Re: back up generator question

2010-11-07 Thread Cliff Rediger
On Nov 2, 7:04 am, ah...clem boneheads...@gmail.com wrote:
 you absolutely MUST have a high quality UPS

I have a APC UPS before our wifi antenna and router AND another APC
UPS before my mini and external drives
so I'm hearing that I should be OK.

 will you
 put the generator outside and run an extension cord in thru a door or
 window?   generators are quite noisy, and an open window, even a
 crack, will let a lot of cold air in.

That's the plan exactly. Not ideal but could work for short outages.

We have a 50KW generator on the property with a auto transfer switch
which serves the main house,
but since there are three meters on the property I guess it didn't
work to
connect the service cottage to the auto system and generator.

The third power drop feeds the well pump, water clarifying equipment,
and
water pressure pump that serve the entire property.
i figure in a pinch I can power cord connect some refrigeration
located at this location as well.
This connection has a manual transfer switch that allows manual hook
up to our 7K Honda powered Dayton portable.

I'm consistently amazed by and appreciative for this List.
It's an invaluable resource of generous expert advise and friendly
helpful opinion.

This thread has been especially interesting: besides providing some
assurance regarding the generator hook up,
it also prompted me to turn off my external drives until they are
needed.

thank you,
Cliff

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-11-07 Thread Cliff Rediger


On Nov 7, 6:07 pm, Cliff Rediger redicl...@yahoo.com wrote:

 That's the plan exactly. Not ideal but could work for short outages.

P.S.  I bought this small generator with the intention of powering
electric tools in the field.
Mostly, I want to power a pneumatic pole chain saw so that I can prune
or 50 yr old walnut trees.
Jury is still out on that one.

Thank you
Cliff

Love's Point Blog: http://4lovespoint.wordpress.com/ (new post
10/31/10)
Peace-Gardens.us:http://peace-gardens.us/  (updated regularly)
Not-Two-Is-Peace: http://www.ispeace723.org/

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-11-02 Thread ah...clem
we live in a rural area, and power outages occasionally last for
days.  we have a generator for such situations, and i run all sorts of
electronics on them.  BUT, you absolutely MUST have a high quality UPS
on any sensitive electronics, or you risk catastrophic failure.  the
output of that generator is NOT a clean sine wave, nor is it
continuously constant voltage or frequency.  a good UPS will correct
this.  and BECAUSE you are running a mini, which does NOT have a
regulated power supply like a desktop and only has a simple rectified
transformer PS, it will be particularly vulnerable.  anyone who says
otherwise thinks they know a lot more than they actually know.  also,
how do you plan to connect your computer to the generator?  will you
put the generator outside and run an extension cord in thru a door or
window?   generators are quite noisy, and an open window, even a
crack, will let a lot of cold air in.  if you wire it thru the main
service entrance of your house, 800 W is certainly not enough to power
the devices that will come on automatically, like the refrigerator,
furnace, etc.  when those kick on automatically, they will overload
the 800 W generator and burn it out.

i suggest that you go the whole 9 yards and get a minimum of 5000 W
generator, and wire it thru the main service entrance, so you can also
have heat and refrigeration, etc, during the power outages.  but you
must arrange it so that you can disconnect from the power grid while
the generator is connected, otherwise when the power comes back on, it
will almost certainly be out-of-phase with the generator, and cause
the generator to fry.  it's not that difficult to do, just add a 50
Amp dual breaker to the box and wire the output of the generator IN
thru that breaker, making sure that the MAIN breaker is off, before
you connect the generator.  you could also spend several thousand
dollars on a device that does this automatically, but if you can
understand how to use a computer, you should be able to handle
throwing a couple of switches in the correct sequence.  then when
there is a power outage and you disconnect from the grid to run your
generator, simply phone the power company and request a courtesy call
to let you know when the power is restored, at which time you will
first disconnect the generator and then turn the MAIN breaker back on.


