Re: [RE-wrenches] Load testing Lithium battery bank

2015-04-02 Thread Chris Schaefer
 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Jerry Shafer
Sent: Wednesday, 18 March, 2015 21:57
To: RE-wrenches
Subject: Re: [RE-wrenches] Load testing Lithium battery bank

We use elite batteries with BMS no problems, the BMS sensor does seem to run 
warm we are now setting up 4, 100 Ah banks with no problems so far.
Jerry

Not at all. The EMS boards are well built and are protected under a cover with 
the terminals. I have not had any failures of the EMS boards or any failure to 
communicate with them.



Larry 

 

 

On Mar 18, 2015 1:52 PM, Bruce Erickson br...@mendocinosolar.com wrote:

If a communication failure with a single cell (not even an actual fault) can 
cause total battery shutdown, does that lead to a lot of nuisance tripping?

 

Bruce Erickson

Mendocino Solar Service

PO Box 1252

Mendocino, CA 95460

707-937-1701

707-937-1741 fax

br...@mendocinosolar.com

 

Celebrating 20 Years in Solar! 1994-2014

 

 

 

 

On Mar 18, 2015, at 8:57 AM, Larry wrote:





Hi Jarmo,

I agree and recognize your urgency in making us aware of the proper use and 
charging of Li-ion batteries as well as the dangers of mistreating them. As an 
early adopter myself, I am very cautious in my approach even to the point of 
refusing to sell to some customers. Lithium battery technology is in a state of 
rapid evolution. 

Not wanting to harp on the GBS brand that I sell, but one of your points goes 
to prove the safety of their integrated approach. You said, ...all it takes is 
one poor connection or broken temp sensor on one cell. The GBS EMS system has 
cell level sensors for temperature (and other data) and each sensor board 
requires constant communication with the CPU. If the EMS fails to communicate 
any information with any cell, the CPU immediately shuts down both safety 
solenoids, disconnecting the battery. With the non integrated systems, failures 
that don't report information to the management system could lead to disaster.

Please keep offering us the knowledge you are gaining as I am a firm believer 
that Lithium technology is a large part of the inevitable replacement the aged 
lead battery.



Larry Crutcher
Starlight Solar Power Systems
 

On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:

Hi: 

I may sound like I'm a detractor against using Lion, but that's not it. 

What I want to bring to light is that, being as the technology is new, not all 
the issues are known and there are things to learn for all early adopters in 
the foreseeable future. 

From what I can gather the framework for the issues lies in that Lion 
technology is based on intercalation, that is, a reversible insertion and 
removal of Li molecules into compounds with microscopically layered 
structures.  This predicates that there must be no chemical reaction in the 
battery, but rather only the shelving of the highly reactive Li ions.  If 
there are any chemical reactions taking place, then in the least the battery 
performance is compromised and in the most there is a thermal event or worse 

There are some very robust Lion battery packs, a favorite of mine being from a 
local company from Vancouver, (well Richmond, which is a suburb of Vancouver).  
It's a small company, but they have designed, developed, built and successfully 
approved their 6 kWh Lion pack for use in large car ferries in Scandinavia.  
The ferries have stacks of these packs in the 100's, in the MWh size.  It can 
be done. 

What I'm advocating is that its best to work with companies that have the time, 
interest and resources to work through the wrinkles, and if not, then carefully 
put in reliable and precise BMS circuitry which includes things like fail safe 
circuits for single point failures of critical sensing circuits, the foremost 
of which is cell temperature.  When you're pushing large currents, all it takes 
is one poor connection or broken temp sensor on one cell.. 

Here's a link to the Lion battery pack manufacturer, Corvus, 

 http://corvus-energy.com/ http://corvus-energy.com/ 

I know they do a good job, but they're not cheap, for now... 

JARMO 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
Sales Application Engineer 
Phone: +604-422-2528 tel:%2B604-422-2528   |   Tech Support: 800-670-0707  |  
 Mobile: +604-505-0291 tel:%2B604-505-0291  
Email:  mailto:jarmo.venalai...@schneider-electric.com 
jarmo.venalai...@schneider-electric.com  |   Site: http://www.xantrex.com/  
www.Xantrex.com  |   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 


 http://www.xantrexrebate.com/ Mail Attachment.gif 


 http://www.xantrex.com/ Mail Attachment.gif 

 https://www.facebook.com/Xantrex Mail Attachment.gif 

 https://twitter.com/Xantrex Mail Attachment.gif 

 https://twitter.com/Xantrex Mail Attachment.gif








___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re

Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Larry

Hi Jarmo,

I agree and recognize your urgency in making us aware of the proper use 
and charging of Li-ion batteries as well as the dangers of mistreating 
them. As an early adopter myself, I am very cautious in my approach even 
to the point of refusing to sell to some customers. Lithium battery 
technology is in a state of rapid evolution.


