All our systems except for 2 are GT. We've also swapped cables, mates, hubs 
etc...to no avail.

On the other hand, the systems that we installed decades ago with GVFX3648's 
are still operating without a glitch.


Wayne Irwin
President
License #CVC56695
State Licensed Solar Contractor
Pure Energy Solar International Inc.
[email protected]
PureEnergySolar.com<http://pureenergysolar.com/>
SolarChargingStation.com<http://solarchargingstation.com/>
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The Sun Is Always Shining!

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.


________________________________
From: RE-wrenches <[email protected]> on behalf of 
Kirpal <[email protected]>
Sent: Monday, March 29, 2021 11:54 AM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Outback_Inverter firmware mismatch

Hello fellow wrenches!
We have had this issue with a couple of systems and it drove us crazy.  This 
was for two  systems that had been programmed to run in mini grid mode. After 
replacing all communication wires with shielded cable, replacing the mate, 
replacing hub, replacing guts from both inverters we still had the problem.  
What finally solved it was changing it to HBX mode.  Havn't had the issue since.
What mode are the inverters/mate programmed to operate in.
Also, of course making sure all firmwares are most current on all updatable 
devices.
Keep us posted if you find the culprit.
Hope that helps!
Sunny Regards,
Kirpal Khalsa
Oregon LRT#25
Oregon Solarworks LLC
www.oregonsolarworks.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.oregonsolarworks.com%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955681657%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=PT8VwcQNTuz6F5Dx6DkjnGpK5R277e7zY08qcRMEoGw%3D&reserved=0>
541-299-0402


On Mon, Mar 29, 2021 at 8:31 AM 
<[email protected]<mailto:[email protected]>>
 wrote:

It seems that battery based inverters are not nearly as reliable as they once 
were. I understand that the Samlex inverters are pretty bulletproof. They are 
coming out with a 120/240V split phase to work with a 48V battery bank. I don't 
know that these are grid interactive, or if they can be stacked.

We need a manufacturer to produce something equivalent to the FX series 
inverters, or the earlier Radians.

What is the best choice for a grid interactive, battery based inverter? I tend 
to lean toward Schneider.

Drake


Drake Chamberlin

Athens Electric LLC

Ohio Electrical Contractor’s License 44810

CO Master Electrician’s License 4526

NABCEP Certified PV Installation Professional

---



On 2021-03-28 12:04, Roland - RES wrote:

Aloha Wayne,

We too have been plagued by this issue, that has been extremely frustrating for 
us and our clients.

The newest 1.4.6 firmware is supposed to fix this issue. We have updated our 
systems with this and so far so good. However because of the sometimes long 
delays between the faults we can't be certain.

Prior to this most common fix was replacing the mate.

Also on FP2 we had a couple factory units have the hub jumpers set for the 
wrong stacking. I believe they were set for parallel operations versus series. 
Strange it would work fine with the jumpers either way for a long time. But 
it's worth a check.

Sent from a IPhone, with touch screen keys on the fly. Please excuse shortcuts 
and typos.

Roland Shackelford
NABCEP CERTIFIED PV INSTALLER
President
Renewable Energy Services (RES), Inc.
Mobile:  808-938-9239<http://808-938-9239/>
www.renewablenergy.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.renewablenergy.com%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955691654%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=SD8HPQTIjhTZEesUuu7pAo6DNKDYZqRArg2TXoajqR8%3D&reserved=0>

On Mar 27, 2021, at 3:11 PM, Wayne Irwin 
<[email protected]<mailto:[email protected]>> wrote:

Wrenches and Lones,

We have had chronic inverter firmware mismatch issues with FLEXpower TWO FXR 
series on many systems.
We've updated the firmware and replaced mates, yet the system failures continue.

The systems will work flawlessly for months and then randomly show error and 
the firmware mismatch. Occasionally the system will discover (on its own) that 
the firmware is the same and turn back on. But usually, the "solution" is to 
unplug the mate and plug it back in and like magic...everything works again 
anywhere from 3 months to a year.

This is disappointing and frustrating to the system owners as well as costly 
and time consuming for us.

Any guidance in resolving this issue would be greatly appreciated.

All these systems have been assembled by Outback.
None of them have OpticsRE.





Wayne Irwin
President
License #CVC56695
State Licensed Solar Contractor
Pure Energy Solar International Inc.
[email protected]
PureEnergySolar.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fpureenergysolar.com%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955691654%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=nCTWCwHCBiRsmRs2EhEvQGkbT341rZlIBgceLYjqrPo%3D&reserved=0>
SolarChargingStation.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fsolarchargingstation.com%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955701648%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=HNZDClCC%2FBJrnV96Q%2FNfUP7us18jqVarsDUPcbIGvGk%3D&reserved=0>
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The Sun Is Always Shining!

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.




_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955711643%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=0bCMs6Nig02uaaT8GwCu23E6MAp7%2FXK4Pd%2FLbPPA7Wo%3D&reserved=0>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955711643%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=axlXyuCgjBCwYoaDmhYQ1wt1M7NzloDkarR14jdDnEQ%3D&reserved=0>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955721638%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=foBd72D9UCAD88Xx7afhhlotHnSbfSOuILo0BX8ws4U%3D&reserved=0>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955731635%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=qgQxyIF90E%2BJu6WCrKGHj8%2BYK2Q4Mc4hoZHYTpR4ya0%3D&reserved=0>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955731635%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=sbhh4rbC%2F3Eru2s7odc8hdLQUPDbo8LjaOlHWzrQhLY%3D&reserved=0>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955741628%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=A71mTAZf5JxZG6lk5CEMAUkZimKVi5WWrBV79fIVDAs%3D&reserved=0>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955741628%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=%2Bl0ete%2BmuLUBqhNHYW%2BXMYT7UPjWl1XhLAqsTS65fQI%3D&reserved=0>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955751622%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=aI%2FXIJhSpriGfszMMx3YbT91yXAkfjtaFSzRmlfpAM0%3D&reserved=0>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955761620%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=wv3XelGKFmsd9jUOZ9XAF7Gl1mv9nfdvJdLKhdAwnMw%3D&reserved=0>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955761620%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=QU2DfYs95LHOlEjHEtpbMjPi3c9od0cA%2F5fbXZSP11c%3D&reserved=0>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955771618%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=WMzZWijJBLS4rtXvzDNajIlmQ1UJpXp8GcCDI3cFWbc%3D&reserved=0>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955771618%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=%2BhJldIKzpRCmkJO9Gka4xTncIawGeOph8zZJtNBpDFw%3D&reserved=0>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955781615%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=qvY4wqf%2BcG0Kyflxvs%2BjhlcprlLeP15oIgcX0govFkY%3D&reserved=0>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955791608%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=XasJtcm6HAvu0WEFq4Rf4x63rrb%2FYTN%2Fuo3t5d9Ca64%3D&reserved=0>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&data=04%7C01%7C%7C1bc8e3dae76545c67adf08d8f2cafdb7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637526300955791608%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=UB0e5XxayuKb%2Fj7Kg28%2BOOJLXKRCuKSTxxwManje0Lg%3D&reserved=0>

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to