On Oct 29, 4:44 pm, Cliff Rediger redicl...@yahoo.com wrote:
 We live in a rural area where power outages occur commonly.
 I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
 Electric Generators

 http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-g...

 in hopes of having back up power to run our WiFi ISP antenna,
 computers and a light or two.
 But, then I seem recalling that there are possible issues in the type
 of power a generator provides and the type computers like to receive.

 Comments and advice appreciated.

 Cliff

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-11-02 Thread Alex Smith (K4RNT)
I believe a transfer switch is a requirement per the National Electric
Code if you want to hook up a generator directly the your home mains.
If anyone goes wrong you could be CRIMINALLY LIABLE, not only for
causing a potential electrical fire, but to damage the power grid.

I suggest you consult an electrician from this point on for help.

Also, transfer switches aren't that expensive when you're talking
about electrical equipment to have in a house. They can cost up to
1000 dollars, potentially more, but that's only if you have a large
number of circuits to connect.

http://www.apcc.com/products/family/index.cfm?id=371

On Tue, Nov 2, 2010 at 09:04, ah...clem boneheads...@gmail.com wrote:
 we live in a rural area, and power outages occasionally last for
 days.  we have a generator for such situations, and i run all sorts of
 electronics on them.  BUT, you absolutely MUST have a high quality UPS
 on any sensitive electronics, or you risk catastrophic failure.  the
 output of that generator is NOT a clean sine wave, nor is it
 continuously constant voltage or frequency.  a good UPS will correct
 this.  and BECAUSE you are running a mini, which does NOT have a
 regulated power supply like a desktop and only has a simple rectified
 transformer PS, it will be particularly vulnerable.  anyone who says
 otherwise thinks they know a lot more than they actually know.  also,
 how do you plan to connect your computer to the generator?  will you
 put the generator outside and run an extension cord in thru a door or
 window?   generators are quite noisy, and an open window, even a
 crack, will let a lot of cold air in.  if you wire it thru the main
 service entrance of your house, 800 W is certainly not enough to power
 the devices that will come on automatically, like the refrigerator,
 furnace, etc.  when those kick on automatically, they will overload
 the 800 W generator and burn it out.

 i suggest that you go the whole 9 yards and get a minimum of 5000 W
 generator, and wire it thru the main service entrance, so you can also
 have heat and refrigeration, etc, during the power outages.  but you
 must arrange it so that you can disconnect from the power grid while
 the generator is connected, otherwise when the power comes back on, it
 will almost certainly be out-of-phase with the generator, and cause
 the generator to fry.  it's not that difficult to do, just add a 50
 Amp dual breaker to the box and wire the output of the generator IN
 thru that breaker, making sure that the MAIN breaker is off, before
 you connect the generator.  you could also spend several thousand
 dollars on a device that does this automatically, but if you can
 understand how to use a computer, you should be able to handle
 throwing a couple of switches in the correct sequence.  then when
 there is a power outage and you disconnect from the grid to run your
 generator, simply phone the power company and request a courtesy call
 to let you know when the power is restored, at which time you will
 first disconnect the generator and then turn the MAIN breaker back on.


 On Oct 29, 4:44 pm, Cliff Rediger redicl...@yahoo.com wrote:
 We live in a rural area where power outages occur commonly.
 I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
 Electric Generators

 http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-g...

 in hopes of having back up power to run our WiFi ISP antenna,
 computers and a light or two.
 But, then I seem recalling that there are possible issues in the type
 of power a generator provides and the type computers like to receive.

 Comments and advice appreciated.

