Re: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-18 Thread Art Michael

Hello Andrew, et al;

World Electricity Supplies which has been referenced in this thread is
available from the Int'l Product Safety Bookshop which can be found on the
Safety Link at:

www.safetylink.com/bookshop.html

Regards, Art Michael
--


On Fri, 18 Jan 2002, Andrew Carson wrote:

 
 Peter
 
 The star distribution with the center point neutral runs from the
 distribution grid substation to the facility. So the utility company
 provides the consumer with the four wires, which they then distribute
 as  required.
 
 In a residential area, the three phases are split every third house,
 providing each residence with a single phase and a neutral. The logic
 here is that if one phase fails, the whole street is not plunged into
 darkness.
 
 A very good handbook I recommend is World Electricity Supplies
 published by BSi Standards. Covers all the worlds distribution voltages
 up to 22kV grid level.  Plus shows you what phase configuration is used
 by the generator to distribute the power.
 
 Peter Tarver wrote:
 
  Andrew -
 
  Please clarify something for me.  Is the utility
  distribution star configured (WYE connected), rather than
  DELTA?  Or are you speaking only wrt typical distribution
  within a building?  (In the US, distribution is generally
  used to reference utility power distribution, for instance,
  distribution transformer, as opposed to facility
  transformer.)
 
  I ask because DELTA is used by utilities in the US and
  Canada to simplify connections save the unnecessary cost of
  running a Neutral (star reference point conductor) between
  distribution transformers (or so it was 'splained to me,
  Lucy).
 
  Regards,
 
  Peter L. Tarver, PE
  Product Safety Manager
  Sanmina-SCI Homologation Services
  peter.tar...@sanmina-sci.com
 
   From: Andrew Carson
  
   Terry
  
   Then nominal EU phase to phase voltage is 400VAC
   with a +6/-10% Tolerance. Distribution is Three
   Phase Star, Earthed Neutral.
  
   Snip 
  
   Andrew Carson - Senior Compliance Engineer, Xyratex, UK
   Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014
 
 --
 
 Andrew Carson - Senior Compliance Engineer, Xyratex, UK
 Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old 
 messages are imported into the new server.
 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-18 Thread Andrew Carson
John is correct, the official UK voltage is 230/400VAC. Just what comes
out the wall socket is not necessarily the same. Those strange tolerance
limits of of 230 +6%/-10% were carefully chosen so the European
suppliers could meet the harmonized level without having to make many
chances.

Crabb, John wrote:

  Just to clarify the position in the UK, although it was stated
 belowthat the nominal voltage is 415V, I am almost certain that the
 DECLAREDVOLTAGE is 400V. I base this on the fact that domestic
 consumerswere advised that the declared voltage changed from 240V to
 230V, and 230 X 1.732 = 400V, and my 1996 BSI World Electricity
 Suppliesshows the UK voltage (and the Italy voltage) to be
 400/230V.In practice, the voltage didn't change - we went from 240 +/-
 6%= 225.6 - 254.4, to 230 -6%/+10% = 216.2 - 253, and the old
 voltagefits within the window of the new voltage, if you accept that
 253 and254.4 are near enough the same.Regards,John Crabb, Development
 Excellence (Product Safety) ,
 NCR  Financial Solutions Group Ltd.,  Discovery Centre, 3 Fulton Road,
 Dundee, Scotland, DD2 4SW
 E-Mail :john.cr...@scotland.ncr.com
 Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.
 VoicePlus  6-341-2289.

  -Original Message-
  From: Paolo Gemma [mailto:paolo.ge...@icn.siemens.it]
  Sent: 17 January 2002 17:56
  To: acar...@uk.xyratex.com
  Cc: emc-p...@majordomo.ieee.org
  Subject: Re: What about 480 VAC in Europe? RE: 2 Phases in
  North America

  Also Italy have a nominal phase to phase of 380VAC.
  Ciao
  Paolo
  At 11:20 1/17/02 +, Andrew Carson wrote:


  Terry
 
  Then nominal EU phase to phase voltage is 400VAC with a
  +6/-10% Tolerance. Distribution is Three Phase Star,
  Earthed Neutral.
 
  Some countries are still a little behind in the voltage
  harmonization e.g.. Belgium is a nominal 380VAC. Other
  have not
  changed as they fall within the tolerance limits already,
  e.g. the UK is a nominal 415VAC
 
  Generally with switch mode supplies, provided your
  incoming wiring feed is changed to take into account the
  Star and not
  Delta, configuration. They can accommodate the voltage
  difference.
 
  Terry Meck wrote:
 
   High all:
  
   I have been away form the forum,  very busy, and a quick
  review notes you have been discussing Power distribution
  in USA.
  
   What about Europe?  We have an application needing 480
  VAC here in USA.
   How compatible will 480 VAC be in Europe?
   Someone told me 390 VAC is more real in Europe. !?!
   How do you see this 480 VAC being impacted by the EN
  61000-3-3 harmonic standard?
  
   Thanks for any input in advance!
  
   Best regards,
   Terry J. Meck
   Senior Compliance/Test Engineer
   tjm...@accusort.com
  

--

Andrew Carson - Senior Compliance Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



Re: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-18 Thread Andrew Carson

Peter

The star distribution with the center point neutral runs from the
distribution grid substation to the facility. So the utility company
provides the consumer with the four wires, which they then distribute
as  required.

In a residential area, the three phases are split every third house,
providing each residence with a single phase and a neutral. The logic
here is that if one phase fails, the whole street is not plunged into
darkness.

A very good handbook I recommend is World Electricity Supplies
published by BSi Standards. Covers all the worlds distribution voltages
up to 22kV grid level.  Plus shows you what phase configuration is used
by the generator to distribute the power.

Peter Tarver wrote:

 Andrew -

 Please clarify something for me.  Is the utility
 distribution star configured (WYE connected), rather than
 DELTA?  Or are you speaking only wrt typical distribution
 within a building?  (In the US, distribution is generally
 used to reference utility power distribution, for instance,
 distribution transformer, as opposed to facility
 transformer.)

 I ask because DELTA is used by utilities in the US and
 Canada to simplify connections save the unnecessary cost of
 running a Neutral (star reference point conductor) between
 distribution transformers (or so it was 'splained to me,
 Lucy).

