Re: Stus-List Inverter to Outlet Via Extension Cord?
I just checked my inverters and they both are "center grounded". They show 60 volts from hot to ground and 60 volts from neutral to ground. This actually has an advantage where if a human gets their hands on a wire and is grounded, they only get a 60 volt shock*. My ground faults work with this setup too. The disadvantage is any equipment that has any interconnection between neutral and ground would cause a dead short. Such a thing should not exist, but sometimes it does and no one notices. It isn't good anyway, but you REALLY don't want mixed neutrals and grounds on a boat. You end up feeding AC into the water to some extent even with good wiring and a lot of AC with bad wiring. * I suspect that this is not on purpose, but rather an artifact of a push-pull design in the inverter that was just easier to do with the center point grounded. More expensive inverters designed for hard wiring do not do this. Joe Coquina C 35 MK I From: CnC-List [mailto:cnc-list-boun...@cnc-list.com] On Behalf Of David via CnC-List Sent: Monday, November 28, 2016 17:48 To: cnc-list@cnc-list.com Cc: David <davidrisc...@msn.com> Subject: Re: Stus-List Inverter to Outlet Via Extension Cord? So I know enough to know to be careful and decided to isolate the inverter to its own dedicated newly installed plug. Properly wired and chassis grounded as well. Its all we will need. Thanks for everyone's input. David F. Risch (401) 419-4650 (cell) From: CnC-List <cnc-list-boun...@cnc-list.com<mailto:cnc-list-boun...@cnc-list.com>> on behalf of Tim Goodyear via CnC-List <cnc-list@cnc-list.com<mailto:cnc-list@cnc-list.com>> Sent: Monday, October 24, 2016 7:12 PM To: cnc-list@cnc-list.com<mailto:cnc-list@cnc-list.com> Cc: Tim Goodyear; Michael Brown Subject: Re: Stus-List Inverter to Outlet Via Extension Cord? Like 'ground' systems, marine systems are required to connect neutral to ground at the source of power, whether that is somewhere at the top of the dock for shore power, or at the generator or inverter. One of the most important connections at the inverter is from chassis ground to the boat's grounding bus. On a marine inverter, there should be a switch that opens the ground to neutral connection when it is providing pass-through shore power and closes it when it is generating AC power itself. I presume that the WM 1kW versions have a neutral/ground connection within them, but it would be very worth checking! Tim Ex-Mojito Newport, RI On Oct 24, 2016, at 2:31 PM, Michael Brown via CnC-List <cnc-list@cnc-list.com<mailto:cnc-list@cnc-list.com>> wrote: Hopefully the inverter will come with very clear instructions on how to handle ground and neutral. For normal power, ie shore power, this is the US code: "The National Electrical Code ( NEC ) requires the AC source to have a Neutral to ground bond and that there be only one such bond in the entire AC system." So only at the distribution panel is there a bond between neutral and ground. They should never be connected together intentionally at the load. This document covers grounding and bonding, may also cure insomnia. https://www.engineereducators.com/docs/groundingandbonding2-2.pdf Grounding an AC system is done to limit the effect of a lightning strike, maybe an upstream over voltage fault. Bonding the green wire that comes in a three prong plug ( also called a ground ) to Neutral at the distribution panel is to ensure a low resistance return path for a fault. So if anything happens the desired effect is that a hot to ground short will occur which in turn will cause an over current surge blowing the circuit breakers. A person can be electrocuted even with a properly installed and grounded AC system without the circuit breakers tripping. Unless an inverter has some specific design that uses a ground bonding the Neutral and ground together is not going to do much. Check out the last Q from Xantrex here: http://www.xantrex.com/documents/tech-doctor/universal/tech4-universal.pdf Similarly with an inverter connected to a battery that is not grounded a GFCI should never trip. Theoretically in a floating system the power has to come out of the Hot lead and return in the Neutral. There will never be a ground fault to trip a GFCI. There is no ground. I suppose an inverter manufacturer could create a third connection back to the power circuit Neutral that bypasses the GFCI. A short to that wire would cause an imbalance and trip the GFCI. Then you would be connecting a floating Neutral to the loads "ground" which may be exactly what the Xantrex article says not to do. Michael Brown Windburn C 30-1 From: Ron Ricci <rvri...@gmail.com<mailto:rvri...@gmail.com>> David, I've followed some of this thread and have a few concerns where some have mentioned using an inexpensive inverter. Using an inverter that is not int
Re: Stus-List Inverter to Outlet Via Extension Cord?
