Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread dan
Last summer I had to recast a post. A first for me. Some "Battery Expert" installed a bank of Trojans with UT posts using flat cable end terminals, then torqued the b Jesus out of them to try to get them to seat. what happened was they either cracked or totally broke off the terminal at the bolt hole. Borrowed a terminal mold from Babe down at Interstate, and use an old manual soldering iron (the kind you have to heat up with a torch or something) so i had plenty of ummph, but no open flame around the battery. Cleaned and tinned the busted terminal first and then set up the mold. It wasn't pretty, but it worked. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] Battery corrosion issue
From: William Miller <will...@millersolar.com>
Date: Thu, January 21, 2016 4:51 pm
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>

Friends: It’s a clearance bolt hole.  Drill it out and install a new one. William  Lic 773985millersolar.com805-438-5600 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris MasonSent: Thursday, January 21, 2016 11:58 AMTo: RE-wrenchesSubject: Re: [RE-wrenches] Battery corrosion issue There's no need to hit the bolt, just press it out with a pulley puller set for two legs.  On Thu, Jan 21, 2016 at 9:40 AM, Tump <t...@swnl.net> wrote:I personally would try to soak the offending post in a solution of baking soda or some other corrosion remover for a while and then gently tap the bolt on both sides. Continuing to do this will eventually loosen the bolt.This IS a thru bolt not something that is threaded. certainly one can drill it out using the step approach  1/8 " then 3/16 then 1/4 till you  get to 5/16. Gently tapping or drilling you should find this removal easier then you thought. Tump On Jan 20, 2016, at 5:34 PM, Ray Walters wrote:The EZ out is for unscrewing a threaded connection,  I've spent a bunch of time with those only to have the EZ out break off in there too.  Then you've got a real mess of hardened tool steel.I would first drill several small 1/8" holes in the lead around the circumference of the bolt.  Then, I think tapping or pressing it out is the way.   The wheel puller would probably work.  You'll end up with an enlarged hole that you can either use a bigger bolt, or washers to deal with.   I agree some of the hardware that comes with cheaper L 16s, is inferior.  I've had plenty of those square heads come off with minimal torque.R.Ray WaltersCTO, Solarray, IncNabcep Certified PV Installer, Licensed Master ElectricianSolar Design Engineer303 505-8760On 1/20/2016 3:04 PM, Roy Rakobitsch wrote:Yup, id pre-drill and use an ez-out, or use a flaring tool as a small press and drive it out. RoyROn Jan 20, 2016 3:54 PM, "Kristopher Schmid" <sol...@legacysolar.com> wrote:Greetings,Do any of you battery gurus have a suggestion for a method of removing a bolt remnant that is corroded into a flag terminal.  Both sides snapped off flush with the flag.  I was thinking try to drill it out or maybe a small gear pulling tool?  I will never again use the non stainless hardware supplied by the manufacturer...Picture attached for reference.Thanks!___List sponsored by Redwood AllianceList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htmlList rules & etiquette:www.re-wrenches.org/etiquette.htmCheck out or update participant bios:www.members.re-wrenches.org ___List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette:www.re-wrenches.org/etiquette.htm Check out or update participant bios:www.members.re-wrenches.org  ___List sponsored by Redwood AllianceList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htmlList rules & etiquette:www.re-wrenches.org/etiquette.htmCheck out or update participant bios:www.members.re-wrenches.org t...@swnl.net               www.SWNL.net            Solarwinds Northernlights      Serving Mid Coast Maine & Northern California                         207-832-7574   Cl. 610-517-8401                              

Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread William Miller
Friends:



It’s a clearance bolt hole.  Drill it out and install a new one.



William





[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Chris Mason
*Sent:* Thursday, January 21, 2016 11:58 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Battery corrosion issue



There's no need to hit the bolt, just press it out with a pulley puller set
for two legs.



On Thu, Jan 21, 2016 at 9:40 AM, Tump  wrote:

I personally would try to soak the offending post in a solution of baking
soda or some other corrosion remover for a while and then gently tap the
bolt on both sides. Continuing to do this will eventually loosen the
bolt.This IS a thru bolt not something that is threaded. certainly one can
drill it out using the step approach  1/8 " then 3/16 then 1/4 till you
 get to 5/16. Gently tapping or drilling you should find this removal
easier then you thought. Tump



On Jan 20, 2016, at 5:34 PM, Ray Walters wrote:



The EZ out is for unscrewing a threaded connection,  I've spent a bunch of
time with those only to have the EZ out break off in there too.  Then
you've got a real mess of hardened tool steel.

