RE: High Pressure Dry Pendents

2010-11-15 Thread Brad Casterline
I guess it's too late to take the dry off city only, before the pump--
(usually in this set-up, the parking goes down and the high rise goes up)--
If 20 ft/sec was spec'd, city water only might not have been utilized-- I
can see 50 pound safety on HUGE dry systems, AND the xtra heavy DP dilemma.

-Original Message-
From: David de Vries [mailto:ddevr...@firetecheng.net] 
Sent: Friday, November 12, 2010 5:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

Sure, I have seen a fair number of popped circuit breakers, switches shut
off, etc. and the air compressor is off, but this is a high rise building
with all the bells and whistles.  Fire alarm panel will be monitored by the
complex and by the municipal remote station.  If there is a low air alarm
(yes, I have seen those fail also), people will know.  
 
That said, I am still not comfortable allowing the 175 sprinklers in a
system that will see about 215 when it trips.  Considering all options,
including running exposed piping with high pressure uprights in the
finished ceiling area (architect throws fit here), install a PRV ahead of
the DPV (contractor throws fit here), separating and heating the finished
ceiling areas and use high pressure pendents on return bends (everyone who
has to come up with money throws fit here), etc.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Fri, 11/12/10, Chris Cahill fpech...@embarqmail.com wrote:


From: Chris Cahill fpech...@embarqmail.com
Subject: RE: High Pressure Dry Pendents
To: sprinklerforum@firesprinkler.org
Date: Friday, November 12, 2010, 7:50 AM


With your subrogation work do you really believe supervised low air protects
against false trips.  Sometimes yes sometimes no IMHO.  How about the one
where the alarm rang for days before the freezer tripped and we got to take
the sprinkler system to the parking lot for a couple days.  Or sometimes the
air compressor runs nearly constantly from a larger leak masking the leak
and finally fails only then revealing the leak before anyone has a real
chance to react to the low air alarm before it trips.  

But I think we digressed.  I wouldn't allow the head if involved.  Just not
worth the risk IMHO.  I though agree it would probably work.  Good news is
they only have to last 10 years.

Chris

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de
Vries
Sent: Thursday, November 11, 2010 6:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

 
Chris, we are designing to avoid the false trip from a dead compressor
(supervised low air), but maybe a little hammer from the fire pump starting
from a dead jockey pump will trip the DPV.  Then you are right; we get the
full static pressure.
 
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: High Pressure Dry Pendents

2010-11-12 Thread Chris Cahill
With your subrogation work do you really believe supervised low air protects
against false trips.  Sometimes yes sometimes no IMHO.  How about the one
where the alarm rang for days before the freezer tripped and we got to take
the sprinkler system to the parking lot for a couple days.  Or sometimes the
air compressor runs nearly constantly from a larger leak masking the leak
and finally fails only then revealing the leak before anyone has a real
chance to react to the low air alarm before it trips.  

But I think we digressed.  I wouldn't allow the head if involved.  Just not
worth the risk IMHO.  I though agree it would probably work.  Good news is
they only have to last 10 years.

Chris

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de
Vries
Sent: Thursday, November 11, 2010 6:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

 
Chris, we are designing to avoid the false trip from a dead compressor
(supervised low air), but maybe a little hammer from the fire pump starting
from a dead jockey pump will trip the DPV.  Then you are right; we get the
full static pressure.
 
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: High Pressure Dry Pendents

2010-11-12 Thread Matt Grise
Would it be possible to heat trace the areas where you need pendants and use 
high pressure standard heads?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries
Sent: Thursday, November 11, 2010 6:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents






Matt, I liked your idea.  That is the way I designed the system to begin with.  
Then the shops came in without the PRV, with a high pressure DPV and high 
pressure uprights on most of the system.  Just a handful of dry pendents, but 
the cut sheet says 175 max.  And I have found none listed for the 215 static 
wet pressure.  So we might end up cutting in a PRV.
 
Yes, George and Thom, I know it will only see about 50 most of the time and may 
not see the full 215 even when the DPV trips.  Although wet sprinklers are 
tested at 500 psi (for a few seconds) and so says the cut sheet, the dry 
sprinkler cut sheet does not say that.  Are they also tested at 500?  The cut 
sheet says tested pneumatically at 100.  Makes me think the procedure is not 
the same and the dry sprinklers are not quite so robust as the wet ones.
 
Chris, we are designing to avoid the false trip from a dead compressor 
(supervised low air), but maybe a little hammer from the fire pump starting 
from a dead jockey pump will trip the DPV.  Then you are right; we get the full 
static pressure.
 