Not wanting to harp on the GBS brand that I sell, but one of your points 
goes to prove the safety of their integrated approach. You said, ...all 
it takes is one poor connection or broken temp sensor on one cell. The 
GBS EMS system has cell level sensors for temperature (and other data) 
and each sensor board requires constant communication with the CPU. If 
the EMS fails to communicate any information with any cell, the CPU 
immediately shuts down both safety solenoids, disconnecting the battery. 
With the non integrated systems, failures that don't report information 
to the management system could lead to disaster.


Please keep offering us the knowledge you are gaining as I am a firm 
believer that Lithium technology is a large part of the inevitable 
replacement the aged lead battery.


Larry Crutcher
Starlight Solar Power Systems
 


On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:

Hi:

I may sound like I'm a detractor against using Lion, but that's not it.

What I want to bring to light is that, being as the technology is new, 
not all the issues are known and there are things to learn for all 
early adopters in the foreseeable future.


From what I can gather the framework for the issues lies in that Lion 
technology is based on intercalation, that is, a reversible insertion 
and removal of Li molecules into compounds with microscopically 
layered structures.  This predicates that there must be no chemical 
reaction in the battery, but rather only the shelving of the highly 
reactive Li ions.  If there are any chemical reactions taking place, 
then in the least the battery performance is compromised and in the 
most there is a thermal event or worse


There are some very robust Lion battery packs, a favorite of mine 
being from a local company from Vancouver, (well Richmond, which is a 
suburb of Vancouver).  It's a small company, but they have designed, 
developed, built and successfully approved their 6 kWh Lion pack for 
use in large car ferries in Scandinavia.  The ferries have stacks of 
these packs in the 100's, in the MWh size.  It can be done.


What I'm advocating is that its best to work with companies that have 
the time, interest and resources to work through the wrinkles, and if 
not, then carefully put in reliable and precise BMS circuitry which 
includes things like fail safe circuits for single point failures of 
critical sensing circuits, the foremost of which is cell temperature. 
 When you're pushing large currents, all it takes is one poor 
connection or broken temp sensor on one cell..


Here's a link to the Lion battery pack manufacturer, Corvus,

http://corvus-energy.com/

I know they do a good job, but they're not cheap, for now...

JARMO

*
Jarmo Venalainen*  | *Schneider Electric **|  Xantrex Brand*  | 
*CANADA*  | *Sales Application Engineer* *
Phone:* +604-422-2528  | *Tech Support:* 800-670-0707  | *Mobile:* 
+604-505-0291 *
Email:* _jarmo.venalainen@schneider-electric.com_ 
mailto:jarmo.venalai...@schneider-electric.com | 
*Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:* 3700 
Gilmore Way, Burnaby, BC V5G4M1

http://www.xantrexrebate.com/
http://www.xantrex.com/ 	https://www.facebook.com/Xantrex 
https://twitter.com/Xantrex 	https://twitter.com/Xantrex







___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Bruce Erickson
If a communication failure with a single cell (not even an actual fault) can 
cause total battery shutdown, does that lead to a lot of nuisance tripping?

Bruce Erickson
Mendocino Solar Service
PO Box 1252
Mendocino, CA 95460
707-937-1701
707-937-1741 fax
br...@mendocinosolar.com

Celebrating 20 Years in Solar! 1994-2014





On Mar 18, 2015, at 8:57 AM, Larry wrote:

 Hi Jarmo,
 
 I agree and recognize your urgency in making us aware of the proper use and 
 charging of Li-ion batteries as well as the dangers of mistreating them. As 
 an early adopter myself, I am very cautious in my approach even to the point 
 of refusing to sell to some customers. Lithium battery technology is in a 
 state of rapid evolution. 
 
 Not wanting to harp on the GBS brand that I sell, but one of your points goes 
 to prove the safety of their integrated approach. You said, ...all it takes 
 is one poor connection or broken temp sensor on one cell. The GBS EMS system 
 has cell level sensors for temperature (and other data) and each sensor board 
 requires constant communication with the CPU. If the EMS fails to communicate 
 any information with any cell, the CPU immediately shuts down both safety 
 solenoids, disconnecting the battery. With the non integrated systems, 
 failures that don't report information to the management system could lead to 
 disaster.
 
