Hi Peter,
thanks for you reply.

 Its hard to tell with motor specifications, sometimes they are RMS and 
 sometimes they are DC (for example lots of large BLDC motors are rated 320V
 which actually means they are 220V AC motors)

I see. I'll stick with 24 V for now, the power supply is a 350 W unit.

 1. initial rotor alignment (if wrong you will have different torque each 
 direction)

I think this is OK, as the motors spin smooth and nice in both directions.

 2. Make sure the deadtime is set to 0

It is set to 0 (line 207 of the hal ini: http://restweiss.de/bldc_1.zip).

 3. Make sure the PWM rate is set fairly high so you dont get current limiting
 from ripple current (40KHz is good for 7I39s)

PWM frequency (is that PWM rate) is set to 20 kHz, but I tried 40 kHz
and it makes no difference.

 4. Make sure you have the 7I39 current limit set to 15A and not 7.5A

Current is limited (still default setting) but I don't think this is the
problem. Using a clampmeter I measure 600 mA max. at stall.

 5. If you have problems at high speeds, consider running LinuxCNC master and 
 raising the servo thread rate as high as you can (good MBs can do 4 KHz or 
 better) (linuxcnc master has a patch to BLDC than extrapolates the 
 commutation 
 angle base on velocity so approximately halves the commutation angle
 error at high speeds)

Oh, that's cool feature, but I only need very low speeds - so no need to
switch I guess.


What's next to investigate?

Greetings
Flo

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Florian Rist
Hi Andy,
I decided to put the system on my desk to investigate the case, this
took a while.

 How are you commutating?

The present configuration is 'qh'(use encoder input, use hall sensor
input). I didn't override the default commutation setting, so I think
its sinusoidal.

Here are my config fies: http://restweiss.de/bldc_1.zip

See you
Flo

PS: The set-up, a three rope system: http://restweiss.de/loop_1.jpg

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Peter C. Wallace
On Sat, 29 Mar 2014, Florian Rist wrote:

 Date: Sat, 29 Mar 2014 23:02:03 +0100
 From: Florian Rist fr...@fs.tum.de
 Reply-To: Enhanced Machine Controller (EMC)
 emc-users@lists.sourceforge.net
 To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net
 Subject: Re: [Emc-users] BLDC Servo Torque Problem?
 
 Hi Peter,
 thanks for you reply.

 Its hard to tell with motor specifications, sometimes they are RMS and
 sometimes they are DC (for example lots of large BLDC motors are rated 320V
 which actually means they are 220V AC motors)

 I see. I'll stick with 24 V for now, the power supply is a 350 W unit.

 1. initial rotor alignment (if wrong you will have different torque each
 direction)

 I think this is OK, as the motors spin smooth and nice in both directions.

 2. Make sure the deadtime is set to 0

 It is set to 0 (line 207 of the hal ini: http://restweiss.de/bldc_1.zip).

 3. Make sure the PWM rate is set fairly high so you dont get current limiting
 from ripple current (40KHz is good for 7I39s)

 PWM frequency (is that PWM rate) is set to 20 kHz, but I tried 40 kHz
 and it makes no difference.

 4. Make sure you have the 7I39 current limit set to 15A and not 7.5A

 Current is limited (still default setting) but I don't think this is the
 problem. Using a clampmeter I measure 600 mA max. at stall.


Where did you measure the current? (you may indeed measure 600mA in the power 
leads with current limiting (7.5A) in the driver)
  If you see a red LED light on the 7I39, you have reached the current limit

Another thing to check is that you have not somehow limited the max PWM value 
so you are not getting sufficient drive voltage (PWM does not get near 100% or 
near 0%)


 5. If you have problems at high speeds, consider running LinuxCNC master and
 raising the servo thread rate as high as you can (good MBs can do 4 KHz or
 better) (linuxcnc master has a patch to BLDC than extrapolates the 
 commutation
 angle base on velocity so approximately halves the commutation angle
 error at high speeds)

 Oh, that's cool feature, but I only need very low speeds - so no need to
 switch I guess.


 What's next to investigate?

 Greetings
 Flo

 --
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users


Peter Wallace
Mesa Electronics

(\__/)
(='.'=) This is Bunny. Copy and paste bunny into your
()_() signature to help him gain world domination.


--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Florian Rist
Hi,
an brief update, because my current measurement was wrong.

I now used a normal ampere meter (Flue 87V) and measured a maximum
current of 3.5 A. (I commanded the motor to a position where the phase I
observed was at maximum current under low load and than increased the
load until the motor stalled. I hope this makes sense.)

But still not close to the current limit.

See you
Flo

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Florian Rist
Hi Peter

 Where did you measure the current?

I measured one phase.

 (you may indeed measure 600mA in the power 
 leads with current limiting (7.5A) in the driver)

The 600 mA was mistake, current reaches 3.5 A actually.