Ron, if the dry pendents could take 225 or 250, why is no mfr listing them for 
that pressure?  Sure, there is a cost, but it seems there would be applications 
for them and a competitive advantage to the mfr (at least the first one!) who 
does list them at high pressure.
 
Craig, all the system components are listed for 250 or 300, except the dry 
sprinklers.

Lastly, the mfr's senior tech services mgr says 175 rated sprinklers are not 
recommended for this application.  And, the hydrostatic test pressure should 
not exceed 225.
 
So, no one knows of a high pressure dry pendent ... even an ugly one??
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



--- On Thu, 11/11/10, Matt Grise m...@afpsprink.com wrote:


From: Matt Grise m...@afpsprink.com
Subject: RE: High Pressure Dry Pendents
To: 'sprinklerforum@firesprinkler.org' sprinklerforum@firesprinkler.org
Date: Thursday, November 11, 2010, 3:57 PM


Nobody liked the pressure reducing valve? What if you put it in front of the 
dry pipe valve?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Thursday, November 11, 2010 3:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

Is all the piping, fittings, etc.,  rated for 300 psi?  If you're worried about 
the heads, don't forget the whole system is technically rated for 175.  


Craig Prahl
CH2MHILL/SPB
864-599-4102

From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries 
[ddevr...@firetecheng.net]
Sent: Wednesday, November 10, 2010 11:42 PM
To: AFSA SprinklerForum
Subject: High Pressure Dry Pendents

I have an open parking garage under a high rise.  Fire pump sized for standpipe 
demand, so it has over 200 psi at the garage level.  Most of the dry pipe 
system in the garage has uprights, but there are some finished ceiling areas 
that need dry pendents.  I have not found any dry pendents listed for more than 
175.  Suggestions?

Of course, for most of the time the system will only see the ~50 psi air, but 
when the valve trips, it will be about 215.  Am I wrong to think the DP's 
should be listed for the static system pressure?

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated



--- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


From: Coastal coastalf...@sc.rr.com
Subject: Re: Pipe Expansion
To: Fletcher, Ron sprinklerforum@firesprinkler.org
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10

RE: High Pressure Dry Pendents

2010-11-12 Thread Thom
If I was going to install std. dry pend I would use ones by a mfg that tests
them to 500Psi, like Globe GL series

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: High Pressure Dry Pendents

2010-11-12 Thread Roland Huggins
it is UL that dictates the test pressures as part of their listing.   
That is a leakage test that is held for one minute.  There is also a  
hydrostatic test at 700 psi for one minute regarding rupture.


Although I agree with the stated concerns and likelihood of successful  
operation with the standard pressure rating, I wouldn't go there since  
it is an explicit violation of NFPA 13.  It's like putting a standard  
tire with a S speed rating on your Viper (or Ford Cobra if you have  
real money) instead of a Y rating.  It will probably work but if (or  
when) it blows out, guess who gets to pay for the new car?


Roland



On Nov 12, 2010, at 9:13 AM, Thom wrote:

If I was going to install std. dry pend I would use ones by a mfg  
that tests

them to 500Psi, like Globe GL series

__


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: High Pressure Dry Pendents

2010-11-12 Thread David de Vries
Sure, I have seen a fair number of popped circuit breakers, switches shut off, 
etc. and the air compressor is off, but this is a high rise building with all 
the bells and whistles.  Fire alarm panel will be monitored by the complex and 
by the municipal remote station.  If there is a low air alarm (yes, I have seen 
those fail also), people will know.  
 
That said, I am still not comfortable allowing the 175 sprinklers in a system 
that will see about 215 when it trips.  Considering all options, including 
running exposed piping with high pressure uprights in the finished ceiling area 
(architect throws fit here), install a PRV ahead of the DPV (contractor throws 
fit here), separating and heating the finished ceiling areas and use high 
pressure pendents on return bends (everyone who has to come up with 
money throws fit here), etc.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Fri, 11/12/10, Chris Cahill fpech...@embarqmail.com wrote:


From: Chris Cahill fpech...@embarqmail.com
Subject: RE: High Pressure Dry Pendents
To: sprinklerforum@firesprinkler.org
Date: Friday, November 12, 2010, 7:50 AM


With your subrogation work do you really believe supervised low air protects
against false trips.  Sometimes yes sometimes no IMHO.  How about the one
where the alarm rang for days before the freezer tripped and we got to take
the sprinkler system to the parking lot for a couple days.  Or sometimes the
air compressor runs nearly constantly from a larger leak masking the leak
and finally fails only then revealing the leak before anyone has a real
chance to react to the low air alarm before it trips.  

But I think we digressed.  I wouldn't allow the head if involved.  Just not
worth the risk IMHO.  I though agree it would probably work.  Good news is
they only have to last 10 years.

