Can anyone explain why changing to Support mode on the generator input
boosts battery charging amps?

The Radian manual explanation for Support mode gives no clue about this
"fix". It only states that Support mode will allow batteries to provide
extra power to loads if demand exceeds max. gen programmed input amps.
I also have an offgrid Radian seeming to undercharge from a genny, and I
just changed its input mode to Support to see what happens.

On Fri, Oct 27, 2023 at 9:28 AM Amos Post via RE-wrenches <
[email protected]> wrote:

> Hi all,
>
> Changing the Gen Input mode to Support did the trick!  Thanks for the
> advice!
>
>
>        Amos Post
>    Integrity Energy
>   W 802.763.7023
>    C 802.291.2188
>     ienergyVT.com <http://www.ienergyvt.com>
>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>
> On Oct 26, 2023, at 9:16 AM, Dana Orzel via RE-wrenches <
> [email protected]> wrote:
>
> This may be far fetched but I have encountered good voltage & low amperage
> = no amperage from solar arrays that baffled me on T/S on others systems &
> ultimately:
> We had voltage & low output amperage to no amperage.
> Turns out there was a junction box that had been forgotten about in the
> crawl space with never tightened split bolts that were crispy black from
> arcing.
> There was enough contact for voltage readings & not enough for any amps to
> flow.
> Double check all connections?
>
> ___________________________________________________
> Dana Orzel  c- 2087217003   e – [email protected]
>
> <Mail Attachment.eml>_______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **[email protected] <[email protected]>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 32st Anniversary 1991-2023!!*

dba Vermont Solar Engineering

802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to