So I know enough to know to be careful and decided to isolate the inverter to its own dedicated newly installed plug. Properly wired and chassis grounded as well. Its all we will need. Thanks for everyone's input. David F. Risch (401) 419-4650 (cell) From: CnC-List <cnc-list-boun...@cnc-list.com> on behalf of Tim Goodyear via CnC-List <cnc-list@cnc-list.com> Sent: Monday, October 24, 2016 7:12 PM To: cnc-list@cnc-list.com Cc: Tim Goodyear; Michael Brown Subject: Re: Stus-List Inverter to Outlet Via Extension Cord? Like 'ground' systems, marine systems are required to connect neutral to ground at the source of power, whether that is somewhere at the top of the dock for shore power, or at the generator or inverter. One of the most important connections at the inverter is from chassis ground to the boat's grounding bus. On a marine inverter, there should be a switch that opens the ground to neutral connection when it is providing pass-through shore power and closes it when it is generating AC power itself. I presume that the WM 1kW versions have a neutral/ground connection within them, but it would be very worth checking! Tim Ex-Mojito Newport, RI On Oct 24, 2016, at 2:31 PM, Michael Brown via CnC-List <cnc-list@cnc-list.com<mailto:cnc-list@cnc-list.com>> wrote: Hopefully the inverter will come with very clear instructions on how to handle ground and neutral. For normal power, ie shore power, this is the US code: "The National Electrical Code ( NEC ) requires the AC source to have a Neutral to ground bond and that there be only one such bond in the entire AC system." So only at the distribution panel is there a bond between neutral and ground. They should never be connected together intentionally at the load. This document covers grounding and bonding, may also cure insomnia. https://www.engineereducators.com/docs/groundingandbonding2-2.pdf Grounding an AC system is done to limit the effect of a lightning strike, maybe an upstream over voltage fault. Bonding the green wire that comes in a three prong plug ( also called a ground ) to Neutral at the distribution panel is to ensure a low resistance return path for a fault. So if anything happens the desired effect is that a hot to ground short will occur which in turn will cause an over current surge blowing the circuit breakers. A person can be electrocuted even with a properly installed and grounded AC system without the circuit breakers tripping. Unless an inverter has some specific design that uses a ground bonding the Neutral and ground together is not going to do much. Check out the last Q from Xantrex here: http://www.xantrex.com/documents/tech-doctor/universal/tech4-universal.pdf Similarly with an inverter connected to a battery that is not grounded a GFCI should never trip. Theoretically in a floating system the power has to come out of the Hot lead and return in the Neutral. There will never be a ground fault to trip a GFCI. There is no ground. I suppose an inverter manufacturer could create a third connection back to the power circuit Neutral that bypasses the GFCI. A short to that wire would cause an imbalance and trip the GFCI. Then you would be connecting a floating Neutral to the loads "ground" which may be exactly what the Xantrex article says not to do. Michael Brown Windburn C 30-1 From: Ron Ricci <rvri...@gmail.com<mailto:rvri...@gmail.com>> David, I've followed some of this thread and have a few concerns where some have mentioned using an inexpensive inverter. Using an inverter that is not intended for marine use or not properly grounded can cause problems. An inverter can produce short duration spikes which exceed the insulation rating of most wires. This becomes an issue in wet areas and will cause insulation failure. There are other issues relating to inducing corrosion. A friend who coincidentally keeps his boat in RI and is the technical support guru for a company that sells variable frequency drives (inverters for AC motors) had to replace his propellers when he used an inverter he bought from Harbor Freight. It was probably fine for anything other than marine use. If the neutral on the inverter is not grounded, the neutral can kill you regardless of the presence of a GFCI. Just my thoughts, Ron Ricci S/V Patriot C 37+ Bristol, RI ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated! ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