 Regards,

 Peter L. Tarver, PE
 Product Safety Manager
 Sanmina-SCI Homologation Services
 peter.tar...@sanmina-sci.com

  From: Andrew Carson
 
  Terry
 
  Then nominal EU phase to phase voltage is 400VAC
  with a +6/-10% Tolerance. Distribution is Three
  Phase Star, Earthed Neutral.
 
  Snip 
 
  Andrew Carson - Senior Compliance Engineer, Xyratex, UK
  Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014

--

Andrew Carson - Senior Compliance Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-18 Thread Crabb, John
Just to clarify the position in the UK, although it was stated below
that the nominal voltage is 415V, I am almost certain that the DECLARED
VOLTAGE is 400V. I base this on the fact that domestic consumers
were advised that the declared voltage changed from 240V to 230V, 
and 230 X 1.732 = 400V, and my 1996 BSI World Electricity Supplies
shows the UK voltage (and the Italy voltage) to be 400/230V.
 
In practice, the voltage didn't change - we went from 240 +/- 6%
= 225.6 - 254.4, to 230 -6%/+10% = 216.2 - 253, and the old voltage
fits within the window of the new voltage, if you accept that 253 and
254.4 are near enough the same.
 
Regards,
John Crabb, Development Excellence (Product Safety) , 
NCR  Financial Solutions Group Ltd.,  Discovery Centre, 3 Fulton Road,
Dundee, Scotland, DD2 4SW 
E-Mail :john.cr...@scotland.ncr.com 
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.   VoicePlus
6-341-2289. 

-Original Message-
From: Paolo Gemma [mailto:paolo.ge...@icn.siemens.it]
Sent: 17 January 2002 17:56
To: acar...@uk.xyratex.com
Cc: emc-p...@majordomo.ieee.org
Subject: Re: What about 480 VAC in Europe? RE: 2 Phases in North America


Also Italy have a nominal phase to phase of 380VAC.
Ciao
Paolo
At 11:20 1/17/02 +, Andrew Carson wrote:



Terry

Then nominal EU phase to phase voltage is 400VAC with a +6/-10% Tolerance.
Distribution is Three Phase Star, Earthed Neutral.

Some countries are still a little behind in the voltage harmonization e.g..
Belgium is a nominal 380VAC. Other have not
changed as they fall within the tolerance limits already, e.g. the UK is a
nominal 415VAC

Generally with switch mode supplies, provided your incoming wiring feed is
changed to take into account the Star and not
Delta, configuration. They can accommodate the voltage difference.

Terry Meck wrote:

 High all:

 I have been away form the forum,  very busy, and a quick review notes you
have been discussing Power distribution in USA.

 What about Europe?  We have an application needing 480 VAC here in USA.
 How compatible will 480 VAC be in Europe?
 Someone told me 390 VAC is more real in Europe. !?!
 How do you see this 480 VAC being impacted by the EN 61000-3-3 harmonic
standard?

 Thanks for any input in advance!

 Best regards,
 Terry J. Meck
 Senior Compliance/Test Engineer
 tjm...@accusort.com





Re: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-18 Thread Paolo Gemma

Also Italy have a nominal phase to phase of 380VAC.
Ciao
Paolo
At 11:20 1/17/02 +, Andrew Carson wrote:


Terry

Then nominal EU phase to phase voltage is 400VAC with a +6/-10% Tolerance. 
Distribution is Three Phase Star, Earthed Neutral.


Some countries are still a little behind in the voltage harmonization 
e.g.. Belgium is a nominal 380VAC. Other have not
changed as they fall within the tolerance limits already, e.g. the UK is a 
nominal 415VAC


Generally with switch mode supplies, provided your incoming wiring feed is 
changed to take into account the Star and not

Delta, configuration. They can accommodate the voltage difference.

Terry Meck wrote:

 High all:

 I have been away form the forum,  very busy, and a quick review notes 
you have been discussing Power distribution in USA.


 What about Europe?  We have an application needing 480 VAC here in USA.
 How compatible will 480 VAC be in Europe?
 Someone told me 390 VAC is more real in Europe. !?!
 How do you see this 480 VAC being impacted by the EN 61000-3-3 harmonic 
standard?


 Thanks for any input in advance!

 Best regards,
 Terry J. Meck
 Senior Compliance/Test Engineer
 tjm...@accusort.com

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old 
messages are imported into the new server.


--

Andrew Carson - Senior Compliance Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



--
Paolo Gemma
Siemens Information and Communication Network spa
Microwave Networks MW RD NSA EMC
SS Padana sup. KM 158 20060 Cassina de'Pecchi (MI) Italy
phone +39 02 9526 6587fax +39 02 9526 6203
mobile +39 348 3690185
e-mail paolo.ge...@icn.siemens.it

--



RE: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-17 Thread Peter Tarver

Andrew -

Please clarify something for me.  Is the utility
distribution star configured (WYE connected), rather than
DELTA?  Or are you speaking only wrt typical distribution
within a building?  (In the US, distribution is generally
used to reference utility power distribution, for instance,
distribution transformer, as opposed to facility
transformer.)

I ask because DELTA is used by utilities in the US and
Canada to simplify connections save the unnecessary cost of
running a Neutral (star reference point conductor) between
distribution transformers (or so it was 'splained to me,
Lucy).


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
peter.tar...@sanmina-sci.com


 From: Andrew Carson

 Terry

 Then nominal EU phase to phase voltage is 400VAC
 with a +6/-10% Tolerance. Distribution is Three
 Phase Star, Earthed Neutral.

 Snip 

 Andrew Carson - Senior Compliance Engineer, Xyratex, UK
 Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-17 Thread Andrew Carson

Terry

Then nominal EU phase to phase voltage is 400VAC with a +6/-10% Tolerance. 
Distribution is Three Phase Star, Earthed Neutral.

Some countries are still a little behind in the voltage harmonization e.g.. 
Belgium is a nominal 380VAC. Other have not
changed as they fall within the tolerance limits already, e.g. the UK is a 
nominal 415VAC

Generally with switch mode supplies, provided your incoming wiring feed is 
changed to take into account the Star and not
Delta, configuration. They can accommodate the voltage difference.