 Cliff

 --
 You received this message because you are a member of G-Group, a group for 
 those using G3, G4, and G5 desktop Macs - with a particular focus on Power 
 Macs.
 The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
 guide is at http://www.lowendmac.com/lists/netiquette.shtml
 To post to this group, send email to g3-5-list@googlegroups.com
 For more options, visit this group at http://groups.google.com/group/g3-5-list




-- 
 ' With the first link, the chain is forged. The first speech
censured, the first thought forbidden, the first freedom denied,
chains us all irrevocably.' Those words were uttered by Judge Aaron
Satie as wisdom and warning... The first time any man's freedom is
trodden on we’re all damaged. - Jean-Luc Picard, quoting Judge Aaron
Satie, Star Trek: TNG episode The Drumhead
- Alex Smith (K4RNT)
- Murfreesboro, Tennessee USA

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-31 Thread Tina K.

On 2010/10/30 20:26, Clark Martin so eloquently wrote:

On Oct 30, 2010, at 5:48 PM, Tina K. wrote:


My Power Mac draws about 500 watts, a Mac Mini is going to use
significantly less, and external HDDs use very little. 800 watts
is more than enough for those two devices.


It's unlikely your PM draws 500 W.  It's power supply is rated for
around that much but actual use is rarely even close to that.  I
haven't tested any PM G4 but the PM G3 BW I tested drew 67 W.

It would be hard to draw 500W, even with the monitor running off the
PM's power supply.


According to Mactracker the maximum wattage for my PM is 604 watts. 
Given that it runs both CPUs at 100% at all times the power consumption 
has to be high considering the amount of heat it puts out. As I 
mentioned previously I have yet to close the window in that room despite 
overnight freezing temperatures.


Tina

--

iMac 20 USB 2 1.25GHz G4 2GB RAM GeForce FX 5200 Ultra 64MB DDR Ubuntu
10.10

Power Mac June 04 2GHz G5DP 8GB RAM GeForce 6800 Ultra DDL 256MB Leopard
10.5.8

PowerBook G4 15 HiRes DLSD 1.67GHz G4 2GB RAM Radeon 9700 128MB DDR
Leopard 10.5.8

--
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-31 Thread Clark Martin

On Oct 30, 2010, at 11:40 PM, Tina K. wrote:

 On 2010/10/30 20:26, Clark Martin so eloquently wrote:
 On Oct 30, 2010, at 5:48 PM, Tina K. wrote:
 
 My Power Mac draws about 500 watts, a Mac Mini is going to use
 significantly less, and external HDDs use very little. 800 watts
 is more than enough for those two devices.
 
 It's unlikely your PM draws 500 W.  It's power supply is rated for
 around that much but actual use is rarely even close to that.  I
 haven't tested any PM G4 but the PM G3 BW I tested drew 67 W.
 
 It would be hard to draw 500W, even with the monitor running off the
 PM's power supply.
 
 According to Mactracker the maximum wattage for my PM is 604 watts. Given 
 that it runs both CPUs at 100% at all times the power consumption has to be 
 high considering the amount of heat it puts out. As I mentioned previously I 
 have yet to close the window in that room despite overnight freezing 
 temperatures.
 

I just checked my dual CPU MDD.  It draws 117 Watts.  The CPUs simply CAN NOT 
draw hundreds of watts.

Clark Martin
Redwood City, CA, USA
Macintosh / Internet Consulting

I'm a designated driver on the Information Super Highway

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-31 Thread JoeTaxpayer


On Oct 31, 2:40 am, Tina K. penguir...@gmail.com wrote:
 On 2010/10/30 20:26, Clark Martin so eloquently wrote:

  On Oct 30, 2010, at 5:48 PM, Tina K. wrote:

  My Power Mac draws about 500 watts, a Mac Mini is going to use
  significantly less, and external HDDs use very little. 800 watts
  is more than enough for those two devices.

  It's unlikely your PM draws 500 W.  It's power supply is rated for
  around that much but actual use is rarely even close to that.  I
  haven't tested any PM G4 but the PM G3 BW I tested drew 67 W.

  It would be hard to draw 500W, even with the monitor running off the
  PM's power supply.

Agreed. I have a full up MDD 1.25GHz G4. (Full = 4 drives. 2GB memory,
etc)
A kill-a-watt device tells me it draws 160W.