Interesting topic considering it does reduce down to connecting three wires more or less. The executive overview is that hopefully the inverter, circuit breaker panel and GFCI will come with good instructions on how they need to be wired. At least some of the GFCI are recommended for use in two wire only retrofits. The requirement is that somewhere at the power source there is a ground. These units may come with a sticker saying "non grounded outlet". The test button still works since it jumpers over the sensing circuitry from hot to neutral, no EGC required. Maybe this will explain it a lot better: https://www.nema.org/Products/Documents/NEMA-GFCI-2012-Field-Representative-Presentation.pdf Check out page 14. A point I was commenting on was that even with a correctly wired AC system, EGC and earth ground bonded together at the correct location and everything to spec a person can still get electrocuted. It is a safety requirement though more so to help the utility with lightning strikes and to ensure the OCPD ( circuit breaker ) trips if a load shorts out. Tongue in cheek was the comment that the ground path is likely the current return if a person gets a shock. If there is a problem with the earth ground even a GFCI may not help. In a marina or club if all the grounds are correctly tied together a persons safety is dependent on the quality of the worst installation using shore power. Michael Brown Windburn C 30-1 From: Josh Muckley"So if the inverter is floating and has no ground you cannot get a ground fault shock. If there is a ground wired in you could get a shock but the GFCI should trip. Maybe having the GFCI in is a good thing in that if there was a defect in the load you would never know it without a ground. With it the GFCI would keep tripping letting you know something is wrong." Michael, As you stated the GFCI is comparing the current on both the hot and neutral. When a difference is sensed it trips the GFCI. You mentioned that without a ground the GFCI won't trip. 2 thoughts come to mind. First, without a ground, the GFCI won't trip during a "test". The pushbutton connects a high resistance to the ground prong creating a leak path for current so in that case you're completely right the GFCI won't trip. Second, the GFCI is still sensitive to a difference in current between hot and neutral. You can wire a GFCI ungrounded and it will still trip during a fault. You need a leak path. Most GFCI outlets are sensitive to 5mA. The idea that the inverter is using an ungrounded system and as a result, you won't trip the GFCI sounds synonymous with the idea that since I'm wearing rubber shoes, standing on carpet, in a wood frame house I won't get shocked by the hot. I can tell you from experience, you will get shocked! All of this discussion about floating AC actually gets me thinking about whether or not the GFCI outlet has a disconnect on both the hot and neutral lines. Even if the GFCI trips the neutral prong may still be connected to the neutral wire which in a home isn't a problem, but with a floating AC system you could still be exposed to voltage. We had problems similar to this while on Navy ships. The crew had bought generic computer surge protectors which all needed replaced with high dollar ones since the generic ones only protect the hot terminal. Josh Muckley S/V Sea Hawk 1989 C 37+ Solomons, MD ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
"So if the inverter is floating and has no ground you cannot get a ground fault shock. If there is a ground wired in you could get a shock but the GFCI should trip. Maybe having the GFCI in is a good thing in that if there was a defect in the load you would never know it without a ground. With it the GFCI would keep tripping letting you know something is wrong." Michael, As you stated the GFCI is comparing the current on both the hot and neutral. When a difference is sensed it trips the GFCI. You mentioned that without a ground the GFCI won't trip. 2 thoughts come to mind. First, without a ground, the GFCI won't trip during a "test". The pushbutton connects a high resistance to the ground prong creating