Re: GFIs, Hairdryers, and Bathtubs ...

1997-09-03 Thread Rick . Koski
   I have been reading some of the responses to this note.  It appears many of 
   us product safety professionals are missing some key points.  I would like 
to 
   thank the author for bringing this up for discussion.  This is what makes 
the 
   bulletin board so valuable.
   
   A GFI is a very simple devices that works by monitoring the amount of 
current 
   that flows in through the hot and out through the neutral. If there is a 
   difference of more than about 3 mA (and no more than 5), the device trips.  
   Basically speaking, out must equal in.  If it doesn't, current has found 
   another path to travel to ground.
   
   A persons resistance to fatal shock varies with a multitude of factors, but 
   it is generally safe to say that anything above an amp flowing through the 
   body is fatal.  Our nerves are designed to handle milli and micro amps, and 
   anything significantly above that will burn them out rapidly. If the nerves 
   don't work, key muscles like the heart become ineffective.
   
   Unless you are filling your bath tub with distilled water, there are enough 
   conductive impurities to allow small amounts of current flow.  In many 
   municipalities that are large amounts of iron in the supplies.  In addition, 
   almost every city adds chlorine, which is somewhat corrosive, and will pull 
   the copper and iron ions off of the distribution system piping.  Again, 
   remember that we are talking about very small amounts of current.
   
   Being a parent myself, I know what it is like to let two young children in 
   the bathtub at the same time.  There was likely water all over the floor, 
the 
   sides of the tub, various toys around the area, etc.  Since there was no GFI 
   breaker installed, I am guessing that this was a fairly old dwelling (GFI's 
   have been required by code since the 70's).  This means the appliances were 
   probably scratched, dinged, dented, etc, and the pipes were copper and cast 
   iron.  It is also code required that metal supply piping in houses be tied 
to 
   ground somewhere in the dwelling, so there ire ample routes to ground.
   
   Most lighting circuits in houses are either 15 or 20 amp circuits.  The 
   breakers are designed to allow for "turn on" surges, meaning they will not 
   immediately trip if current flow crosses the threshold.  Some breakers will 
   operate at 20% overage for u to 5 minutes.  Also,  breakers are generally 
   only guaranteed to be accurate for a limited number of trips. There may in 
   the case have been a full 15 or 20 amps going to ground.  Even though these 
   girls were at the opposite end of the tub, they were able to get enough of 
   that current flow to kill them, even if it wasn't the entire amount 
   
   Any way you look at this, it was a tragedy.  I reject the idea that this was 
   just a bad set of circumstances.  The NFPA claims that bathroom 
   electrocutions have drooped by over 90% since the requirement for GFI 
   breakers was added to the Code.  This is a compelling statistic. 
   
   The bottom line is that the newspapers were right when they stated that this 
   event would not have occurred for want of a $20.00 item available at any 
   hardware store.  If you are evaluating system designs, and there are single 
   phase low power systems where people could come in contact with electricity 
   and water at the same time, remember this.  The Code requires GFI's 
   essentially anywhere there is water, and/or portable hand tools (drills, 
   mixers, and yes even hair dryers). The way implement this requirement 
   determines if we consider the code a proactive approach, or an obstacle.  I 
   have often seen convenience outlets in machine tools that are not GFI 
   protected, and heard the argument that a GFI is not required by the code.  
   This misses the point. Lets make sure that we all learn the important 
lessons 
   from this event.
   
   Rick Koski
   Director, ES&H
   SEMI/SEMATECH


__ Reply Separator _
Subject: GFIs, Hairdryers, and Bathtubs ...
Author:  dmck...@paragon-networks.com
List-Post: emc-pstc@listserv.ieee.org
Date:8/13/97 11:51 AM


Recently somewhere back in the news (couple of weeks ago), 
two children died when one of them used a hairdryer in 
the tub.  A discussion this accident with some lead me 
to a counter-intuitive result from my experience in 
product safety. 

** 

Given Situation #1: 

1. Person in a tub of water sitting at the opposite 
   end of the tub than the drain. 

2. The tub is ungrounded with water in it.  Ungrounded 
   meaning that the drain is plastic piping. 

3. A 2-wire hair dryer (either On or OFF) is dropped 
   into  the water at the drain end of the tub. The person 
   in the tub is neither in contact with the hairdryer, 
   not anything that would be grounded. 

   The hairdryer has a plastic case. 

Result: 

1. Since t

Re: New test finger

1997-09-03 Thread Ray_Russell
 
 Juan,
 
 Thanks for bringing this up. I thought I would check into for use at 
 our company also, so I checked with ED&D. I've been happy with the 
 other probes that I previously bought from them.
 