Slight tangent - at 15 cents/KWH each 100W costs $131/yr for a 24/7
device. Nearly $210/yr to power this. As it was an extra, used as a
server for TiVo shows, I now keep it off unless it's called to
action.

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-31 Thread Doug McNutt
At 21:29 -0400 10/30/10, Kevin Barth wrote:
All generators are NOT created equal.  Some produce MUCH cleaner output than 
others.  Spikes and surges can destroy sensitive electronics.  Square 
Wave-producing generators may power lights and freezers just fine, but they 
will not work well with computers.

Square wave producing inverters, electronic devices that convert DC to AC are 
common.  Generators or alternators that generate electricity from a moving 
shaft driven by some kind of engine just don't do that. Perhaps you're thinking 
about a solar panel that converts DC to AC using an inverter.

But the real point is that  computers of the G4 time period will run fine on 
160 volts or so DC of either polarity, let alone square waves. Really old 
stuff, think Apple II, used input power transformers and 60 Hz fans which do 
demand AC power.

It's conceivable that very new power converters in modern electronics need sine 
waves because of circuitry that guarantees low harmonic content in the current 
drawn by the computer. That kind of circuitry is going to be required in the 
likes of LED and compact florescent lighting but it's not here yet.

Of course any power source needs to include transient overvoltage protection. 
Around here at 7000 feet MSL lightning does that regularly and can appear as a 
kilovolt or so between the ethernet port and the power plug. Nasty, and 
probably worse on city power than on a local generator.

-- 

--  Halloween  == Oct 31 == Dec 25 == Christmas  --

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-31 Thread Clark Martin

On Oct 31, 2010, at 2:24 PM, Doug McNutt wrote:

 At 21:29 -0400 10/30/10, Kevin Barth wrote:
 All generators are NOT created equal.  Some produce MUCH cleaner output than 
 others.  Spikes and surges can destroy sensitive electronics.  Square 
 Wave-producing generators may power lights and freezers just fine, but they 
 will not work well with computers.
 
 Square wave producing inverters, electronic devices that convert DC to AC are 
 common.  Generators or alternators that generate electricity from a moving 
 shaft driven by some kind of engine just don't do that. Perhaps you're 
 thinking about a solar panel that converts DC to AC using an inverter.
 
 But the real point is that  computers of the G4 time period will run fine on 
 160 volts or so DC of either polarity, let alone square waves. Really old 
 stuff, think Apple II, used input power transformers and 60 Hz fans which do 
 demand AC power.

Uh, Apple ][s used a switching power supply.  It was one of the first personal 
computers to do so.  And it had no fan, AC or DC.

But you are right that the average switching power supply is rather insensitive 
to the power feeding it.  In general they are insensitive to electrical noise.  
They are more of a source of noise rather than being sensitive to it.



Clark Martin
Redwood City, CA, USA
Macintosh / Internet Consulting

I'm a designated driver on the Information Super Highway

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread James Pritchett
If the output is a sine wave the computer will like it.  But if the output
is a square wave of modified square wave like from the low end power
inverters some electronic freak out or crash or never takeoff like electric
motors.  Start the generator and test the devices you want to use
with it, you will soon find out if going to work.  SAFETY FIRST

On Fri, Oct 29, 2010 at 1:51 PM, Alex Smith (K4RNT)
shadowhun...@gmail.comwrote:

 You'll probably want to purchase a UPS and a transfer switch as well.

 http://www.apcc.com/products/family/index.cfm?id=165#anchor1
 http://www.apcc.com/products/family/index.cfm?id=371

 You'll also want to make sure that your power is clean from transient
 surges, so a UPS would be a good thing to have, given that most
 higher-end UPSes condition the incoming power.

 Your choice of generator looks OK, but the power rating it provides
 would probably be a little low for this application.

 Hope this helps.