a leak path for current so in that case you're completely right the GFCI won't trip. Second, the GFCI is still sensitive to a difference in current between hot and neutral. You can wire a GFCI ungrounded and it will still trip during a fault. You need a leak path. Most GFCI outlets are sensitive to 5mA. The idea that the inverter is using an ungrounded system and as a result, you won't trip the GFCI sounds synonymous with the idea that since I'm wearing rubber shoes, standing on carpet, in a wood frame house I won't get shocked by the hot. I can tell you from experience, you will get shocked! All of this discussion about floating AC actually gets me thinking about whether or not the GFCI outlet has a disconnect on both the hot and neutral lines. Even if the GFCI trips the neutral prong may still be connected to the neutral wire which in a home isn't a problem, but with a floating AC system you could still be exposed to voltage. We had problems similar to this while on Navy ships. The crew had bought generic computer surge protectors which all needed replaced with high dollar ones since the generic ones only protect the hot terminal. Josh Muckley S/V Sea Hawk 1989 C 37+ Solomons, MD On Oct 24, 2016 7:07 PM, "Michael Brown via CnC-List"wrote: > I think you have it, that is how a GFCI works. > > In the case of an inverter that is floating use of a ground is a bit of an > oxymoron. > > The principle is that every electron that comes out of one connection has > to go > back to the other connection. If the GFCI is directly connected to the two > connections > on the inverter, then two connections to the load the current should > always be > the same. There is no other path for the electrons to take. > > As Joe points out you should be able to grab either line and stand in a > puddle > of water without getting a shock or tripping the GFCI. There is no path > for the > current back to the other terminal. > > If you add a ground or connect to a ground now there is a second path > likely to whichever side is deemed the neutral. That connection is to the > power source and bypasses the GFCI. So if the ground conducts any > current the flow through the GFCI is not balanced and it will trip. > > The ground lead does not have to connect to the GFCI, maybe it does > but there is no need. > > The two UL standards, which may seem a bit strange at first, make sense > in that they accommodate what may be already in place that the inverter > is connecting to. In a power failure backup mode to a wired building there > will be a ground to neutral bond already at the distribution panel if the > inverter is connecting there. With no utility involved ( off grid ) the > wiring > codes may still require a ground and bonding in the inverter. > > On a boat I do not know what to recommend. If the loads ( appliances ) > are all three prong, all the outlets are wired with ground and the inverter > supports a bonded ground and GFCI maybe that is the way to hook it up. > If the inverter auto switches from battery to shore power then you are > wired normally when on shore power. If the AC is stand alone or a three > pole switch completely disconnects when going to shore power wiring > in a ground and GFCI is not going to hurt. Doesn't help much either. > > So if the inverter is floating and has no ground you cannot get a ground > fault shock. If there is a ground wired in you could get a shock but the > GFCI should trip. Maybe having the GFCI in is a good thing in that if there > was a defect in the load you would never know it without a ground. With > it the GFCI would keep tripping letting you know something is wrong. > > Not that there is ever any wiring problems on old sailboats > > Michael Brown > Windburn > C 30-1 > > > From: Tortuga > > "Similarly with an inverter connected to a battery that is not grounded a > GFCI should > never trip. Theoretically in a floating system the power has to come out > of > the Hot > lead and return in the Neutral. There will never be a ground fault to trip > a GFCI. > There is no ground." > > I'm not an electrician, but my limited understanding is that a Ground > Fault > Circuit Interrupter monitors the hot and neutral leads and
Re: Stus-List Inverter to Outlet Via Extension Cord?
