Re: [PSES] POE creepage clearances

2012-11-26 Thread Joe Randolph


Hi Ian:
I think the short answer to your question is that under 60950 there are
no requirements for creepage and clearance distance between the Ethernet
circuit and ordinary SELV circuits that are user-contactable. This
is because under 60950, Ethernet is classified as an SELV circuit.
There are no requirements to separate one SELV circuit from
another.
Where this issue becomes confusing is that under the Ethernet 802.3
standard, an Ethernet port must provide a 1500 VRMS isolation barrier
between the Ethernet conductors and earth. This is a legacy
requirement whose origins seem to have been lost in the sands of
time. However, I believe the consensus view is that the original
intent of this requirement was to protect against ground loops and was
not related to user safety. Nevertheless, the 802.3 isolation
requirement has sometimes been treated as though it is a safety
requirement. Note that the 802.3 requirement is for a simple
dielectric test, with no reference to creepage, clearance, or distance
through solid insulation.
So, in principle, there are no safety isolation requirements for your
application, since both of the proposed power supplies have a SELV
output. This makes the entire device a SELV circuit (unless there
are other ports on the device that are not SELV).


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com


Dear colleagues

We are developing a hand held product that is powered from +48V DC over
Ethernet or from an external +12V DC wall wart PSU. The maximum internal
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements
between the “primary” Ethernet circuit and the “secondary” circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am
assuming a safety isolation creepage  clearance is required.

Many thanks in advance;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.com
www.allen-heath.com
A DMH Pro Company.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org 
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site
at
http://product-compliance.oc.ieee.org/
can be used for graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net 
Mike Cantwell mcantw...@ieee.org 
For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org 
David Heald dhe...@gmail.com 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc.


Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher  j.bac...@ieee.org
David Heald dhe...@gmail.com



Re: [PSES] POE creepage clearances

2012-11-26 Thread JIM WIESE
Be careful Joe,

There is a UL PAG that says that PoE must be treated as a TNV1, but overvoltage 
tests can be waived from Annex NAC.  It is a botched PAG that needs to be fixed 
for other reasons.  Also if it crosses the boundary between buildings it needs 
to be treated as TNV-1 even for international safety standards which may impose 
creepage and Clearance distances.

Also people forget there can be a lot of current coming from a shared PoE DC 
supply and eventhough safety requirement creepage and clearances  do not apply 
between the high and low voltage rails it is good to impose separation so you 
don't have a fire.

Jim

Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.commailto:jim.wi...@adtran.com


From: Joe Randolph [mailto:j...@randolph-telecom.com]
Sent: Monday, November 26, 2012 1:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances

Hi Ian:

I think the short answer to your question is that under 60950 there are no 
requirements for creepage and clearance distance between the Ethernet circuit 
and ordinary SELV circuits that are user-contactable.  This is because under 
60950, Ethernet is classified as an SELV circuit.  There are no requirements to 
separate one SELV circuit from another.

Where this issue becomes confusing is that under the Ethernet 802.3 standard, 
an Ethernet port must provide a 1500 VRMS isolation barrier between the 
Ethernet conductors and earth.  This is a legacy requirement whose origins seem 
to have been lost in the sands of time.  However, I believe the consensus view 
is that the original intent of this requirement was to protect against ground 
loops and was not related to user safety.  Nevertheless, the 802.3 isolation 
requirement has sometimes been treated as though it is a safety requirement.  
Note that the 802.3 requirement is for a simple dielectric test, with no 
reference to creepage, clearance, or distance through solid insulation.

So, in principle, there are no safety isolation requirements for your 
application, since both of the proposed power supplies have a SELV output.  
This makes the entire device a SELV circuit (unless there are other ports on 
the device that are not SELV).




Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.comhttp://www.randolph-telecom.com/





Dear colleagues

We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum internal 
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements between the 
?primary? Ethernet circuit and the ?secondary? circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am assuming 
a safety isolation creepage  clearance is required.

Many thanks in advance;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.commailto:ian.mcbur...@dmh-global.com
www.allen-heath.comhttp://www.allen-heath.com/
A DMH Pro Companyhttp://www.dmh-global.com/.