Chris

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de
Vries
Sent: Thursday, November 11, 2010 6:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

 
Chris, we are designing to avoid the false trip from a dead compressor
(supervised low air), but maybe a little hammer from the fire pump starting
from a dead jockey pump will trip the DPV.  Then you are right; we get the
full static pressure.
 
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: High Pressure Dry Pendents

2010-11-11 Thread Matt Grise
Have you looked into pressure reducing valves? I don't know if there are any 
that are listed for dry system use though...

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries
Sent: Wednesday, November 10, 2010 10:42 PM
To: AFSA SprinklerForum
Subject: High Pressure Dry Pendents

I have an open parking garage under a high rise.  Fire pump sized for standpipe 
demand, so it has over 200 psi at the garage level.  Most of the dry pipe 
system in the garage has uprights, but there are some finished ceiling areas 
that need dry pendents.  I have not found any dry pendents listed for more than 
175.  Suggestions?  
 
Of course, for most of the time the system will only see the ~50 psi air, but 
when the valve trips, it will be about 215.  Am I wrong to think the DP's 
should be listed for the static system pressure?

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


From: Coastal coastalf...@sc.rr.com
Subject: Re: Pipe Expansion
To: Fletcher, Ron sprinklerforum@firesprinkler.org
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ  

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed,
 well on
 unrestrained steel.  A fitting does not in itself restrain the pipe.
 Either
 the pipe moves or the want to move is translated into some internal
 force.
 The effect of the expansion it dependent on the fittings and the
 restraintment.  

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston
Coastal Fire Protection
Coastal                            mailto:coastalf...@sc.rr.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: High Pressure Dry Pendents

2010-11-11 Thread Ron Greenman
What's the criteria for that 175 psi limit. I don't think it's burst
pressure. Is it that haven't been tested for operation any higher than
175? Are 225 heads a special more robust head than 175 heads? Or are
they just 175 heads that got tested and listed to 225. I remember PT
tests in the Army. The performance criteria was always X number in Y
time. You were done when you exhausted either so it was that one could
meet X in Y in be done and pass although not out of strength and so
still be able to continue and perform X in Y. I this a similar thing?
And if so how willing are you to put that PE behind exceeding the
listing?

On Thu, Nov 11, 2010 at 3:43 AM, Matt Grise m...@afpsprink.com wrote:
 Have you looked into pressure reducing valves? I don't know if there are any 
 that are listed for dry system use though...

 Matt Grisé PE*, LEED AP
 Sales Engineer
 Alliance Fire Protection
 *Licensed in KS  MO

 913.888.0647 ph
 913.888.0618 f
 913.927.0222 cell
 www. AFPsprink.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries
 Sent: Wednesday, November 10, 2010 10:42 PM
 To: AFSA SprinklerForum
 Subject: High Pressure Dry Pendents

 I have an open parking garage under a high rise.  Fire pump sized for 
 standpipe demand, so it has over 200 psi at the garage level.  Most of the 
 dry pipe system in the garage has uprights, but there are some finished 
 ceiling areas that need dry pendents.  I have not found any dry pendents 
 listed for more than 175.  Suggestions?

 Of course, for most of the time the system will only see the ~50 psi air, but 
 when the valve trips, it will be about 215.  Am I wrong to think the DP's 
 should be listed for the static system pressure?

 Dave

 David A. de Vries, P.E., CSP
 Firetech Engineering Incorporated



 --- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


 From: Coastal coastalf...@sc.rr.com
 Subject: Re: Pipe Expansion
 To: Fletcher, Ron sprinklerforum@firesprinkler.org
 Date: Wednesday, November 10, 2010, 6:41 PM


 Hello Ron,

 It is not a building, Wooden walkway to a floating dock.

 Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed,
 well on
 unrestrained steel.  A fitting does not in itself restrain the pipe.
 Either
 the pipe moves or the want to move is translated into some internal
 force.
 The effect of the expansion it dependent on the fittings and the
 restraintment.

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)



 --
 Best regards,
 Charles Thurston
 Coastal Fire Protection
 Coastal                            mailto:coastalf...@sc.rr.com

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical 

RE: High Pressure Dry Pendents

2010-11-11 Thread George Church
Considering all sprinklers are tested at 500 PSI, I doubt that they raise
that to 700 and market those that stay together as high pressure. Dave,
assuming the dry system supply- fire pump?- is 215, you could run a water
delivery calc with a head operating and see if the pressure in the system
really reaches 215 PSI with the decrease in pressure as water fills the
pipe, and then when its full (or its equalized with trapped air) is one
head flowing enough to bring the pressure below 175?