Like 'ground' systems, marine systems are required to connect neutral to ground at the source of power, whether that is somewhere at the top of the dock for shore power, or at the generator or inverter. One of the most important connections at the inverter is from chassis ground to the boat's grounding bus. On a marine inverter, there should be a switch that opens the ground to neutral connection when it is providing pass-through shore power and closes it when it is generating AC power itself. I presume that the WM 1kW versions have a neutral/ground connection within them, but it would be very worth checking! Tim Ex-Mojito Newport, RI > On Oct 24, 2016, at 2:31 PM, Michael Brown via CnC-List >wrote: > > Hopefully the inverter will come with very clear instructions on how to > handle ground and neutral. > > For normal power, ie shore power, this is the US code: > > "The National Electrical Code ( NEC ) requires the AC source to have a > Neutral to ground bond > and that there be only one such bond in the entire AC system." > > So only at the distribution panel is there a bond between neutral and ground. > They should > never be connected together intentionally at the load. This document covers > grounding and > bonding, may also cure insomnia. > > https://www.engineereducators.com/docs/groundingandbonding2-2.pdf > > Grounding an AC system is done to limit the effect of a lightning strike, > maybe an upstream > over voltage fault. Bonding the green wire that comes in a three prong plug ( > also called a > ground ) to Neutral at the distribution panel is to ensure a low resistance > return path for > a fault. So if anything happens the desired effect is that a hot to ground > short will occur > which in turn will cause an over current surge blowing the circuit breakers. > > A person can be electrocuted even with a properly installed and grounded AC > system > without the circuit breakers tripping. > > Unless an inverter has some specific design that uses a ground bonding the > Neutral and > ground together is not going to do much. Check out the last Q from Xantrex > here: > > http://www.xantrex.com/documents/tech-doctor/universal/tech4-universal.pdf > > Similarly with an inverter connected to a battery that is not grounded a GFCI > should > never trip. Theoretically in a floating system the power has to come out of > the Hot > lead and return in the Neutral. There will never be a ground fault to trip a > GFCI. > There is no ground. > > I suppose an inverter manufacturer could create a third connection back to the > power circuit Neutral that bypasses the GFCI. A short to that wire would cause > an imbalance and trip the GFCI. Then you would be connecting a floating > Neutral to the loads "ground" which may be exactly what the Xantrex article > says > not to do. > > Michael Brown > Windburn > C 30-1 > > > > > From: Ron Ricci > > David, > > I've followed some of this thread and have a few concerns where some have > mentioned using an inexpensive inverter. > > Using an inverter that is not intended for marine use or not properly > grounded can cause problems. An inverter can produce short duration spikes > which exceed the insulation rating of most wires. This becomes an issue in > wet areas and will cause insulation failure. > > There are other issues relating to inducing corrosion. A friend who > coincidentally keeps his boat in RI and is the technical support guru for a > company that sells variable frequency drives (inverters for AC motors) had > to replace his propellers when he used an inverter he bought from Harbor > Freight. It was probably fine for anything other than marine use. > > If the neutral on the inverter is not grounded, the neutral can kill you > regardless of the presence of a GFCI. > > Just my thoughts, > > Ron Ricci > S/V Patriot > C 37+ > Bristol, RI > ___ > > This list is supported by the generous donations of our members. If you wish > to make a contribution to offset our costs, please go to: > https://www.paypal.me/stumurray > > All Contributions are greatly appreciated! ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
I think you have it, that is how a GFCI works. In the case of an inverter that is floating use of a ground is a bit of an oxymoron. The principle is that every electron that comes out of one connection has to go back to the other connection. If the GFCI is directly connected to the two connections on the inverter, then two connections to the load the current should always be the same. There is no other path for the electrons to take. As Joe points out you should be able to grab either line and stand in a puddle of water without getting a shock or tripping the GFCI. There is no path for the current back to the other terminal. If you add a ground or connect to a ground now there is a second path likely to whichever side is deemed the neutral. That connection is to the power source and bypasses the GFCI. So if the ground conducts any current the flow through the GFCI is not balanced and it will trip. The ground lead does not have to connect to the GFCI, maybe it does but there is no need. The two UL standards, which may seem a bit strange at first, make sense