 Regards,
 
 Ray Russell
 ray_russ...@leco.com
 
 
 Here is their response: 
 
 
 Thank you for your message! Yes, we do offer that probe.  It is the 
 Fingernail Probe (FNP-01) and it is $895.00.  We are currently out of 
 stock for these, and the lead time is approximately 4-6 weeks.
 
 Please let me know if I can be of any more help, or if you would like 
 to go ahead and place the order.
 
 Thank you and best regards,
 
 Rita Fischer
 Educated Design & Development
 email:  prodsaf...@aol.com
 


__ Reply Separator _
Subject: New test finger
Author:  =?iso-8859-1?Q?Juan_Pedro_Pe=F1a?=  at Internet
List-Post: emc-pstc@listserv.ieee.org
Date:9/2/97 10:33 AM


As many of you probably know, the last version of IEC 335-1 introduces a 
new test finger including a nail, rather different to the usual one. I 
have asked my usual suppliers for it, but I have only received negative 
or no answer.
 
Does anybody know where can I buy that new test finger?
 
Thank you very much.
 
 
Juan P. Pena  / Electrical Safety Area
Company: CETECOM, S.A. (http://www.cetecom.es ) 
e-mail: jpp...@cetecom.es
 
 


Re: GFIs, Hairdryers, and Bathtubs ... -Reply

1997-09-03 Thread James Sketoe
Don't forget, the low impedance path from the  black (high side of
switch) to water to human to water to neutral (white wire.) It doesn't go
to ground and may not even trip the GFI!

>>>  09/02/97
06:33pm >>>
 

You forgot two major assumptions:

1) The impedance of the water and 
2)the impedance of the human in water.

In water, the human has orders of magnitude of lower impedance, and
therefore, 
the majority of the current will flow through the human assuming there is
a path
to ground. It is highly unlikely that there is no path to ground. In most
home 
building codes, plastic piping is not allowed due to fire codes (they melt) 
perhaps with the exception of waste pipe (most of them are cast iron)
Recently 
in the bay area, a girl was electrocuted in a swimming pool due to a
faulty 
lighting wire. Yes, the breaker triped but too late.

Also, don't forget that there are many unsuspecting grounds. The faucet,
dings 
and scrapes on the porcelain or enamel, wet wood, concrete, stucco,
morter etc. 
Those are all better conductors than tap water.

Hans

__ Reply Separator
_
Subject: GFIs, Hairdryers, and Bathtubs ...
Author:  Non-HP-dmckean (dmck...@paragon-networks.com) at
HP-ColSprings,mimegw5
List-Post: emc-pstc@listserv.ieee.org
Date:8/13/97 9:51 AM


Recently somewhere back in the news (couple of weeks ago), 
two children died when one of them used a hairdryer in 
the tub.  A discussion this accident with some lead me 
to a counter-intuitive result from my experience in 
product safety. 
 
** 
 
Given Situation #1: 
 
1. Person in a tub of water sitting at the opposite 
   end of the tub than the drain. 
 
2. The tub is ungrounded with water in it.  Ungrounded 
   meaning that the drain is plastic piping. 
 
3. A 2-wire hair dryer (either On or OFF) is dropped 
   into  the water at the drain end of the tub. The person 
   in the tub is neither in contact with the hairdryer, 
   not anything that would be grounded. 
 
   The hairdryer has a plastic case. 
 
Result: 
 
1. Since there is no path to ground from the hairdryer 
   through the person in the tub to ground, no current 
   should flow *thru* the person in the tub. The person 
   is in no harm.  
 
2. Since no current is flowing through ground, 
   the GFI won't trip.  If the water allows sufficient 
   current to flow by shorting between the HOT and 
   NEUTRAL in the hairdryer, the breaker will trip.  
 
** 
 
Given Situation #2: 
 
Same as situation #1 except that the drain is now 
a grounded metal pipe. 
 
Is there a sufficient parallel path to be lethal 
to the person in the tub?  Seems as though the 
parallel path for the hairdryer is straight to 
the drain. 
 
Result: 
 
1. Person is still unharmed. 
 
2. GFI trips. 
 
** 
 
Are my conclusions correct? 
 
Is the only time one can be electrocuted in a tub 
when they are in contact with a ground and holding 
the hairdryer? 
 
Is a person really killed in a tub with hairdryer 
by drowning rather than electrocution? 
 
I'm beginning to doubt that I know exactly how 
a person is killed in a tub with a hairdryer. 
 
Or, am I making this way more complicated 
than it is? 
 