 Please keep offering us the knowledge you are gaining as I am a firm believer 
 that Lithium technology is a large part of the inevitable replacement the 
 aged lead battery.
 Larry Crutcher
 Starlight Solar Power Systems
  
 On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:
 Hi: 
 
 I may sound like I'm a detractor against using Lion, but that's not it. 
 
 What I want to bring to light is that, being as the technology is new, not 
 all the issues are known and there are things to learn for all early 
 adopters in the foreseeable future. 
 
 From what I can gather the framework for the issues lies in that Lion 
 technology is based on intercalation, that is, a reversible insertion and 
 removal of Li molecules into compounds with microscopically layered 
 structures.  This predicates that there must be no chemical reaction in the 
 battery, but rather only the shelving of the highly reactive Li ions.  If 
 there are any chemical reactions taking place, then in the least the battery 
 performance is compromised and in the most there is a thermal event or worse 
 
 There are some very robust Lion battery packs, a favorite of mine being from 
 a local company from Vancouver, (well Richmond, which is a suburb of 
 Vancouver).  It's a small company, but they have designed, developed, built 
 and successfully approved their 6 kWh Lion pack for use in large car ferries 
 in Scandinavia.  The ferries have stacks of these packs in the 100's, in the 
 MWh size.  It can be done. 
 
 What I'm advocating is that its best to work with companies that have the 
 time, interest and resources to work through the wrinkles, and if not, then 
 carefully put in reliable and precise BMS circuitry which includes things 
 like fail safe circuits for single point failures of critical sensing 
 circuits, the foremost of which is cell temperature.  When you're pushing 
 large currents, all it takes is one poor connection or broken temp sensor on 
 one cell.. 
 
 Here's a link to the Lion battery pack manufacturer, Corvus, 
 
 http://corvus-energy.com/ 
 
 I know they do a good job, but they're not cheap, for now... 
 
 JARMO 
 
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
 Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
 +604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  | 
   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
 Mail Attachment.gif
 Mail Attachment.gifMail Attachment.gif   
 Mail Attachment.gif   Mail Attachment.gif
 
 
 
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Larry
Not at all. The EMS boards are well built and are protected under a 
cover with the terminals. I have not had any failures of the EMS boards 
or any failure to communicate with them.


Larry

On 3/18/15 4:52 PM, Bruce Erickson wrote:
If a communication failure with a single cell (not even an actual 
fault) can cause total battery shutdown, does that lead to a lot of 
nuisance tripping?


*Bruce Erickson*
Mendocino Solar Service
PO Box 1252
Mendocino, CA 95460
707-937-1701
707-937-1741 fax
br...@mendocinosolar.com mailto:br...@mendocinosolar.com

/Celebrating 20 Years in Solar!/1994-2014







___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Jerry Shafer
We use elite batteries with BMS no problems, the BMS sensor does seem to
run warm we are now setting up 4, 100 Ah banks with no problems so far.
Jerry
On Mar 18, 2015 1:52 PM, Bruce Erickson br...@mendocinosolar.com wrote:

 If a communication failure with a single cell (not even an actual fault)
 can cause total battery shutdown, does that lead to a lot of nuisance
 tripping?

 *Bruce Erickson*
 Mendocino Solar Service
 PO Box 1252
 Mendocino, CA 95460
 707-937-1701
 707-937-1741 fax
 br...@mendocinosolar.com

 *Celebrating 20 Years in Solar!* 1994-2014





 On Mar 18, 2015, at 8:57 AM, Larry wrote:

  Hi Jarmo,

 I agree and recognize your urgency in making us aware of the proper use
 and charging of Li-ion batteries as well as the dangers of mistreating
 them. As an early adopter myself, I am very cautious in my approach even to
 the point of refusing to sell to some customers. Lithium battery technology
 is in a state of rapid evolution.

 Not wanting to harp on the GBS brand that I sell, but one of your points
 goes to prove the safety of their integrated approach. You said, ...all
 it takes is one poor connection or broken temp sensor on one cell. The
 GBS EMS system has cell level sensors for temperature (and other data) and
 each sensor board requires constant communication with the CPU. If the EMS
 fails to communicate any information with any cell, the CPU immediately
 shuts down both safety solenoids, disconnecting the battery. With the non
 integrated systems, failures that don't report information to the
 management system could lead to disaster.