Or depending on what the value of the contents is, susceptibility to water
damage, owner tolerance for risk, it wouldn't be a quantum leap to allow a
little over 200 PSI- where we often hydro for min 2 hrs anyway- and ask the
AHJ to APPROVE the higher pressure. If I was entitled to an opinion, it
would be that this would be fine.

glc

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, November 11, 2010 3:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: High Pressure Dry Pendents

What's the criteria for that 175 psi limit. I don't think it's burst
pressure. Is it that haven't been tested for operation any higher than 175?
Are 225 heads a special more robust head than 175 heads? Or are they just
175 heads that got tested and listed to 225. I remember PT tests in the
Army. The performance criteria was always X number in Y time. You were done
when you exhausted either so it was that one could meet X in Y in be done
and pass although not out of strength and so still be able to continue and
perform X in Y. I this a similar thing?
And if so how willing are you to put that PE behind exceeding the listing?

On Thu, Nov 11, 2010 at 3:43 AM, Matt Grise m...@afpsprink.com wrote:
 Have you looked into pressure reducing valves? I don't know if there are
any that are listed for dry system use though...

 Matt Grisé PE*, LEED AP
 Sales Engineer
 Alliance Fire Protection
 *Licensed in KS  MO

 913.888.0647 ph
 913.888.0618 f
 913.927.0222 cell
 www. AFPsprink.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David 
 de Vries
 Sent: Wednesday, November 10, 2010 10:42 PM
 To: AFSA SprinklerForum
 Subject: High Pressure Dry Pendents

 I have an open parking garage under a high rise.  Fire pump sized for
standpipe demand, so it has over 200 psi at the garage level.  Most of the
dry pipe system in the garage has uprights, but there are some finished
ceiling areas that need dry pendents.  I have not found any dry pendents
listed for more than 175.  Suggestions?

 Of course, for most of the time the system will only see the ~50 psi air,
but when the valve trips, it will be about 215.  Am I wrong to think the
DP's should be listed for the static system pressure?

 Dave

 David A. de Vries, P.E., CSP
 Firetech Engineering Incorporated



 --- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


 From: Coastal coastalf...@sc.rr.com
 Subject: Re: Pipe Expansion
 To: Fletcher, Ron sprinklerforum@firesprinkler.org
 Date: Wednesday, November 10, 2010, 6:41 PM


 Hello Ron,

 It is not a building, Wooden walkway to a floating dock.

 Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same 
 ambient conditions wouldn't the expansion rates kind of offset each 
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same 
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed, 
 well on unrestrained steel.  A fitting does not in itself restrain 
 the pipe.
 Either
 the pipe moves or the want to move is translated into some internal 
 force.
 The effect of the expansion it dependent on the fittings and the 
 restraintment.

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe

Re: High Pressure Dry Pendents

2010-11-11 Thread Chris Cahill
What about a dead air compressor that causes a false trip? More likely than one 
head flowing.  Or a cracked drum drip valve?  Will have 215 psi then.

Chris
-Original Message-
From: George Church for...@ptd.net
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Thu, 11 Nov 2010 16:22:24 
To: sprinklerforum@firesprinkler.org
Reply-To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

Considering all sprinklers are tested at 500 PSI, I doubt that they raise
that to 700 and market those that stay together as high pressure. Dave,
assuming the dry system supply- fire pump?- is 215, you could run a water
delivery calc with a head operating and see if the pressure in the system
really reaches 215 PSI with the decrease in pressure as water fills the
pipe, and then when its full (or its equalized with trapped air) is one
head flowing enough to bring the pressure below 175?

Or depending on what the value of the contents is, susceptibility to water
damage, owner tolerance for risk, it wouldn't be a quantum leap to allow a
little over 200 PSI- where we often hydro for min 2 hrs anyway- and ask the
AHJ to APPROVE the higher pressure. If I was entitled to an opinion, it
would be that this would be fine.

glc

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, November 11, 2010 3:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: High Pressure Dry Pendents

What's the criteria for that 175 psi limit. I don't think it's burst
pressure. Is it that haven't been tested for operation any higher than 175?
Are 225 heads a special more robust head than 175 heads? Or are they just
175 heads that got tested and listed to 225. I remember PT tests in the
Army. The performance criteria was always X number in Y time. You were done
when you exhausted either so it was that one could meet X in Y in be done
and pass although not out of strength and so still be able to continue and
perform X in Y. I this a similar thing?
And if so how willing are you to put that PE behind exceeding the listing?

On Thu, Nov 11, 2010 at 3:43 AM, Matt Grise m...@afpsprink.com wrote:
 Have you looked into pressure reducing valves? I don't know if there are
any that are listed for dry system use though...

