Yes what Jay said - need a block diagram with available power flows on this one.  If you've been working with Sol-Ark you probably covered the basics but just for the rest of us to be assured:

I assume:

1)  you are using the Radian only as an AC Grid-Tie inverter - no batteries on it? 2) that you are aware that the AC Coupled wattage plus the DC wattage on the Sol-Ark's MPPTs must be within the total allowed for solar generation 3) that you have the AC Coupled output of the Radian connected to the GEN breaker of the Sol-Ark 4) that you have the software set for the GEN breaker to be AC Coupled and have checked all other software items with Sol-Ark needed for AC coupling

just as a starting base for us to understand what may be happening.

And some of the techs at Sol-Ark are in training - have you talked to the tech lead,  Dustin Douglas?  He's the official Sol-Ark rep on this list but I just saw him at InterSolar and he said he has been just too busy to chime in here much.  I'm scheduled to speak with him soon - I'll see if he can find the time if he hasn't already talked to you.


Best,

Jeff


Vince McClellan <mailto:[email protected]>
January 19, 2022 at 3:15 PM
Is anyone on the list familiar with AC coupling Sol-Ark inverters?
We haven't been able to AC couple an existing Outback Radian system to a new system that we built with 3, Sol-Ark 12K inverters and 3, Blue Ion batteries. Each time we have tested the system the Sol-Ark inverters accept the power from the Radian inverter until we turn on the DC power from the new solar array to the Sol-Ark inverters. As soon as there is significant DC power coming from the solar array the Sol-Ark inverters freq-watt turns on for a brief second and disconnects the Radian inverter even when the Blue Ion batteries are below the programmed state of charge threshold. If we don't turn on the DC power from the new solar array the Radian will connect and stay connected.

We have been working with Sol-Ark for several months now to get this system to accept the incoming power from the Radian without freq-watt kicking in on the Sol-Ark inverters and disconnecting the Radian inverter. Sol-Ark has sent two software revisions to the Sol-Ark inverters and we are still experiencing the same problem.

Can anyone think of what we might be missing and where to direct our troubleshooting efforts next?

Thanks,

Vince McClellan
Energy Design
NABCEP PV Installation Professional
p. (541) 485-8122 <tel:%28541%29%20485-8122>  f. (541) 338-8202 <tel:%28541%29%20338-8202>

If you have received this email and are not the intended recipient please delete this email. Copying, or using any part, content, or attachment of this email is strictly prohibited.


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to