I would first drill several small 1/8" holes in the lead around the
circumference of the bolt.  Then, I think tapping or pressing it out is the
way.   The wheel puller would probably work.  You'll end up with an
enlarged hole that you can either use a bigger bolt, or washers to deal
with.

I agree some of the hardware that comes with cheaper L 16s, is inferior.
I've had plenty of those square heads come off with minimal torque.

R.Ray Walters

CTO, Solarray, Inc

Nabcep Certified PV Installer,

Licensed Master Electrician

Solar Design Engineer

303 505-8760

On 1/20/2016 3:04 PM, Roy Rakobitsch wrote:

Yup, id pre-drill and use an ez-out, or use a flaring tool as a small press
and drive it out.

RoyR

On Jan 20, 2016 3:54 PM, "Kristopher Schmid"  wrote:

Greetings,

Do any of you battery gurus have a suggestion for a method of removing a
bolt remnant that is corroded into a flag terminal.  Both sides snapped off
flush with the flag.  I was thinking try to drill it out or maybe a small
gear pulling tool?  I will never again use the non stainless hardware
supplied by the manufacturer...

Picture attached for reference.

Thanks!


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___

List sponsored by Redwood Alliance



List Address: RE-wrenches@lists.re-wrenches.org



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

www.members.re-wrenches.org





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



*t...@swnl.net *   *www.SWNL.net
<http://www.SWNL.net>*

Solarwinds Northernlights

*   Serving Mid Coast Maine & Northern California*
* 207-832-7574 <207-832-7574>   Cl. 610-517-8401
<610-517-8401>  *

  *Blair "TUMP" May*


*     MAINE'S CHARTER  **
NABCEP"Certified PV Installer"*


*   MAINE'S CHARTER   **
Trace Xantrex "Certified" Dealer / Installer"*








___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread Chris Mason
There's no need to hit the bolt, just press it out with a pulley puller set
for two legs.

On Thu, Jan 21, 2016 at 9:40 AM, Tump  wrote:

> I personally would try to soak the offending post in a solution of baking
> soda or some other corrosion remover for a while and then gently tap the
> bolt on both sides. Continuing to do this will eventually loosen the
> bolt.This IS a thru bolt not something that is threaded. certainly one can
> drill it out using the step approach  1/8 " then 3/16 then 1/4 till you
>  get to 5/16. Gently tapping or drilling you should find this removal
> easier then you thought. Tump
>
> On Jan 20, 2016, at 5:34 PM, Ray Walters wrote:
>
> The EZ out is for unscrewing a threaded connection,  I've spent a bunch of
> time with those only to have the EZ out break off in there too.  Then
> you've got a real mess of hardened tool steel.
>
> I would first drill several small 1/8" holes in the lead around the
> circumference of the bolt.  Then, I think tapping or pressing it out is the
> way.   The wheel puller would probably work.  You'll end up with an
> enlarged hole that you can either use a bigger bolt, or washers to deal
> with.
>
> I agree some of the hardware that comes with cheaper L 16s, is inferior.
> I've had plenty of those square heads come off with minimal torque.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer303 505-8760
>
> On 1/20/2016 3:04 PM, Roy Rakobitsch wrote:
>
> Yup, id pre-drill and use an ez-out, or use a flaring tool as a small
> press and drive it out.
>
> RoyR
> On Jan 20, 2016 3:54 PM, "Kristopher Schmid" 
> wrote:
>
>> Greetings,
>>
>> Do any of you battery gurus have a suggestion for a method of removing a
>> bolt remnant that is corroded into a flag terminal.  Both sides snapped off
>> flush with the flag.  I was thinking try to drill it out or maybe a small
>> gear pulling tool?  I will never again use the non stainless hardware
>> supplied by the manufacturer...
>>
>> Picture attached for reference.
>>
>> Thanks!
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> *t...@swnl.net*   *www.SWNL.net*
> Solarwinds Northernlights
> *   Serving Mid Coast Maine & Northern California*
> * 207-832-7574 <207-832-7574>   Cl. 610-517-8401
> <610-517-8401>  *
>   *Blair "TUMP" May*
>
>
> *     MAINE'S CHARTER  *   *
> NABCEP"Certified PV Installer"*
>
>
> *   MAINE'S CHARTER   **
> Trace Xantrex "Certified" Dealer / Installer"*
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com 
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Ch

Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread Bill Loesch
Has the idea of using some solution of baking soda to minimize the 
existing corrosion has already been suggested?


Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094

On 1/21/2016 9:09 AM, frenergy wrote:
I wonder if by the rounded shape of the flag, Todd's idea might work 
fine with still a significant amount of contact area.



On 1/20/2016 2:02 PM, toddc...@finestplanet.com wrote:


whoops, was that a flag terminal? i looked at it wrong and thought it 
was a post terminal.


todd



On Wednesday, January 20, 2016 2:01pm, toddc...@finestplanet.com said:



On Wednesday, January 20, 2016 1:53pm, "Kristopher Schmid" 
 said:


Greetings,

Do any of you battery gurus have a suggestion for a method of 
removing a bolt remnant that is corroded into a flag terminal.  Both 
sides snapped off flush with the flag.  I was thinking try to drill 
it out or maybe a small gear pulling tool?  I will never again use 
the non stainless hardware supplied by the manufacturer...


Picture attached for reference.

Thanks!




Sent from Finest Planet WebMail.



Sent from Finest Planet WebMail.


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread Luke Christy
I would go with the puller idea. Grab a small gear puller at Napa or Autozone 
and use a large socket or something similar as a spacer on the back side so 
that the puller jaws don't dig into the soft lead.
The challenge may be finding a puller with a small enough bolt to push through 
the terminal hole.

I have also had luck driving out broken bolts with a pin punch. It can get a 
bit dicey though as you have to back up the terminal with something massive to 
absorb the force and keep it from bending and it really requires three hands to 
achieve.

-Luke

NABCEP Certified PV Installation Professional™: Certification #031409-25 
NABCEP Certified Solar Heating Installer™: Certification #ST032611-03 
CoSEIA Certified PV Installer 
 
Solar Gain Services, LLC
PO Box 531
Monte Vista, CO 81144
sgsrenewab...@gmail.com
719.588.3044
www.sgsrenewables.com

> On Jan 20, 2016, at 14:53, Kristopher Schmid  wrote:
> 
> Greetings,
> 
> Do any of you battery gurus have a suggestion for a method of removing a bolt 
> remnant that is corroded into a flag terminal.  Both sides snapped off flush 
> with the flag.  I was thinking try to drill it out or maybe a small gear 
> pulling tool?  I will never again use the non stainless hardware supplied by 
> the manufacturer...
> 
> Picture attached for reference.
> 
> Thanks!
> 
> <_20160120_155125.JPG>
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Battery corrosion issue

2016-01-21 Thread Dana
My first thought was wheel puller with a very small flat file [jewelers
type] worked around the edges first.

 

__

Dana Orzel 

Great Solar Works, Inc -  NABCEP # 051112-136

d...@solarwork.com  - www.solarwork.com 

O - 970.626.5253F - 970.626.4140   c - 208.721.7003

"Responsible Technologies for Responsible People since 1988"  

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Tump
Sent: Thursday, January 21, 2016 6:41 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery corrosion issue

 

I personally would try to soak the offending post in a solution of baking
soda or some other corrosion remover for a while and then gently tap the
bolt on both sides. Continuing to do this will eventually loosen the
bolt.This IS a thru bolt not something that is threaded. certainly one can
drill it out using the step approach  1/8 " then 3/16 then 1/4 till you  get
to 5/16. Gently tapping or drilling you should find this removal easier then
you thought. Tump

On Jan 20, 2016, at 5:34 PM, Ray Walters wrote:





The EZ out is for unscrewing a threaded connection,  I've spent a bunch of
time with those only to have the EZ out break off in there too.  Then you've
got a real mess of hardened tool steel.

I would first drill several small 1/8" holes in the lead around the
circumference of the bolt.  Then, I think tapping or pressing it out is the
way.   The wheel puller would probably work.  You'll end up with an enlarged
hole that you can either use a bigger bolt, or washers to deal with.   

I agree some of the hardware that comes with cheaper L 16s, is inferior.
I've had plenty of those square heads come off with minimal torque.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/20/2016 3:04 PM, Roy Rakobitsch wrote:

Yup, id pre-drill and use an ez-out, or use a flaring tool as a small press
and drive it out. 

