Interesting. I'm pretty sure Sol-Ark does current monitoring to calculate
SOC in open loop based on the aH capacity you enter on the battery screen.
I have quadrupled the capacity and watched the SOC decline at about 1/4 the
expected rate based on the load.

I imagine the Sol-Max AIO does the same. It has an aH field in the settings
that is only used for open loop (lead acid mode).

Even Solar Assistant takes a stab at SoC using programmed aH capacity and
load and charge reported by the inverter.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208



On Wed, Aug 26, 2026, 6:11 PM Zeke Yewdall <[email protected]> wrote:

> Per Jason's comment on Sol-Ark in open loop.
>
> From what I know, none of the AIO's ( at least Sol-ark, EG4 and Sol-max)
> do AH counting in-out to determine SOC when operated in open loop.  Even
> though, as (usually) the only thing in the system you'd think they could.
> Instead they use some form of voltage based algorithm, which in my
> experience, often leaves much to be desired.  In my SolArk/Fortress system,
> I had to turn SOC completely off and only do stuff based on voltage,
> unfortunately.
>
>
>>  It's pretty wild to watch
>> the discrepancy between a large EG4 rack-mounted bank versus what a
>> Sol-Ark
>> 15K reports in open loop. I have watched this pretty closely at a few
>> sites, and the Sol-Ark seems to be all over the map.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to