I also have a new (7 month old) PAE system with 2-4448 Inverters (stacked) that 
we are having some strange issues with.  The most troublesome issue is the new 
Rheem wall-hung LP instant water heater/boiler is throwing an Error Code 12 
which is supposedly a “Flame Failure”.  It’s a brand new installation with new 
tanks and lines and the gas guys have doubled checked everything.  We are now 
wondering if it might be related to the power supply.  The other indications 
that it could be related are flickering lights, a 12V battery charger (AC plug 
in type) that won’t work off inverter power (but will when plugged into the 
genny, and I’m seeing a little bit of wondering in the Hz on my simple Exeltech 
volt meter.  

Magnum recommended a run capacitor on the boiler circuit.  I installed that on 
Friday and still had the error code come up 4 times over the weekend.

Any thoughts?  

Best,
Amos


       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    ienergyVT.com <http://www.ienergyvt.com/>
        Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>

> On Jan 9, 2022, at 7:26 PM, Ray <[email protected]> wrote:
> 
> Long runs of URD direct buried?  Just a nick into the metal can corrode the 
> cable all the way through over time.  We use conduit for almost everything 
> anymore.  The savings with URD doesn't pan out, when you have to abandon the 
> line after 10 years.
> 
> Ray Walters
> Remote Solar
> 303 505-8760
> On 1/9/22 5:10 PM, Jerry Shafer wrote:
>> I would look at connections first, lug that is not as tight as it ne we do 
>> to be, a breaker failing, outlets that are either push in wires or have 
>> loose connections. Eliminate what you can before looking at the inverters
>> 
>> On Sun, Jan 9, 2022, 11:36 AM Jeremy Rodriguez <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>>> 
>>> Hello
>>> we have a lot of PAE series magnum inverters out there.
>>> One client lately has been experiencing voltage drop and failure of PCBs in 
>>> two of his household appliances.  I know it’s common to have some dimming 
>>> of the lights when a well pump or other large load kicks on, but has anyone 
>>> ran across a solution to alleviate the problem or boost up the voltage / 
>>> condition it, in any way ?
>>> I’m not sure if this just happens with low battery voltage, or always 
>>> The inverter is located ~ 300 ft from the main electrical panel with 
>>> #2/2/2/4 URD feeders to an outdoor disco, then 8 AWG copper to the mains 
>>> panel. 
>>> 4448 PAE with one string of 6CS21P Batteries. 
>>> 
>>> 
>> Jeremy Rodriguez 
>> Solar Installation / Design Expert 
>> All Solar, Inc.
>> 1453 M St
>> Penrose Colorado 
>>> 
>>> 
>>> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to