 If you see a red LED light on the 7I39, you have reached the current limit

Oh, in deed it dose light up, it flickers a bit, though.

I'll pull the current limit jumper and report back. Thanks.

 Another thing to check is that you have not somehow limited the max PWM value 
 so you are not getting sufficient drive voltage (PWM does not get near 100% 
 or 
 near 0%)

This would be done using hal scope, right? I'll try that.

See you
Flo


--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Andy Pugh


On 29 Mar 2014, at 22:08, Florian Rist fr...@fs.tum.de wrote:

 How are you commutating?
 
 The present configuration is 'qh'(use encoder input, use hall sensor
 input). I didn't override the default commutation setting, so I think
 its sinusoidal.

It is probably worth checking that it works properly in plain h mode as a 
test that the hall pattern is correct. 

But the 600mA at stall looks like the real issue. 
--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Florian Rist
Hi Andy

 It is probably worth checking that it works properly in plain 
 h mode as a test that the hall pattern is correct.

I'll try.

What would be the best setting? The drivers have 3 hall sensors and a
4000 CPR encoder with index.

 But the 600mA at stall looks like the real issue. 

No, this was my mistake, I just took a reading somewhere without
thinking, the correct maximum is 3.5 A.

Greeting
Flo

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread andy pugh
On 29 March 2014 23:17, Florian Rist fr...@fs.tum.de wrote:

 What would be the best setting? The drivers have 3 hall sensors and a
 4000 CPR encoder with index.

qh is almost certainly the best. You could try qhi if, and only if,
you are sure of the index pulse orientation.

-- 
atp
If you can't fix it, you don't own it.
http://www.ifixit.com/Manifesto

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Florian Rist
Hi Peter,

 I'll pull the current limit jumper and report back. Thanks.

OK, now the jumper are moved from left to right and I reached 6 A max.
on one phase. Better. Torque does not feel much stronger though.

And the over current LED still light up. But now the current limit is
protecting the driver.

The drive does not feel very stiff, I can rotate it about 10° maybe 20°
before the maximum current is reached. This is a PID settings issue, right?

See you
Flo

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-29 Thread Florian Rist
Hi Andy

 qh is almost certainly the best. You could try qhi if, and only
 if, you are sure of the index pulse orientation.

I don't know the orientation aka offset, but I tried to measure it, by
observing the index signal, the encoder counter and the hall sensors in
hal scope. I think I got it right but it doesn't help.

See you
Flo



--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-27 Thread andy pugh
On 27 March 2014 17:31, Florian Rist fr...@fs.tum.de wrote:

   Mesa 7i39-LV
   Nanotec DB57L01 + 4000 CPR endoder

How are you commutating?

-- 
atp
If you can't fix it, you don't own it.
http://www.ifixit.com/Manifesto

--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] BLDC Servo Torque Problem?

2014-03-27 Thread Peter C. Wallace
On Thu, 27 Mar 2014, Florian Rist wrote:

 Date: Thu, 27 Mar 2014 18:31:12 +0100
 From: Florian Rist fr...@fs.tum.de
 Reply-To: Enhanced Machine Controller (EMC)
 emc-users@lists.sourceforge.net
 To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net
 Subject: [Emc-users] BLDC Servo Torque Problem?
 
 Hi,
 I have some problems in setting up BLDC servos, I just don't manage to
 get enough torque. Here's the set-up:

  Intel D525MW
  Mesa 5i23
  Mesa 7i39-LV
  Nanotec DB57L01 + 4000 CPR endoder

 The servos are rated 24V DC, 4.6A (peak 17A). My power supply is 24V DC
 SNT rated at 500W.

 I suppose I just don't get the PID settings right, but before
 investigating this a question regarding power supply:

 Is the 24V supply correct? Or do I misread the BLDC data sheet and the
 24V is a  RMS rating?

 cu
 Flo


The 7I39LV is limited to 30VDC max

Its hard to tell with motor specifications, sometimes they are RMS and 
sometimes they are DC (for example lots of large BLDC motors are rated 320V
which actually means they are 220V AC motors)

If you dont have enough torque, a couple things to check are

1. initial rotor alignment (if wrong you will have different torque each 
direction)

2. Make sure the deadtime is set to 0

3. Make sure the PWM rate is set fairly high so you dont get current limiting
from ripple current (40KHz is good for 7I39s)

4. Make sure you have the 7I39 current limit set to 15A and not 7.5A

5. If you have problems at high speeds, consider running LinuxCNC master and 
raising the servo thread rate as high as you can (good MBs can do 4 KHz or 
better)
  (linuxcnc master has a patch to BLDC than extrapolates the commutation angle 
base on velocity so approximately halves the commutation angle error at high 
speeds)


 --
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users


Peter Wallace
Mesa Electronics

(\__/)
(='.'=) This is Bunny. Copy and paste bunny into your
()_() signature to help him gain world domination.


--
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users