in that they accommodate what may be already in place that the inverter is connecting to. In a power failure backup mode to a wired building there will be a ground to neutral bond already at the distribution panel if the inverter is connecting there. With no utility involved ( off grid ) the wiring codes may still require a ground and bonding in the inverter. On a boat I do not know what to recommend. If the loads ( appliances ) are all three prong, all the outlets are wired with ground and the inverter supports a bonded ground and GFCI maybe that is the way to hook it up. If the inverter auto switches from battery to shore power then you are wired normally when on shore power. If the AC is stand alone or a three pole switch completely disconnects when going to shore power wiring in a ground and GFCI is not going to hurt. Doesn't help much either. So if the inverter is floating and has no ground you cannot get a ground fault shock. If there is a ground wired in you could get a shock but the GFCI should trip. Maybe having the GFCI in is a good thing in that if there was a defect in the load you would never know it without a ground. With it the GFCI would keep tripping letting you know something is wrong. Not that there is ever any wiring problems on old sailboats Michael Brown Windburn C 30-1 From: Tortuga"Similarly with an inverter connected to a battery that is not grounded a GFCI should never trip. Theoretically in a floating system the power has to come out of the Hot lead and return in the Neutral. There will never be a ground fault to trip a GFCI. There is no ground." I'm not an electrician, but my limited understanding is that a Ground Fault Circuit Interrupter monitors the hot and neutral leads and interrupts the circuit almost instantly if it detects a difference between them. The ground lead does not come into it. The Xantrex Freedom HF 1000 that I mentioned in an earlier post is *UL458* -listed. "The two UL standards differ in how they handle AC system grounding: *UL1741*-listed inverters must allow for the neutral-to-ground bond to *only* occur at the main AC service panel. *UL458*-listed inverters have internal neutral-to-ground switching relays to allow for this bond to occur at the inverter if in off-grid mode, OR at the utility power service if it is connected to a utility hookup." Perhaps I'm missing something. Derek Kennedy SV Tortuga, 30 mk1 Ballantyne's Cove, NS ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
GFCI outlets compare current in the hot and neutral and trip if it is not the same. If an inverter has no connection at all to ground, i.e. a floating AC system, connecting either hot or neutral to ground would have no effect and not trip the ground fault. You could, in theory, sit neck deep in water and hold onto one of the AC wires and not feel a thing. (DO NOT TRY AT HOME) The reason shore power works with GCFI outlets is the neutral and ground are connected. If you come into contact with a hot wire and your body is grounded at all, the current will flow out the hot, through you, and back to ground via some other means than the neutral wire. The ground fault senses this and trips. Likewise leaks and shorts to a grounded piece of equipment would trip it. Do note you can still kill yourself by grabbing hot and neutral. I have a 300 watt and 1000 watt inverter and can switch between them. Either one will trip the ground faults if tested, so they both connect the AC side to ground somehow back through the DC negative connection. I need to go test them and see exactly how. It could be the standard neutral to ground connection or it could be something goofy like the power transistors being grounded at a center point and each side of the AC circuit is on one side of a center ground. Just an FYI, am 99% sure commercial ships got away from grounding issues and use floating AC. Joe Coquina C 35 MK I From: CnC-List [mailto:cnc-list-boun...@cnc-list.com] On Behalf Of Tortuga via CnC-List Sent: Monday, October 24, 2016 15:49 To: cnc-list@cnc-list.com Cc: Tortuga <tortugas...@gmail.com> Subject: Re: Stus-List Inverter to Outlet Via Extension Cord? "Similarly with an inverter connected to a battery that is not grounded a GFCI should never trip. Theoretically in a floating system the power has to come out of the Hot lead and return in the Neutral. There will never be a ground fault to trip a GFCI. There is no ground." I'm not an electrician, but my limited understanding is that a Ground Fault Circuit Interrupter monitors the hot and neutral leads and interrupts the circuit almost instantly if it detects a difference between them. The ground lead does not come into it. The Xantrex Freedom HF 1000 that I mentioned in an earlier post is UL458-listed. "The two UL standards differ in how they handle AC system grounding: UL1741-listed inverters must allow for the neutral-to-ground bond to only occur at the main AC service panel. UL458-listed inverters have internal neutral-to-ground switching relays to allow for this bond to occur at the inverter if in off-grid mode, OR at the utility power service if it is connected to a utility hookup." Perhaps I'm missing something. Derek Kennedy SV Tortuga, 30 mk1 Ballantyne's Cove, NS ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