Comments? 
 
 
 
 



Immunity of Optocouplers to Electromagnetic Disturbances

1997-09-03 Thread Viggo Brøndegaard Nielsen
The Society for Reliability and Environmental Testing, SPM has issued a report 
with a comparative analysis of optocouplers* immunity performance when exposed 
to typical EMC tests. 

The general results of this report are:

*   Some - and not all - optocouplers can successfully be used in apparatus 
for galvanic insulation of inputs/outputs in industrial electromagnetic 
environ*ments and without additional common mode filters.

*   The present data sheets on optocouplers do not provide sufficient 
information to design an apparatus and predict all the normal electromagnetic 
immunity parameters. This report can help the design and prediction, but tests 
are still required.

*   All optocouplers will produce a short wrong output signal, when exposed 
to normal fast common mode transients/burst. 

24 different optocouplers from six different manufacturers were subjected to 
electro*magnetic immunity tests, which are commonly used for test of commercial 
apparatus aimed at industrial environments. The disturbances were surge 
transients, fast tran*sients/burst, conducted radio frequency signals, and 
radio frequency electromagnetic fields. The report is: "Immunity of 
Optocouplers to Electromagnetic Disturbances", SPM-139 by Viggo Brøndegaard 
Nielsen, DELTA Electronics Testing. Members of SPM automatically receive the 
report, and others can buy the report from SPM - price DKK 1200.-. Contact Ms. 
Lisbeth Valentiner, DELTA Danish Electronics, Light & Acoustics, Telephone: +45 
42 86 77 22, e-mail: s...@delta.dk.





SPM is an independent organisation consisting of more than 100 company members 
in Scandinavia. SPM initiates and finances unprejudiced investigations of 
common interest for its members - mainly in the field of reliability problems 
and testing of electronic components and materials.

List of some other SPM reports: http://www.delta.dk/spm/rapplist/welcome.htm


GFI Function

1997-09-03 Thread DenBleyker, R. (919-543-7251 TL 441)
In all of the discussions of hair-dryer in a tub scenario, no one has discussed
the GFI and how it works.  It senses the current in both power leads, and if
they are not equal, it trips OFF.  Thus it assumes that any current flowing
between phase/neutral is good, any current in the phase lead not returning in
the neutral is not-good.

Ignoring the physical fact that pure water is an excellent insulator---

dropping the hair dryer in an older home with metal piping will probably result
in instant trip-out, since some current will find a path back via the pipes to
electrical earth.

dropping the hair dryer in a newer home with all plastic piping is probably a
more hazardous situation.  The GFI will not trip out, and a person may provide
a lower impedance path between phase/neutral connections in the dryer than the
surrounding water.  Our bodies are flooded with a saline solution (blood) and
are very conductive once the skin is bypassed.

I have done some work in the crawl-space of my daughters' home in Durham NC,
and know for certain that the waste/water lines are all plastic.  There could
be a grounding circuit but I am not aware of it.  Naturally the tub & surround
are all plastic also.

The warnings provided with hair dryers and similar appliances warning against
their use in wet areas must be observed.

bo...@vnet.ibm.com


Re: New test finger

1997-09-03 Thread Ben Wrigley
-- Original message from Juan Pedro Peña --

> As many of you probably know, the last version of IEC 335-1 introduces a new
> test finger including a nail, rather different to the usual one. I have asked
> my usual suppliers for it, but I have only received negative or no answer.
>
> Does anybody know where can I buy that new test finger?
>
> Thank you very much.
>
>
> Juan P. Pena  /   Electrical Safety Area
> Company: CETECOM, S.A. (http://www.cetecom.es )
> e-mail: jpp...@cetecom.es

Juan

We bought one of these test fingers just over two years ago from the following
manufacturer:

Startrite Designs Ltd
Courteney Road
Hoath Way
Gillingham
Kent
ME8 0RZ
UK

Phone: +44 1634 233216
Fax: +44 1634 373516

Contact: John Masters

It cost about GBP 800 to buy and GBP 30 a year for calibration.

I hope this helps.

Regards

--

Ben Wrigley
Senior Approvals Specialist

KTL
Saxon Way
Priory Park West
Hull
HU13 9PB
UK

Phone:  +44 (0)1482 801801
Fax:+44 (0)1482 801806
Web:http://www.ktl.co.uk
Email:  bwrig...@ktl.co.uk


50,000 and Counting -- Thank you!

1997-09-03 Thread Art Michael
Hello pstc-ers,

The Safety Link (http://www.safetylink.com) noted the entry of its
50,000th visitor today, 2 September 1997.  Our counter was started in
December of 1995 and the website has been active since the Summer of that
year.   

