I must agree spent quite a bit of time trying to figure WTF over. Then i saw it 
was an architect design. He must have been paying himself cause I have no idea 
why someone would want to try to integrate all this stuff while the tech 
support had nothing to say but; "that won’t work”. Hope for your sake it was 
T&M. T
> On Jan 20, 2022, at 2:25 PM, Jeff Clearwater <[email protected]> 
> wrote:
> 
> Hi Vince and All,
> 
> Loving this insightful discussion on the technical subtleties of this set-up 
> - but I'm wondering if I'm missing the Why?  What is this design trying to 
> accomplish?  What were the overriding design drivers?
> 
> Is it a case of incremental design where one system needed to grow but a 
> separate system was added?  Are they physically close to each other?
> 
> Are you trying to leverage the outputs so the loads have the advantage of 
> both outputs simultaneously?
> 
> If you solve this one AC coupling cut-out issue - is the system then 
> optimized and exactly what does that optimization accomplish?
> 
> I understand if you don't want to take the time to explain all this but I'm 
> just curious - is there a useful architecture out there that I'm missing?
> 
> Can the PV and battery resources be combined into one system? - (perhaps by 
> selling the AGMs and Radian and buying more lithium and Sol-Arks?)
> 
> Seems like control and fine tuning and troubleshooting ongoing would be a 
> hassle with such complexity - but then again we sometimes work with what we 
> got!
> 
> As Nick said - they are lucky to have you!  Question is how to best serve 
> that design!
> 
> Best,
> 
> Jeff
>> Vince McClellan <mailto:[email protected]>  January 20, 2022 at 
>> 10:32 AM
>> Thanks again for your input. I'll check the Blue Ion battery voltage the 
>> next time on site with and without the Radian AC coupled. I'm also going to 
>> check in with Sol-Ark and see if the inverters respond to high battery  
>> voltage when they are in closed loop with the BMS on the battery. I've 
>> always assumed that the Sol-Ark's software just responds to the SOC from the 
>> BMS. 
>> That would be a possible connection between the freq-watt function on the 
>> Sol-Ark and DC power from the solar array. I was really scratching my head 
>> on where the possible connection could be between incoming DC power and the 
>> freq-watt function on the Sol-Arks. 
>> 
>> Vince McClellan
>> Energy Design
>> NABCEP PV Installation Professional
>> p. (541) 485-8122 <tel:%28541%29%20485-8122>  f. (541) 338-8202 
>> <tel:%28541%29%20338-8202>
>> 
>> If you have received this email and are not the intended recipient please 
>> delete this email. Copying, or using any part, content, or attachment of 
>> this email is strictly prohibited. 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> Pieter Huebner <mailto:[email protected]>  January 20, 2022 at 
>> 6:41 AM
>> Vince, Although you have an AC bussed connection, the issue may not be the 
>> opposite as ours. In Our case the battery buss voltage goes high when the 
>> solar array is enabled. If you are also experiencing DC buss excursions you 
>> can trigger frequency shifting. If you haven't already done so, I suggest 
>> that you closely monitor the battery voltage when the solar array is 
>> charging both with and without the Radian AC bussing connected.
>> Pieter
>>  
>> <image.png>
>>  
>> From: RE-wrenches <[email protected]> 
>> <mailto:[email protected]> On Behalf Of Vince 
>> McClellan
>> Sent: Wednesday, January 19, 2022 11:16 PM
>> To: RE-wrenches <[email protected]> 
>> <mailto:[email protected]>
>> Subject: Re: [RE-wrenches] Sol-Ark AC Coupling Issues
>>  
>> Thanks Pieter
>> We seem to have the opposite problem from what you are experiencing. Our 
>> freq-watt regulation of the Radian inverter by the Sol-Ark inverters seems 
>> to be actuated by the DC power from the solar array that is DC connected to 
>> the Sol-Ark inverters. It is supposed to be actuated by the SOC of the Blue 
>> Ion batteries, but that is inconsistent at best. We can turn the DC power 
>> from the solar array on on the master inverter, but when we try using the 
>> MPPT channels on the two other inverters it briefly actuates the freq-watt 
>> function of the Sol-Ark disconnecting the Radian inverter. 
>> 
>> Vince McClellan
>> Energy Design
>> NABCEP PV Installation Professional
>> p. (541) 485-8122 <tel:%28541%29%20485-8122>  f. (541) 338-8202 
>> <tel:%28541%29%20338-8202>
>> 
>> If you have received this email and are not the intended recipient please 
>> delete this email. Copying, or using any part, content, or attachment of 
>> this email is strictly prohibited. 
>>  
>>  
>> On Wed, Jan 19, 2022 at 8:20 PM Pieter Huebner 
>> <[email protected] <mailto:[email protected]>> wrote:
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> Vince McClellan <mailto:[email protected]>  January 19, 2022 at 
>> 9:15 PM
>> Thanks Pieter
>> We seem to have the opposite problem from what you are experiencing. Our 
>> freq-watt regulation of the Radian inverter by the Sol-Ark inverters seems 
>> to be actuated by the DC power from the solar array that is DC connected to 
>> the Sol-Ark inverters. It is supposed to be actuated by the SOC of the Blue 
>> Ion batteries, but that is inconsistent at best. We can turn the DC power 
>> from the solar array on on the master inverter, but when we try using the 
>> MPPT channels on the two other inverters it briefly actuates the freq-watt 
>> function of the Sol-Ark disconnecting the Radian inverter. 