 Please keep offering us the knowledge you are gaining as I am a firm
 believer that Lithium technology is a large part of the inevitable
 replacement the aged lead battery.

 Larry Crutcher
 Starlight Solar Power Systems


 On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:

 Hi:

 I may sound like I'm a detractor against using Lion, but that's not it.

 What I want to bring to light is that, being as the technology is new, not
 all the issues are known and there are things to learn for all early
 adopters in the foreseeable future.

 From what I can gather the framework for the issues lies in that Lion
 technology is based on intercalation, that is, a reversible insertion and
 removal of Li molecules into compounds with microscopically layered
 structures.  This predicates that there must be no chemical reaction in the
 battery, but rather only the shelving of the highly reactive Li ions.  If
 there are any chemical reactions taking place, then in the least the
 battery performance is compromised and in the most there is a thermal event
 or worse

 There are some very robust Lion battery packs, a favorite of mine being
 from a local company from Vancouver, (well Richmond, which is a suburb of
 Vancouver).  It's a small company, but they have designed, developed, built
 and successfully approved their 6 kWh Lion pack for use in large car
 ferries in Scandinavia.  The ferries have stacks of these packs in the
 100's, in the MWh size.  It can be done.

 What I'm advocating is that its best to work with companies that have the
 time, interest and resources to work through the wrinkles, and if not, then
 carefully put in reliable and precise BMS circuitry which includes things
 like fail safe circuits for single point failures of critical sensing
 circuits, the foremost of which is cell temperature.  When you're pushing
 large currents, all it takes is one poor connection or broken temp sensor
 on one cell..

 Here's a link to the Lion battery pack manufacturer, Corvus,

 http://corvus-energy.com/

 I know they do a good job, but they're not cheap, for now...

 JARMO


 * Jarmo Venalainen*  |  * Schneider Electric **  |  Xantrex Brand*  |
 *CANADA*  |   *Sales Application Engineer*
 * Phone:* +604-422-2528  |   *Tech Support:* 800-670-0707  |   *Mobile:*
 +604-505-0291
 * Email:* *jarmo.venalai...@schneider-electric.com*
 jarmo.venalai...@schneider-electric.com  |   *Site:** www.Xantrex.com*
 http://www.xantrex.com/  |   *Address:* 3700 Gilmore Way, Burnaby, BC
 V5G4M1
   Mail Attachment.gif http://www.xantrexrebate.com/  Mail
 Attachment.gif http://www.xantrex.com/ Mail Attachment.gif
 https://www.facebook.com/Xantrex Mail Attachment.gif
 https://twitter.com/Xantrex Mail Attachment.gif
 https://twitter.com/Xantrex




___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 

Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Max Balchowsky
We're leaning toward the LiFePO4 batteries (low internal resistance) GBS have  
a medium high resistance so they warm faster and have a lower C rate 
efficiency, were gathering info as we go.. Max Balchowsky
Design Engineer
Golden Bridge Development
1048 Irvine Ave Suite 217
Newport Beach, Ca. 92660
760-403-6810Building a Better Future For The Next Generation

  From: Larry la...@starlightsolar.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org 
 Sent: Wednesday, March 18, 2015 8:57 AM
 Subject: Re: [RE-wrenches] Load testing Lithium battery bank
   
 Hi Jarmo,
 
 I agree and recognize your urgency in making us aware of the proper use and 
charging of Li-ion batteries as well as the dangers of mistreating them. As an 
early adopter myself, I am very cautious in my approach even to the point of 
refusing to sell to some customers. Lithium battery technology is in a state of 
rapid evolution. 
 
 Not wanting to harp on the GBS brand that I sell, but one of your points goes 
to prove the safety of their integrated approach. You said, ...all it takes is 
one poor connection or broken temp sensor on one cell. The GBS EMS system has 
cell level sensors for temperature (and other data) and each sensor board 
requires constant communication with the CPU. If the EMS fails to communicate 
any information with any cell, the CPU immediately shuts down both safety 
solenoids, disconnecting the battery. With the non integrated systems, failures 
that don't report information to the management system could lead to disaster.
 
 Please keep offering us the knowledge you are gaining as I am a firm believer 
that Lithium technology is a large part of the inevitable replacement the aged 
lead battery.
 Larry Crutcher
Starlight Solar Power Systems
  

On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:
  
Hi: 
 
 I may sound like I'm a detractor against using Lion, but that's not it. 
 
 What I want to bring to light is that, being as the technology is new, not all 
the issues are known and there are things to learn for all early adopters in 
the foreseeable future. 
 
