So the issue ended up being , as far as we can tell at this point , a loose 
neutral connection at the first load distribution panel feeding all loads after 
the inverter.

Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.

On Jan 12, 2022, at 3:18 PM, Sindelar Solar <[email protected]> wrote:

 Amos,
I installed an MS-4448AE (not PAE) in late 2008 that wouldn't fire up a Buderus 
hydronic boiler. Ultimately it was replaced with a Lochinvar and that solved 
the issue. Magnum asked for the Buderus for testing, but that never happened, 
as once the problem was resolved by the heating contractor it was forgotten.

This issue was addressed on this list around 2/10/09, if you'd care to peruse 
the archives. To make it easier, I'll forward you a few of the emails, 
including a compendium of Wrenches responses, off list.

I'll also note that I have used a MS4024AE in my own home since 2010. It's been 
flawlessly reliable. However, every time the fridge comes on the lights 
flicker, especially one chandelier with 6 40W incandescent bulbs on a rotary 
dimmer. And one client with a MS4448PAE I installed in 2011 complained that 
while the inverter worked well, anything in his home with a clock built in ran 
slow and had to be reset at least monthly.
Allan

On 1/10/2022 1:11 PM, Amos Post wrote:
I also have a new (7 month old) PAE system with 2-4448 Inverters (stacked) that 
we are having some strange issues with.  The most troublesome issue is the new 
Rheem wall-hung LP instant water heater/boiler is throwing an Error Code 12 
which is supposedly a “Flame Failure”.  It’s a brand new installation with new 
tanks and lines and the gas guys have doubled checked everything.  We are now 
wondering if it might be related to the power supply.  The other indications 
that it could be related are flickering lights, a 12V battery charger (AC plug 
in type) that won’t work off inverter power (but will when plugged into the 
genny, and I’m seeing a little bit of wondering in the Hz on my simple Exeltech 
volt meter.
Magnum recommended a run capacitor on the boiler circuit.  I installed that on 
Friday and still had the error code come up 4 times over the weekend.
Any thoughts?
Best,
Amos
<IE%20LOGO%20150x78.jpg>


       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    ienergyVT.com<http://www.ienergyvt.com>
        Facebook<https://www.facebook.com/integrityenergyllp?ref=hl>

On Jan 9, 2022, at 7:26 PM, Ray <[email protected]<mailto:[email protected]>> 
wrote:

Long runs of URD direct buried?  Just a nick into the metal can corrode the 
cable all the way through over time.  We use conduit for almost everything 
anymore.  The savings with URD doesn't pan out, when you have to abandon the 
line after 10 years.

Ray Walters
Remote Solar
303 505-8760

On 1/9/22 5:10 PM, Jerry Shafer wrote:
I would look at connections first, lug that is not as tight as it ne we do to 
be, a breaker failing, outlets that are either push in wires or have loose 
connections. Eliminate what you can before looking at the inverters

On Sun, Jan 9, 2022, 11:36 AM Jeremy Rodriguez 
<[email protected]<mailto:[email protected]>> wrote:
Hello
we have a lot of PAE series magnum inverters out there.
One client lately has been experiencing voltage drop and failure of PCBs in two 
of his household appliances.  I know it’s common to have some dimming of the 
lights when a well pump or other large load kicks on, but has anyone ran across 
a solution to alleviate the problem or boost up the voltage / condition it, in 
any way ?
I’m not sure if this just happens with low battery voltage, or always
The inverter is located ~ 300 ft from the main electrical panel with #2/2/2/4 
URD feeders to an outdoor disco, then 8 AWG copper to the mains panel.
4448 PAE with one string of 6CS21P Batteries.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado
--
Allan Sindelar
[email protected]<mailto:[email protected]>
(no longer) NABCEP Certified PV Installation Professional (as I let it expire 
after 18+ years)
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to