Re: [MBZ] OT: Generator voltage spikes

2006-12-22 Thread David Brodbeck
Mitch Haley wrote:
 Jim Cathey wrote:
   
 Yes.  This fellow had a 220V generator that did _not_ have a center
 tap, which meant that unless the two 110V sides of the home's wiring
 were _exactly_ balanced as to load (and they never, ever are) one
 side was going to see more than 110V, and one less.  Up to and
 probably including 200+V on one side.
 

 So if I were to hook up a 100W light to one half of the 240 outlet
 on such a genny, I'd get 0v through the lamp and 240v on the open
 side? Now I understand why the motor repair guy told me to do that
 for a test. 
   

Yeah, although in that case no current would flow.  With no center tap,
everything on one side of the outlet is simply in series with everything
on the other side.  In series loads, the current is the same but the
voltage varies.  So if you put two 100W bulbs in, one on each side,
they'd split the voltage 50/50 and each would get 120V.  But if you put
in one 100W bulb and one 60W bulb, the 100W bulb will see 90V and the
60W bulb will see 150V.  The greater the imbalance gets, the higher the
voltage difference will become.  And in a household this would vary as
stuff was turned on and off, making matters worse.




Re: [MBZ] OT: Generator voltage spikes

2006-12-22 Thread Mitch Haley

I have a question about these non center tapped generators.
How do the 110-120v outlets work on these, or do they even
have 120v outlets?

Mitch.




Re: [MBZ] OT: Generator voltage spikes

2006-12-22 Thread Jim Cathey

I have a question about these non center tapped generators.
How do the 110-120v outlets work on these, or do they even
have 120v outlets?


They wouldn't/couldn't.  But the lack of a center tap could
be because it's broken, not because it shouldn't have one.
Best to check!  And of course your self-made cable-of-death
could be wrong, and fry your house goodies.

-- Jim




Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Zeitgeist

Follow up:  It's been nearly a week and we're still without power.  The nice
folks all around me have power, but for some reason I live on a cursed
circuit, which is tied to the worst of the storm damage nearly a mile from
here.  I'm already thinking of ways to create alternatives for powering all
my low amperage needs off of solar and wind with battery backup and storage,
so that this unfortunate stuff doesn't happen in the future.

I have a 3700 watt generator, but don't quite know of a simple means to tie
into my home circuitry to run all my essentials (well, h2o heater,
dishwasher, etc.).  Does anyone make a retro-kit to tie directly into a
preexisting fuse box?  Of course, this includes turning off the main
breaker, so the power doesn't feed back and torch those dudes who will
eventually get to fixing my service when they're damned good and ready.

I've had exactly one shower in that time, which brings the fragrance level
up a few notches around here.  The kids are going stir crazy, and I'd like
to just lock them outside for a few hours to quiet them down, but apparently
the killjoys at DSHS wouldn't take too kindly to my parental/logistical
philosophy.  I purchased another battery for running the modem and puter,
which I swap out with the ones in my two MBs from time to time.

On 12/16/06, Zeitgeist [EMAIL PROTECTED] wrote:


I'm presently without power, and may be for some time, due to recent wind
storm activity.  My generator blew up my surge protector, so I'm running
my DSL modem off of the battery from my van, and using our laptop
w/wireless.  I strongly suspect our generator is malfunctioning and pumping
an unregulated voltage supply, which unfortunately blows stuff up.  Is there
an external voltage rectifying unit I can purchase which will avoid this
situation so it doesn't keep happening every time I fire up the generator?




--
Casey
Olympia, WA
Biodiesel: I drive in a persistent vegetative state
'87 300TD intercooler/propane #22 0-60mph 7.3sec (220k)
'84 300D (218k)
Gashuffer:
'89 Vanagon Wolfsburg Edition (187K)
http://users.zhonka.net/zeitgeist/Misc/IMG_0171.JPG


Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Mitch Haley


Zeitgeist wrote:
 I have a 3700 watt generator, but don't quite know of a simple means to tie
 into my home circuitry to run all my essentials (well, h2o heater,
 dishwasher, etc.). 

