The "R" inverters have had a persistent issue that the list discussed
recently. You get an error "inverter firmware mismatch". This results in
losing a phase and then can be cleared by power cycling the Mate 3s and
will work ok for a while and then repeat. The latest firmware for the
Mate3s attempts to solve this but we will see...

This has been an ongoing and frustrating issue with the fxr inverters. In
my experience, this doesn't happen with fx inverters, or Radian inverters
at all. Outback tech support had been all over the place on this but I
think, with this latest firmwate release, acknowledge the issue.

Good luck

On Mon, May 17, 2021, 4:43 PM Jay <[email protected]> wrote:

> Hi dave
>
> You’ll need a new hub and mate 3S.
>
>
> And check to make sure the main breakers are 250 amp.
>
> Jay
> Peltz power.
>
>
>
>
>
> On May 17, 2021, at 8:21 AM, [email protected] wrote:
>
> 
>
> I am considering swapping in new OutBack inverters into one of my
> neighborhoods 24V off grid systems. It now has two FX2524’s. The demands on
> the system have grown, now a two family home with a 240Vac mini-split for
> air conditioning and a 240Vac Grundfos SQ 1/2hp sub pump to be added this
> summer to the system. Drilling a well for a back-up to the gravity fed
> spring water which has been getting too low during the past few summers.
>
> I’m assuming that I should go with two VFXR3524’s.
>
> Will this be a direct swap in as far as having the same wiring setup into
> an OutBack Flexware system? And will it work with an older Mate?
>
> Anything else I should know about these OutBack “R” inverters?
>
>
>
> Dave Palumbo
>
> Hyde Park, VT
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to