> On May 14, 2025, at 10:57 AM, Chris Daum via RE-wrenches 
> <[email protected]> wrote:
> 
> Just as an aside, is anyone else having major noise problems with the EG4 
> inverters?  We’ve only sold one and its output is – seriously --  90 
> decibels.  My customer is rather deaf but his wife is not and it’s driving 
> her/them nuts.  I am rather reluctant to sell another unless they have a 
> separate power shed or the like.  
>  
> Chris Daum
> Oasis Montana Inc. 
>  
> From: RE-wrenches <[email protected] 
> <mailto:[email protected]>> On Behalf Of Maverick 
> Brown via RE-wrenches
> Sent: Wednesday, May 14, 2025 10:18 AM
> To: RE-wrenches <[email protected] 
> <mailto:[email protected]>>
> Cc: Maverick Brown <[email protected] 
> <mailto:[email protected]>>
> Subject: Re: [RE-wrenches] Midnite AIO Generator Functionality
>  
> In the case of extra redundancy, I have installed the EG4 Chargeverter and a 
> 30A L14-30 Inlet and made the customer a suitable length L14-30 Extension 
> Cord that they can use with their manual start secondary / tertiary portable 
> generator just in case the primary generator has failed to start. The 
> Chargeverter is quite small and can handle about 5kW of charge just in case… 
> The charge voltage is programmable as is the current. It is inverter and 
> battery agnostic.
>  
> The Chargeverter used to be inexpensive compared to what it does. The last 
> time I checked it is over $700 and also always seems to be on backorder. 
> Still worth it. The Chargeverter has two wire start and can start based on 
> voltage and SOC (if that is where the batteries are communicating / not that 
> useful for most cases).
>  
> If the Chargeverter is the primary generator AC to DC Charger, all AIO 
> inverters could benefit from DC Generator = Y / N setting. Reference : 
> Available setting on XW and Outback. 
>  
> For that matter, I am sure there are other suitable chargers that can be 
> added as an emergency spare. Ten years ago or more, I added an IOTA charger 
> to 24V FX inverter so the customer could use their Honda 2000 to charge the 
> battery without the warbling electricity going into the house because FX sans 
> PF correction… Remember those fun days?
>  
> Grid
> > Inverter / Battery / Solar
> >> Generator
> >>> Generator
> >>>> Candles
>  
>  
> <image001.jpg>
>  
>  
>  
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
>  • Solar Commander Remote Power
>  • SunFlow Systems Cathodic Protection 
> [email protected] <mailto:[email protected]>
> 512-460-9825
> 
> 
>> On May 14, 2025, at 8:55 AM, Jason Szumlanski via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>>  
>> That is the idea, but the generator startup is not guaranteed (i.e.out of 
>> fuel, battery dead, etc). It's not a failsafe solution. 
>>  
>> The AIO really needs a dedicated GEN input that is not controlled with a NO 
>> relay. Or let us use the Grid input for the generator. The generator input 
>> logic is severely flawed. If there is an AC source, it should be able to 
>> charge the battery without user intervention. 
>>  
>> 
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>  
>> On Mon, May 12, 2025, 5:25 PM Dave Tedeyan via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>>> Jason, 
>>> Cant you just make the AGS turn on the generator before the inverter gets 
>>> to the LBCO? Maybe this is more difficult if you do not have closed loop 
>>> comms and the SOC drifts. I am just working through my first Midnite AIO 
>>> setup now, so I cannot speak to the nuances of how it will work with that 
>>> yet.
>>> Cheers,
>>> Dave
>>>  
>>> On Mon, May 12, 2025 at 4:01 PM Ray Walters via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>>> That has not been my experience.  I have had to manually reboot Solark 
>>>> systems numerous time off grid.  If there is snow on the array or 
>>>> otherwise low PV output for a few days, the no load draw of the BMS then 
>>>> takes the battery voltage low enough to shut the battery off.   This would 
>>>> be a different situation with a knowledgeable owner onsite full time, but 
>>>> for vacation properties, it will go into complete shut down, not coming 
>>>> back.
>>>> Which gets into the manual and tech support for Solark:  its really not 
>>>> clear what the different settings do, and how they interact.  I'm sure 
>>>> there are engineers that know, but they aren't at Tech support. At least 
>>>> you can change the programming on the touch screen, and you don't have to 
>>>> get a quirky app up off grid to do basic changes.  
>>>> BTW, what happens when the developers quit keeping the App updated, 10 
>>>> years from now, and you can't access the programming?  Planned 
>>>> Obsolescence?  That 33 yr old Trace Inverter is still doing its job.....