 From what I can gather the framework for the issues lies in that Lion 
technology is based on intercalation, that is, a reversible insertion and 
removal of Li molecules into compounds with microscopically layered structures. 
 This predicates that there must be no chemical reaction in the battery, but 
rather only the shelving of the highly reactive Li ions.  If there are any 
chemical reactions taking place, then in the least the battery performance is 
compromised and in the most there is a thermal event or worse 
 
 There are some very robust Lion battery packs, a favorite of mine being from a 
local company from Vancouver, (well Richmond, which is a suburb of Vancouver).  
It's a small company, but they have designed, developed, built and successfully 
approved their 6 kWh Lion pack for use in large car ferries in Scandinavia.  
The ferries have stacks of these packs in the 100's, in the MWh size.  It can 
be done. 
 
 What I'm advocating is that its best to work with companies that have the 
time, interest and resources to work through the wrinkles, and if not, then 
carefully put in reliable and precise BMS circuitry which includes things like 
fail safe circuits for single point failures of critical sensing circuits, the 
foremost of which is cell temperature.  When you're pushing large currents, all 
it takes is one poor connection or broken temp sensor on one cell.. 
 
 Here's a link to the Lion battery pack manufacturer, Corvus, 
 
 http://corvus-energy.com/ 
 
 I know they do a good job, but they're not cheap, for now... 
 
 JARMO 
 
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  |   
Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
  
|   |
|   |   |   |  |

 
  
 
 
 
 
 
| 
  |

 
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



  ___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Luke Christy
Larry,

I've been checking out the [current] viability of Li+ technologies for RE 
systems, and I'm encouraged to hear of the success you've apparently had. 
What is the typical kWh size of the battery packs you've been putting together? 
Are you sourcing the GBS batteries directly from the manufacturer?

I appreciate both your and Jarmo's comments about the safety concerns with this 
rapidly evolving technology.  
Feeling good about the long term safety of a large RE-scale Li-ion battery pack 
for my customers has been a major stumbling block for me thus far. 

Thanks,
-Luke


Luke Christy

NABCEP Certified PV Installation Professional™: Certification #031409-25 
NABCEP Certified Solar Heating Installer™: Certification #ST032611-03   
CoSEIA Certified PV Installer 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
sgsrenewab...@gmail.com
719.588.3044
www.sgsrenewables.com

   







___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Larry

Hi Chris,

Thanks for the recommendation. I received a quote from Comrent$1800 
to rent a load for 1 week. Ouch! I'll go with the $10 water elements and 
a little fabrication time. I have AH counters and controllers to stop 
the discharge.


Thank you,

Larry Crutcher
Starlight Solar Power Systems

On 3/17/15 2:38 PM, Chris Mason wrote:
Load banks are for rent, I am in the generator business and it is a 
common requirement to provide a load bank upon installation.

http://www.comrent.com/Solutions/load-bank-rentals.html


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Jarmo . Venalainen
Hi:

Please be careful when working with solar system size Lithium packs on the 
cell level.

We have been doing on-going testing with Lion battery packs from various 
suppliers and even with their built in temp sensors and other BMS 
circuits, have already had two thermal events.

Lion is very unforgiving with regards low state of charge, high state of 
charge, temperature (110F is the max temp at which they should be charged 
and 140F is the max they can handle).

Given the low thermal mass of Lion cells, a high rate of discharge or 
charge quickly gets the cell temperature into the 110F+ range.

As soon as you cross the line things start happening and if the BMS 
doesn't put a stop to it by turning the battery pack off, it's a very 
quick slide down the hill from there.

JARMO
_
 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  | 
  Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 








*** Please consider the environment before printing this e-mail




From:
Larry la...@starlightsolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
03/17/2015 11:41 AM
Subject:
[RE-wrenches] Load testing Lithium battery bank
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



I am repairing and restoring a pair of poorly designed lithium-ion 
battery bank that suffered over discharge, damaging many cells. After 
cell replacement I need to perform a discharge test with a 10kW load to 
verify the remaining capacity. The battery voltage is 105 volts @ 100% 
SoC and 89.6 volts @ 0%

I would like advice on how I can create an economical 10kW load. Water 
heating element? Wire wound resistors? Are there any GT inverters that 
will operate at these voltages?

Thanks.

-- 


Larry Crutcher
Starlight Solar Power Systems

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Larry
I was thinking of mounting the water heat elements into an aluminum 
plate, laying the plate flat over a 55 gallon drum and filling the water 
level up to the plate. Stratified water may make the top pretty hot but 
I guess it will work.


