To clarify a conversation I had with a reliable source.
Does the FNDC take charge of the parameters for charging when used with all
OB gear and a Hub?
Of course we should have no BTS plugged in with Lithiums.
I was told yesterday that a battery bank had failed due to overcharging by
the FNDC and was not going to be covered under warranty. Not my system.
Cold temps sent the absorb voltage 2 Volts higher.

Thanks !

Jeremy Rodriguez
All Solar Inc.
Penrose CO
719-276-4954
Established 1998

On Wed, Aug 26, 2026 at 2:09 PM Zeke Yewdall <[email protected]>
wrote:

> I did not expect this to be such a controversial topic... but since it
> is... here goes :P
>
> I consider having an AH counting SOC meter absolutely vital on most LFP
> projects -- at least on any older equipment.  Voltage is just way too flat
> on LFP to make any reasonable decisions based on it, except below 25% SOC
> maybe, and above 90% SOC.  But that entire range in between there is very
> difficult to tell where you are based on voltage.  And most of the older
> LFP had no display for SOC (or at best a couple segment bar graph), and no
> way to do comms to them for many of them either.  So to allow the customer
> to actually know what their batteries are doing, and make decisions on
> operation, they need to know SOC -- especially at middle levels where
> decisions can still be made (other than it's full, or it's empty, start the
> generator asap).
>
> Even on lead acid batteries, I would almost always do an AH counting SOC
> meter rather than relying on voltage, as it was just too complicated for
> about 75% of customers to grasp voltage -- that's it's non-linear, 0 volts
> is no 0% charged, and that it changes at the same SOC depending on whether
> you are charging or discharging.
>
> I've used the FNDC, Victron Smartshunts, and Trimetrics on LFP batteries.
> And even a Schneider conext battery monitor thing once or twice.  For the
> most part, I've been quite happy with how they've functioned.
>
> Thats not to say that there aren't a number of issues with AH counting SOC
> meters, whether on lead acid or lithium batteries, and there are some cases
> where they just don't work.
>
> With lead acid, the biggest issue was usually declining battery capacity
> over time lead to the SOC being unreasonably high compared to reality.  So
> it worked great to begin with, but 4 or 5 years later, it would start
> kicking the generator on (or shutting down) at much higher indicated SOC
> than it used to.
>
> For lithium, SOC drift can definitely be a problem.  I do tell people they
> need to get the SOC to 100% once every two weeks minimum, in the winter, to
> prevent this -- 1% accuracy error per day doesn't sound bad... till you go
> a full month without recalibrating....
>
> Many BMS's built into the batteries experience the same issues with SOC
> drift too. Most internal BMS's are blind to currents less than 1 amp or so,
> so people who are very good at conserving electricity, reducing their loads
> to less than an amp per battery for large portions of the day or at night,
> seem to have bigger issues with SOC drift than heavy users.
>
> The new heated batteries are a big problem with AH counting, and can cause
> the SOC meter to be completely wrong and useless at times.  I have not
> figured out a way around that yet (other than not using heated batteries in
> cold climates... they have many other drawbacks IMO, compared to a separate
> heating system that's not internal).
>
> SOC meters that reset to 100% if they lose power, rather than retaining
> SOC, can also be a problem if you ever trigger the emergency protection on
> the lithium battery.  Battery shuts off from low state of charge then SOC
> meter resets to 100%, then customer is super confused.  The Victron shunts
> are the only ones I've found that can be programmed to keep the same SOC
> over a power outage.  Batteries that disconnect just the charging FET due
> to cold temperatures, can also cause a unintended reset, by making it
> appear the battery rises to absorb voltage with very low amperage while
> charging, when really it's just the charge FET is off.
>
> For any new systems, I am coming around to using closed loop batteries of
> the same manufacturer as the AIO inverter, and everything is just built
> in... the BMS reports to the inverter, everything is based on the BMS
> control, and the same monitor shows SOC along with everything else.  My
> first attemps at closed loop control were disasters, and I stayed away from
> that for several years, but recently I've been much happier with it and the
> level of control it gives you.   So that's a different case, and eventually
> that'll be all the systems out there.  But for now... there's a lot of
> legacy systems still out there, and first gen lithium batteries on legacy
> equipment -- no SOC display on batteries and no comms.  So, that's where I
> still believe that AH counting SOC meters are critical for system
> operation, as long as the customers know the potential trip-ups and don't
> view the SOC meter as gospel.
>
> Zeke
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to