Re: current carrying conductors

2001-08-18 Thread Rich Nute




Hi Richard:


A number of good comments have been made.

I'm not sure anyone covered the fact that
two wires make a bundle, and therefore each
single in that bundle must be derated.

So, a single 10 AWG is good for 32 amps at
20 C.  But, two 10 AWG wires in the same 
bundle are only good for 31 amps each at 20 C.

Here's a caculator that might be of interest,
but use cautiously as the calculator may not
apply to your situation:

http://www.geocities.com/CapeCanaveral/Lab/9643/awg.htm


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: current carrying conductors

2001-08-18 Thread Doug McKean

According to the Belden wire table, 10awg carrying 
32 amps will produce a 35C rise above ambient. And 
according to them, the bundling factor is 1.0 for 1, 2, 
or 3 bundled wires.  If you're qualifying anything up 
around 40C high temp, your wire's going to be 75C.  

5C doesn't give you much overhead for 80C rated 
wire.  So, you might want to think long and hard about 
using 80C rated wire for such an application.  IMO, you'd 
have to start with a minimum 105C rated wire. 

8awg at 32 amps looks more like 23C rise above ambient. 

- Doug McKean 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




RE: current carrying conductors

2001-08-17 Thread Scott Lacey

Richard,

The larger single wire, with appropriate ring lug, is actually the preferred
construction. The two wire method is used in cases where something else in
the system, such as a multi-wire connector, will only accept the smaller
gauge wire. In that case each ring lug MUST be secured with its own star
washer and nut. The stack up would be:

Ring lug #1, star washer, nut, ring lug #2, star washer, nut.

The screw or stud must be long enough for the top nut to have full thread
engagement.

Hope this is of help.
Scott Lacey

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Stone, Richard A
(Richard)
Sent: Friday, August 17, 2001 9:01 AM
To: emc-p...@majordomo.ieee.org
Subject: current carrying conductors



Group,

can you substitute one large wire 6 awg. ( handlles 63 amps. max )
for two smaller wires ( 10 awg. carries 32 amps. max. )  in Parallel.
They would 1/2 the current and disperse heat better.

The accepting screw terminal would allow for proper threading and tightness
of connection.
since you would have 2 ring lugs on one terninal instead of two.

thank you,
Richard,

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




RE: current carrying conductors

2001-08-17 Thread Peter Tarver

Yes.

Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina Homologation Services
peter.tar...@sanmina.com

 -Original Message-
 From: owner-emc-p...@majordomo.ieee.org
 [mailto:owner-emc-p...@majordomo.ieee.org]On 
 Behalf Of Stone, Richard A
 (Richard)
 
 Group,
 
 can you substitute one large wire 6 awg. ( 
 handlles 63 amps. max )
 for two smaller wires ( 10 awg. carries 32 amps. 
 max. )  in Parallel.
 They would 1/2 the current and disperse heat better.
 
 The accepting screw terminal would allow for 
 proper threading and tightness
 of connection.
 since you would have 2 ring lugs on one terninal 
 instead of two.
 
 thank you,
 Richard,
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: current carrying conductors

2001-08-17 Thread Andrew Carson

As a quick and simple answer, No. In a single fault condition, one cable
becomes lose / detached. The reaming 32 amp capable see the full 63 amps. The
result smoke, flame, etc.
Expressly forbidden in some standards and knocked out by others under the
single fault conditions.

Only way to do this is to fuse each cable individually to 32 amps. Then it
might be allowed depending on the exact configuration of the circuit.




Stone, Richard A (Richard) wrote:

 Group,

 can you substitute one large wire 6 awg. ( handlles 63 amps. max )
 for two smaller wires ( 10 awg. carries 32 amps. max. )  in Parallel.
 They would 1/2 the current and disperse heat better.

 The accepting screw terminal would allow for proper threading and tightness
 of connection.
 since you would have 2 ring lugs on one terninal instead of two.

 thank you,
 Richard,

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://www.rcic.com/  click on Virtual Conference Hall,

--

Andrew Carson - Product Safety Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: current carrying conductors

2001-08-17 Thread SERGIO LUIZ DA ROCHA LOURES SERGIO

What happen, if one of these wire looses?

Sérgio Rocha Loures
Siemens Ltda. - Brazil
Supply Chain - Quality and Engineering
IC SC QE L
Tel:  +55 41 341-5755
Fax: +55 41 341-5058
E-mail: sergioro...@siemens.com.br

 Stone, Richard A (Richard) rsto...@lucent.com 17/08/01 10:01 

Group,

can you substitute one large wire 6 awg. ( handlles 63 amps. max )
for two smaller wires ( 10 awg. carries 32 amps. max. )  in Parallel.
They would 1/2 the current and disperse heat better.

The accepting screw terminal would allow for proper threading and tightness
of connection.
since you would have 2 ring lugs on one terninal instead of two.

thank you,
Richard,

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




current carrying conductors

2001-08-17 Thread Stone, Richard A (Richard)

Group,

can you substitute one large wire 6 awg. ( handlles 63 amps. max )
for two smaller wires ( 10 awg. carries 32 amps. max. )  in Parallel.
They would 1/2 the current and disperse heat better.

The accepting screw terminal would allow for proper threading and tightness
of connection.
since you would have 2 ring lugs on one terninal instead of two.

thank you,
Richard,

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,