Larry

On 3/17/15 1:07 PM, Ray Walters wrote:
Those look like your solution.  Also water can take more heat with 
less trouble than air heaters.  I've had air heaters start melting 
things, etc.  You can just install those in the side of a 55 gal 
barrel with a bulkhead fitting, or yes, weld the appropriate plumbing 
fitting to the side of the barrel. Might even be able to install them 
into a section of pipe with  Ts and run water through it to cool the 
elements.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/17/2015 1:40 PM, Larry wrote:

Hey Ray,

I remember seeing huge banks of light bulbs as loads back in the 
early 70's.


I need to test the entire bank as one unit as the first cell of 32 to 
reach 2.8 volts determines the capacity for the bank. I just saw Home 
Depot has a 2kW 120 volt water heater for $10. Guess I need to do 
some welding.


Thank you,

Larry Crutcher
Starlight Solar Power Systems

On 3/17/15 11:59 AM, Ray Walters wrote:

Hi Larry,

I think you hit on the best load already: water heater elements 
rated for 120 v.  We have also used dump loads for wind turbines 
like the air heating elements from Bergey, but they are only about 1 
kW each.  Another possible source are the resistor banks for old 
golf carts (before they had controllers, they used resistor banks to 
operate at slow speeds)
A very long time ago, an inverter company had a demonstration that 
used a large bank of incandescent light bulbs.  They used to make a 
300 watt bulb for mining, so 33 of those would work. (maybe a few 
more bulbs, since your voltage is bit lower than 120 v)  Cheap 
electric space heaters would work too.  You also might look around 
at an electronics surplus store.
Whatever you do, it sounds like a lot of time and work to set up. 
Any chance of doing a smaller load test for subsets of the total 
bank?  You might be able to use a standard 12 v battery load tester 
then.


Good Luck.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/17/2015 12:41 PM, Larry wrote:
I am repairing and restoring a pair of poorly designed lithium-ion 
battery bank that suffered over discharge, damaging many cells. 
After cell replacement I need to perform a discharge test with a 
10kW load to verify the remaining capacity. The battery voltage is 
105 volts @ 100% SoC and 89.6 volts @ 0%


I would like advice on how I can create an economical 10kW load. 
Water heating element? Wire wound resistors? Are there any GT 
inverters that will operate at these voltages?


Thanks.



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Larry
I am repairing and restoring a pair of poorly designed lithium-ion 
battery bank that suffered over discharge, damaging many cells. After 
cell replacement I need to perform a discharge test with a 10kW load to 
verify the remaining capacity. The battery voltage is 105 volts @ 100% 
SoC and 89.6 volts @ 0%


I would like advice on how I can create an economical 10kW load. Water 
heating element? Wire wound resistors? Are there any GT inverters that 
will operate at these voltages?


Thanks.

--


Larry Crutcher
Starlight Solar Power Systems

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Chris Mason
Load banks are for rent, I am in the generator business and it is a common
requirement to provide a load bank upon installation.
http://www.comrent.com/Solutions/load-bank-rentals.html


On Tue, Mar 17, 2015 at 4:35 PM, Ray Walters r...@solarray.com wrote:

 Hi James;

 So couldn't Larry weld in rigid conduit fittings?  Aren't they NPSM, or do
 I have that wrong? I suppose the Zinc plating would make a messier weld and
 possibly be poisonous

 Also to Chris Mason, I was not aware that load banks were available for
 rent.  That sounds like a good option to consider.  Do you have a
 recommendation on who rents those?

 3rd response to Jarmo:  do you have any pictures of the Li+ thermal
 issues?  Are we talking structure fire potential, or just destruction of
 the batteries themselves?
 Is this another reason not to use plywood battery boxes?

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760


  Note that water heater elements are NPSM (National Pipe Straight
 Mechanical) and not NPT. So you need that type of half coupling or bung
 to weld in. The vegi-oil people seem to have this sort of stuff as they
 build water heater elements into things.



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
 org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org




-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com http://www.cometenergysystems.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Jarmo . Venalainen
Hi:

I cant put out anything which may show proprietary info, but here are a 
couple close up fragments of images of failure trials where the BMS system 
was not able to catch the issue before the event went out of bounds 
thermal.

 

As you can see some kind of corrosive gas coated many surfaces inside the 
battery pack while reacting with and discoloring any aluminium which was 
in the near vicinity of the cells

I definitely would not use any material other than metal or some other 
very chemical/heat/fire resistant materials in and around Lion cells and 
I'd vent the battery pack to the outdoors.