Terry Meck wrote:

 High all:

 I have been away form the forum,  very busy, and a quick review notes you 
 have been discussing Power distribution in USA.

 What about Europe?  We have an application needing 480 VAC here in USA.
 How compatible will 480 VAC be in Europe?
 Someone told me 390 VAC is more real in Europe. !?!
 How do you see this 480 VAC being impacted by the EN 61000-3-3 harmonic 
 standard?

 Thanks for any input in advance!

 Best regards,
 Terry J. Meck
 Senior Compliance/Test Engineer
 tjm...@accusort.com

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old 
 messages are imported into the new server.

--

Andrew Carson - Senior Compliance Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-16 Thread Terry Meck

High all:

I have been away form the forum,  very busy, and a quick review notes you have 
been discussing Power distribution in USA.

What about Europe?  We have an application needing 480 VAC here in USA.
How compatible will 480 VAC be in Europe?  
Someone told me 390 VAC is more real in Europe. !?!
How do you see this 480 VAC being impacted by the EN 61000-3-3 harmonic 
standard?

Thanks for any input in advance!


Best regards,
Terry J. Meck
Senior Compliance/Test Engineer
tjm...@accusort.com



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Harmonics, WAS: 2 Phases in North America

2001-12-18 Thread John Woodgate

I read in !emc-pstc that Hans Mellberg emcconsult...@yahoo.com wrote
(in 20011218072701.24359.qm...@web13003.mail.yahoo.com) about
'Harmonics, WAS: 2 Phases in North America', on Mon, 17 Dec 2001:
A harmonic frequency does NOT imply a multiplier of, but one that
sympathetically resonates with the fundamental.

Harmonics are integer multiples; it is overtones that are defined in
terms of resonances. In many mechanical systems, overtones are not exact
harmonic frequencies.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Harmonics, WAS: 2 Phases in North America

2001-12-18 Thread Hans Mellberg

If one uses the analogies from tuning forks, then it should be obvious. The 
first
harmonic or the fundamental, is the the first sympathetic resonance of the 
adjacent
tuning fork which happens to be the fundamental. And, it so happens that by
definitions the first harmonic IS the fundamental. It is not usually referred 
to as
by the order of; It simply is the first, second, third etc harmonic of the
fundamental. A harmonic frequency does NOT imply a multiplier of, but one that
sympathetically resonates with the fundamental.


=
Best Regards
Hans Mellberg
Regulatory Compliance  EMC Design Services Consultant
By the Pacific Coast next to Silicon Valley,
Santa Cruz, CA, USA
408-507-9694

__
Do You Yahoo!?
Check out Yahoo! Shopping and Yahoo! Auctions for all of
your unique holiday gifts! Buy at http://shopping.yahoo.com
or bid at http://auctions.yahoo.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread Ken Javor

As you are well aware, the physics behind acoustics and electromagnetics are
very similar.  The term overtone definitely has an acoustic pedigree,
whereas the term harmonic has been adopted by electrical engineering.  But
the 1st overtone explicitly contains the info that we are talking about a
component at a higher frequency than the fundamental.  The term harmonic
simply means that the various components are related to each other by ratios
of whole numbers, including the number one.  The fundamental is the first
harmonic.  The second harmonic is the first overtone.  This seems eminently
sensible, intuitively appealing, and as I said previously, these are
accepted definitions going back decades in my experience, but likely
hundreds of years.  Should not be a topic involving lengthy debate.

--
From: bogdan matoga bogda...@pacbell.net
To: Ken Javor ken.ja...@emccompliance.com
Cc: Cortland Richmond 72146@compuserve.com, ieee pstc list
emc-p...@ieee.org
Subject: Re: 2 Phases in North America
Date: Mon, Dec 17, 2001, 1:44 PM


 Ken:
 I think that you did not miss too much - my Physics 101 however was over 50
 years ago and harmonics were only
 mentioned in acoustics! Now, who wins?
 Greetings,
 Bogdan.

 Ken Javor wrote:

 I haven't been following this train but my recollection of definitions from
 Physics 101 more than a quarter century ago is that the fundamental is the
 first harmonic.  The first overtone is the second harmonic.  These are/were
 accepted definitions.

 --
 From: Cortland Richmond 72146@compuserve.com
 To: bogdan matoga bogda...@pacbell.net, ieee pstc list emc-p...@ieee.org
 Subject: Re: 2 Phases in North America
 Date: Mon, Dec 17, 2001, 12:04 AM
 

 
  If we're smart (are we?) we'll say fundamental, and let whoever wants to
  argue what 2nd means have the arena all to themselves!
 
  I would say there are harmonics of the second order, third order, and so
  on, to which we refer, in short, as the second and third harmonics (and so
  on). Don't forget, though, where the terms came from; what IS harmonic
  motion, hmm?
 
  Cortland
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Michael Garretson:pstc_ad...@garretson.org
   Dave Healddavehe...@mediaone.net
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
  All emc-pstc postings are archived and searchable on the web at:
  No longer online until our new server is brought online and the old
  messages are imported into the new server.
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.


 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread Cortland Richmond

John Shinn wrote:

 If we refer back to the series, and refer to the n-th term, we
 would all be on the same page (and harmonic).

And in harmony!

Cortland

(disclaimer: my views, not Alcatel's!)





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 2 Phases in North America

2001-12-17 Thread John Shinn

This whole issue boils down to semantics and how we count and use numbers.
The first issue is what is a harmonic.  A harmonic is a multiple of the
fundamental.

This can be seen when we look at the Fourier series:

V(t) = a(0) + a(1)sin(wt) + a(2)sin(wt) + a(3)sin(wt) + ...

where a(n) is the magnitude of the n-th term in the series
and w is angular frequency (radians/sec)

Then the 0-th term would represent any DC component present,
the 1-th (or 1-st) would represent the fundamental,
and the 2-th (or 2-nd) would represent 2 times the fundamental, or
the second harmonic, etc.

If we refer back to the series, and refer to the n-th term, we
would all be on the same page (and harmonic).

John Shinn, P.E.