-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.netmailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.orgmailto:j.bac...@ieee.org
David Heald dhe...@gmail.commailto:dhe...@gmail.com
-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee

Re: [PSES] POE creepage clearances

2012-11-26 Thread Ron Pickard
Hi Joe,
I agree that an Ethernet circuit would be considered to be an SELV circuit and 
that would be true if the POE circuit were completely on premise generally, 
which would categorize this as a Class III product according to IEC/UL 60950-1 
2nd Ed. given that the external power supply is a limited power source (LPS). 
However, TNV-1 creepage/clearance requirements would apply if the POE were to 
be exposed to overvoltages from telecommunication networks (essentially off 
premise) requiring Basic insulation. I make this distinction as Ian did not 
mention where the POE circuit originates.

Best regards,

Ron

From: Joe Randolph [mailto:j...@randolph-telecom.com]
Sent: Monday, November 26, 2012 12:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances

Hi Ian:

I think the short answer to your question is that under 60950 there are no 
requirements for creepage and clearance distance between the Ethernet circuit 
and ordinary SELV circuits that are user-contactable.  This is because under 
60950, Ethernet is classified as an SELV circuit.  There are no requirements to 
separate one SELV circuit from another.

Where this issue becomes confusing is that under the Ethernet 802.3 standard, 
an Ethernet port must provide a 1500 VRMS isolation barrier between the 
Ethernet conductors and earth.  This is a legacy requirement whose origins seem 
to have been lost in the sands of time.  However, I believe the consensus view 
is that the original intent of this requirement was to protect against ground 
loops and was not related to user safety.  Nevertheless, the 802.3 isolation 
requirement has sometimes been treated as though it is a safety requirement.  
Note that the 802.3 requirement is for a simple dielectric test, with no 
reference to creepage, clearance, or distance through solid insulation.

So, in principle, there are no safety isolation requirements for your 
application, since both of the proposed power supplies have a SELV output.  
This makes the entire device a SELV circuit (unless there are other ports on 
the device that are not SELV).




Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.commailto:j...@randolph-telecom.com
http://www.randolph-telecom.comhttp://www.randolph-telecom.com/





Dear colleagues

We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum internal 
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements between the 
?primary? Ethernet circuit and the ?secondary? circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am assuming 
a safety isolation creepage  clearance is required.

Many thanks in advance;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.commailto:ian.mcbur...@dmh-global.com
www.allen-heath.comhttp://www.allen-heath.com/
A DMH Pro Companyhttp://www.dmh-global.com/.

-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.netmailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.orgmailto:j.bac...@ieee.org
David Heald dhe...@gmail.commailto:dhe...@gmail.com
-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.netmailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy

Re: [PSES] POE creepage clearances

2012-11-26 Thread Joe Randolph


Jim, Ron:
I agree that *if* the Ethernet cable extends outside the building for a
*considerable* distance, it's safety classification enters a no-man's
land in terms of safety classification. UL attempted to address
such situations with their PAG on POE, which states that POE lines that
are routed outside should be treated as TNV-1, but ordinary POE that is
routed inside can be treated as SELV. This leaves some ambiguity
because often the manufacturer does not know whether the user's POE
network uses outside lines.
A few months ago, those of us on the IEEE Telecom TAC had a very robust
discussion about this problem and possible ways to resolve it in a clear
manner. Unfortunately, we were unable to come up with a simple
solution.
The fact remains that under IEC 69050 and it's national derivations,
Ethernet is classified as SELV and for the vast majority of applications,
this classification is entirely appropriate. Now that *some* users
are stringing Ethernet cables outside, the question can be asked,
at what cable length does my Ethernet cable become subject to the
same safety threats as a TNV-1 circuit? The only official
attempt to answer this question is the UL PAG for UL 60950, and even this
attempt has some ambiguities.
Given that the maximum length of an Ethernet cable is specified in 802.3
to be 100 meters, it can be argued that this is insufficient to create
the same level of exposure hazard as a conventional phone line that can
easily exceed 5000 meters.
Getting back to Ian's original question, though, one could ask what the
effect would be of classifying his Ethernet port as a TNV-1
circuit. I'm speaking from memory here, but as I recall the TNV-1
classification does not invoke explicit creepage and clearance distances
(these are only called out for TNV-2 and TNV-3 circuits). I think
the only isolation requirement for TNV-1 is a dielectric test of 1000
VRMS to user-contractible points and/or 1500 VRMS to hand-held
items. In other words, if his design meets the 1500 VRMS isolation
requirement called out in 802.3, it will also meet the TNV-1 isolation
requirement in IEC 60950.
Now I know that the TNV-1 requirements in IEC 60950 are expanded in the
UL/CSA version to cover power cross testing, and the Australian version
uses a higher isolation test. However, I'm not going to get caught
up in these nuances unless Ian tells us these countries are important for
his particular product, *and* that he thinks he has to classify his
Ethernet interface as TNV-1. 

Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com


Be
careful Joe,

There is a UL PAG that says that PoE must be treated as a TNV1, but
overvoltage tests can be waived from Annex NAC. It is a botched PAG
that needs to be fixed for other reasons. Also if it crosses the
boundary between buildings it needs to be treated as TNV-1 even for
international safety standards which may impose creepage and Clearance
distances.

Also people forget there can be a lot of current coming from a shared PoE
DC supply and eventhough safety requirement creepage and clearances
do not apply between the high and low voltage rails it is good to impose
separation so you don’t have a fire.

Jim

Jim
Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com



From: Joe Randolph
[mailto:j...@randolph-telecom.com]

Sent: Monday, November 26, 2012 1:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances

Hi Ian:
I think the short answer to your question is that under 60950 there are
no requirements for creepage and clearance distance between the Ethernet
circuit and ordinary SELV circuits that are user-contactable. This
is because under 60950, Ethernet is classified as an SELV circuit.
There are no requirements to separate one SELV circuit from
another.
Where this issue becomes confusing is that under the Ethernet 802.3
standard, an Ethernet port must provide a 1500 VRMS isolation barrier
between the Ethernet conductors and earth. This is a legacy
requirement whose origins seem to have been lost in the sands of
time. However, I believe the consensus view is that the original
intent of this requirement was to protect against ground loops and was
not related to user safety. Nevertheless, the 802.3 isolation
requirement has sometimes been treated as though it is a safety
requirement. Note that the 802.3 requirement is for a simple
dielectric test, with no reference to creepage, clearance, or distance
through solid insulation.
So, in principle, there are no safety isolation requirements for your
application, since both of the proposed power supplies have a SELV
output. This makes the entire device a SELV circuit (unless there
are other ports on the device that are not SELV).


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j

Re: [PSES] POE creepage clearances

2012-11-26 Thread Ralph . McDiarmid
The external DC power supply needs to be SELV too, not just energy 
limited.
___ 


Ralph McDiarmid  |   Schneider Electric   |  Solar Business  |   CANADA  | 
  Regulatory Compliance Engineering




From:
Ron Pickard rpick...@equinoxpayments.com
To:
EMC-PSTC@LISTSERV.IEEE.ORG, 
Date:
11/26/2012 12:38 PM
Subject:
Re: [PSES] POE creepage  clearances



Hi Joe,
I agree that an Ethernet circuit would be considered to be an SELV circuit 
and that would be true if the POE circuit were completely on premise 
generally, which would categorize this as a Class III product according to 
IEC/UL 60950-1 2nd Ed. given that the external power supply is a limited 
power source (LPS). However, TNV-1 creepage/clearance requirements would 
apply if the POE were to be exposed to overvoltages from telecommunication 
networks (essentially off premise) requiring Basic insulation. I make this 
distinction as Ian did not mention where the POE circuit originates.
 
Best regards,
 
Ron
 
From: Joe Randolph [mailto:j...@randolph-telecom.com] 
Sent: Monday, November 26, 2012 12:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances
 
Hi Ian:

I think the short answer to your question is that under 60950 there are no 
requirements for creepage and clearance distance between the Ethernet 
circuit and ordinary SELV circuits that are user-contactable.  This is 
because under 60950, Ethernet is classified as an SELV circuit.  There are 
no requirements to separate one SELV circuit from another.

Where this issue becomes confusing is that under the Ethernet 802.3 
standard, an Ethernet port must provide a 1500 VRMS isolation barrier 
between the Ethernet conductors and earth.  This is a legacy requirement 
whose origins seem to have been lost in the sands of time.  However, I 
believe the consensus view is that the original intent of this requirement 
was to protect against ground loops and was not related to user safety. 
Nevertheless, the 802.3 isolation requirement has sometimes been treated 
as though it is a safety requirement.  Note that the 802.3 requirement is 
for a simple dielectric test, with no reference to creepage, clearance, or 
distance through solid insulation.