What I do (not NEC approved) is wire up a patch cord with a dryer plug
on one end, and a plug that fits the 240v socket on the generator on the
other end. Turn off all the breakers, especially the main. Plug the
generator into your dryer outlet and turn on the dryer breaker. Then
turn on your well pump. Once your tank is full, turn on the fridge,
and maybe the coffee pot and some lights. I do not think you will want
to turn on the electric water heater. I ended up cooking breakfast on
the propane grill because I could not run a single burner on the stove
to cook pancakes with a 5600w generator. I had two freezers and the
fridge going, you might be able to run a stove burner or water heater
if its the only thing you have on. The main breaker stays off until
the generator is detached from the house, you don't want to light up
the guy trying to fix your power line, and you don't want anybody else
messing with your breakers, because they might turn the main on.

Mitch.




Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Mitch Haley


Mitch Haley wrote:
 What I do (not NEC approved) is wire up a patch cord with a dryer plug
 on one end, and a plug that fits the 240v socket on the generator on the
 other end. 

Boy, did I forget something. First test the genny, to make sure it
has two good 120v sides on the 240v circuit. A light bulb will do
for testing. I start by turning on the well pump with my genny, but
I already know my genny won't kill the well pump. If you use the wrong
genny (maybe Jim Cathey can tell us why) the well pump is the most
expensive thing you could fry, so it's a bad place to start.




Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Jim Cathey
I have a 3700 watt generator, but don't quite know of a simple means 
to tie

into my home circuitry to run all my essentials (well, h2o heater,


A male-to-male 'pins-o-death' (as I call it) cable you make up
yourself.  I usually just pick up a dryer plug that mates with
a handy one and flange on a 30A twist-lock 220V plug that mates
with the genny.  If yours has one of those.  If all it has is
two regular 115V outlets things get more interesting, especially
if it isn't built as a center-tapped 220V generator!


dishwasher, etc.).  Does anyone make a retro-kit to tie directly into a
preexisting fuse box?  Of course, this includes turning off the main


No, it's extremely against the electrical code so you'll never be
able to buy one pre-built.


breaker, so the power doesn't feed back and torch those dudes who will
eventually get to fixing my service when they're damned good and ready.


Crucial.  Absolutely crucial.  Besides, your hard-earned power would
run down the line to the neighbors, and probably all be spent where
you can't get any benefit from it.


to turn on the electric water heater. I ended up cooking breakfast on
the propane grill because I could not run a single burner on the stove
to cook pancakes with a 5600w generator. I had two freezers and the
fridge going, you might be able to run a stove burner or water heater


_One_ 220V heating appliance is the limit for this class of generator.
Maybe none, depends on the appliance.  (Single burner, or oven, etc.)
Hot water heater is usually about 4000-4500W.

Every 220V genny I know of is built as two 115V generators of half
rating.  You _cannot_ take the maximum rating from only one side, but
only half.  So, you must monitor the current draw on both legs of the
220V output to make sure that neither side is drawing more than half
the rated value.  Or your generator will die.  220V loads are
inherently symmetrical, it's all the 110V stuff you have to watch
out for.

-- Jim




Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Jim Cathey

I already know my genny won't kill the well pump. If you use the wrong
genny (maybe Jim Cathey can tell us why) the well pump is the most
expensive thing you could fry, so it's a bad place to start.


Undervoltage will kill motors, though well pumps these days
usually have some solid-state protection circuitry located at
the bore head.

-- Jim




Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Mitch Haley


Jim Cathey wrote:
 Undervoltage will kill motors, though well pumps these days
 usually have some solid-state protection circuitry located at
 the bore head.

I had a motor/generator repairman tell me of the time a contractor
killed every appliance in the house when he had a non-center tapped
genny and hooked it up like I do through the dryer outlet of a new
home. He told me to see if I could run a light bulb off each side of
the 240v outlet to test if it was safe. Do you know what he was
talking about?
I found I could run a trouble light off either side of my old
Coleman, so I've been going whole house (minus resistance heating
stuff) ever since.




