Dave,

If the AHJ is happy with the remote power down of the inverter (and now the PV array if on the roof or if it enters a building other than a power shed) I'd say that's great. You can't make the inverter much safer than shutting it down. A remote battery disconnect may only de-energize another few feet of battery cable anyway. But I know in California it will be a while until the 2020 NEC is adopted, when it is adopted, you might find the AHJ just saying it has to be done with a battery disconnect.

If you are putting in a remote power off circuit or remote disconnect: does it get treated as fire safety equipment? Special MC cable? Metal conduit? Remote shut switch off grouped with the service disconnect? Is all of the equipment listed for emergency shut use? Is it good enough for a nuclear power plant safety system too? Where do we stop?

Does anyone wonder why the cabin in the woods flies under the radar rather than attempting to comply with the excess of regulations that get heaped on a small power system?

Kent Osterberg
Blue Mountain Solar



On 10/20/2020 8:50 AM, Dave Angelini Offgrid Solar wrote:

Thanks Kent,

A question, most of the Sierra AHJ's only care, and that is rare, that there is a remote power off like Outback and Schneider have already. I understand it is not a battery disco, and even though there is one in these systems, what is your response please?

I mostly dislike power sheds as people need an excuse to go there and observe. I mostly use a garage or outside house wall to build a bat room. Appreciate your thoughts. Insurance issues are not as important these days as many of us no longer can get itCry

*Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail [email protected] <mailto:[email protected]> text 209 813 0060*

On Mon, 19 Oct 2020 22:33:03 -0700, Kent Osterberg <[email protected]> wrote:

Ray,

Per NEC 480 batteries below 48 volts didn't need a readily accessible disconnect within site of the batteries. That's unchanged in the 2020 Code, you don't have to have a readily accessible disconnect within site of the batteries. That's a good thing considering the environment near lead acid batteries. A disconnect switch still isn't required in the 48-volt battery room.

Yes, if you put a 48-volt battery in a one or two-family dwelling, an outside (remote) emergency disconnect is required. That is going to be a pain that may add hundreds of dollars to the cost of small off-grid systems. You might get away with a mushroom switch and a 24-volt tap on the batteries to activate a remote trip breaker. But considering that it is a fire-safety related circuit it is probably best to spend the money for the bird box.

At the very least 480.7(B) should make off-grid folks think about using a power shed. The power shed is not a dwelling so 2020 NEC 480.7(B) doesn't apply.

Kent Osterberg
Blue Mountain Solar


On 10/19/2020 8:34 PM, Ray wrote:

I've used Blue Planet, so I guess I have used an actual UL listed ESS, even though they don't include the charge controller or inverter.  I knew they were UL, but I double checked and it is the UL 9540 standard mentioned in 706. So in this case, we could ignore 480, but are held to 706. Regardless of 480 or 706, both are possibly requiring the outside remote disconnect.  Besides Midnite's remote trip breakers, and the dreaded Bird House, what other options are there to meet this new requirement?   Can the Blue Planet be tripped remotely?

and still my initial question:

Under 480.7, are batteries below 60v still required to have the remote disconnect?  They are exempted from having a disconnect at all in 480.7(A)......quite confusing.

Ray Walters
Remote Solar
303 505-8760
On 10/19/20 7:06 PM, Jerry Shafer wrote:
Wrenches
Blue planet are fire and UL listed systems both on there 48 Volt and the LX flavors
Jerry

On Mon, Oct 19, 2020, 5:51 PM Ray <[email protected] <mailto:[email protected]>> wrote:

    The notes in the NEC 2020 Handbook for article 706 clearly
    state that 706 only covers ESS which is an assembly of
    components, and that the total assembly must be listed under UL
    9540.

    Further it states: "/A group of separate components that
    includes storage batteries, that is provided with support
    systems (racks), charge controllers, and inverters, and that
    does NOT have an overall listing as an ESS is a storage battery
    system and as such is subject to the requirements of article 480"/

    and just in case someone says the notes don't matter, 706.5
    says: "/Energy Storage systems shall be listed"/.