So, in principle, there are no safety isolation requirements for your 
application, since both of the proposed power supplies have a SELV output. 
 This makes the entire device a SELV circuit (unless there are other ports 
on the device that are not SELV).




Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com





Dear colleagues
 
We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum internal 
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements 
between the ?primary? Ethernet circuit and the ?secondary? circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am 
assuming a safety isolation creepage  clearance is required.
 
Many thanks in advance;
 
Ian McBurney
Design Engineer
 
Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom
 
+44 (0)1326 370121

ian.mcbur...@dmh-global.com
www.allen-heath.com
A DMH Pro Company.
 
-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org 

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in 
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net 
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org 
David Heald dhe...@gmail.com 
-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in 
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators

Re: [PSES] POE creepage clearances

2012-11-26 Thread Ron Pickard
Hi Ralph,
Thanks for pointing that out, but I didn't think I had to mention that since 
Ian had already noted it being +12Vdc.

Best regards,

Ron

From: ralph.mcdiar...@schneider-electric.com 
[mailto:ralph.mcdiar...@schneider-electric.com]
Sent: Monday, November 26, 2012 5:22 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances

The external DC power supply needs to be SELV too, not just energy limited.
___

Ralph McDiarmid  |   Schneider Electric   |  Solar Business  |   CANADA  |   
Regulatory Compliance Engineering


From:

Ron Pickard rpick...@equinoxpayments.commailto:rpick...@equinoxpayments.com

To:

EMC-PSTC@LISTSERV.IEEE.ORGmailto:EMC-PSTC@LISTSERV.IEEE.ORG,

Date:

11/26/2012 12:38 PM

Subject:

Re: [PSES] POE creepage  clearances






Hi Joe,
I agree that an Ethernet circuit would be considered to be an SELV circuit and 
that would be true if the POE circuit were completely on premise generally, 
which would categorize this as a Class III product according to IEC/UL 60950-1 
2nd Ed. given that the external power supply is a limited power source (LPS). 
However, TNV-1 creepage/clearance requirements would apply if the POE were to 
be exposed to overvoltages from telecommunication networks (essentially off 
premise) requiring Basic insulation. I make this distinction as Ian did not 
mention where the POE circuit originates.

Best regards,

Ron

From: Joe Randolph [mailto:j...@randolph-telecom.com]
Sent: Monday, November 26, 2012 12:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORGmailto:EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances

Hi Ian:

I think the short answer to your question is that under 60950 there are no 
requirements for creepage and clearance distance between the Ethernet circuit 
and ordinary SELV circuits that are user-contactable.  This is because under 
60950, Ethernet is classified as an SELV circuit.  There are no requirements to 
separate one SELV circuit from another.

Where this issue becomes confusing is that under the Ethernet 802.3 standard, 
an Ethernet port must provide a 1500 VRMS isolation barrier between the 
Ethernet conductors and earth.  This is a legacy requirement whose origins seem 
to have been lost in the sands of time.  However, I believe the consensus view 
is that the original intent of this requirement was to protect against ground 
loops and was not related to user safety.  Nevertheless, the 802.3 isolation 
requirement has sometimes been treated as though it is a safety requirement.  
Note that the 802.3 requirement is for a simple dielectric test, with no 
reference to creepage, clearance, or distance through solid insulation.

So, in principle, there are no safety isolation requirements for your 
application, since both of the proposed power supplies have a SELV output.  
This makes the entire device a SELV circuit (unless there are other ports on 
the device that are not SELV).




Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.commailto:j...@randolph-telecom.com
http://www.randolph-telecom.comhttp://www.randolph-telecom.com/





Dear colleagues

We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum internal 
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements between the 
?primary? Ethernet circuit and the ?secondary? circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am assuming 
a safety isolation creepage  clearance is required.

Many thanks in advance;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.commailto:ian.mcbur...@dmh-global.com
www.allen-heath.comhttp://www.allen-heath.com/
A DMH Pro Companyhttp://www.dmh-global.com/.