Re: [MBZ] OT: Generator voltage spikes

2006-12-21 Thread Mitch Haley


Jim Cathey wrote:
 
 Yes.  This fellow had a 220V generator that did _not_ have a center
 tap, which meant that unless the two 110V sides of the home's wiring
 were _exactly_ balanced as to load (and they never, ever are) one
 side was going to see more than 110V, and one less.  Up to and
 probably including 200+V on one side.

So if I were to hook up a 100W light to one half of the 240 outlet
on such a genny, I'd get 0v through the lamp and 240v on the open
side? Now I understand why the motor repair guy told me to do that
for a test. 

Mitch.




Re: [MBZ] OT: Generator voltage spikes

2006-12-19 Thread Mitch Haley


Jim Cathey wrote:
 I'd been impressed with it up 'til that point.  The load bar was
 only on 2 or 3 out of 6 at that time, though there were four
 computers on, with monitors, and the network gear.

So what do you have there, a kw or so of ocmputers?
Adds a whole new meaning to electric home heating system.




Re: [MBZ] OT: Generator voltage spikes

2006-12-19 Thread Jim Cathey

run the UPS side fully
isolated from the line via the inverter,
so no surprises, because the system is always running via the
batteries,


That's supposedly what this unit does.  It won't even power up
anything unless the batteries are good.


So what do you have there, a kw or so of ocmputers?
Adds a whole new meaning to electric home heating system.


I just measured it, 650W to the UPS on the old Maytag wattmeter.
Should have handled it fine, and it did when moving the plug to
and from the Maytag.

Something about the nature of the power spiking the other day
really PO'd it, and me too.

-- Jim




Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread Zeitgeist

Would Boeing Surplus be a good source for these?  Where can one locate the
new gel cells?

Can these be purchased new at a computer supply place, like Office Depot?



On 12/16/06, David Brodbeck [EMAIL PROTECTED] wrote:


Higher-end computer UPS units will do it.  Look for one with
buck/boost capability.  APC's SmartUPS line has this, for example, but
their cheaper BackUPS line does not.  A UPS would also let you keep
loads running while you shut the generator down to refuel.

Used or surplus UPSs are often a good deal because a lot of people
discard them when the batteries fail.  The batteries are usually
easy-to-replace, standard-size gel cells.  I recently picked up three
APC BackUPS units for $1 each at a computer surplus place, and all of
them just needed new batteries.



Casey
Olympia, WA
Biodiesel: I drive in a persistent vegetative state
'87 300TD intercooler/propane #22 0-60mph 7.3sec (220k)
'84 300D (218k)
Gashuffer:
'89 Vanagon Wolfsburg Edition (187K)
http://users.zhonka.net/zeitgeist/Misc/IMG_0171.JPG


Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread David Brodbeck
Zeitgeist wrote:
 Would Boeing Surplus be a good source for these?  Where can one locate the
 new gel cells?

For used UPS units, RePC is often a good bet.  Check out the AS IS
aisle, particularly -- that's where I got three of them for $1 each.  I
don't usually see them at Boeing.

Gel cells can be gotten from battery dealers (like Batteries Plus) or
from mail-order electronic houses.  Last time I bought some, Mouser
Electronics (http://www.mouser.com/) had a decent price.  The
disadvantage with mail order is you're paying to ship all that lead. ;)
 APC also sells replacement batteries for all their units, but I find
they're usually cheaper elsewhere.



Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread Mitch Haley


OK Don wrote:
 
 I just replaced the batteries in my APC Smart UPS 2200. It uses 8 12
 volt batteries, series parallel at 24V. The batteries are Panasonic
 LC-R127R2P. The best deal I found was at Portable Power Systems, Inc.
 - http://www.gotbatteries.com/

12v, 7AH, $20.50x8.  
I wonder what two trolling motor batteries of 40+AH would cost?
And if wet cells would enjoy the charging regime of the UPS?




Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread David Brodbeck
Mitch Haley wrote:
 12v, 7AH, $20.50x8.  
 I wonder what two trolling motor batteries of 40+AH would cost?
 And if wet cells would enjoy the charging regime of the UPS?