 On Fri, Oct 29, 2010 at 15:44, Cliff Rediger redicl...@yahoo.com wrote:
  We live in a rural area where power outages occur commonly.
  I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
  Electric Generators
 
 
 http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-generator-66619.html

 --
  ' With the first link, the chain is forged. The first speech
 censured, the first thought forbidden, the first freedom denied,
 chains us all irrevocably.' Those words were uttered by Judge Aaron
 Satie as wisdom and warning... The first time any man's freedom is
 trodden on we’re all damaged. - Jean-Luc Picard, quoting Judge Aaron
 Satie, Star Trek: TNG episode The Drumhead
 - Alex Smith (K4RNT)
 - Murfreesboro, Tennessee USA

 --
 You received this message because you are a member of G-Group, a group for
 those using G3, G4, and G5 desktop Macs - with a particular focus on Power
 Macs.
 The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our
 netiquette guide is at http://www.lowendmac.com/lists/netiquette.shtml
 To post to this group, send email to g3-5-list@googlegroups.com
 For more options, visit this group at
 http://groups.google.com/group/g3-5-list




-- 
-
  James D. Pritchett
   15163 S.W. Walker Rd. Apt. G
  Portland OR, 97006-7106
 -

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Jonas Lopez
NONSENSE - what you have will work just fine -- you do NOT need anything else.

Done this for years!.

JML.
--- On Fri, 10/29/10, Alex Smith (K4RNT) shadowhun...@gmail.com wrote:

From: Alex Smith (K4RNT) shadowhun...@gmail.com
Subject: Re: back up generator question
To: g3-5-list@googlegroups.com
Date: Friday, October 29, 2010, 1:51 PM

You'll probably want to purchase a UPS and a transfer switch as well.

http://www.apcc.com/products/family/index.cfm?id=165#anchor1
http://www.apcc.com/products/family/index.cfm?id=371

You'll also want to make sure that your power is clean from transient
surges, so a UPS would be a good thing to have, given that most
higher-end UPSes condition the incoming power.

Your choice of generator looks OK, but the power rating it provides
would probably be a little low for this application.

Hope this helps.

On Fri, Oct 29, 2010 at 15:44, Cliff Rediger redicl...@yahoo.com wrote:
 We live in a rural area where power outages occur commonly.
 I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
 Electric Generators

 http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-generator-66619.html

-- 
 ' With the first link, the chain is forged. The first speech
censured, the first thought forbidden, the first freedom denied,
chains us all irrevocably.' Those words were uttered by Judge Aaron
Satie as wisdom and warning... The first time any man's freedom is
trodden on we’re all damaged. - Jean-Luc Picard, quoting Judge Aaron
Satie, Star Trek: TNG episode The Drumhead
- Alex Smith (K4RNT)
- Murfreesboro, Tennessee USA

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list



  

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Cliff Rediger
On Oct 29, 1:51 pm, Alex Smith (K4RNT) shadowhun...@gmail.com
wrote:
 Your choice of generator looks OK, but the power rating it provides
 would probably be a little low for this application.

not knowing too much about electricity 800 watts seems like a lot for
our use.
How much juice does a mac mini and external HD pull?

I do have a UPS on my computer and one on our WiFi antenna power.

testing sounds right, of course, but I wonder what failure would
look like?
what are the risks?

On Oct 29, 1:51 pm, Jonas Lopes  wrote:
NONSENSE - what you have will work just fine -- you do NOT need anything else.
Done this for years!.

That's encouraging.

Thanks for all the input.

Cliff

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Tina K.

On 2010/10/30 18:43, Cliff Rediger so eloquently wrote:

not knowing too much about electricity 800 watts seems like a lot for
our use.
How much juice does a mac mini and external HD pull?


My Power Mac draws about 500 watts, a Mac Mini is going to use 
significantly less, and external HDDs use very little. 800 watts is more 
than enough for those two devices.


