All that is required is "restraint". That can be 12 ga. wire if you so choose.
Look at NFPA 13, 2013 ed., 9.2.3.7 & the Annex material for it. The same
criteria goes back two or three editions.
Thank you,
Bob Knight, CE
_
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Taylor Schumacher
Sent: Thursday, June 09, 2016 1:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lateral support for sprigs
I have an AHJ in Iowa (non-seismic) looking for a listing for lateral
supp
Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Taylor Schumacher
Sent: Thursday, June 09, 2016 1:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lateral support for sprigs
I have an AHJ in Iowa (non-seismic) looking for a listing for lateral
supports on sprigs i
I have an AHJ in Iowa (non-seismic) looking for a listing for lateral supports
on sprigs in an attic. We have sprigs for back to back attic sprinklers running
from the main to the peak of the roof and have them supported with loop hanger
ring-rod-and threaded fastener.