-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of
lfresea...@aol.com
Sent: Monday, December 17, 2001 7:52 AM
To: mhopk...@thermokeytek.com; bogda...@pacbell.net;
cortland.richm...@alcatel.com
Cc: r...@canoga.com; john...@itesafety.com; bar...@melbpc.org.au;
emc-p...@majordomo.ieee.org
Subject: Re: 2 Phases in North America



Mike,

I don't go with you on this one...

0 implies nothing ( prehaps 0 ac )  ... therefore the 0th harmonic is
dc???

if a squarewave is made up of odd harmonics, we would have to rethink
that,
correct?

Derek.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread bogdan matoga

Ken:
I think that you did not miss too much - my Physics 101 however was over 50 
years ago and harmonics were only
mentioned in acoustics! Now, who wins?
Greetings,
Bogdan.

Ken Javor wrote:

 I haven't been following this train but my recollection of definitions from
 Physics 101 more than a quarter century ago is that the fundamental is the
 first harmonic.  The first overtone is the second harmonic.  These are/were
 accepted definitions.

 --
 From: Cortland Richmond 72146@compuserve.com
 To: bogdan matoga bogda...@pacbell.net, ieee pstc list emc-p...@ieee.org
 Subject: Re: 2 Phases in North America
 Date: Mon, Dec 17, 2001, 12:04 AM
 

 
  If we're smart (are we?) we'll say fundamental, and let whoever wants to
  argue what 2nd means have the arena all to themselves!
 
  I would say there are harmonics of the second order, third order, and so
  on, to which we refer, in short, as the second and third harmonics (and so
  on). Don't forget, though, where the terms came from; what IS harmonic
  motion, hmm?
 
  Cortland
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Michael Garretson:pstc_ad...@garretson.org
   Dave Healddavehe...@mediaone.net
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
  All emc-pstc postings are archived and searchable on the web at:
  No longer online until our new server is brought online and the old
  messages are imported into the new server.
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old 
 messages are imported into the new server.




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread bogdan matoga

Gentlemen:
I certainly did not intend to start philosophical contortions!
Season's greetings and a harmonic(*) New Year!
Bogdan.
(*) Now what will this start

lfresea...@aol.com wrote:

 Mike,

 I don't go with you on this one...

 0 implies nothing ( prehaps 0 ac )  ... therefore the 0th harmonic is
 dc???

 if a squarewave is made up of odd harmonics, we would have to rethink that,
 correct?

 Derek.




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread John Woodgate

I read in !emc-pstc that lfresea...@aol.com wrote (in 169.5d0f58e.294f6
e...@aol.com) about '2 Phases in North America', on Mon, 17 Dec 2001:
0 implies nothing ( prehaps 0 ac )  ... therefore the 0th harmonic is 
dc???

That fits with Fourier analysis.

if a squarewave is made up of odd harmonics, we would have to rethink that, 
correct?

Indeed.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread Cortland Richmond

I can see that this subject hasn't fazed ANYONE.

Cortland
(speaking, as usual, for myself - and not my
employer)



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 2 Phases in North America

2001-12-17 Thread Wagner, John P (John)
Electric utilities genreate and distribute 3 phase power.  At the load,
then, some power conversion strategy is employed to derive 2 phase
power.  For instance, by adding a secondary winging on a 3 phase
transformer on phases A and B with 47% of the winding on phase A and 53%
on phase B, the resultant is a voltage lagging phase A by 90 degrees.
The turns ratio between primary and secondary is adjusted to get the
desired secondary voltage on the new phase.

This is essentially what capacitor start single phase motors do --
temporarily derive a phase approximately 90 degreees from the single
phase, so that there is some rotational torque for starting.  Once
running, this is no longer necessary and the start winding drops out.
On a 2 phase motor, the second phase remains in the circuit.

John P. Wagner
Regulatory Compliance  Mandatory Standards
AVAYA Strategic Standards.
1300 W. 120th Ave, Room B3-D16
Phone/Fax: (303) 538-4241
johnwag...@avaya.com





 --
 From: Hans Mellberg[SMTP:emcconsult...@yahoo.com]
 Reply To: Hans Mellberg
 Sent: Saturday, December 15, 2001 11:00 AM
 To:   Cortland Richmond; bogda...@pacbell.net
 Cc:   Robert Johnson; 'Barry Esmore'; 'EMC-PSTC Forum'
 Subject:  Re: 2 Phases in North America
 
 
 ok folks. This topic needs to be clarified.
 
 With respect to each other, by definition, two conductors have a
 potential
 difference at 180 degrees. Period. The 90 degree stuff may pertain to
 current but
 not to voltage. You would need a four-phase transformer to get 90
 degree phasing and
 simply it does not exist. Voltage, is usually measured: wrt ground,
 wrt other
 reference conductor such as neutral or wrt to another voltage (hot)
 conductor. In
 some cases, the voltage difference between ground and two other
 conductors may be
 120/240 degrees such as in a three phase system. So, no matter how you
 measure
 voltage it will either be at 120, 180 or 240 degrees wrt to some other
 conductor. 
 
 In the US there have been many systems of low voltage (staying below
 480V)distribution yielding the following voltages:
 
 480/240/120 
 480/208/120 from three three phase
 480/230/115 single split phase
 230/115 single split phase motor control voltage
 220/110 single split phase older home voltages
 208/120 from three phase
 480/277 (for fluorescent lighting) 
 117 (where did this come from? seen in many older HP instruments)
 Open Delta (3, 4 or 5 wire, when one is grounded into neutral its
 called a
 stinger)
 Split phase (three or four wire)
 Y (four and five wire)
 
 Hope this stirrs the pot
 
 
 =
 Best Regards
 Hans Mellberg
 Regulatory Compliance  EMC Design Services Consultant
 By the Pacific Coast next to Silicon Valley,
 Santa Cruz, CA, USA
 408-507-9694
 
 __
 Do You Yahoo!?
 Check out Yahoo! Shopping and Yahoo! Auctions for all of
 your unique holiday gifts! Buy at http://shopping.yahoo.com
 or bid at http://auctions.yahoo.com
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the
 old messages are imported into the new server.
 


RE: 2 Phases in North America

2001-12-17 Thread Peter Tarver

Failed on the first try.  Let's try again.