-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.netmailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.orgmailto:j.bac...@ieee.org
David Heald

Re: [PSES] POE creepage clearances

2012-11-26 Thread Bill Owsley
SELV is 60 vdc but not if outdoor or wet environment - right ???
Then it drops to 30 vdc?
So Ethernet is inside only for easy compliance ??
Maybe one can extend the inside environment to an outside application by 
careful use and implementation of conduit and enclosures...
We get lazy and apply the creepage and clearance and keep moving.
ps. I am not a safety engineer and have no clue...
I suspect that the 1500 v isolation came from a single fault introduced at the 
PoE injector that tied primary to secondary and thus the PoE device needed to 
also have the isolation to withstand that fault.
Add up how many isolation transformers are in the circuits back to primary 
and/or TNV-1.




 From: ralph.mcdiar...@schneider-electric.com 
ralph.mcdiar...@schneider-electric.com
To: EMC-PSTC@LISTSERV.IEEE.ORG 
Sent: Monday, November 26, 2012 7:21 PM
Subject: Re: [PSES] POE creepage  clearances
 

The external DC power supply needs to be
SELV too, not just energy limited.
___

Ralph McDiarmid  |  Schneider Electric   |  Solar
Business  |   CANADA  |   Regulatory
Compliance Engineering
 



From:  Ron Pickard rpick...@equinoxpayments.com  
To:  EMC-PSTC@LISTSERV.IEEE.ORG,   
Date:  11/26/2012 12:38 PM  
Subject:  Re: [PSES] POE creepage  clearances 

 


Hi Joe, 
I agree that an Ethernet circuit would
be considered to be an SELV circuit and that would be true if the POE circuit
were completely on premise generally, which would categorize this as a
Class III product according to IEC/UL 60950-1 2nd Ed. given
that the external power supply is a limited power source (LPS). However,
TNV-1 creepage/clearance requirements would apply if the POE were to be
exposed to overvoltages from telecommunication networks (essentially off
premise) requiring Basic insulation. I make this distinction as Ian did
not mention where the POE circuit originates. 
  
Best regards, 
  
Ron 
  
From: Joe Randolph [mailto:j...@randolph-telecom.com] 
Sent: Monday, November 26, 2012 12:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances 
  
Hi Ian:

I think the short answer to your question is that under 60950 there are
no requirements for creepage and clearance distance between the Ethernet
circuit and ordinary SELV circuits that are user-contactable.  This
is because under 60950, Ethernet is classified as an SELV circuit.  There
are no requirements to separate one SELV circuit from another.

Where this issue becomes confusing is that under the Ethernet 802.3 standard,
an Ethernet port must provide a 1500 VRMS isolation barrier between the
Ethernet conductors and earth.  This is a legacy requirement whose
origins seem to have been lost in the sands of time.  However, I believe
the consensus view is that the original intent of this requirement was
to protect against ground loops and was not related to user safety.  
Nevertheless,
the 802.3 isolation requirement has sometimes been treated as though it
is a safety requirement.  Note that the 802.3 requirement is for a
simple dielectric test, with no reference to creepage, clearance, or distance
through solid insulation.

So, in principle, there are no safety isolation requirements for your 
application,
since both of the proposed power supplies have a SELV output.  This
makes the entire device a SELV circuit (unless there are other ports on
the device that are not SELV).




Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com




 
Dear colleagues

We are developing a hand held product that is powered from +48V DC over
Ethernet or from an external +12V DC wall wart PSU. The maximum internal
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements between
the ?primary? Ethernet circuit and the ?secondary? circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am assuming
a safety isolation creepage  clearance is required.

Many thanks in advance;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.com
www.allen-heath.com
A
DMH Pro Company.

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site
at http://product-compliance.oc.ieee.org/can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org

Re: [PSES] POE creepage clearances

2012-11-26 Thread Richard Nute
Gentlemen:


Please recall that Ethernet is isolated from the sender/receiver
circuits at each end of the Ethernet circuit (where the isolation
in the equipment usually is a part of the Ethernet RJ45 connector).

The isolation is 1500 V rms.  Why?  Because building transients
magnetically couple into the Ethernet cable within the building
wiring.