>>>> Ray Walters
>>>> Remote Solar
>>>>  
>>>>  
>>>> On 5/12/2025 11:33 AM, MDElectricSolar via RE-wrenches wrote:
>>>>> We have been using the Solark inverter for GTBB and off grid clients. In 
>>>>> the case of low battery cut out the solar does stay alive in the 
>>>>> background and will recharge the batteries when the sun comes out the 
>>>>> next day and turn itself back on and provide AC power output. 
>>>>>  
>>>>> Michael D Nelson
>>>>> MD Electric & Solar, Inc.
>>>>> 707-684-0064 mobile
>>>>> 707-884-1862 office
>>>>> www.mdelectricsolar.com <http://www.mdelectricsolar.com/>
>>>>> www.facebook.com/mdelectricandsolar 
>>>>> <http://www.facebook.com/mdelectricandsolar>
>>>>>  
>>>>> 
>>>>> 
>>>>>> On May 12, 2025, at 10:13 AM, Ray Walters via RE-wrenches 
>>>>>> <[email protected]> 
>>>>>> <mailto:[email protected]> wrote:
>>>>>> 
>>>>>> 
>>>>>> So the bypass switch gets the house power on, and I too always recommend 
>>>>>> a hard bypass switch. However, you still need a 48 v power supply to get 
>>>>>> the battery system back up, and that's becoming a serious pain in my 
>>>>>> aging backside.  Until AIOs with Li+ batteries, lead acid would have 
>>>>>> enough voltage to get the charge controller to come back on, and 
>>>>>> eventually the customer could get the inverter back on too.  No special 
>>>>>> trip out. 
>>>>>> We need an independent circuit that would sense array voltage, and wake 
>>>>>> up the battery, so it could take a charge: a backup battery for the 
>>>>>> offgrid battery.  Without that, AIOs and Li+ batteries are not self 
>>>>>> healing like Lead Acid.  We are going backwards fast, but with an 
>>>>>> amazing amount of new Chinese technology driving the jalopy in reverse.  
>>>>>> (Danger Will Robinson)
>>>>>> Ray Walters
>>>>>> Remote Solar
>>>>>> On 5/12/2025 10:54 AM, Jason Szumlanski via RE-wrenches wrote:
>>>>>>> We always recommend a transfer switch to bypass the inverter and send 
>>>>>>> generator power to the loads. Most clients take us up on it. For 
>>>>>>> retrofits, sometimes there can be space limitations, however. 
>>>>>>>  
>>>>>>> As for the function of the AIO, there is no integrated mechanical 
>>>>>>> bypass, and since there is an internal relay controlling the generator 
>>>>>>> input (or smart load output on that breaker), I think the default 
>>>>>>> function is for the relay to open when the inverter turns off. AC 
>>>>>>> voltage on the load side of the breaker does not close the relay and 
>>>>>>> turn the inverter back on automatically.
>>>>>>> 
>>>>>>> 
>>>>>>> Jason Szumlanski 
>>>>>>> Principal Solar Designer | Florida Solar Design Group
>>>>>>> NABCEP Certified Solar Professional (PVIP)
>>>>>>> Florida State Certified Solar Contractor CVC56956
>>>>>>> Florida Certified Electrical Contractor EC13013208
>>>>>>>  
>>>>>>>  
>>>>>>> On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via 
>>>>>>> RE-wrenches <[email protected] 
>>>>>>> <mailto:[email protected]>> wrote:
>>>>>>>> All sounds wrong to me. Call Midnite.  
>>>>>>>>  
>>>>>>>> Typically there is a AC bypass mechanical switch that allows the gen 
>>>>>>>> to bypass the inverter and power loads.
>>>>>>>>  
>>>>>>>>  
>>>>>>>> Dave Angelini Offgrid Solar
>>>>>>>> "we go where powerlines don't"
>>>>>>>>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/  
>>>>>>>> <http://members.sti.net/offgridsolar/>
>>>>>>>> e-mail  [email protected] <mailto:[email protected]>
>>>>>>>> text 209 813 0060
>>>>>>>>  
>>>>>>>> On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:
>>>>>>>>> Maybe I'm missing something, but it seems like there is a flaw in the 
>>>>>>>>> logic for how generator integration works with this product. Unlike 
>>>>>>>>> some of the other AIOs, you can't put the generator on the Grid input 
>>>>>>>>> in an off-grid scenario. You have to use the Generator smart load 
>>>>>>>>> breaker, which isn't a dedicated generator input, but a programmable 
>>>>>>>>> circuit. This is problematic because it seemingly has a normally open 
>>>>>>>>> internal relay that closes only when the inverter is ON. At least, 
>>>>>>>>> that's how it seems to work in my limited experience.