Peter

 -Original Message-
 From: Peter Tarver [mailto:peter.tar...@sanmina.com]
 Sent: Friday, December 14, 2001 8:57 AM
 To: 'EMC-PSTC Forum'
 Cc: 'Barry Esmore'
 Subject: RE: 2 Phases in North America
 
 
 This is a recurring topic.
 
 While referred to generally as single-phase, 
 two phases, as Bob Johnson indicated, are present 
 in most homes.  This is also called split-phase.
 
 I make to representation about the products this 
 company sells, but there is a depiction of this 
 power arrangement at
 
 http://www.itvss.com/pdf/spliti.pdf
 
 on the first page of the Adobe Acrobat document 
 (though only one winding of the three-phase, 
 delta connected transformer is shown).
 
 Regards,
 
 Peter L. Tarver, PE
 Product Safety Manager
 Sanmina Homologation Services
 peter.tar...@sanmina.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread Ken Javor

I haven't been following this train but my recollection of definitions from
Physics 101 more than a quarter century ago is that the fundamental is the
first harmonic.  The first overtone is the second harmonic.  These are/were
accepted definitions.

--
From: Cortland Richmond 72146@compuserve.com
To: bogdan matoga bogda...@pacbell.net, ieee pstc list emc-p...@ieee.org
Subject: Re: 2 Phases in North America
Date: Mon, Dec 17, 2001, 12:04 AM



 If we're smart (are we?) we'll say fundamental, and let whoever wants to
 argue what 2nd means have the arena all to themselves!

 I would say there are harmonics of the second order, third order, and so
 on, to which we refer, in short, as the second and third harmonics (and so
 on). Don't forget, though, where the terms came from; what IS harmonic
 motion, hmm?

 Cortland

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread Lfresearch

Mike,

I don't go with you on this one...

0 implies nothing ( prehaps 0 ac )  ... therefore the 0th harmonic is 
dc???

if a squarewave is made up of odd harmonics, we would have to rethink that, 
correct?

Derek.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 2 Phases in North America

2001-12-17 Thread Mike Hopkins

This could be interesting::; if 50/60 is the 0th, then 100/120 would be the
1st ?? Makes sense to me!! No harmonics of the fundamental frequency would
be the 0th; and 1st harmonic would be at twice the fundamental
frequency.

(I know this is not the convention, but it seems logical: first harmonic is
fundamental plus the fundamental (once); second is the fundamental plus the
fundamental x 2, etc. ). I like it!

Mike Hopkins
Thermo KeyTek


-Original Message-
From: bogdan matoga [mailto:bogda...@pacbell.net]
Sent: Sunday, December 16, 2001 8:03 PM
To: Cortland Richmond
Cc: Jayasinghe, Ryan; Robert Johnson; 'Barry Esmore'; 'EMC-PSTC Forum'
Subject: Re: 2 Phases in North America



Cortland:
I always thought that 50 Hz or respectively 60 Hz was the 0-th harmonic!
Was
I mistaken? (I would not be surprised!) (: -) !!
Bogdan.

Cortland Richmond wrote:

 This is rather similar to asking what the first harmonic of the power line
 frequency is.  (grin!)

 Cortland

 Jayasinghe, Ryan wrote:

  180° out of phase?
 




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 2 Phases in North America

2001-12-17 Thread Crabb, John
Bill - you absolutely correct in describing the North American system as 
single-phase, 3 wire. After all, that is how it is described in Annex V,
Figure V.4 of IEC60950:1999 - and there is NO WAY that IEC TC74
could be wrong, is there ? (especially since the US committee must
have voted yes, to include this change, the purpose of which was to
educate those of us who weren't too clear on the subject).
 
Fortunately I am on holiday (vacation) from tonight until January 3,
so to all our readers, best wishes for the Christmas season, and a 
happy and prosperous 2002.
John Crabb, Development Excellence (Product Safety) , 
NCR  Financial Solutions Group Ltd.,  Kingsway West, Dundee, Scotland. DD2
3XX 
E-Mail :john.cr...@scotland.ncr.com 
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.   VoicePlus
6-341-2289. 

-Original Message-
From: Bill Lawrence [mailto:wlawr...@capecod.net]
Sent: 14 December 2001 22:33
To: 'Wagner, John P (John)'; 'Robert Johnson'; 'Cortland Richmond'
Cc: 'Barry Esmore'; 'EMC-PSTC Forum'
Subject: RE: 2 Phases in North America


Two Phase / 5 Wire (4 hots and a neutral) was a common power distribution
in US cities in the early part of this century.  Many early motors are
2-phase motors.  I learned about this when helping with connection of
these motors to run on a 3 phase power system via a special Scott-T
transformer connection.
 
The correct designation for the 120/240 power system described is Single
Phase / 3 Wire.
 
Bill Lawrence



Re: 2 Phases in North America

2001-12-17 Thread Cortland Richmond

If we're smart (are we?) we'll say fundamental, and let whoever wants to
argue what 2nd means have the arena all to themselves!

I would say there are harmonics of the second order, third order, and so
on, to which we refer, in short, as the second and third harmonics (and so
on). Don't forget, though, where the terms came from; what IS harmonic
motion, hmm?

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-17 Thread bogdan matoga

Cortland:
I always thought that 50 Hz or respectively 60 Hz was the 0-th harmonic! Was
I mistaken? (I would not be surprised!) (: -) !!
Bogdan.

Cortland Richmond wrote:

 This is rather similar to asking what the first harmonic of the power line
 frequency is.  (grin!)

 Cortland

 Jayasinghe, Ryan wrote:

  180° out of phase?
 




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-15 Thread Hans Mellberg

ok folks. This topic needs to be clarified.

With respect to each other, by definition, two conductors have a potential
difference at 180 degrees. Period. The 90 degree stuff may pertain to current 
but
not to voltage. You would need a four-phase transformer to get 90 degree 
phasing and
simply it does not exist. Voltage, is usually measured: wrt ground, wrt other
reference conductor such as neutral or wrt to another voltage (hot) conductor. 
In
some cases, the voltage difference between ground and two other conductors may 
be
120/240 degrees such as in a three phase system. So, no matter how you measure
voltage it will either be at 120, 180 or 240 degrees wrt to some other 
conductor. 