Tina

--

iMac 20 USB 2 1.25GHz G4 2GB RAM GeForce FX 5200 Ultra 64MB DDR Ubuntu 
10.10


Power Mac June 04 2GHz G5DP 8GB RAM GeForce 6800 Ultra DDL 256MB Leopard 
10.5.8


PowerBook G4 15 HiRes DLSD 1.67GHz G4 2GB RAM Radeon 9700 128MB DDR 
Leopard 10.5.8


--
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Kevin Barth
And do you have the same generator he does?  Or are you familiar enough with
the output of the generator he has to make the claim?

All generators are NOT created equal.  Some produce MUCH cleaner output than
others.  Spikes and surges can destroy sensitive electronics.  Square
Wave-producing generators may power lights and freezers just fine, but they
will not work well with computers.

Unless you are sure what your generator produces (and the only way to really
be sure is to hook it up to a scope and look at the resulting wave pattern,
or find someone who has done that), you will be much safer getting some kind
of a power conditioner.  It doesn't have to be anything elaborate.  Just
something with a voltage regulator in it to eliminate spikes and a filter to
convert square waves to sine.   Most decent UPSes will do it, or if you're
handy with a soldering iron, there are schematics for appropriate circuits
on the web.


On Sat, Oct 30, 2010 at 11:20 AM, Jonas Lopez jonaslo...@yahoo.com wrote:

 NONSENSE - what you have will work just fine -- you do NOT need anything
 else.

 Done this for years!.

 JML.

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Daggett Ken


On 30 Oct 2010, at 17:48:13 PDT, Tina K. wrote:


On 2010/10/30 18:43, Cliff Rediger so eloquently wrote:

not knowing too much about electricity 800 watts seems like a lot for
our use.
How much juice does a mac mini and external HD pull?


My Power Mac draws about 500 watts, a Mac Mini is going to use  
significantly less, and external HDDs use very little. 800 watts is  
more than enough for those two devices.

--
Don't forget to add in any other devices such as monitor and such. My  
little 800w Honda does OK, but it takes surprisingly few devices to  
max it out.


Ken

--
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Kevin Barth
 not knowing too much about electricity 800 watts seems like a lot for
 our use.
 How much juice does a mac mini and external HD pull?


Well under 800 Watts.   Depends on what you are using for a monitor, of
course.

Per Apple, Mac Mini (without monitor) uses 85-110 Watts.

http://support.apple.com/kb/HT3468

External hard drive power consumption can be tricky to measure, because
under typical patterns of usage, they tend to spin up and down a lot.   But
even at peak usage, it should consume under 15 watts

http://www.tomshardware.com/reviews/-external-hard-drive,2045-16.html

Add to that whatever monitor you're using.   No LCD monitor of standard size
should exceed the 675 Watts you have left, or come close to doing so.  The
article below may help give you an idea of typical values, or you could
purchase an inexpensive device called a Kill-A-Watt to get a more accurate
reading.

I do have a UPS on my computer and one on our WiFi antenna power.

 testing sounds right, of course, but I wonder what failure would
 look like?
 what are the risks?


Power Spikes: best case scenario, blown fuse or circuit breaker.   worst
case scenario; smoke, explosion, and damage to your computer.

Square Wave instead of sine: best case scenario: no symptoms.   It works
just fine.   Worst case - equipment simply fails to power up, or does so but
doesn't function properly.   Never seen equipment seriously damaged because
it was fed a square wave instead of a sine - it tends to just not work
right.

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Clark Martin

On Oct 30, 2010, at 5:48 PM, Tina K. wrote:

 On 2010/10/30 18:43, Cliff Rediger so eloquently wrote:
 not knowing too much about electricity 800 watts seems like a lot for
 our use.
 How much juice does a mac mini and external HD pull?
 
 My Power Mac draws about 500 watts, a Mac Mini is going to use significantly 
 less, and external HDDs use very little. 800 watts is more than enough for 
 those two devices.
 