RoyR

On Jan 20, 2016 3:54 PM, "Kristopher Schmid"  wrote:

Greetings,

Do any of you battery gurus have a suggestion for a method of removing a
bolt remnant that is corroded into a flag terminal.  Both sides snapped off
flush with the flag.  I was thinking try to drill it out or maybe a small
gear pulling tool?  I will never again use the non stainless hardware
supplied by the manufacturer...

Picture attached for reference.

Thanks!


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 








___
List sponsored by Redwood Alliance
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 
 

 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

 

t...@swnl.net
mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>
http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
www.SWNL.net

Solarwinds Northernlights   

   Serving Mid Coast Maine & Northern California
 207-832-7574   Cl. 610-517-8401


  Blair "TUMP" May

     MAINE'S CHARTER 
  NABCEP"Certified PV Installer" 
   
    MAINE'S CHARTER 
  Trace Xantrex "Certified" Dealer / Installer"

 

 

 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com

Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread frenergy
I wonder if by the rounded shape of the flag, Todd's idea might work 
fine with still a significant amount of contact area.



On 1/20/2016 2:02 PM, toddc...@finestplanet.com wrote:


whoops, was that a flag terminal? i looked at it wrong and thought it 
was a post terminal.


todd



On Wednesday, January 20, 2016 2:01pm, toddc...@finestplanet.com said:



On Wednesday, January 20, 2016 1:53pm, "Kristopher Schmid" 
 said:


Greetings,

Do any of you battery gurus have a suggestion for a method of removing 
a bolt remnant that is corroded into a flag terminal.  Both sides 
snapped off flush with the flag.  I was thinking try to drill it out 
or maybe a small gear pulling tool?  I will never again use the non 
stainless hardware supplied by the manufacturer...


Picture attached for reference.

Thanks!




Sent from Finest Planet WebMail.



Sent from Finest Planet WebMail.


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-21 Thread Tump
I personally would try to soak the offending post in a solution of baking soda 
or some other corrosion remover for a while and then gently tap the bolt on 
both sides. Continuing to do this will eventually loosen the bolt.This IS a 
thru bolt not something that is threaded. certainly one can drill it out using 
the step approach  1/8 " then 3/16 then 1/4 till you  get to 5/16. Gently 
tapping or drilling you should find this removal easier then you thought. Tump
On Jan 20, 2016, at 5:34 PM, Ray Walters wrote:

> The EZ out is for unscrewing a threaded connection,  I've spent a bunch of 
> time with those only to have the EZ out break off in there too.  Then you've 
> got a real mess of hardened tool steel.
> 
> I would first drill several small 1/8" holes in the lead around the 
> circumference of the bolt.  Then, I think tapping or pressing it out is the 
> way.   The wheel puller would probably work.  You'll end up with an enlarged 
> hole that you can either use a bigger bolt, or washers to deal with.   
> 
> I agree some of the hardware that comes with cheaper L 16s, is inferior.  
> I've had plenty of those square heads come off with minimal torque.
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 1/20/2016 3:04 PM, Roy Rakobitsch wrote:
>> Yup, id pre-drill and use an ez-out, or use a flaring tool as a small press 
>> and drive it out.
>> 
>> RoyR
>> 
>> On Jan 20, 2016 3:54 PM, "Kristopher Schmid"  wrote:
>> Greetings,
>> 
>> Do any of you battery gurus have a suggestion for a method of removing a 
>> bolt remnant that is corroded into a flag terminal.  Both sides snapped off 
>> flush with the flag.  I was thinking try to drill it out or maybe a small 
>> gear pulling tool?  I will never again use the non stainless hardware 
>> supplied by the manufacturer...
>> 
>> Picture attached for reference.
>> 
>> Thanks!
>> 
>> 
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> 
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> t...@swnl.net   www.SWNL.net
> Solarwinds Northernlights   
>Serving Mid Coast Maine & Northern California
>  207-832-7574   Cl. 610-517-8401  
> 
>   Blair "TUMP" May
>  MAINE'S CHARTER 
>   NABCEP"Certified PV Installer" 
>
>     MAINE'S CHARTER 
>   Trace Xantrex "Certified" Dealer / Installer"
> 


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-20 Thread Ray Walters
The EZ out is for unscrewing a threaded connection,  I've spent a bunch 
of time with those only to have the EZ out break off in there too.  Then 
you've got a real mess of hardened tool steel.


