outside remote disconnect.  Besides Midnite's remote trip breakers, and the dreaded Bird House, what other options are there to meet this new requirement?   Can the Blue Planet be tripped remotely?

and still my initial question:

Under 480.7, are batteries below 60v still required to have the remote disconnect?  They are exempted from having a disconnect at all in 480.7(A)......quite confusing.

Ray Walters
Remote Solar
303 505-8760

On 10/19/20 7:06 PM, Jerry Shafer wrote:
Wrenches
Blue planet are fire and UL listed systems both on there 48 Volt and the LX flavors
Jerry

On Mon, Oct 19, 2020, 5:51 PM Ray <[email protected] <mailto:[email protected]>> wrote:

    The notes in the NEC 2020 Handbook for article 706 clearly state
    that 706 only covers ESS which is an assembly of components, and
    that the total assembly must be listed under UL 9540.

    Further it states: "/A group of separate components that includes
    storage batteries, that is provided with support systems (racks),
    charge controllers, and inverters, and that does NOT have an
    overall listing as an ESS is a storage battery system and as such
    is subject to the requirements of article 480"/

    and just in case someone says the notes don't matter, 706.5 says:
    "/Energy Storage systems shall be listed"/.

    So, since I have never used an actual listed ESS, I'm back to 480.
    Specifically, 480.7 (A) says we need a disconnect for batteries
    over 60 vdc (48v should be exempt) and then 480.7(B) says houses
    need to have an outside disconnect for the batteries labeled
    "Emergency Disconnect".

    So here's the real question:   Does 480.7(A) exempt us from 480.7(B)?

    Ray Walters
    Remote Solar
    303 505-8760

    On 3/9/19 8:08 PM, Brian Mehalic wrote:
    Hi Glenn, I don't completely agree with your interpretation of
    ESS systems and the application of Article 706.  Yes, an ESS
    /could/ provide 120/240 VAC (e.g. the Powerwall), but the figures
    in Article 690 show three different configurations where the
    output of the ESS is not AC, and where the ESS disconnect comes
    before any power electronics (like a multimode inverter, as shown
    in the AC and DC coupled systems) or loads (as shown in the
    stand-alone system). Are those ESS connected to other systems
    which utilize stored energy to provide AC power? Yes, but the key
    is "connected to other systems" - in many cases the ESS only
    provides DC.  In fact the definition of ESS clearly states this -
    it /can/ have AC or DC output, and it /may/ include power
    electronics (but may not).

    My understanding is that the 60 volt limit (which is obviously
    problematic in a world where 48 VDC batteries and ESS are very
    common) was inserted in order to exempt other devices that store
    energy (such as UPS, or battery backup in fire alarms/exit
    signage/etc.) from the 706 requirements.

    Cheers,

    Brian Mehalic
    NABCEP Certified Solar PV Installation Professional™ R031508-59
    National Electrical Code® CMP-4 Member
    (520) 204-6639

    Solar Energy International
    http://www.solarenergy.org

    SEI Professional Services
    http://www.seisolarpros.com <http://www.seisolarpros.com>



    On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt <[email protected]
    <mailto:[email protected]>> wrote:

        Hi Ray,

        This is a conversation I have had some time ago with a number
        of my fellow inspectors and code experts. When the 2017 NEC
        came out, I agreed with Mike Holt and Bill Brooks' assessment
        that the new article was poorly written and did not apply to
        most systems being installed today. After much discussion
        through my Cadmus network of authorities, it emerged that
        indeed 706 apples to the typical residential systems.
        So Energy Storage Systems (ESS) are the point of article 706,
        and I believe that the key point is that the SYSTEM is
        generating AC voltage of 120VAC or 240VAC, making the system
        fall under article 706.

        Batteries themselves are minimally covered by NEC 480, NFPA
        1, and the IFC as applicable locally.
        So, the bottom line is that the new article does cover the
        work we do when systems provide or interface with 120VAC or
        above (making the system operation exceeding the 60V AC trigger).

        My initial problem was believing that the article applied to
        a component (the battery bank), and not the system (all
        components taken together as a generator/storage system). It
        is an easy misunderstanding to make.

        Hope this helps!

        -Glenn Burt

        -----Original Message-----
        From: RE-wrenches <[email protected]
        <mailto:[email protected]>> On Behalf
        Of Ray
        Sent: Saturday, March 09, 2019 12:41 PM
        To: RE-wrenches <[email protected]
        <mailto:[email protected]>>
        Cc: Bill Brooks <[email protected]
        <mailto:[email protected]>>; Bill Brooks
        <[email protected] <mailto:[email protected]>>
        Subject: [RE-wrenches] NEC for Batteries < 60v ??

        Hi Everyone;

        I'm updating all my verbage on plansets, and I just realized
        that the newly created article 706 covering Energy Storage
        Systems is only for Over 60 VDC (706.1)  Also article 480 for
        batteries only requires disconnecting means over 60 VDC ?!
        (480.7).   I'm not about to not have a disconnect, so now
        that NEC pulled battery systems out of 690,  where do we go
        for guidance on normal battery systems: 12, 24, 48 VDC?

        Overall, I welcome most of the changes in NEC 2017, like
        separating off grid systems into articles 706, and 710, but
        it seems us off grid installers need some more clarification.

        Thanks,

        --
        Ray Walters
        Remote Solar
        303 505-8760

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:[email protected]  
<mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to