>> 
>> Vince McClellan
>> Energy Design
>> NABCEP PV Installation Professional
>> p. (541) 485-8122 <tel:%28541%29%20485-8122>  f. (541) 338-8202 
>> <tel:%28541%29%20338-8202>
>> 
>> If you have received this email and are not the intended recipient please 
>> delete this email. Copying, or using any part, content, or attachment of 
>> this email is strictly prohibited. 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> Pieter Huebner <mailto:[email protected]>  January 19, 2022 at 
>> 8:20 PM
>> Vince, For what it is worth:
>> We have also been working on similar issues when using multiple Solark 
>> inverters connected in parallel. The issue has been that parallel Solark 
>> inverters don't seem to be able to properly regulate the battery charge 
>> voltage. Although Solark technical support has been outstanding, and with 
>> their help we have diminished the severity but not solved the issue.  For 
>> the sites that we currently have deployed for the interim we had to resort 
>> to turning down the charge voltage set points in order to protect the 
>> Lithium batteries. and avoid BMS shutdowns. We have a client with an 
>> existing outback system and were planning to expand the existing system 
>> using AC bussed Solark 12K inverters with additional battery and solar 
>> capacity (the site is 100% off grid, and has evolved into a micro grid), but 
>> are now going a different direction. Although we have not yet attempted an 
>> AC bussed Solark system, I suspect that the issues you are having are 
>> related to the battery voltage regulation problem we have experienced.
>> Pieter
>> <image.png>
>>  
>>  
>> From: RE-wrenches <[email protected]> 
>> <mailto:[email protected]> On Behalf Of Vince 
>> McClellan
>> Sent: Wednesday, January 19, 2022 5:16 PM
>> To: RE-wrenches <[email protected]> 
>> <mailto:[email protected]>
>> Subject: [RE-wrenches] Sol-Ark AC Coupling Issues
>>  
>> Is anyone on the list familiar with AC coupling Sol-Ark inverters?
>>  
>> We haven't been able to AC couple an existing Outback Radian system to a new 
>> system that we built with 3, Sol-Ark 12K inverters and 3, Blue Ion 
>> batteries. Each time we have tested the system the Sol-Ark inverters accept 
>> the power from the Radian inverter until we turn on the DC power from the 
>> new solar array to the Sol-Ark inverters. As soon as there is significant DC 
>> power coming from the solar array the Sol-Ark inverters freq-watt turns on 
>> for a brief second and disconnects the Radian inverter even when the Blue 
>> Ion batteries are below the programmed state of charge threshold. If we 
>> don't turn on the DC power from the new solar array the Radian will connect 
>> and stay connected. 
>>  
>> We have been working with Sol-Ark for several months now to get this system 
>> to accept the incoming power from the Radian without freq-watt kicking in on 
>> the Sol-Ark inverters and disconnecting the Radian inverter. Sol-Ark has 
>> sent two software revisions to the Sol-Ark inverters and we are still 
>> experiencing the same problem. 
>>  
>> Can anyone think of what we might be missing and where to direct our 
>> troubleshooting efforts next? 
>>  
>> Thanks, 
>> 
>> Vince McClellan
>> Energy Design
>> NABCEP PV Installation Professional
>> p. (541) 485-8122 <tel:%28541%29%20485-8122>  f. (541) 338-8202 
>> <tel:%28541%29%20338-8202>
>> 
>> If you have received this email and are not the intended recipient please 
>> delete this email. Copying, or using any part, content, or attachment of 
>> this email is strictly prohibited. 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> Vince McClellan <mailto:[email protected]>  January 19, 2022 at 
>> 3:15 PM
>> Is anyone on the list familiar with AC coupling Sol-Ark inverters?
>>  
>> We haven't been able to AC couple an existing Outback Radian system to a new 
>> system that we built with 3, Sol-Ark 12K inverters and 3, Blue Ion 
>> batteries. Each time we have tested the system the Sol-Ark inverters accept 
>> the power from the Radian inverter until we turn on the DC power from the 
>> new solar array to the Sol-Ark inverters. As soon as there is significant DC 
>> power coming from the solar array the Sol-Ark inverters freq-watt turns on 
>> for a brief second and disconnects the Radian inverter even when the Blue 
>> Ion batteries are below the programmed state of charge threshold. If we 
>> don't turn on the DC power from the new solar array the Radian will connect 
>> and stay connected. 
>> 
>> We have been working with Sol-Ark for several months now to get this system 
>> to accept the incoming power from the Radian without freq-watt kicking in on 
>> the Sol-Ark inverters and disconnecting the Radian inverter. Sol-Ark has 
>> sent two software revisions to the Sol-Ark inverters and we are still 
>> experiencing the same problem. 
>> 
>> Can anyone think of what we might be missing and where to direct our 
>> troubleshooting efforts next? 
>> 
>> Thanks, 
>> 
>> Vince McClellan
>> Energy Design
>> NABCEP PV Installation Professional
>> p. (541) 485-8122 <tel:%28541%29%20485-8122>  f. (541) 338-8202 
>> <tel:%28541%29%20338-8202>
>> 
>> If you have received this email and are not the intended recipient please 
>> delete this email. Copying, or using any part, content, or attachment of 
>> this email is strictly prohibited. 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> Tump 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>[email protected]
>        www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to