>>>>>>>>>  
>>>>>>>>> Why is this a problem? If the battery capacity drops below the low 
>>>>>>>>> voltage cutoff, the inverter turns off. You have to turn the inverter 
>>>>>>>>> ON for the generator relay to close so you can charge the battery, 
>>>>>>>>> but since the battery is too low, the inverter won't turn on. You 
>>>>>>>>> would have to reprogram the inverter to drop the cutoff voltage/SOC 
>>>>>>>>> below the current battery state. For people who do not want to use 
>>>>>>>>> AGS, or if AGS fails to start the generator for any reason, getting 
>>>>>>>>> the generator to charge the battery manually is no easy task.
>>>>>>>>>  
>>>>>>>>> Moreover, turning the generator on manually when the inverter is in 
>>>>>>>>> an OFF state will not pass power to the loads, and will not turn the 
>>>>>>>>> inverter ON automatically. You have to get the inverter turned ON 
>>>>>>>>> somehow so that the generator power can pass through to the loads. 
>>>>>>>>> And since the startup sequence for this inverter is very quirky, 
>>>>>>>>> non-intuitive, and unreliable, that makes the problem even worse. I'm 
>>>>>>>>> not sure if you can even turn the inverter ON when there is generator 
>>>>>>>>> input and the battery is too low. I don't think you can because the 
>>>>>>>>> relay is open and the inverter doesn't even see generator voltage 
>>>>>>>>> when it is in an OFF state.
>>>>>>>>> This seems like a serious oversight and a reason to go with one of 
>>>>>>>>> the other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV 
>>>>>>>>> will both immediately power loads and start charging when the 
>>>>>>>>> generator is on, regardless of whether the generator is connected to 
>>>>>>>>> the Grid or Generator input. Any AC input immediately passes through 
>>>>>>>>> to the loads. This is because those inverters stay "on" when a low 
>>>>>>>>> battery condition is met, and they simply stop using the battery to 
>>>>>>>>> invert power if the battery conditions do not allow it, based on the 
>>>>>>>>> settings. 
>>>>>>>>>  
>>>>>>>>> The logic of the Midnite AIOs turning "off" when battery cutoff is 
>>>>>>>>> met and opening the generator relay doesn't make sense to me. Am I 
>>>>>>>>> wrong about how this works?
>>>>>>>>>  
>>>>>>>>> Jason Szumlanski 
>>>>>>>>> Principal Solar Designer
>>>>>>>>> Florida Solar Design Group
>>>>>>>>>  
>>>>>>>>>  
>>>>>>>>>  
>>>>>>>>> _______________________________________________
>>>>>>>>> List sponsored by Redwood Alliance
>>>>>>>>> 
>>>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>>>> <http://re-wrenches.org/>
>>>>>>>>> 
>>>>>>>>> List Address: [email protected] 
>>>>>>>>> <mailto:[email protected]>
>>>>>>>>> 
>>>>>>>>> Change listserver email address & settings:
>>>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>>> 
>>>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>>>> the other:
>>>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>>> 
>>>>>>>>> List rules & etiquette:
>>>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>>>> 
>>>>>>>>> Check out or update participant bios:
>>>>>>>>> http://www.members.re-wrenches.org 
>>>>>>>>> <http://www.members.re-wrenches.org/>
>>>>>>>> _______________________________________________
>>>>>>>> List sponsored by Redwood Alliance
>>>>>>>> 
>>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>>> <http://re-wrenches.org/>
>>>>>>>> 
>>>>>>>> List Address: [email protected] 
>>>>>>>> <mailto:[email protected]>
>>>>>>>> 
>>>>>>>> Change listserver email address & settings:
>>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>> 
>>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>>> the other:
>>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>> 
>>>>>>>> List rules & etiquette:
>>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>>> 
>>>>>>>> Check out or update participant bios:
>>>>>>>> http://www.members.re-wrenches.org 
>>>>>>>> <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>>> 
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>>  
>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>> <http://re-wrenches.org/>
>>>>>>>  
>>>>>>> List Address: [email protected] 
>>>>>>> <mailto:[email protected]>
>>>>>>>  
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>  
>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>> the other:
>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>  
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>>  
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>>  
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>  
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>>  
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>>  
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>  
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>  
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>  
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>  
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to