RE: limited current circuits in IT equipment

2007-05-07 Thread emc-p...@ieee.org
From: Scott Aldous Sent: Friday, May 04, 2007 3:14 PM If a fuse or circuit breaker is used, then the short circuit current limit is actually 1000 divided by the open circuit voltage, per table 2C Care should be taken here. Maximum available current might not occur at short-circuit.

RE: limited current circuits in IT equipment

2007-05-04 Thread emc-p...@ieee.org
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of ted.eck...@apcc.com Sent: Friday, May 04, 2007 2:44 PM To: oconne...@tamuracorp.com Cc: emc-p...@ieee.org Subject: Re: limited current circuits in IT equipment Hello Brian, Under IEC 60950-1:2005 clause 2.1.1, bare parts of a SELV

Re: limited current circuits in IT equipment

2007-05-04 Thread emc-p...@ieee.org
Hello Brian, Under IEC 60950-1:2005 clause 2.1.1, bare parts of a SELV circuit may be accessible to the operator. Limited current circuits need not be at SELV voltages. They are specified as a circuit that doesn't have the current capability such that there is hazardous energy

RE: limited current circuits in IT equipment

2007-05-04 Thread emc-p...@ieee.org
Brian - Contact with an SELV circuit where there's no energy hazard is acceptable, regardless of other construction features (assuming those other construction features also comply with the standard). One presumes your client understand there's a fire hazard associated with a 10 A circuit.

limited current circuits in IT equipment

2007-05-04 Thread emc-p...@ieee.org
A customer would like a 10Vdc/8A contact to be exposed to the end user. I would like to say no because this would not meet the requirement for an LCC ckt. But as I read from the sacred scrolls of 60950-1, it was noted that if the exposed part is not at a Hazardous voltage (reliably SELV) or

Re: Limited Current

2001-09-18 Thread John Woodgate
I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in 200109181539.iaa02...@epgc196.sdd.hp.com) about 'Limited Current', on Tue, 18 Sep 2001: No, I am not sure that there would be measurable x-radiation at the faceplate of an 8 kV 1-inch crt. But, based on the above technical facts, I

Re: Limited Current

2001-09-18 Thread Rich Nute
Hi John: Are you sure that you can get appreciable X-radiation at 8 kV? In the days of monochrome TV with 9 and 12 inch tubes running at 8 kV, we never bothered about X rays, but projection sets running at 25 kV were known as a radiation hazard. Maybe tolerance levels have been

Re: Limited Current

2001-09-18 Thread John Woodgate
I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in 200109172148.oaa00...@epgc196.sdd.hp.com) about 'Limited Current', on Mon, 17 Sep 2001: Beware of x-radiation from this crt. Larger crt's operating at 8 kV have relatively thick faceplates which attenuate the x-radiation

Re: Limited Current

2001-09-17 Thread Rich Nute
. Except as permitted in 2.4.6, segregation of parts of LIMITED CURRENT CIRCUITS from other circuits shall be as described in 2.3 for SELV Circuits So what this tells me is if the stored charge is less than 45 uC (2.4.6), it is considered safe with only basic

Limited Current

2001-09-17 Thread Rick Busche
, segregation of parts of LIMITED CURRENT CIRCUITS from other circuits shall be as described in 2.3 for SELV Circuits So what this tells me is if the stored charge is less than 45 uC (2.4.6), it is considered safe with only basic insulation? If over the stored charge limit, it must

Re: UL1950 and Clause 2.4.2, Limited Current Circuits

1998-06-19 Thread Peter E. Perkins
PSNet, Rich is absolutely correct... and this use of the 990 network is being recommended as an update to 950 - in a future update to the standard... The advantage of this network is that one does not have to look at each harmonic individually; the network does that and sums them into

Re: UL1950 and Clause 2.4.2, Limited Current Circuits

1998-06-18 Thread Rich Nute
Dear Group, 2.4.2 of UL1950 defines the upper current limit for Limited Current Circuits when the frequency is above 1kHz as 0.7mA multiplied by the frequency in kilohertz (up to 70mA peak). Since the limit increases (up to 70mA) as the frequency goes up, one can assume

Re: UL1950 and Clause 2.4.2, Limited Current Circuits

1998-06-11 Thread ed . price
--- On Thu, 11 Jun 1998 19:50:14 +0900 F.Goto go...@a-pex.co.jp wrote: Dear Group, 2.4.2 of UL1950 defines the upper current limit for Limited Current Circuits when the frequency is above 1kHz as 0.7mA multiplied by the frequency in kilohertz (up to 70mA peak). Since the limit increases

UL1950 and Clause 2.4.2, Limited Current Circuits

1998-06-11 Thread F.Goto
Dear Group, 2.4.2 of UL1950 defines the upper current limit for Limited Current Circuits when the frequency is above 1kHz as 0.7mA multiplied by the frequency in kilohertz (up to 70mA peak). Since the limit increases (up to 70mA) as the frequency goes up, one can assume that the human body