Hello fellow wrenches! We have had this issue with a couple of systems and it drove us crazy. This was for two systems that had been programmed to run in mini grid mode. After replacing all communication wires with shielded cable, replacing the mate, replacing hub, replacing guts from both inverters we still had the problem. What finally solved it was changing it to HBX mode. Havn't had the issue since. What mode are the inverters/mate programmed to operate in. Also, of course making sure all firmwares are most current on all updatable devices. Keep us posted if you find the culprit. Hope that helps! Sunny Regards, Kirpal Khalsa Oregon LRT#25 Oregon Solarworks LLC www.oregonsolarworks.com 541-299-0402
On Mon, Mar 29, 2021 at 8:31 AM <drake.chamber...@redwoodalliance.org> wrote: > It seems that battery based inverters are not nearly as reliable as they > once were. I understand that the Samlex inverters are pretty bulletproof. > They are coming out with a 120/240V split phase to work with a 48V battery > bank. I don't know that these are grid interactive, or if they can be > stacked. > > We need a manufacturer to produce something equivalent to the FX series > inverters, or the earlier Radians. > > What is the best choice for a grid interactive, battery based inverter? I > tend to lean toward Schneider. > > Drake > > > Drake Chamberlin > > Athens Electric LLC > > Ohio Electrical Contractor’s License 44810 > > CO Master Electrician’s License 4526 > > NABCEP Certified PV Installation Professional > --- > > > > On 2021-03-28 12:04, Roland - RES wrote: > > Aloha Wayne, > > We too have been plagued by this issue, that has been extremely > frustrating for us and our clients. > > The newest 1.4.6 firmware is supposed to fix this issue. We have updated > our systems with this and so far so good. However because of the sometimes > long delays between the faults we can't be certain. > > Prior to this most common fix was replacing the mate. > > Also on FP2 we had a couple factory units have the hub jumpers set for the > wrong stacking. I believe they were set for parallel operations versus > series. Strange it would work fine with the jumpers either way for a long > time. But it's worth a check. > > Sent from a IPhone, with touch screen keys on the fly. Please excuse > shortcuts and typos. > > > > Roland Shackelford > NABCEP CERTIFIED PV INSTALLER > President > Renewable Energy Services (RES), Inc. > Mobile: *808-938-9239 <http://808-938-9239/>* > www.renewablenergy.com > > On Mar 27, 2021, at 3:11 PM, Wayne Irwin <pureenergyso...@hotmail.com> > wrote: > > Wrenches and Lones, > > We have had chronic inverter firmware mismatch issues with FLEXpower TWO > FXR series on many systems. > We've updated the firmware and replaced mates, yet the system failures > continue. > > The systems will work flawlessly for months and then randomly show error > and the firmware mismatch. Occasionally the system will discover (on its > own) that the firmware is the same and turn back on. But usually, the > "solution" is to unplug the mate and plug it back in and like > magic...everything works again anywhere from 3 months to a year. > > This is disappointing and frustrating to the system owners as well as > costly and time consuming for us. > > *Any guidance in resolving this issue would be greatly appreciated.* > > All these systems have been assembled by Outback. > None of them have OpticsRE. > > > > > Wayne Irwin > President > License #CVC56695 > State Licensed Solar Contractor > Pure Energy Solar International Inc. > wa...@pureenergysolar.com > PureEnergySolar.com <http://pureenergysolar.com/> > SolarChargingStation.com <http://solarchargingstation.com/> > 352 377-6527 Office > 352 336-3299 Fax > 352 316-1637 Cell > > The Sun Is Always Shining! > > The content of this message is Pure Energy Solar Confidential. If you are > not the intended recipient and have received this message in error, any use > or distribution is prohibited. Please notify me immediately by reply e-mail > and delete this message from your computer system. Thank you. > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org