I'm sure there will be many perfectly reliable and safe packs, but soon 
there will also be something like a melted laptop or cell phone on 
steroids as a typical solar system battery has about 3000X as much energy 
as the cell phone/laptop.

JARMO
_
 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  | 
  Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 








*** Please consider the environment before printing this e-mail




From:
Ray Walters r...@solarray.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
03/17/2015 01:35 PM
Subject:
Re: [RE-wrenches] Load testing Lithium battery bank
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



Hi James;

So couldn't Larry weld in rigid conduit fittings?  Aren't they NPSM, or 
do I have that wrong? I suppose the Zinc plating would make a messier 
weld and possibly be poisonous

Also to Chris Mason, I was not aware that load banks were available for 
rent.  That sounds like a good option to consider.  Do you have a 
recommendation on who rents those?

3rd response to Jarmo:  do you have any pictures of the Li+ thermal 
issues?  Are we talking structure fire potential, or just destruction of 
the batteries themselves?
Is this another reason not to use plywood battery boxes?

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760


 Note that water heater elements are NPSM (National Pipe Straight 
 Mechanical) and not NPT. So you need that type of half coupling or 
 bung to weld in. The vegi-oil people seem to have this sort of stuff 
 as they build water heater elements into things.



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Larry

Hi Jarmo,

One of the reasons I chose to sell and install GBS batteries is the 
chemistry is safer, they have vent caps (like AGM) and they offer an 
integrated solution where the battery, EMS/BMS and CPU are all designed 
specifically for each other instead of adding various parts from 
different manufacturers. The chemistry is LFMP (lithium iron manganese) 
not LFP. There are seven monitored fault events, including temperature, 
current and voltage, that will disconnect the battery from any load or 
any charge source.


Since we are installing in RV's, there are multiple charge sources and 
all must be controlled. The systems I design do this very well. Also, 
our charge and discharge rates are far lower than the industry normally 
expects; rarely reaching .5C.


I have seen private videos of destructive testing of GBS cells. Steel 
rods fired through entire packs; slow crush tests from top and sides, 
impact tests, even cells blown away on a gun range (that was more for 
fun I think as not too likely you will experience that). No fire, no 
thermal events. Bottom line for me is these are likely the safest 
Lithium battery I can offer. Many customers have already had shut down 
events because they were not being responsible. A simple reset and 
they're back in business.


What was the lithium chemistry that you had trouble with?

Thank you,

Larry Crutcher

On 3/17/15 12:49 PM, jarmo.venalai...@schneider-electric.com wrote:

Hi:

Please be careful when working with solar system size Lithium packs on 
the cell level.


We have been doing on-going testing with Lion battery packs from 
various suppliers and even with their built in temp sensors and other 
BMS circuits, have already had two thermal events.


Lion is very unforgiving with regards low state of charge, high state 
of charge, temperature (110F is the max temp at which they should be 
charged and 140F is the max they can handle).


Given the low thermal mass of Lion cells, a high rate of discharge or 
charge quickly gets the cell temperature into the 110F+ range.


As soon as you cross the line things start happening and if the BMS 
doesn't put a stop to it by turning the battery pack off, it's a very 
quick slide down the hill from there.


JARMO
_
*
Jarmo Venalainen*  | *Schneider Electric **|  Xantrex Brand*  | 
*CANADA*  | *Sales Application Engineer* *
Phone:* +604-422-2528  | *Tech Support:* 800-670-0707  | *Mobile:* 
+604-505-0291 *
Email:* _jarmo.venalainen@schneider-electric.com_ 
mailto:jarmo.venalai...@schneider-electric.com | 
*Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:* 3700 
Gilmore Way, Burnaby, BC V5G4M1

http://www.xantrexrebate.com/
http://www.xantrex.com/ 	https://www.facebook.com/Xantrex 
https://twitter.com/Xantrex 	https://twitter.com/Xantrex





*** Please consider the environment before printing this e-mail



From:   Larry la...@starlightsolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org,
Date:   03/17/2015 11:41 AM
Subject:[RE-wrenches] Load testing Lithium battery bank
Sent by:RE-wrenches re-wrenches-boun...@lists.re-wrenches.org




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Ray Walters

Hi Larry,

I think you hit on the best load already: water heater elements rated 
for 120 v.  We have also used dump loads for wind turbines like the air 
heating elements from Bergey, but they are only about 1 kW each.  
Another possible source are the resistor banks for old golf carts 
(before they had controllers, they used resistor banks to operate at 
slow speeds)
A very long time ago, an inverter company had a demonstration that used 
a large bank of incandescent light bulbs.  They used to make a 300 watt 
bulb for mining, so 33 of those would work.  (maybe a few more bulbs, 
since your voltage is bit lower than 120 v)  Cheap electric space 
heaters would work too.  You also might look around at an electronics 
surplus store.
Whatever you do, it sounds like a lot of time and work to set up. Any 
chance of doing a smaller load test for subsets of the total bank?  You 
might be able to use a standard 12 v battery load tester then.