In the US there have been many systems of low voltage (staying below
480V)distribution yielding the following voltages:

480/240/120 
480/208/120 from three three phase
480/230/115 single split phase
230/115 single split phase motor control voltage
220/110 single split phase older home voltages
208/120 from three phase
480/277 (for fluorescent lighting) 
117 (where did this come from? seen in many older HP instruments)
Open Delta (3, 4 or 5 wire, when one is grounded into neutral its called a
stinger)
Split phase (three or four wire)
Y (four and five wire)

Hope this stirrs the pot


=
Best Regards
Hans Mellberg
Regulatory Compliance  EMC Design Services Consultant
By the Pacific Coast next to Silicon Valley,
Santa Cruz, CA, USA
408-507-9694

__
Do You Yahoo!?
Check out Yahoo! Shopping and Yahoo! Auctions for all of
your unique holiday gifts! Buy at http://shopping.yahoo.com
or bid at http://auctions.yahoo.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 2 Phases in North America

2001-12-15 Thread Brent DeWitt
Hi all,

Even though I am an electrical engineer, I'm terribly confused by this post.
I have always believed (and on a few occasions measured) the standard US
home system feed.  There is no choice of 240 volts.  The 220 volt feed
used by larger devices is two 118 VAC phases 120 degrees apart.  The math
seems to work.

WRT Cortland's post, I guess I don't see ground (or close to it neutral)
as having a phase.  If that is believable, then a single phase system is
not so hard to believe.

Just a few thoughts,

Brent DeWitt
  -Original Message-
  From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of bogdan matoga
  Sent: Friday, December 14, 2001 3:12 PM
  To: Cortland Richmond
  Cc: Robert Johnson; 'Barry Esmore'; 'EMC-PSTC Forum'
  Subject: Re: 2 Phases in North America


  Dear Esquire:
  May I suggest that you partake in a course called Basic Electricity 001?
  Bogdan.
  Cortland Richmond wrote:

 By the definition below, *single phase* AC would require one wire with
no return.  I want to see THAT one work before I pay for it!
Cortland Richmond
(the above being my own opinion, not a statement of my employer's)

Robert Johnson wrote:

  This has just reopened the old two phase controversy again. Ed has
done a good job of describing the systems in detail, but be careful with the
terms.
  Ask an electrical engineer about a 120/240 volt home service and he
will call it a two phase system. Two phases 180 degrees out of phase is
technically correct.
--- This message is from the
IEEE EMC Society Product Safety Technical Committee emc-pstc discussion
list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To
cancel your subscription, send mail to: majord...@ieee.org with the single
line: unsubscribe emc-pstc For help, send mail to the list administrators:
Michael Garretson: pstc_ad...@garretson.org Dave Heald
davehe...@mediaone.net For policy questions, send mail to: Richard Nute:
ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are
archived and searchable on the web at: No longer online until our new server
is brought online and the old messages are imported into the new server.



Re: 2 Phases in North America

2001-12-15 Thread Cortland Richmond

This is rather similar to asking what the first harmonic of the power line
frequency is.  (grin!)

Cortland

Jayasinghe, Ryan wrote:

 180° out of phase?



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-15 Thread John Woodgate

I read in !emc-pstc that Price, Ed ed.pr...@cubic.com wrote (in
b78135310217d511907c0090273f5190d0b...@curly.ds.cubic.com) about '2
Phases in North America', on Thu, 13 Dec 2001:
At this point, you still have a single-phase system. The voltage is 
240 Vrms, from one hot line to the other. The voltage from each 
hot line to neutral (and ground) is 120 Vrms. 

Well, you can also look at it as a two-phase system with 180 degrees
between phases. But since the load is very rarely balanced, so the
neutral is normally a current-carrying conductor, it doesn't really meet
the criteria of a poly-phase system.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 2 Phases in North America

2001-12-14 Thread Cortland Richmond

Should have put a (grin) symbol in that.

I've always understood two phase to mean a
distribution system using three wires, one common,
with two conductors  whose phase differed by 90
degrees. These were used, I believe, mainly for
motors. I think this is what the original question
was asking for.

Cheers!

Cortland

bogdan matoga wrote:

 Dear Esquire:
 May I suggest that you partake in a course called
 Basic Electricity 001?
 Bogdan.

 Cortland Richmond wrote:

  By the definition below, *single phase* AC
 would require one wire with no return.  I want
 to see THAT one work before I pay for it!

 Cortland Richmond
 (the above being my own opinion, not a statement
 of my employer's)



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 2 Phases in North America

2001-12-14 Thread Bill Lawrence
RE: 2 Phases in North AmericaTwo Phase / 5 Wire (4 hots and a neutral) was
a common power distribution in US cities in the early part of this century.
Many early motors are 2-phase motors.  I learned about this when helping
with connection of these motors to run on a 3 phase power system via a
special Scott-T transformer connection.

The correct designation for the 120/240 power system described is Single
Phase / 3 Wire.

Bill Lawrence
  -Original Message-
  From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Wagner, John P (John)
  Sent: Friday, December 14, 2001 3:14 PM
  To: Robert Johnson; Cortland Richmond
  Cc: Barry Esmore; EMC-PSTC Forum
  Subject: RE: 2 Phases in North America


  Actually, 2 phase systems have a phase rotation of 90 degrees, not 180.
Two phase systems have been used for control motors and the like, but are
fairly rare these days.  180 degree rotation between phases is a center
tapped single phase system.  The proper terminology is, I believe, split
phase.

  John P. Wagner
  Regulatory Compliance  Mandatory Standards
  AVAYA Strategic Standards.
  1300 W. 120th Ave, Room B3-D16
  Phone/Fax: (303) 538-4241
  johnwag...@avaya.com






--
From:   Cortland Richmond[SMTP:cortland.richm...@alcatel.com]
Reply To:   Cortland Richmond
Sent:   Friday, December 14, 2001 10:38 AM
To: Robert Johnson
Cc: 'Barry Esmore'; 'EMC-PSTC Forum'
Subject:Re: 2 Phases in North America

By the definition below, *single phase* AC would require one wire with
no return.  I want to see THAT one work before I pay for it!