It's unlikely your PM draws 500 W.  It's power supply is rated for around that 
much but actual use is rarely even close to that.  I haven't tested any PM G4 
but the PM G3 BW I tested drew 67 W.  

It would be hard to draw 500W, even with the monitor running off the PM's power 
supply.

 Tina
 
 -- 
 
 iMac 20 USB 2 1.25GHz G4 2GB RAM GeForce FX 5200 Ultra 64MB DDR Ubuntu 10.10
 
 Power Mac June 04 2GHz G5DP 8GB RAM GeForce 6800 Ultra DDL 256MB Leopard 
 10.5.8
 
 PowerBook G4 15 HiRes DLSD 1.67GHz G4 2GB RAM Radeon 9700 128MB DDR Leopard 
 10.5.8
 

Clark Martin
Redwood City, CA, USA
Macintosh / Internet Consulting

I'm a designated driver on the Information Super Highway

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-30 Thread Amanda Ward
Hey Cliff...

On Oct 29, 2010, at 1:44 PM, Cliff Rediger wrote:

 We live in a rural area where power outages occur commonly.
 I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
 Electric Generators
 
 http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-generator-66619.html
 
 in hopes of having back up power to run our WiFi ISP antenna,
 computers and a light or two.
 But, then I seem recalling that there are possible issues in the type
 of power a generator provides and the type computers like to receive.
 
 Comments and advice appreciated.
 
 Cliff

There are a few things to consider. A backup generator (or DC to AC invertor) 
might provide a square wave output that your electronics might not like. I had 
one such invertor that trashed the PS for my Sony laptop several years ago. 
I don't know the generator you purchased, but lower end units can provide power 
with spikes/transients that could play havoc with electronic devices. Using a 
UPS to filter the output might be a good idea.

Not saying you have a problem, just offering a couple of thoughts if you do!

We used to have the dreaded rolling blackouts, here in the SF area, a few 
years ago and I had three huge Fortress UPS units to keep the systems running. 
Fortunately, those blackouts are a thing of the past.

Amanda

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


back up generator question

2010-10-29 Thread Cliff Rediger
We live in a rural area where power outages occur commonly.
I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
Electric Generators

http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-generator-66619.html

in hopes of having back up power to run our WiFi ISP antenna,
computers and a light or two.
But, then I seem recalling that there are possible issues in the type
of power a generator provides and the type computers like to receive.

Comments and advice appreciated.

Cliff

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com
For more options, visit this group at http://groups.google.com/group/g3-5-list


Re: back up generator question

2010-10-29 Thread Alex Smith (K4RNT)
You'll probably want to purchase a UPS and a transfer switch as well.

http://www.apcc.com/products/family/index.cfm?id=165#anchor1
http://www.apcc.com/products/family/index.cfm?id=371

You'll also want to make sure that your power is clean from transient
surges, so a UPS would be a good thing to have, given that most
higher-end UPSes condition the incoming power.

Your choice of generator looks OK, but the power rating it provides
would probably be a little low for this application.

Hope this helps.

On Fri, Oct 29, 2010 at 15:44, Cliff Rediger redicl...@yahoo.com wrote:
 We live in a rural area where power outages occur commonly.
 I just purchased a 800 Rated Watts/900 Max Watts Portable  Chicago
 Electric Generators

 http://www.harborfreight.com/800-rated-watts-900-max-watts-portable-generator-66619.html

-- 
 ' With the first link, the chain is forged. The first speech
censured, the first thought forbidden, the first freedom denied,
chains us all irrevocably.' Those words were uttered by Judge Aaron
Satie as wisdom and warning... The first time any man's freedom is
trodden on we’re all damaged. - Jean-Luc Picard, quoting Judge Aaron
Satie, Star Trek: TNG episode The Drumhead
- Alex Smith (K4RNT)
- Murfreesboro, Tennessee USA

-- 
You received this message because you are a member of G-Group, a group for 
those using G3, G4, and G5 desktop Macs - with a particular focus on Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to g3-5-list@googlegroups.com