 Matt Grisé PE*, LEED AP
 Sales Engineer
 Alliance Fire Protection
 *Licensed in KS  MO

 913.888.0647 ph
 913.888.0618 f
 913.927.0222 cell
 www. AFPsprink.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David 
 de Vries
 Sent: Wednesday, November 10, 2010 10:42 PM
 To: AFSA SprinklerForum
 Subject: High Pressure Dry Pendents

 I have an open parking garage under a high rise.  Fire pump sized for
standpipe demand, so it has over 200 psi at the garage level.  Most of the
dry pipe system in the garage has uprights, but there are some finished
ceiling areas that need dry pendents.  I have not found any dry pendents
listed for more than 175.  Suggestions?

 Of course, for most of the time the system will only see the ~50 psi air,
but when the valve trips, it will be about 215.  Am I wrong to think the
DP's should be listed for the static system pressure?

 Dave

 David A. de Vries, P.E., CSP
 Firetech Engineering Incorporated



 --- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


 From: Coastal coastalf...@sc.rr.com
 Subject: Re: Pipe Expansion
 To: Fletcher, Ron sprinklerforum@firesprinkler.org
 Date: Wednesday, November 10, 2010, 6:41 PM


 Hello Ron,

 It is not a building, Wooden walkway to a floating dock.

 Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same 
 ambient conditions wouldn't the expansion rates kind of offset each 
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same 
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed, 
 well on unrestrained steel.  A fitting does not in itself restrain 
 the pipe.
 Either
 the pipe moves or the want to move is translated into some internal 
 force.
 The effect of the expansion it dependent on the fittings and the 
 restraintment.

___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ

RE: High Pressure Dry Pendents

2010-11-11 Thread Craig.Prahl
Is all the piping, fittings, etc.,  rated for 300 psi?  If you're worried about 
the heads, don't forget the whole system is technically rated for 175.  


Craig Prahl
CH2MHILL/SPB
864-599-4102

From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries 
[ddevr...@firetecheng.net]
Sent: Wednesday, November 10, 2010 11:42 PM
To: AFSA SprinklerForum
Subject: High Pressure Dry Pendents

I have an open parking garage under a high rise.  Fire pump sized for standpipe 
demand, so it has over 200 psi at the garage level.  Most of the dry pipe 
system in the garage has uprights, but there are some finished ceiling areas 
that need dry pendents.  I have not found any dry pendents listed for more than 
175.  Suggestions?

Of course, for most of the time the system will only see the ~50 psi air, but 
when the valve trips, it will be about 215.  Am I wrong to think the DP's 
should be listed for the static system pressure?

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated



--- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


From: Coastal coastalf...@sc.rr.com
Subject: Re: Pipe Expansion
To: Fletcher, Ron sprinklerforum@firesprinkler.org
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed,
 well on
 unrestrained steel.  A fitting does not in itself restrain the pipe.
 Either
 the pipe moves or the want to move is translated into some internal
 force.
 The effect of the expansion it dependent on the fittings and the
 restraintment.

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)



--
Best regards,
Charles Thurston
Coastal Fire Protection
Coastalmailto:coastalf...@sc.rr.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: High Pressure Dry Pendents

2010-11-11 Thread Matt Grise
Nobody liked the pressure reducing valve? What if you put it in front of the 
dry pipe valve?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Thursday, November 11, 2010 3:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

Is all the piping, fittings, etc.,  rated for 300 psi?  If you're worried about 
the heads, don't forget the whole system is technically rated for 175.  


Craig Prahl
CH2MHILL/SPB
864-599-4102

From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries 
[ddevr...@firetecheng.net]
Sent: Wednesday, November 10, 2010 11:42 PM
To: AFSA SprinklerForum
Subject: High Pressure Dry Pendents

I have an open parking garage under a high rise.  Fire pump sized for standpipe 
demand, so it has over 200 psi at the garage level.  Most of the dry pipe 
system in the garage has uprights, but there are some finished ceiling areas 
that need dry pendents.  I have not found any dry pendents listed for more than 
175.  Suggestions?

Of course, for most of the time the system will only see the ~50 psi air, but 
when the valve trips, it will be about 215.  Am I wrong to think the DP's 
should be listed for the static system pressure?

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated



--- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


From: Coastal coastalf...@sc.rr.com
Subject: Re: Pipe Expansion
To: Fletcher, Ron sprinklerforum@firesprinkler.org
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed,
 well on
 unrestrained steel.  A fitting does not in itself restrain the pipe.
 Either
 the pipe moves or the want to move is translated into some internal
 force.
 The effect of the expansion it dependent on the fittings and the
 restraintment.