Cortland Richmond
(the above being my own opinion, not a statement of my employer's)

Robert Johnson wrote:

  This has just reopened the old two phase controversy again. Ed has
done a good job of describing the systems in detail, but be careful with the
terms.

  Ask an electrical engineer about a 120/240 volt home service and he
will call it a two phase system. Two phases 180 degrees out of phase is
technically correct.

--- This message is from the
IEEE EMC Society Product Safety Technical Committee emc-pstc discussion
list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To
cancel your subscription, send mail to: majord...@ieee.org with the single
line: unsubscribe emc-pstc For help, send mail to the list administrators:
Michael Garretson: pstc_ad...@garretson.org Dave Heald
davehe...@mediaone.net For policy questions, send mail to: Richard Nute:
ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are
archived and searchable on the web at: No longer online until our new server
is brought online and the old messages are imported into the new server.

attachment: winmail.dat

Re: 2 Phases in North America

2001-12-14 Thread bogdan matoga
Dear Esquire:
May I suggest that you partake in a course called Basic Electricity
001?
Bogdan.

Cortland Richmond wrote:

  By the definition below, *single phase* AC would require one wire
 with no return.  I want to see THAT one work before I pay for it!

 Cortland Richmond
 (the above being my own opinion, not a statement of my employer's)

 Robert Johnson wrote:

 This has just reopened the old two phase controversy again. Ed has
 done a good job of describing the systems in detail, but be careful
 with the terms.

 Ask an electrical engineer about a 120/240 volt home service and he
 will call it a two phase system. Two phases 180 degrees out of phase
 is technically correct.

 --- This message is from the
 IEEE EMC Society Product Safety Technical Committee emc-pstc
 discussion list. Visit our web site at:
 http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription,
 send mail to: majord...@ieee.org with the single line: unsubscribe
 emc-pstc For help, send mail to the list administrators: Michael
 Garretson: pstc_ad...@garretson.org Dave Heald davehe...@mediaone.net
 For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim
 Bacher: j.bac...@ieee.org All emc-pstc postings are archived and
 searchable on the web at: No longer online until our new server is
 brought online and the old messages are imported into the new server.




RE: 2 Phases in North America

2001-12-14 Thread Wagner, John P (John)
Actually, 2 phase systems have a phase rotation of 90 degrees, not 180.
Two phase systems have been used for control motors and the like, but
are fairly rare these days.  180 degree rotation between phases is a
center tapped single phase system.  The proper terminology is, I
believe, split phase.
John P. Wagner
Regulatory Compliance  Mandatory Standards
AVAYA Strategic Standards.
1300 W. 120th Ave, Room B3-D16
Phone/Fax: (303) 538-4241
johnwag...@avaya.com





 --
 From: Cortland Richmond[SMTP:cortland.richm...@alcatel.com]
 Reply To: Cortland Richmond
 Sent: Friday, December 14, 2001 10:38 AM
 To:   Robert Johnson
 Cc:   'Barry Esmore'; 'EMC-PSTC Forum'
 Subject:  Re: 2 Phases in North America
 
 By the definition below, *single phase* AC would require one wire with
 no return.  I want to see THAT one work before I pay for it! 
 
 Cortland Richmond 
 (the above being my own opinion, not a statement of my employer's) 
 
 Robert Johnson wrote: 
 
   This has just reopened the old two phase controversy again. Ed
 has done a good job of describing the systems in detail, but be
 careful with the terms.
 
   Ask an electrical engineer about a 120/240 volt home service and
 he will call it a two phase system. Two phases 180 degrees out of
 phase is technically correct.
 
 --- This message is from the
 IEEE EMC Society Product Safety Technical Committee emc-pstc
 discussion list. Visit our web site at:
 http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription,
 send mail to: majord...@ieee.org with the single line: unsubscribe
 emc-pstc For help, send mail to the list administrators: Michael
 Garretson: pstc_ad...@garretson.org Dave Heald davehe...@mediaone.net
 For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim
 Bacher: j.bac...@ieee.org All emc-pstc postings are archived and
 searchable on the web at: No longer online until our new server is
 brought online and the old messages are imported into the new server. 
 


Re: 2 Phases in North America

2001-12-14 Thread Cortland Richmond




By the definition below, *single phase* AC would require one wire with
no return. I want to see THAT one work before I pay for it!
Cortland Richmond
(the above being my own opinion, not a statement of my employer's)
Robert Johnson wrote:

This
has just reopened the old two phase controversy again. Ed has done a good
job of describing the systems in detail, but be careful with the terms.




Ask
an electrical engineer about a 120/240 volt home service and he will call
it a two phase system. Two phases 180 degrees out of phase is technically
correct.







---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old messages are imported into the new server.


RE: 2 Phases in North America

2001-12-14 Thread Robert Johnson
This has just reopened the old two phase controversy again. Ed has done
a good job of describing the systems in detail, but be careful with the
terms.
Ask an electrical engineer about a 120/240 volt home service and he will
call it a two phase system. Two phases 180 degrees out of phase is
technically correct.
Ask an electrician and he will tell you the only way to get two phases
is to start with three phases and leave one out (and will also tell you
the engineer is nuts). He is talking about two phases 120 degrees apart.
The electrician will use two phases to either save copper or
transformers, and allow for future expansion.
There is a pretty important distinction, since you can regenerate the
third phase (although inefficiently) using transformers on the 120
degree case, but not with the 180 degree case.
The three phase rotation is of course crucial for rotating machinery.
For single phase or the 180 degree case, you need to generate starting
torque using capacitors to delay a phase.
As a result, you should just avoid the use of the term two phase. Talk
about a 120/240 volt center tapped service, or two phases of a 120/208
volt three phase service.
 
In answer to your original question, I would say essentially 100% of
homes, and most of the businesses or buildings serving up to about 10
employees will have the 120/240 volt center tapped service (distributing
120 v single phase 3 wire to most prewired locations). Most businesses
larger than that will receive a 120/208 volt three phase service (or a
higher voltage three phase service), again distributing 120 v single
phase 3 wire to most locations (using privately owned step down
transformers if needed). Approximately 40% of homes (the older ones)
and a few older business buildings will have 120 v single phase 2 wire
(no ground) instead of 3 wire wiring in the building.
 