Consider two buildings.  The NEC requires the neutral to be
grounded at each building service entrance.  Therefore, the
neutral is grounded at two points, which places the ground
in parallel with the neutral, and, VOILA! the ground between
the two buildings is a current-carrying conductor.  Isolation
from ground is required because, otherwise, the Ethernet
conductors would be in parallel with the ground and would
become a third current carrying conductor between the two
buildings.  And would quickly open due to the current.

As I understand POE...

http://hw-server.com/images/supply_diagram.png

POE is a common-mode circuit between two Ethernet
pair conductors.  As shown in the diagram, the powered
device must have a DC-DC converter which is isolated
from ground (again, 1500 V RMS).

http://www.poweroverethernet.com/associated/files/file_334_1114621476.pdf

POE is a maximum 48 V DC.  This circuit comprises SELV
between poles, and a Limited Current Circuit between
each pole and ground.

The Ethernet standards require isolation between:

(1) the Ethernet circuits and the internal equipment circuits
(provided by the RJ45) and

(2) the DC-DC converter input and output (provided by the
equipment).

However, 60950-1 does not require clearance or creepage
across these isolations.


Best regards,
Rich



-Original Message- 
From: Bill Owsley
Sent: Monday, November 26, 2012 5:48 PM
To: ralph.mcdiar...@schneider-electric.com ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances


SELV is 60 vdc but not if outdoor or wet environment - right ???
Then it drops to 30 vdc?
So Ethernet is inside only for easy compliance ??
Maybe one can extend the inside environment to an outside application by 
careful use and implementation of conduit and enclosures...
We get lazy and apply the creepage and clearance and keep moving.
ps. I am not a safety engineer and have no clue...
I suspect that the 1500 v isolation came from a single fault introduced at 
the PoE injector that tied primary to secondary and thus the PoE device 
needed to also have the isolation to withstand that fault.
Add up how many isolation transformers are in the circuits back to primary 
and/or TNV-1.


From: ralph.mcdiar...@schneider-electric.com 
ralph.mcdiar...@schneider-electric.com
To: EMC-PSTC@LISTSERV.IEEE.ORG
Sent: Monday, November 26, 2012 7:21 PM
Subject: Re: [PSES] POE creepage  clearances



The external DC power supply needs to be SELV too, not just energy limited.
___

Ralph McDiarmid  |   Schneider Electric   |  Solar Business  |   CANADA  | 
Regulatory Compliance Engineering



From:  Ron Pickard rpick...@equinoxpayments.com   To: 
EMC-PSTC@LISTSERV.IEEE.ORG,   Date:  11/26/2012 12:38 PM   Subject:  Re: 
[PSES] POE creepage  clearances



Hi Joe,
I agree that an Ethernet circuit would be considered to be an SELV circuit 
and that would be true if the POE circuit were completely on premise 
generally, which would categorize this as a Class III product according to 
IEC/UL 60950-1 2nd Ed. given that the external power supply is a limited 
power source (LPS). However, TNV-1 creepage/clearance requirements would 
apply if the POE were to be exposed to overvoltages from telecommunication 
networks (essentially off premise) requiring Basic insulation. I make this 
distinction as Ian did not mention where the POE circuit originates.

Best regards,

Ron

From: Joe Randolph [mailto:j...@randolph-telecom.com]
Sent: Monday, November 26, 2012 12:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] POE creepage  clearances

Hi Ian:

I think the short answer to your question is that under 60950 there are no 
requirements for creepage and clearance distance between the Ethernet 
circuit and ordinary SELV circuits that are user-contactable.  This is 
because under 60950, Ethernet is classified as an SELV circuit.  There are 
no requirements to separate one SELV circuit from another.

Where this issue becomes confusing is that under the Ethernet 802.3 
standard, an Ethernet port must provide a 1500 VRMS isolation barrier 
between the Ethernet conductors and earth.  This is a legacy requirement 
whose origins seem to have been lost in the sands of time.  However, I 
believe the consensus view is that the original intent of this requirement 
was to protect against ground loops and was not related to user safety. 
Nevertheless, the 802.3 isolation requirement has sometimes been treated as 
though it is a safety requirement.  Note that the 802.3 requirement is for a 
simple dielectric test, with no reference

[PSES] POE creepage clearances

2012-11-23 Thread Mcburney, Ian
Dear colleagues

We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum internal 
voltage will be the +48V POE.
Can anyone let me know what the creepage and clearance requirements between the 
primary Ethernet circuit and the secondary circuit.
The product will be tested to IEC 60950 or possibly IEC 60065 so I am assuming 
a safety isolation creepage  clearance is required.