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)



--
Best regards,
Charles Thurston
Coastal Fire Protection
Coastalmailto:coastalf...@sc.rr.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum

RE: High Pressure Dry Pendents

2010-11-11 Thread Craig.Prahl
If the drum drip is cracked water will be flowing.  Unliely that you'll 
overpresurize the system.  Even still 215 is not that big of a deal since you'd 
be testing at 200 psi minimum.  The system should be capable of sustaining 215 
for the amount of time it would take someone to respond and fix the problem.

Craig Prahl
CH2MHILL/SPB
864-599-4102

From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill 
[fpech...@embarqmail.com]
Sent: Thursday, November 11, 2010 4:44 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: High Pressure Dry Pendents

What about a dead air compressor that causes a false trip? More likely than one 
head flowing.  Or a cracked drum drip valve?  Will have 215 psi then.

Chris
-Original Message-
From: George Church for...@ptd.net
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Thu, 11 Nov 2010 16:22:24
To: sprinklerforum@firesprinkler.org
Reply-To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

Considering all sprinklers are tested at 500 PSI, I doubt that they raise
that to 700 and market those that stay together as high pressure. Dave,
assuming the dry system supply- fire pump?- is 215, you could run a water
delivery calc with a head operating and see if the pressure in the system
really reaches 215 PSI with the decrease in pressure as water fills the
pipe, and then when its full (or its equalized with trapped air) is one
head flowing enough to bring the pressure below 175?

Or depending on what the value of the contents is, susceptibility to water
damage, owner tolerance for risk, it wouldn't be a quantum leap to allow a
little over 200 PSI- where we often hydro for min 2 hrs anyway- and ask the
AHJ to APPROVE the higher pressure. If I was entitled to an opinion, it
would be that this would be fine.

glc

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, November 11, 2010 3:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: High Pressure Dry Pendents

What's the criteria for that 175 psi limit. I don't think it's burst
pressure. Is it that haven't been tested for operation any higher than 175?
Are 225 heads a special more robust head than 175 heads? Or are they just
175 heads that got tested and listed to 225. I remember PT tests in the
Army. The performance criteria was always X number in Y time. You were done
when you exhausted either so it was that one could meet X in Y in be done
and pass although not out of strength and so still be able to continue and
perform X in Y. I this a similar thing?
And if so how willing are you to put that PE behind exceeding the listing?

On Thu, Nov 11, 2010 at 3:43 AM, Matt Grise m...@afpsprink.com wrote:
 Have you looked into pressure reducing valves? I don't know if there are
any that are listed for dry system use though...

 Matt Grisé PE*, LEED AP
 Sales Engineer
 Alliance Fire Protection
 *Licensed in KS  MO

 913.888.0647 ph
 913.888.0618 f
 913.927.0222 cell
 www. AFPsprink.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David
 de Vries
 Sent: Wednesday, November 10, 2010 10:42 PM
 To: AFSA SprinklerForum
 Subject: High Pressure Dry Pendents

 I have an open parking garage under a high rise.  Fire pump sized for
standpipe demand, so it has over 200 psi at the garage level.  Most of the
dry pipe system in the garage has uprights, but there are some finished
ceiling areas that need dry pendents.  I have not found any dry pendents
listed for more than 175.  Suggestions?

 Of course, for most of the time the system will only see the ~50 psi air,
but when the valve trips, it will be about 215.  Am I wrong to think the
DP's should be listed for the static system pressure?

 Dave

 David A. de Vries, P.E., CSP
 Firetech Engineering Incorporated



 --- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


 From: Coastal coastalf...@sc.rr.com
 Subject: Re: Pipe Expansion
 To: Fletcher, Ron sprinklerforum@firesprinkler.org
 Date: Wednesday, November 10, 2010, 6:41 PM


 Hello Ron,

 It is not a building, Wooden walkway to a floating dock.

 Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same
 protection as a full expansion loop.


 Subject: Re: Pipe

RE: High Pressure Dry Pendents

2010-11-11 Thread Thom
I personally would not worry about the heads, not being rated for the 215#
As stated below the 200 Psi is the minimum test pressure or as 13 says or
50# over operating pressure so test it to 265# for 2hours and sleep well.
175# is operating pressure and your operating pressure is 50Psi air most of
the time. True if the system trips your operating pressure is then 215#, but
it will not be a sustained pressure, as they will drain and reset the
system, and no way will it exceed the test pressure of 265.







Even still 215 is not that big of a deal since you'd be testing at 200 psi
minimumCraig Prahl
CH2MHILL/SPB

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: High Pressure Dry Pendents

2010-11-11 Thread Ron Greenman
The steel  pipe and fittings we use are rated (not listed 'cause they
don't need to be) at 150 psi WOG. WOG is water, oil, gas. The 150 is
for gas and the fluid rating is twice that (300 psi) which is why we
can use the same old pipe in those systems where we need 250 psi
listed sprinkler components.