There are of course some small businesses (e.g. a photoprocessing lab or
small machine shop) which require three phase service and likewise some
rather large businesses (like offices) which can get by on single phase
service. It depends on history and location. I, for example, have three
phase available in my home shop generated by a rotary phase converter,
because it is several miles to commercial three phase service (and also
a more expensive monthly connection fee).
 
The next question is, if choosing a feed for a product, what should you
pick? My simplified North American recommendation would be:
Up to 2500 W, stick with single phase 120 v. (Up to 16 amps for standard
receptacles, up to 24 amps for dedicated receptacles)
Up to 5 KW try for single phase which will work on either 240 or 208
volts. (allowing connection to either 120/240 V center tapped or 120/208
V three phase services).
Up to 25 KW aim for 120/208 three phase service, but you may want to
offer a 277/480 V option.
Above 25 KW you probably need to offer multiple options or make custom
arrangements with customers based on available service. 277/480 V is the
next common service in use.
For rotating machinery, you probably need to consider three phase as
soon as you go above 1 or 2 horsepower (1 KW)
For home products, consider Class II products to comfortably serve most
customers with 2 wire receptacles.
 
Bob Johnson
ITE Safety
 
-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Price, Ed
Sent: Thursday, December 13, 2001 8:23 PM
To: 'Barry Esmore'; EMC-PSTC Forum
Subject: RE: 2 Phases in North America
 
 
-Original Message-
From: Barry Esmore [mailto:bar...@melbpc.org.au]
Sent: Thursday, December 13, 2001 2:39 PM
To: EMC-PSTC Forum
Subject: 2 Phases in North America
Hi All,
 
Can someone provide an estimate of the percentage of homes and
businesses that have 2 phases in Canada and the USA? Also, what is the
most common voltage between phases?
 
Thanks and regards
Barry Esmore
 
AUS-TICK
281 Lawrence Rd
Mt Waverley
Vic  3149
Australia
 
Ph: + 61 3 9886 1345
Fax: + 61 3 9884 7272 
 
 
Barry:
 
 
AFIK, just about zero percent of USA homes have two-phase power. Heavy
industrial will have a 3-phase delta feed, and light industrial and
commercial will have a 3-phase wye feed.
 
However, homes are usually fed by a three-wire system. A transformer
changes a single-phase, two-wire distribution feed (about 12 kV) to a
center-tapped, 240 Vrms output. One transformer often serves about 10-20
homes. The center-tap is grounded, and the three output wires are routed
pole-to-pole. Each individual customer (home) has a three-wire feeder
cable (called a drop) connected from a junction on the pole to a
power-panel on the house. At the house power-panel, the neutral wire is
again grounded. Each 240 Vrms line-to-line is routed through a power
meter and then to a bank of circuit breakers.
 
At this point, you still have a single-phase system. The voltage is 240
Vrms, from one hot line to the other. The voltage from each hot line
to neutral (and ground) is 120

RE: 2 Phases in North America

2001-12-14 Thread Price, Ed
 

-Original Message-
From: Barry Esmore [mailto:bar...@melbpc.org.au]
Sent: Thursday, December 13, 2001 2:39 PM
To: EMC-PSTC Forum
Subject: 2 Phases in North America


Hi All,
 
Can someone provide an estimate of the percentage of homes and businesses
that have 2 phases in Canada and the USA? Also, what is the most common
voltage between phases?
 
Thanks and regards
Barry Esmore
 
AUS-TICK
281 Lawrence Rd
Mt Waverley
Vic  3149
Australia
 
Ph: + 61 3 9886 1345
Fax: + 61 3 9884 7272 
 

 
Barry:
 
 
AFIK, just about zero percent of USA homes have two-phase power. Heavy
industrial will have a 3-phase delta feed, and light industrial and
commercial will have a 3-phase wye feed.
 
However, homes are usually fed by a three-wire system. A transformer changes
a single-phase, two-wire distribution feed (about 12 kV) to a center-tapped,
240 Vrms output. One transformer often serves about 10-20 homes. The
center-tap is grounded, and the three output wires are routed pole-to-pole.
Each individual customer (home) has a three-wire feeder cable (called a
drop) connected from a junction on the pole to a power-panel on the house.
At the house power-panel, the neutral wire is again grounded. Each 240 Vrms
line-to-line is routed through a power meter and then to a bank of circuit
breakers.
 
At this point, you still have a single-phase system. The voltage is 240
Vrms, from one hot line to the other. The voltage from each hot line to
neutral (and ground) is 120 Vrms. Small loads (lights, outlets) are
connected from one hot to the neutral (with an attempt by the electrician to
balance the expected power draw). Heavy loads (water heater, clothes dryer,
air conditioning, heating and cooking) are connected from one hot to the
other hot line.
 
The typical three-wire electrical outlet in a USA home has a hot, a
neutral, and a safety ground connection. The hot-to-neutral is 120 Vrms,
the hot-to-safety ground is also 120 Vrms, and the neutral-to-safety ground
is supposed to be zero Vrms (but often is a half-volt or so). Power flows in
the hot-to-neutral circuit, and must not be routed into the safety ground.
 
Much older homes may have a two-wire outlet, with a safety ground attached
to the outlet box. If you have (typically) an appliance that needs a safety
ground, the consumer is expected to make the ground to the box with an
adapter and a pig-tail wire to the cover-plate screw! This is usually
ignored by the consumer.
 
Regards,
 
Ed
 

Ed Price 
ed.pr...@cubic.com 
Electromagnetic Compatibility Lab 
Cubic Defense Systems 
San Diego, CA  USA 
858-505-2780  (Voice) 
858-505-1583  (Fax) 
Military  Avionics EMC Services Is Our Specialty 
Shake-Bake-Shock - Metrology - Reliability Analysis  



2 Phases in North America

2001-12-13 Thread Barry Esmore
Hi All,

Can someone provide an estimate of the percentage of homes and businesses that 
have 2 phases in Canada and the USA? Also, what is the most common voltage 
between phases?

Thanks and regards
Barry Esmore

AUS-TICK
281 Lawrence Rd
Mt Waverley
Vic  3149
Australia

Ph: + 61 3 9886 1345
Fax: + 61 3 9884 7272