Good Luck.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/17/2015 12:41 PM, Larry wrote:
I am repairing and restoring a pair of poorly designed lithium-ion 
battery bank that suffered over discharge, damaging many cells. After 
cell replacement I need to perform a discharge test with a 10kW load 
to verify the remaining capacity. The battery voltage is 105 volts @ 
100% SoC and 89.6 volts @ 0%


I would like advice on how I can create an economical 10kW load. Water 
heating element? Wire wound resistors? Are there any GT inverters that 
will operate at these voltages?


Thanks.



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Chris Mason
I would rent a load bank, it will give you the versatility to change loads
as needed.

On Tue, Mar 17, 2015 at 2:41 PM, Larry la...@starlightsolar.com wrote:

 I am repairing and restoring a pair of poorly designed lithium-ion battery
 bank that suffered over discharge, damaging many cells. After cell
 replacement I need to perform a discharge test with a 10kW load to verify
 the remaining capacity. The battery voltage is 105 volts @ 100% SoC and
 89.6 volts @ 0%

 I would like advice on how I can create an economical 10kW load. Water
 heating element? Wire wound resistors? Are there any GT inverters that will
 operate at these voltages?

 Thanks.

 --


 Larry Crutcher
 Starlight Solar Power Systems

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
 org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org




-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com http://www.cometenergysystems.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread Larry

Hey Ray,

I remember seeing huge banks of light bulbs as loads back in the early 
70's.


I need to test the entire bank as one unit as the first cell of 32 to 
reach 2.8 volts determines the capacity for the bank. I just saw Home 
Depot has a 2kW 120 volt water heater for $10. Guess I need to do some 
welding.


Thank you,

Larry Crutcher
Starlight Solar Power Systems

On 3/17/15 11:59 AM, Ray Walters wrote:

Hi Larry,

I think you hit on the best load already: water heater elements rated 
for 120 v.  We have also used dump loads for wind turbines like the 
air heating elements from Bergey, but they are only about 1 kW each.  
Another possible source are the resistor banks for old golf carts 
(before they had controllers, they used resistor banks to operate at 
slow speeds)
A very long time ago, an inverter company had a demonstration that 
used a large bank of incandescent light bulbs.  They used to make a 
300 watt bulb for mining, so 33 of those would work.  (maybe a few 
more bulbs, since your voltage is bit lower than 120 v)  Cheap 
electric space heaters would work too.  You also might look around at 
an electronics surplus store.
Whatever you do, it sounds like a lot of time and work to set up. Any 
chance of doing a smaller load test for subsets of the total bank?  
You might be able to use a standard 12 v battery load tester then.


Good Luck.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/17/2015 12:41 PM, Larry wrote:
I am repairing and restoring a pair of poorly designed lithium-ion 
battery bank that suffered over discharge, damaging many cells. After 
cell replacement I need to perform a discharge test with a 10kW load 
to verify the remaining capacity. The battery voltage is 105 volts @ 
100% SoC and 89.6 volts @ 0%


I would like advice on how I can create an economical 10kW load. 
Water heating element? Wire wound resistors? Are there any GT 
inverters that will operate at these voltages?


Thanks.



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-17 Thread James Jefferson Jarvis

On 3/17/2015 3:07 PM, Ray Walters wrote:

Those look like your solution.  Also water can take more heat with less
trouble than air heaters.  I've had air heaters start melting things,
etc.  You can just install those in the side of a 55 gal barrel with a
bulkhead fitting, or yes, weld the appropriate plumbing fitting to the
side of the barrel. Might even be able to install them into a section of
pipe with  Ts and run water through it to cool the elements.


Note that water heater elements are NPSM (National Pipe Straight 
Mechanical) and not NPT. So you need that type of half coupling or 
bung to weld in. The vegi-oil people seem to have this sort of stuff 
as they build water heater elements into things.



--
-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
www.aprsworld.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org