I truly wish inverter and battery manufacturers would come up with a
standard. Like an OBD II thing. They could have standard registers and then
manufacturer specific codes.

Can't we all just get along? 🥺


Jason


On Wed, Aug 26, 2026, 6:05 PM Bill P. Battagin <[email protected]> wrote:

> Zeke and Jason,
>
>             And so with all that said would a Midnite *Power* MNPF16
> closed loop with a (any) Midnite *Solar* inverter (EG: Little Rosie).
> Zeke, you know where I'm going with this but seemed like a good question
> for all wrenches.  Since the Midnite divorce, are the now two  "Midnite"
> parties programming their respective brains (BMS/MNGP2/Whiz bang Jr.) to
> play nicely together?  Oh yeah and now MidnitePower is Sol-Max.
>
> Bill
>
> Feather River Solar Electric
> 5575 Genesee Rd
> <https://www.google.com/maps/search/5575+Genesee+Rd?entry=gmail&source=g>.(billing,
> USPS, UPS, FedEx)
> 4291 Nelson St
> <https://www.google.com/maps/search/4291+Nelson+St?entry=gmail&source=g>.
> (freight delivery)
> Taylorsville, CA  95983
> 530.284.7849, 530.258.1641 cell
> CA C10 Lic# 874049
> Solar Powered since 1982
>
> ------------------------------
> *From: *"Jason Szumlanski" <[email protected]>
> *To: *"List for professional installers of home-scale renewable energy
> systems" <[email protected]>
> *Sent: *Wednesday, August 26, 2026 1:23:41 PM
> *Subject: *Re: [Re-wrenches] Wacky FNDC behavior
>
> Zeke's last paragraph says it all. The AIOs from Sol-Max and EG4 are
> pretty good at reporting an accurate SOC, regardless of charge and
> discharge rate, as long as the manufacturer-matched batteries reach 100%
> reasonably often. Even when the batteries sit in the mid-range for
> several days, the SOC seems to remain pretty accurate. When they hover near
> the low end for extended periods is where they will drop to zero without
> warning.
>
> I find it hard to trust external shunts for Lead Acid over time for the
> reasons Zeke mentioned, and for the reasons I mentioned previously
> regarding aH capacity depending on rate of charge/discharge. And for LFP,
> it generally makes more sense to rely on the battery BMS stated SOC, even
> though that can't be completely accurate, either. It's pretty wild to watch
> the discrepancy between a large EG4 rack-mounted bank versus what a Sol-Ark
> 15K reports in open loop. I have watched this pretty closely at a few
> sites, and the Sol-Ark seems to be all over the map.
>
> I have pretty limited experience with the Victron shunts, so I can't speak
> to those. I am getting ready to do a small Multiplus installation where SOC
> is going to be important due to tight margins between solar production and
> load, so I will be interested to see how well it does.
>
> Jason
>
>
>
> On Wed, Aug 26, 2026 at 4:09 PM Zeke Yewdall <[email protected]>
> wrote:
>
>> I did not expect this to be such a controversial topic... but since it
>> is... here goes :P
>>
>> I consider having an AH counting SOC meter absolutely vital on most LFP
>> projects -- at least on any older equipment.  Voltage is just way too flat
>> on LFP to make any reasonable decisions based on it, except below 25% SOC
>> maybe, and above 90% SOC.  But that entire range in between there is very
>> difficult to tell where you are based on voltage.  And most of the older
>> LFP had no display for SOC (or at best a couple segment bar graph), and no
>> way to do comms to them for many of them either.  So to allow the customer
>> to actually know what their batteries are doing, and make decisions on
>> operation, they need to know SOC -- especially at middle levels where
>> decisions can still be made (other than it's full, or it's empty, start the
>> generator asap).
>>
>> Even on lead acid batteries, I would almost always do an AH counting SOC
>> meter rather than relying on voltage, as it was just too complicated for
>> about 75% of customers to grasp voltage -- that's it's non-linear, 0 volts
>> is no 0% charged, and that it changes at the same SOC depending on whether
>> you are charging or discharging.
>>
>> I've used the FNDC, Victron Smartshunts, and Trimetrics on LFP
>> batteries.  And even a Schneider conext battery monitor thing once or
>> twice.  For the most part, I've been quite happy with how they've
>> functioned.
>>
>> Thats not to say that there aren't a number of issues with AH counting
>> SOC meters, whether on lead acid or lithium batteries, and there are some
>> cases where they just don't work.
>>
>> With lead acid, the biggest issue was usually declining battery capacity
>> over time lead to the SOC being unreasonably high compared to reality.  So
>> it worked great to begin with, but 4 or 5 years later, it would start
>> kicking the generator on (or shutting down) at much higher indicated SOC
>> than it used to.
>>
>> For lithium, SOC drift can definitely be a problem.  I do tell people
>> they need to get the SOC to 100% once every two weeks minimum, in the
>> winter, to prevent this -- 1% accuracy error per day doesn't sound bad...
>> till you go a full month without recalibrating....
>>
>> Many BMS's built into the batteries experience the same issues with SOC
>> drift too. Most internal BMS's are blind to currents less than 1 amp or so,
>> so people who are very good at conserving electricity, reducing their loads
>> to less than an amp per battery for large portions of the day or at night,
>> seem to have bigger issues with SOC drift than heavy users.
>>
>> The new heated batteries are a big problem with AH counting, and can
>> cause the SOC meter to be completely wrong and useless at times.  I have
>> not figured out a way around that yet (other than not using heated
>> batteries in cold climates... they have many other drawbacks IMO, compared
>> to a separate heating system that's not internal).
>>
>> SOC meters that reset to 100% if they lose power, rather than retaining
>> SOC, can also be a problem if you ever trigger the emergency protection on
>> the lithium battery.  Battery shuts off from low state of charge then SOC
>> meter resets to 100%, then customer is super confused.  The Victron shunts
>> are the only ones I've found that can be programmed to keep the same SOC
>> over a power outage.  Batteries that disconnect just the charging FET due
>> to cold temperatures, can also cause a unintended reset, by making it
>> appear the battery rises to absorb voltage with very low amperage while
>> charging, when really it's just the charge FET is off.
>>
>> For any new systems, I am coming around to using closed loop batteries of
>> the same manufacturer as the AIO inverter, and everything is just built
>> in... the BMS reports to the inverter, everything is based on the BMS
>> control, and the same monitor shows SOC along with everything else.  My
>> first attemps at closed loop control were disasters, and I stayed away from
>> that for several years, but recently I've been much happier with it and the
>> level of control it gives you.   So that's a different case, and eventually
>> that'll be all the systems out there.  But for now... there's a lot of
>> legacy systems still out there, and first gen lithium batteries on legacy
>> equipment -- no SOC display on batteries and no comms.  So, that's where I
>> still believe that AH counting SOC meters are critical for system
>> operation, as long as the customers know the potential trip-ups and don't
>> view the SOC meter as gospel.
>>
>> Zeke
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to