On Thu, Nov 11, 2010 at 2:29 PM, Thom tmcma...@firetechinc.com wrote:
 I personally would not worry about the heads, not being rated for the 215#
 As stated below the 200 Psi is the minimum test pressure or as 13 says or
 50# over operating pressure so test it to 265# for 2hours and sleep well.
 175# is operating pressure and your operating pressure is 50Psi air most of
 the time. True if the system trips your operating pressure is then 215#, but
 it will not be a sustained pressure, as they will drain and reset the
 system, and no way will it exceed the test pressure of 265.







 Even still 215 is not that big of a deal since you'd be testing at 200 psi
 minimumCraig Prahl
 CH2MHILL/SPB

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: High Pressure Dry Pendents

2010-11-11 Thread David de Vries





Matt, I liked your idea.  That is the way I designed the system to begin with.  
Then the shops came in without the PRV, with a high pressure DPV and high 
pressure uprights on most of the system.  Just a handful of dry pendents, but 
the cut sheet says 175 max.  And I have found none listed for the 215 static 
wet pressure.  So we might end up cutting in a PRV.
 
Yes, George and Thom, I know it will only see about 50 most of the time and may 
not see the full 215 even when the DPV trips.  Although wet sprinklers are 
tested at 500 psi (for a few seconds) and so says the cut sheet, the dry 
sprinkler cut sheet does not say that.  Are they also tested at 500?  The cut 
sheet says tested pneumatically at 100.  Makes me think the procedure is not 
the same and the dry sprinklers are not quite so robust as the wet ones.
 
Chris, we are designing to avoid the false trip from a dead compressor 
(supervised low air), but maybe a little hammer from the fire pump starting 
from a dead jockey pump will trip the DPV.  Then you are right; we get the full 
static pressure.
 
Ron, if the dry pendents could take 225 or 250, why is no mfr listing them for 
that pressure?  Sure, there is a cost, but it seems there would be applications 
for them and a competitive advantage to the mfr (at least the first one!) who 
does list them at high pressure.
 
Craig, all the system components are listed for 250 or 300, except the dry 
sprinklers.

Lastly, the mfr's senior tech services mgr says 175 rated sprinklers are not 
recommended for this application.  And, the hydrostatic test pressure should 
not exceed 225.
 
So, no one knows of a high pressure dry pendent ... even an ugly one??
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



--- On Thu, 11/11/10, Matt Grise m...@afpsprink.com wrote:


From: Matt Grise m...@afpsprink.com
Subject: RE: High Pressure Dry Pendents
To: 'sprinklerforum@firesprinkler.org' sprinklerforum@firesprinkler.org
Date: Thursday, November 11, 2010, 3:57 PM


Nobody liked the pressure reducing valve? What if you put it in front of the 
dry pipe valve?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Thursday, November 11, 2010 3:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Pressure Dry Pendents

Is all the piping, fittings, etc.,  rated for 300 psi?  If you're worried about 
the heads, don't forget the whole system is technically rated for 175.  


Craig Prahl
CH2MHILL/SPB
864-599-4102

From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries 
[ddevr...@firetecheng.net]
Sent: Wednesday, November 10, 2010 11:42 PM
To: AFSA SprinklerForum
Subject: High Pressure Dry Pendents

I have an open parking garage under a high rise.  Fire pump sized for standpipe 
demand, so it has over 200 psi at the garage level.  Most of the dry pipe 
system in the garage has uprights, but there are some finished ceiling areas 
that need dry pendents.  I have not found any dry pendents listed for more than 
175.  Suggestions?

Of course, for most of the time the system will only see the ~50 psi air, but 
when the valve trips, it will be about 215.  Am I wrong to think the DP's 
should be listed for the static system pressure?

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated



--- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


From: Coastal coastalf...@sc.rr.com
Subject: Re: Pipe Expansion
To: Fletcher, Ron sprinklerforum@firesprinkler.org
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
 Sent: Wednesday, November 10, 2010 3:04 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: RE: Pipe Expansion

 Also remember that a simple change in direction can provide the same
 protection as a full expansion loop.


 Subject: Re: Pipe Expansion

 The expansion is the expansion no matter what fittings are employed,
 well on
 unrestrained steel.  A fitting does not in itself restrain the pipe.
 Either
 the pipe moves or the want to move is translated into some internal
 force.
 The effect of the expansion it dependent on the fittings

Re: High Pressure Dry Pendents

2010-11-11 Thread Ron Greenman
David,

The manufacturer's guy will always say not to exceed the listing and
if you know one well enough and he trusts your discretion you might
even get a yeah it will probably work but we haven't tested it that
way so no. As to why no on has spent the dough to list it that way and
get that competitive advantage maybe no one sees a market except for a
handful of these things on a rare occasion. I dislike the PRV idea
since I've tested enough of these things in fire systems and they seem
to have a high failure rate from disuse. Two cents talking.

