s Consultant
PO Box 23427
Tigard, ORe 97281-3427
503/452-1201
p.perk...@ieee.org
-Original Message-
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Tuesday, September 19, 2017 2:00 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details ->
e being used.
Brian
-Original Message-
From: mickm [mailto:mjmay...@gmail.com]
Sent: Tuesday, September 19, 2017 1:08 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] power strip details
Ralph,
The IEEE is a not-for-profit organisation, but if there is a chance
of making money they will do s
;
To: EMC-PSTC@listserv.ieee.org
Sent: 19/09/2017 18:56:32
Subject: Re: [PSES] power strip details
I trust all the good background information in C62.41.1 doesn't get
lost when pull the standard in 2018. Hopefully it gets transferred
(and perhaps revised) to a new IEEE std.
I will haza
iance
Engineering
Solar Business
Schneider Electric
-Original Message-
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Tuesday, September 19, 2017 1:17 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
Good info. What is an MSPD?
With best wishes DESIGN IT IN
n.co.uk J M Woodgate and
Associates Rayleigh England
UK is a sovereignty, not a Zollverein-ty
From: Adam Dixon [mailto:lanterna.viri...@gmail.com]
Sent: Tuesday, September 19, 2017 9:32 AM
To: John Woodgate
Cc: EMC-PSTC@listserv.ieee.org
Subject: Re: [PSES] power strip details
>Fr
...@gmail.com]
> Sent: Tuesday, September 19, 2017 8:51 AM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: [PSES] power strip details
>
> IEEE Std. C62.41.1 (2002 - reaffirmed 2008) contains a mountain of
> information. If you go to A.2.2.3 Voltages induced in cables adjacent to
> d
:51 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] power strip details
IEEE Std. C62.41.1 (2002 - reaffirmed 2008) contains a mountain of information.
If you go to A.2.2.3 Voltages induced in cables adjacent to down-conductors, it
covers the induced voltage in an open-circuit loop by a nearby
...@gmail.com
https://ictsp-essays.info
-- Original Message --
From: "Richard Nute"
To: EMC-PSTC@listserv.ieee.org
Sent: 18/09/2017 18:58:00
Subject: Re: [PSES] power strip details
Hi Ralph:
Thanks for the reference. My comments are validated by ANSI C62.41.1 .
Best regards
@LISTSERV.IEEE.ORG
Subject: RE: [PSES] power strip details
While I agree that an SPD at the service entrance seems to be the way to
suppress surges resulting from direct/near/far lightning strokes, ANSI C62.4.1
writes about switching transients on circuits which cause oscillatory surges on
the mains. SPD at
: [PSES] power strip details
I believe the principal culprit is the extreme magnetic field that surrounds
the conductors when the surge protector operates rather than the current in the
PE conductor. This field can generate high voltages in adjacent and nearby
low-voltage conductors such as
: [PSES] power strip details
While I agree that an SPD at the service entrance seems to be the way to
suppress surges resulting from direct/near/far lightning strokes, ANSI C62.4.1
writes about switching transients on circuits which cause oscillatory surges on
the mains. SPD at service entrance
From: mickm [mailto:mjmay...@gmail.com]
Sent: Saturday, September 16, 2017 1:40 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] power strip details
John,
It seems to me that TC 108 documents really devise surge protection
component tests rather that complete equipment tests and
of the other branches.
Rich
From: mickm [mailto:mjmay...@gmail.com]
Sent: Saturday, September 16, 2017 1:40 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] power strip details
John,
It seems to me that TC 108 documents really devise surge protection
component tests rather
equipment. Looks like a win-win situation for MSPD manufacturers.
Regards,
Mick Maytum
Safety and Telecom
Standards
mjmay...@gmail.com
Ictsp-essays.info
-- Original Message --
From: "John Woodgate"
To: EMC-PSTC@listserv.ieee.org
Sent: 16/09/2017 08:04:59
Subject: Re: [P
igh England
UK is a sovereignty, not a Zollverein-ty
From: Richard Nute [mailto:ri...@ieee.org]
Sent: Friday, September 15, 2017 10:56 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
In my opinion, surge suppression in a power strip or in a product may
protec
riginal Message-
From: Richard Nute [mailto:ri...@ieee.org]
Sent: Friday, September 15, 2017 6:34 PM
To: Nyffenegger, Dave; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] power strip details
Only codes have free access. Couldn't find the handbook in free access.
Rich
-Origin
Only codes have free access. Couldn't find the handbook in free access.
Rich
-Original Message-
From: Nyffenegger, Dave [mailto:dave.nyffeneg...@bhemail.com]
Sent: Friday, September 15, 2017 1:45 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
Free a
t: Re: [PSES] power strip details
In my opinion, surge suppression in a power strip or in a product may protect
the local environment from overvoltage, but may create additional overvoltages
elsewhere on the system.
Many surge suppression techniques place a momentary short-circuit on the mains.
Subject: Re: [PSES] power strip details
I invite you to also read the Preface in the NEC 2014 Handbook. It provides an
interesting history.
Ralph McDiarmid
Product Compliance
Engineering
Solar Business
Schneider Electric
-Original Message-
From: Richard Nute [mailto:ri...@ieee.org]
Sent
overvoltages.