We would like to thank all of our visitors as well as our Corporate
Supporters.  Your continued visits and support affirm our intent that
the Safety Link serve as a useful resource for electrical product safety
professionals.

And, for those not familiar with the sites offerings, we invite you to
surf in and check out the web's most comprehensive collection of
electrical product safety resources. 

ThanX again, Art Michael, Webmaster of the Safety Link.




Re: IEEE Conference

1997-09-03 Thread MikonCons
Charles:

Kudos to you!!!  Your offer is one that should be a "standard operating
procedure" to our community.  Sharing knowledge, interpretations, and
opinions in discussions seems to be a lost art that was practiced in the 18th
and 19th centuries, but (contrary to expectations) died out in the 20th
century that features "improved communications" with the advent of
electronic-based communications.  The sharing of insights in our EMC
community will enhance the abilities of participants and help earn the
respect of those outside the community.

That said, I was unable (because of contractual commitments) to attend the
EMC conference in Austin and would greatly appreciate seeing commentaries
from any attendees on the most informative papers, and what they learned.  I
will soon have a copy of the conference proceedings; however, our activities
move in real time and delays mean less-informed decisions in the here and
now.

(Not to resurrect a controversial subject, but the use of attachments to the
forum E-mail would probably simplify consolidation of member's commentaries
by those who wish to download the comments into a separate directory for
perusal as time allows.)

Respectfully,
Mike Conn, Owner
Mikon Consulting


Re: GFIs, Hairdryers, and Bathtubs ...

1997-09-03 Thread HANS_MELLBERG
 

You forgot two major assumptions:

1) The impedance of the water and 
2)the impedance of the human in water.

In water, the human has orders of magnitude of lower impedance, and therefore, 
the majority of the current will flow through the human assuming there is a path
to ground. It is highly unlikely that there is no path to ground. In most home 
building codes, plastic piping is not allowed due to fire codes (they melt) 
perhaps with the exception of waste pipe (most of them are cast iron) Recently 
in the bay area, a girl was electrocuted in a swimming pool due to a faulty 
lighting wire. Yes, the breaker triped but too late.

Also, don't forget that there are many unsuspecting grounds. The faucet, dings 
and scrapes on the porcelain or enamel, wet wood, concrete, stucco, morter etc. 
Those are all better conductors than tap water.

Hans

__ Reply Separator _
Subject: GFIs, Hairdryers, and Bathtubs ...
Author:  Non-HP-dmckean (dmck...@paragon-networks.com) at HP-ColSprings,mimegw5
List-Post: emc-pstc@listserv.ieee.org
Date:8/13/97 9:51 AM


Recently somewhere back in the news (couple of weeks ago), 
two children died when one of them used a hairdryer in 
the tub.  A discussion this accident with some lead me 
to a counter-intuitive result from my experience in 
product safety. 
 
** 
 
Given Situation #1: 
 
1. Person in a tub of water sitting at the opposite 
   end of the tub than the drain. 
 
2. The tub is ungrounded with water in it.  Ungrounded 
   meaning that the drain is plastic piping. 
 
3. A 2-wire hair dryer (either On or OFF) is dropped 
   into  the water at the drain end of the tub. The person 
   in the tub is neither in contact with the hairdryer, 
   not anything that would be grounded. 
 
   The hairdryer has a plastic case. 
 
Result: 
 
1. Since there is no path to ground from the hairdryer 
   through the person in the tub to ground, no current 
   should flow *thru* the person in the tub. The person 
   is in no harm.  
 
2. Since no current is flowing through ground, 
   the GFI won't trip.  If the water allows sufficient 
   current to flow by shorting between the HOT and 
   NEUTRAL in the hairdryer, the breaker will trip.  
 
** 
 
Given Situation #2: 
 
Same as situation #1 except that the drain is now 
a grounded metal pipe. 
 
Is there a sufficient parallel path to be lethal 
to the person in the tub?  Seems as though the 
parallel path for the hairdryer is straight to 
the drain. 
 
Result: 
 
1. Person is still unharmed. 
 
2. GFI trips. 
 
** 
 
Are my conclusions correct? 
 
Is the only time one can be electrocuted in a tub 
when they are in contact with a ground and holding 
the hairdryer? 
 
Is a person really killed in a tub with hairdryer 
by drowning rather than electrocution? 
 
I'm beginning to doubt that I know exactly how 
a person is killed in a tub with a hairdryer. 
 
Or, am I making this way more complicated 
than it is? 
 
Comments?