"Similarly with an inverter connected to a battery that is not grounded a GFCI should never trip. Theoretically in a floating system the power has to come out of the Hot lead and return in the Neutral. There will never be a ground fault to trip a GFCI. There is no ground." I'm not an electrician, but my limited understanding is that a Ground Fault Circuit Interrupter monitors the hot and neutral leads and interrupts the circuit almost instantly if it detects a difference between them. The ground lead does not come into it. The Xantrex Freedom HF 1000 that I mentioned in an earlier post is *UL458* -listed. "The two UL standards differ in how they handle AC system grounding: *UL1741*-listed inverters must allow for the neutral-to-ground bond to *only* occur at the main AC service panel. *UL458*-listed inverters have internal neutral-to-ground switching relays to allow for this bond to occur at the inverter if in off-grid mode, OR at the utility power service if it is connected to a utility hookup." Perhaps I'm missing something. Derek Kennedy SV Tortuga, 30 mk1 Ballantyne's Cove, NS ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
Hopefully the inverter will come with very clear instructions on how to handle ground and neutral. For normal power, ie shore power, this is the US code: "The National Electrical Code ( NEC ) requires the AC source to have a Neutral to ground bond and that there be only one such bond in the entire AC system." So only at the distribution panel is there a bond between neutral and ground. They should never be connected together intentionally at the load. This document covers grounding and bonding, may also cure insomnia. https://www.engineereducators.com/docs/groundingandbonding2-2.pdf Grounding an AC system is done to limit the effect of a lightning strike, maybe an upstream over voltage fault. Bonding the green wire that comes in a three prong plug ( also called a ground ) to Neutral at the distribution panel is to ensure a low resistance return path for a fault. So if anything happens the desired effect is that a hot to ground short will occur which in turn will cause an over current surge blowing the circuit breakers. A person can be electrocuted even with a properly installed and grounded AC system without the circuit breakers tripping. Unless an inverter has some specific design that uses a ground bonding the Neutral and ground together is not going to do much. Check out the last Q from Xantrex here: http://www.xantrex.com/documents/tech-doctor/universal/tech4-universal.pdf Similarly with an inverter connected to a battery that is not grounded a GFCI should never trip. Theoretically in a floating system the power has to come out of the Hot lead and return in the Neutral. There will never be a ground fault to trip a GFCI. There is no ground. I suppose an inverter manufacturer could create a third connection back to the power circuit Neutral that bypasses the GFCI. A short to that wire would cause an imbalance and trip the GFCI. Then you would be connecting a floating Neutral to the loads "ground" which may be exactly what the Xantrex article says not to do. Michael Brown Windburn C 30-1 From: Ron RicciDavid, I've followed some of this thread and have a few concerns where some have mentioned using an inexpensive inverter. Using an inverter that is not intended for marine use or not properly grounded can cause problems. An inverter can produce short duration spikes which exceed the insulation rating of most wires. This becomes an issue in wet areas and will cause insulation failure. There are other issues relating to inducing corrosion. A friend who coincidentally keeps his boat in RI and is the technical support guru for a company that sells variable frequency drives (inverters for AC motors) had to replace his propellers when he used an inverter he bought from Harbor Freight. It was probably fine for anything other than marine use. If the neutral on the inverter is not grounded, the neutral can kill you regardless of the presence of a GFCI. Just my thoughts, Ron Ricci S/V Patriot C 37+ Bristol, RI ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
I have a West Marine 1000 Watt inverter that I wired to a few outlets with no apparent ill effects. I use a shore power sensing relay I got from West to switch them between inverter and shore power. I used a GFCI outlet and it works when I test it. I have not tested a neutral>ground leak, maybe I should? The relay switches both hot and neutral wires and the green wire stays common. So far the biggest shock danger I have found with inverters is people assuming the shore power cord being disconnected = no AC power anywhere. (http://www.westmarine.com/buy/kisae-technology--ac-transfer-switches--P014159982?recordNum=18) Joe Coquina -Original Message- From: CnC-List [mailto:cnc-list-boun...@cnc-list.com] On Behalf Of Ron Ricci via CnC-List Sent: Monday, October 24, 2016 09:20 To: cnc-list@cnc-list.com Cc: Ron Ricci <rvri...