Rich
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, September 15, 2017 9:15 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
John,
I think surge suppression on power strips is more of a Marketing Gimmick
than anything. We all know
PM
To: Ralph McDiarmid ;
EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] power strip details
"Apparently, the NEC 'code' was derived originally from the IEC."
Not according to Mike Holt. See:
http://www.mikeholt.com/nec-history-a
AM
To: Ralph McDiarmid
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
The NEC does allow 100% rated breakers, as long as they are Listed for this
purpose and used inside a proper enclosure (such that operation is not outside
the Listing test parameters). More information
"Apparently, the NEC 'code' was derived originally from the IEC."
Not according to Mike Holt. See:
http://www.mikeholt.com/nec-history-and-purpose.php
Rich
-
This message is from the IEEE Product Safety Engineering Society emc-ps
tric
From: Pete Perkins [mailto:0061f3f32d0c-dmarc-requ...@ieee.org]
Sent: Thursday, September 14, 2017 9:55 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] power strip details
Esteemed colleagues,
Here in North America a domestic or commercial multi-outlet
power strip would
; Product Compliance
> Engineering
> Solar Business
> Schneider Electric
>
>
> From: Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org]
> Sent: Friday, September 15, 2017 6:35 AM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: Re: [PSES] power strip details
>
> The r
nce
Engineering
Solar Business
Schneider Electric
From: Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org]
Sent: Friday, September 15, 2017 6:35 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
The rating on a North American circuit breaker is not its trip current.
; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] power strip details
Is this surge suppression a) effective, b) necessary? I have seen comments that
suggest 'No' for both a) and b).
With best wishes DESIGN IT IN! OOO - Own Opinions Only
www.jmwa.demon.co.uk<http://www.jmwa.demon.co.uk/&
52-1201
<mailto:p.perk...@ieee.org> p.perk...@ieee.org
From: Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org]
Sent: Friday, September 15, 2017 6:35 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
The rating on a North American circuit breaker is
503/452-1201
<mailto:p.perk...@ieee.org> p.perk...@ieee.org
From: John Allen [mailto:09cc677f395b-dmarc-requ...@ieee.org]
Sent: Friday, September 15, 2017 7:31 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
Ted
Thanks for correcting me on breaker c
13:44
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
This is slightly off topic but you might find this interesting. People are
too smart for their own good.
When Yanks travel to Europe, they bring along their phone chargers, computer
chargers, notepad chargers, razer chargers,
at "Live" &
"Neutral" connections on the US sockets & plugs are the opposite way around
to those on the UK BS 1363 sockets & plugs! J)
From: Nyffenegger, Dave [mailto:dave.nyffeneg...@bhemail.com]
Sent: 15 September 2017 14:07
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subj
Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org]
Sent: 15 September 2017 14:35
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
The rating on a North American circuit breaker is not its trip current. It
is the rated current. UL 489 requires circuit breakers
t]
Sent: 15 September 2017 13:16
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] power strip details
Pete,
Before last year's TC108 meeting in Frankfurt, I purchased a German Schucko
European Power Strip from Amazon. It had 3 AC receptacles and 2 US
-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
This is slightly off topic but you might find this interesting. People are too
smart for their own good.
When Yanks travel to Europe, they bring along their phone chargers, computer
chargers, notepad chargers, razer chargers, etc., a
Europe and plug it in, BAM!! SMOKE!!!
I know two people who have done this.
Enjoy your weekend.
The Other Brian
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Friday, September 15, 2017 8:29 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
Yes, the marking on
ption of a very few devices certified on both
continents) recognized on the "opposite" sides of "The Pond".
John Allen
W. London, UK
From: Don Gies [mailto:ddg...@verizon.net]
Sent: 15 September 2017 13:16
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip det
PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
Pete,
Before last year's TC108 meeting in Frankfurt, I purchased a German Schucko
European Power Strip from Amazon. It had 3 AC receptacles and 2 USB
outputs.
Its ratings are:
"Maximum Charge: 3680W,16A/250V~
erizon.net
(732) 207-7828
From: John Allen [mailto:09cc677f395b-dmarc-requ...@ieee.org]
Sent: Friday, September 15, 2017 4:32 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
Unlike the US/Canada (etc), there is no derating factor for UK mains wall
outlets. A 1
in detail on
what it requires.
John Allen
W.London, UK
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: 15 September 2017 07:36
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] power strip details
UK household power strips are rated at 13 A and include a 13 A fuse. Oth
uk J M Woodgate and
Associates Rayleigh England
UK is a sovereignty, not a Zollverein-ty
From: Pete Perkins [mailto:0061f3f32d0c-dmarc-requ...@ieee.org]
Sent: Friday, September 15, 2017 5:55 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] power strip details
Esteemed coll
Esteemed colleagues,
Here in North America a domestic or commercial multi-outlet
power strip would be cord connected thru a duplex outlet protected by a 15A
(or sometimes 20A) circuit breaker. The max load allowed in the circuit by
the US NEC would be (80% of 15A) 12A for the t
41 matches
Mail list logo