On Thu, Nov 11, 2010 at 4:21 PM, David de Vries
ddevr...@firetecheng.net wrote:





 Matt, I liked your idea.  That is the way I designed the system to begin 
 with.  Then the shops came in without the PRV, with a high pressure DPV 
 and high pressure uprights on most of the system.  Just a handful of dry 
 pendents, but the cut sheet says 175 max.  And I have found none listed for 
 the 215 static wet pressure.  So we might end up cutting in a PRV.

 Yes, George and Thom, I know it will only see about 50 most of the time 
 and may not see the full 215 even when the DPV trips.  Although wet 
 sprinklers are tested at 500 psi (for a few seconds) and so says the cut 
 sheet, the dry sprinkler cut sheet does not say that.  Are they also tested 
 at 500?  The cut sheet says tested pneumatically at 100.  Makes me think the 
 procedure is not the same and the dry sprinklers are not quite so robust as 
 the wet ones.

 Chris, we are designing to avoid the false trip from a dead compressor 
 (supervised low air), but maybe a little hammer from the fire pump starting 
 from a dead jockey pump will trip the DPV.  Then you are right; we get the 
 full static pressure.

 Ron, if the dry pendents could take 225 or 250, why is no mfr listing them 
 for that pressure?  Sure, there is a cost, but it seems there would be 
 applications for them and a competitive advantage to the mfr (at least the 
 first one!) who does list them at high pressure.

 Craig, all the system components are listed for 250 or 300, except the dry 
 sprinklers.

 Lastly, the mfr's senior tech services mgr says 175 rated sprinklers are not 
 recommended for this application.  And, the hydrostatic test 
 pressure should not exceed 225.

 So, no one knows of a high pressure dry pendent ... even an ugly one??


 Dave

 David A. de Vries, P.E., CSP
 Firetech Engineering Incorporated
 2715 Harrison St.
 Evanston, IL 60201
 Tel: 847-733-0944
 Fax: 847-866-6255



 --- On Thu, 11/11/10, Matt Grise m...@afpsprink.com wrote:


 From: Matt Grise m...@afpsprink.com
 Subject: RE: High Pressure Dry Pendents
 To: 'sprinklerforum@firesprinkler.org' sprinklerforum@firesprinkler.org
 Date: Thursday, November 11, 2010, 3:57 PM


 Nobody liked the pressure reducing valve? What if you put it in front of the 
 dry pipe valve?

 Matt Grisé PE*, LEED AP
 Sales Engineer
 Alliance Fire Protection
 *Licensed in KS  MO

 913.888.0647 ph
 913.888.0618 f
 913.927.0222 cell
 www. AFPsprink.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
 craig.pr...@ch2m.com
 Sent: Thursday, November 11, 2010 3:44 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: High Pressure Dry Pendents

 Is all the piping, fittings, etc.,  rated for 300 psi?  If you're worried 
 about the heads, don't forget the whole system is technically rated for 175.


 Craig Prahl
 CH2MHILL/SPB
 864-599-4102
 
 From: sprinklerforum-boun...@firesprinkler.org 
 [sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries 
 [ddevr...@firetecheng.net]
 Sent: Wednesday, November 10, 2010 11:42 PM
 To: AFSA SprinklerForum
 Subject: High Pressure Dry Pendents

 I have an open parking garage under a high rise.  Fire pump sized for 
 standpipe demand, so it has over 200 psi at the garage level.  Most of the 
 dry pipe system in the garage has uprights, but there are some finished 
 ceiling areas that need dry pendents.  I have not found any dry pendents 
 listed for more than 175.  Suggestions?

 Of course, for most of the time the system will only see the ~50 psi air, but 
 when the valve trips, it will be about 215.  Am I wrong to think the DP's 
 should be listed for the static system pressure?

 Dave

 David A. de Vries, P.E., CSP
 Firetech Engineering Incorporated



 --- On Wed, 11/10/10, Coastal coastalf...@sc.rr.com wrote:


 From: Coastal coastalf...@sc.rr.com
 Subject: Re: Pipe Expansion
 To: Fletcher, Ron sprinklerforum@firesprinkler.org
 Date: Wednesday, November 10, 2010, 6:41 PM


 Hello Ron,

 It is not a building, Wooden walkway to a floating dock.

 Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

 Since the building and the sprinkler system are subject to the same
 ambient conditions wouldn't the expansion rates kind of offset each
 other?

 Ron Fletcher
 Aero Automatic
 Phoenix, AZ

 -Original Message