    So, since I have never used an actual listed ESS, I'm back to
    480. Specifically, 480.7 (A) says we need a disconnect for
    batteries over 60 vdc (48v should be exempt) and then 480.7(B)
    says houses need to have an outside disconnect for the
    batteries labeled "Emergency Disconnect".

    So here's the real question:   Does 480.7(A) exempt us from
    480.7(B)?

    Ray Walters
    Remote Solar
    303 505-8760

    On 3/9/19 8:08 PM, Brian Mehalic wrote:
    Hi Glenn, I don't completely agree with your interpretation of
    ESS systems and the application of Article 706.  Yes, an ESS
    /could/ provide 120/240 VAC (e.g. the Powerwall), but the
    figures in Article 690 show three different configurations
    where the output of the ESS is not AC, and where the ESS
    disconnect comes before any power electronics (like a
    multimode inverter, as shown in the AC and DC coupled systems)
    or loads (as shown in the stand-alone system). Are those ESS
    connected to other systems which utilize stored energy to
    provide AC power? Yes, but the key is "connected to other
    systems" - in many cases the ESS only provides DC.  In fact
    the definition of ESS clearly states this - it /can/ have AC
    or DC output, and it /may/ include power electronics (but may
    not).
    My understanding is that the 60 volt limit (which is obviously
    problematic in a world where 48 VDC batteries and ESS are very
    common) was inserted in order to exempt other devices that
    store energy (such as UPS, or battery backup in fire
    alarms/exit signage/etc.) from the 706 requirements.
    Cheers,
    Brian Mehalic
    NABCEP Certified Solar PV Installation Professional™ R031508-59
    National Electrical Code® CMP-4 Member
    (520) 204-6639
    Solar Energy International
    http://www.solarenergy.org
    SEI Professional Services
    http://www.seisolarpros.com <http://www.seisolarpros.com>

    On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt
    <[email protected] <mailto:[email protected]>> wrote:

        Hi Ray,

        This is a conversation I have had some time ago with a
        number of my fellow inspectors and code experts. When the
        2017 NEC came out, I agreed with Mike Holt and Bill
        Brooks' assessment that the new article was poorly written
        and did not apply to most systems being installed today.
        After much discussion through my Cadmus network of
        authorities, it emerged that indeed 706 apples to the
        typical residential systems.
        So Energy Storage Systems (ESS) are the point of article
        706, and I believe that the key point is that the SYSTEM
        is generating AC voltage of 120VAC or 240VAC, making the
        system fall under article 706.

        Batteries themselves are minimally covered by NEC 480,
        NFPA 1, and the IFC as applicable locally.
        So, the bottom line is that the new article does cover the
        work we do when systems provide or interface with 120VAC
        or above (making the system operation exceeding the 60V AC
        trigger).

        My initial problem was believing that the article applied
        to a component (the battery bank), and not the system (all
        components taken together as a generator/storage system).
        It is an easy misunderstanding to make.

        Hope this helps!

        -Glenn Burt

        -----Original Message-----
        From: RE-wrenches
        <[email protected]
        <mailto:[email protected]>> On
        Behalf Of Ray
        Sent: Saturday, March 09, 2019 12:41 PM
        To: RE-wrenches <[email protected]
        <mailto:[email protected]>>
        Cc: Bill Brooks <[email protected]
        <mailto:[email protected]>>; Bill Brooks
        <[email protected] <mailto:[email protected]>>
        Subject: [RE-wrenches] NEC for Batteries < 60v ??

        Hi Everyone;

        I'm updating all my verbage on plansets, and I just
        realized that the newly created article 706 covering
        Energy Storage Systems is only for Over 60 VDC (706.1) 
        Also article 480 for batteries only requires disconnecting
        means over 60 VDC ?! (480.7).   I'm not about to not have
        a disconnect, so now that NEC pulled battery systems out
        of 690,  where do we go for guidance on normal battery
        systems: 12, 24, 48 VDC?

        Overall, I welcome most of the changes in NEC 2017, like
        separating off grid systems into articles 706, and 710,
        but it seems us off grid installers need some more
        clarification.

        Thanks,

        --
        Ray Walters
        Remote Solar
        303 505-8760

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:[email protected]  
<mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't
    work, try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to