Many thanks in advance;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.commailto:ian.mcbur...@dmh-global.com
www.allen-heath.comhttp://www.allen-heath.com/
A DMH Pro Companyhttp://www.dmh-global.com/.


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] POE creepage clearances

2012-11-23 Thread John Woodgate
In message 
7b970d3d82cee74c920c2e6b0d3b837720be4...@sn2prd0610mb358.namprd06.prod.o
utlook.com, dated Fri, 23 Nov 2012, Mcburney, Ian 
ian.mcbur...@dmh-global.com writes:


We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum 
internal voltage will be the +48V POE.


Can anyone let me know what the creepage and clearance requirements 
between the ?primary? Ethernet circuit and the ?secondary? circuit.


Insufficient data. Is the secondary circuit electrically accessible to 
the user?


The product will be tested to IEC 60950 or possibly IEC 60065 so I am 
assuming a safety isolation creepage  clearance is required.


Do you not have those standards (60950-1 and 60065)? You should be 
looking at IEC 62368-1 as well for a new product development.

--
OOO - Own Opinions Only. See www.jmwa.demon.co.uk
The longer it takes to make a point, the more obtuse it proves to be.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] POE creepage clearances

2012-11-23 Thread Mcburney, Ian
Hello John;

The front  rear panel is painted metal. The base  sides are a plastic 
moulding.
So yes; the secondary circuit is electrically accessible to the user as the 
circuit board is mounted to the front panel using metal pillars.

I have not started applying IEC 62368-1 as the testing agency I use has not 
recommend it. Is IEC 62368-1 the preferred option as opposed to IEC 60065 
/60950 with most testing agencies now?

Regards;

Ian McBurney
Design Engineer

Allen  Heath Ltd
Kernick Industrial Estate
Penryn, Cornwall
TR10 9LU
United Kingdom

+44 (0)1326 370121

ian.mcbur...@dmh-global.com
www.allen-heath.com
A DMH Pro Company.

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John Woodgate
Sent: 23 November 2012 11:40
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: POE creepage  clearances

In message
7b970d3d82cee74c920c2e6b0d3b837720be4...@sn2prd0610mb358.namprd06.prod.o
utlook.com, dated Fri, 23 Nov 2012, Mcburney, Ian 
ian.mcbur...@dmh-global.com writes:

We are developing a hand held product that is powered from +48V DC over 
Ethernet or from an external +12V DC wall wart PSU. The maximum 
internal voltage will be the +48V POE.

Can anyone let me know what the creepage and clearance requirements 
between the ?primary? Ethernet circuit and the ?secondary? circuit.

Insufficient data. Is the secondary circuit electrically accessible to the user?

The product will be tested to IEC 60950 or possibly IEC 60065 so I am 
assuming a safety isolation creepage  clearance is required.

Do you not have those standards (60950-1 and 60065)? You should be looking at 
IEC 62368-1 as well for a new product development.
--
OOO - Own Opinions Only. See www.jmwa.demon.co.uk The longer it takes to make a 
point, the more obtuse it proves to be.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] POE creepage clearances

2012-11-23 Thread John Woodgate
In message 
7b970d3d82cee74c920c2e6b0d3b837720be5...@sn2prd0610mb358.namprd06.prod.o
utlook.com, dated Fri, 23 Nov 2012, Mcburney, Ian 
ian.mcbur...@dmh-global.com writes:


I have not started applying IEC 62368-1 as the testing agency I use has 
not recommend it. Is IEC 62368-1 the preferred option as opposed to IEC 
60065 /60950 with most testing agencies now?


For new designs, IEC/EN 62368-1 may come into mandatory effect before 
the end-of-life of your product. It is huge, and very different from the 
standards it will replace, so your designers and safety experts need to 
begin to get up to speed on it long before it becomes mandatory.


I just don't understand how you can work without having copies of the 
standards you need to apply. There are now ways of getting them without 
paying hundreds of pounds but it isn't wise to discuss that too much on 
a public mailing list.

--
OOO - Own Opinions Only. See www.jmwa.demon.co.uk
The longer it takes to make a point, the more obtuse it proves to be.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com