What I don’t understand is that the inverter was limiting amps while the 
generator was not.  
If the generator wasn’t able to produce the power, then it would have had the 
usual issues which causes the inverter to drop it and then reconnect. 
But that wasn’t happening so it appears the generator is doing fine. 

Its 3% per 1000, and the variables of density altitude are:  temperature, 
humidity, air pressure, elevation.  

I don’t understand why the generator support would allow for higher amps as 
well?

jay 

> On Oct 27, 2023, at 11:40 AM, Darryl Thayer via RE-wrenches 
> <[email protected]> wrote:
> 
> You have had many good suggestions but note you are on border line power, at 
> 2200 teet your power is down 10% note gen's are 80% of name plate, and you 
> are asking for 7.2 kW from a Genny that with atmospheric correction is 7.2 kW
> 
> On Fri, Oct 27, 2023, 8:27 AM Amos Post via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
> Hi all,
> 
> Changing the Gen Input mode to Support did the trick!  Thanks for the advice! 
> 
> 
>        Amos Post
>    Integrity Energy
>   W 802.763.7023
>    C 802.291.2188
>     ienergyVT.com <http://www.ienergyvt.com/>
>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
> 
>> On Oct 26, 2023, at 9:16 AM, Dana Orzel via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>> This may be far fetched but I have encountered good voltage & low amperage = 
>> no amperage from solar arrays that baffled me on T/S on others systems & 
>> ultimately: 
>> We had voltage & low output amperage to no amperage.
>> Turns out there was a junction box that had been forgotten about in the 
>> crawl space with never tightened split bolts that were crispy black from 
>> arcing.
>> There was enough contact for voltage readings & not enough for any amps to 
>> flow.
>> Double check all connections?
>>  
>> ___________________________________________________
>> Dana Orzel  c- 2087217003   e – [email protected] 
>> <mailto:[email protected]>
>>  
>> <Mail Attachment.eml>_______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to