RE: current carrying conductors

2001-08-20 Thread Peter Tarver
The following is from a separate e-mail I sent to Richard Stone that I though the rest of the group might find interest in. In this e-mail exchange, the US NEC was referenced and so the following is based on the US NEC. In your post, you did not specify whether the conductors were a part of th

Re: current carrying conductors

2001-08-18 Thread Rich Nute
Hi Richard: A number of good comments have been made. I'm not sure anyone covered the fact that two wires make a bundle, and therefore each single in that bundle must be derated. So, a single 10 AWG is good for 32 amps at 20 C. But, two 10 AWG wires in the same bundle are only good for 31

Re: current carrying conductors

2001-08-17 Thread Doug McKean
According to the Belden wire table, 10awg carrying 32 amps will produce a 35C rise above ambient. And according to them, the bundling factor is 1.0 for 1, 2, or 3 bundled wires. If you're qualifying anything up around 40C high temp, your wire's going to be 75C. 5C doesn't give you much ove

RE: current carrying conductors

2001-08-17 Thread Scott Lacey
...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Stone, Richard A (Richard) Sent: Friday, August 17, 2001 9:01 AM To: emc-p...@majordomo.ieee.org Subject: current carrying conductors Group, can you substitute one large wire 6 awg. ( handlles 63 amps. max ) for two smaller wires

RE: current carrying conductors

2001-08-17 Thread Peter Tarver
Yes. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com > -Original Message- > From: owner-emc-p...@majordomo.ieee.org > [mailto:owner-emc-p...@majordomo.ieee.org]On > Behalf Of Stone, Richard A > (Richard) > > Group, > > can yo

Re: current carrying conductors

2001-08-17 Thread Andrew Carson
As a quick and simple answer, No. In a single fault condition, one cable becomes lose / detached. The reaming 32 amp capable see the full 63 amps. The result smoke, flame, etc. Expressly forbidden in some standards and knocked out by others under the single fault conditions. Only way to do this i

Re: current carrying conductors

2001-08-17 Thread SERGIO LUIZ DA ROCHA LOURES SERGIO
What happen, if one of these wire looses? Sérgio Rocha Loures Siemens Ltda. - Brazil Supply Chain - Quality and Engineering IC SC QE L Tel: +55 41 341-5755 Fax: +55 41 341-5058 E-mail: sergioro...@siemens.com.br >>> "Stone, Richard A (Richard)" 17/08/01 10:01 >>> Group, can you substitute on

current carrying conductors

2001-08-17 Thread Stone, Richard A (Richard)
Group, can you substitute one large wire 6 awg. ( handlles 63 amps. max ) for two smaller wires ( 10 awg. carries 32 amps. max. ) in Parallel. They would 1/2 the current and disperse heat better. The accepting screw terminal would allow for proper threading and tightness of connection. since yo