@gmail.com> Subject: Re: Stus-List Inverter to Outlet Via Extension Cord? David, I've followed some of this thread and have a few concerns where some have mentioned using an inexpensive inverter. Using an inverter that is not intended for marine use or not properly grounded can cause problems. An inverter can produce short duration spikes which exceed the insulation rating of most wires. This becomes an issue in wet areas and will cause insulation failure. There are other issues relating to inducing corrosion. A friend who coincidentally keeps his boat in RI and is the technical support guru for a company that sells variable frequency drives (inverters for AC motors) had to replace his propellers when he used an inverter he bought from Harbor Freight. It was probably fine for anything other than marine use. If the neutral on the inverter is not grounded, the neutral can kill you regardless of the presence of a GFCI. Just my thoughts, Ron Ricci S/V Patriot C 37+ Bristol, RI David via CnC-List <cnc-list@cnc-list.com> wrote: We have minimal inverter needs and would like to wire the 1000w inverter directly to a dedicated outlet. It does not have power outputs but two receptacles for plugs. I believe I can wire an extension cord to a outlet (assuming adequately rated and quality components), but I would like to know of any pitfalls that others may have found. Thanks in advance. David F. Risch (401) 419-4650 (cell) ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated! ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
David, I've followed some of this thread and have a few concerns where some have mentioned using an inexpensive inverter. Using an inverter that is not intended for marine use or not properly grounded can cause problems. An inverter can produce short duration spikes which exceed the insulation rating of most wires. This becomes an issue in wet areas and will cause insulation failure. There are other issues relating to inducing corrosion. A friend who coincidentally keeps his boat in RI and is the technical support guru for a company that sells variable frequency drives (inverters for AC motors) had to replace his propellers when he used an inverter he bought from Harbor Freight. It was probably fine for anything other than marine use. If the neutral on the inverter is not grounded, the neutral can kill you regardless of the presence of a GFCI. Just my thoughts, Ron Ricci S/V Patriot C 37+ Bristol, RI David via CnC-Listwrote: We have minimal inverter needs and would like to wire the 1000w inverter directly to a dedicated outlet. It does not have power outputs but two receptacles for plugs. I believe I can wire an extension cord to a outlet (assuming adequately rated and quality components), but I would like to know of any pitfalls that others may have found. Thanks in advance. David F. Risch (401) 419-4650 (cell) ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
Your basic "modified sine" cheap inverter has two hot connections, neither of which can be connected to ground. There is no "neutral". So long as you understand this, then ok. What it means is that if you connect to a single outlet as you describe, or to a string of outlets, what would otherwise be the neutral must not connect to the ground anywhere. Ever. Steve Thomas C MKIII Port Stanley, ON David via CnC-Listwrote: We have minimal inverter needs and would like to wire the 1000w inverter directly to a dedicated outlet. It does not have power outputs but two receptacles for plugs. I believe I can wire an extension cord to a outlet (assuming adequately rated and quality components), but I would like to know of any pitfalls that others may have found. Thanks in advance. David F. Risch (401) 419-4650 (cell) ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Re: Stus-List Inverter to Outlet Via Extension Cord?
Use a GFCI outlet at the least. > On Oct 23, 2016, at 2:24 PM, David via CnC-Listwrote: > > We have minimal inverter needs and would like to wire the 1000w inverter > directly to a dedicated outlet. It does not have power outputs but two > receptacles for plugs. > > > I believe I can wire an extension cord to a outlet (assuming adequately rated > and quality components), but I would like to know of any pitfalls that others > may have found. > > > Thanks in advance. > > David F. Risch > (401) 419-4650 (cell) > ___ > > This list is supported by the generous donations of our members. If you wish > to make a contribution to offset our costs, please go to: > https://www.paypal.me/stumurray > > All Contributions are greatly appreciated! ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!
Stus-List Inverter to Outlet Via Extension Cord?
We have minimal inverter needs and would like to wire the 1000w inverter directly to a dedicated outlet. It does not have power outputs but two receptacles for plugs. I believe I can wire an extension cord to a outlet (assuming adequately rated and quality components), but I would like to know of any pitfalls that others may have found. Thanks in advance. David F. Risch (401) 419-4650 (cell) ___ This list is supported by the generous donations of our members. If you wish to make a contribution to offset our costs, please go to: https://www.paypal.me/stumurray All Contributions are greatly appreciated!