I would first drill several small 1/8" holes in the lead around the 
circumference of the bolt.  Then, I think tapping or pressing it out is 
the way.   The wheel puller would probably work.  You'll end up with an 
enlarged hole that you can either use a bigger bolt, or washers to deal 
with.


I agree some of the hardware that comes with cheaper L 16s, is 
inferior.  I've had plenty of those square heads come off with minimal 
torque.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/20/2016 3:04 PM, Roy Rakobitsch wrote:


Yup, id pre-drill and use an ez-out, or use a flaring tool as a small 
press and drive it out.


RoyR

On Jan 20, 2016 3:54 PM, "Kristopher Schmid" > wrote:


Greetings,

Do any of you battery gurus have a suggestion for a method of
removing a bolt remnant that is corroded into a flag terminal. 
Both sides snapped off flush with the flag. I was thinking try to

drill it out or maybe a small gear pulling tool?  I will never
again use the non stainless hardware supplied by the manufacturer...

Picture attached for reference.

Thanks!


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm


Check out or update participant bios:
www.members.re-wrenches.org 




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-20 Thread Allan Sindelar

  
  
Kristopher,
You might start with a smaller pilot hole and an easy-out or other
screw extractor. I have never seen this, so consider it just a
suggestion.
Allan


  
  
  
  
  
  
  
  
  
  
  
Allan Sindelar
  al...@sindelarsolar.com
  NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive
  Energy,
  Inc.
505 780-2738 cell


 
  

On 1/20/2016 2:53 PM, Kristopher Schmid
  wrote:


  Greetings,
  Do any of you battery gurus have a suggestion for a
method of removing a bolt remnant that is corroded into a flag
terminal.  Both sides snapped off flush with the flag.  I was
thinking try to drill it out or maybe a small gear pulling
tool?  I will never again use the non stainless hardware
supplied by the manufacturer...
  Picture attached for reference.
  Thanks!
  
  
  
  ___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-20 Thread Roy Rakobitsch
Yup, id pre-drill and use an ez-out, or use a flaring tool as a small press
and drive it out.

RoyR
On Jan 20, 2016 3:54 PM, "Kristopher Schmid"  wrote:

> Greetings,
>
> Do any of you battery gurus have a suggestion for a method of removing a
> bolt remnant that is corroded into a flag terminal.  Both sides snapped off
> flush with the flag.  I was thinking try to drill it out or maybe a small
> gear pulling tool?  I will never again use the non stainless hardware
> supplied by the manufacturer...
>
> Picture attached for reference.
>
> Thanks!
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-20 Thread toddcory
whoops, was that a flag terminal? i looked at it wrong and thought it was a post terminal.
 
todd
 
 

On Wednesday, January 20, 2016 2:01pm, toddc...@finestplanet.com said:


On Wednesday, January 20, 2016 1:53pm, "Kristopher Schmid"  said:

Greetings,
Do any of you battery gurus have a suggestion for a method of removing a bolt remnant that is corroded into a flag terminal.  Both sides snapped off flush with the flag.  I was thinking try to drill it out or maybe a small gear pulling tool?  I will never again use the non stainless hardware supplied by the manufacturer...
Picture attached for reference.
Thanks!

Sent from Finest Planet WebMail.Sent from Finest Planet WebMail.___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-20 Thread toddcory


On Wednesday, January 20, 2016 1:53pm, "Kristopher Schmid"  said:

Greetings,
Do any of you battery gurus have a suggestion for a method of removing a bolt remnant that is corroded into a flag terminal.  Both sides snapped off flush with the flag.  I was thinking try to drill it out or maybe a small gear pulling tool?  I will never again use the non stainless hardware supplied by the manufacturer...
Picture attached for reference.
Thanks!
Sent from Finest Planet WebMail.___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery corrosion issue

2016-01-20 Thread Dan Fink
I'd try an EZ-out screw extractor bit. Handy to have a whole set in the
work truck anyways.

Dan Fink
Adjunct Professor, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Accredited Continuing Education Providers™
970.672.4342



On Wed, Jan 20, 2016 at 2:53 PM, Kristopher Schmid 
wrote:

> Greetings,
>
> Do any of you battery gurus have a suggestion for a method of removing a
> bolt remnant that is corroded into a flag terminal.  Both sides snapped off
> flush with the flag.  I was thinking try to drill it out or maybe a small
> gear pulling tool?  I will never again use the non stainless hardware
> supplied by the manufacturer...
>
> Picture attached for reference.
>
> Thanks!
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org