Should be OK.  You'd have all the usual disadvantages of wet cells,
though -- acid drips, flammable vapors that have to be vented outside, etc.




Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread OK Don

I think that gel cells require a more gentle charging than wet cells.
If this is true, the trolling motor batteries should do fine.

On 12/17/06, Mitch Haley [EMAIL PROTECTED] wrote:



OK Don wrote:

 I just replaced the batteries in my APC Smart UPS 2200. It uses 8 12
 volt batteries, series parallel at 24V. The batteries are Panasonic
 LC-R127R2P. The best deal I found was at Portable Power Systems, Inc.
 - http://www.gotbatteries.com/

12v, 7AH, $20.50x8.
I wonder what two trolling motor batteries of 40+AH would cost?
And if wet cells would enjoy the charging regime of the UPS?





--
OK Don, KD5NRO
Norman, OK
The Americans will always do the right thing... after they've
exhausted all the alternatives.
Sir Winston Churchill
'90 300D, '87 300SDL, '81 240D, '78 450SLC, '97 Ply Grand Voyager



Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread Craig McCluskey
On Sun, 17 Dec 2006 10:41:18 -0500 Mitch Haley [EMAIL PROTECTED] wrote:

 If it's twelve volt, you can just put a spare group 49 from your mbz
 next to it and wire it up. That'll really extend your runtime.

Yes, but you can't use your runtime very many times. Automotive batteries
are not meant to be discharged significantly. They'll only take that about
a dozen times.


Craig



Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread Jim Cathey
I'm presently without power, and may be for some time, due to recent 
wind
storm activity.  My generator blew up my surge protector, so I'm 
running my
DSL modem off of the battery from my van, and using our laptop 
w/wireless.

I strongly suspect our generator is malfunctioning and pumping an
unregulated voltage supply, which unfortunately blows stuff up.  Is 
there an

external voltage rectifying unit I can purchase which will avoid this
situation so it doesn't keep happening every time I fire up the 
generator?


You may find that all your gear runs just fine 'unprotected'.

I use an APC 2kW smart-UPS on the computer bank.  Got it at auction for
$35 with another 400W back-UPS.  Both obviously in need of batteries.
I put four 75AH gell cells on the 2kW unit as it uses a 48V battery
bank.  $300.  Works great when you yank the plug out of the wall, but in
the recent windstorm the power yo-yo'd a couple of times, and the APC
killed power to the computers for a second, then came on steadily.
Of course, they'd all lost it by then.  I was not happy.

It is not easy, apparently, to design a backup power supply system
that can properly handle all the ills that power lines are subject to.

-- Jim




Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread kevin kraly
I would anticipate that this one has one 12V gel cell or two smaller 6V ones 
since it's about 11x13 and 7 or 8 deep.  It's gotten to where it won't 
hold a charge at all, so they (or it) must be bad.


Kevin in Hillsboro, OR
1983 300SD 265K miles, Ursula 





Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread OK Don

That doesn't sound like it's working right - my APC 2200 unit handles
everything the power company dishes out (or doesn't dish out) just
fine. Two PCs, printer, all the network gear, amateur radio, sound
system, all run without a hiccup while the lights are flickering off,
going off for half an hour, etc. Wind induced power events are
common here.


I use an APC 2kW smart-UPS on the computer bank.  Got it at auction for
$35 with another 400W back-UPS.  Both obviously in need of batteries.
I put four 75AH gell cells on the 2kW unit as it uses a 48V battery
bank.  $300.  Works great when you yank the plug out of the wall, but in
the recent windstorm the power yo-yo'd a couple of times, and the APC
killed power to the computers for a second, then came on steadily.
Of course, they'd all lost it by then.  I was not happy.

It is not easy, apparently, to design a backup power supply system
that can properly handle all the ills that power lines are subject to.

-- Jim


--
OK Don, KD5NRO
Norman, OK
The Americans will always do the right thing... after they've
exhausted all the alternatives.
Sir Winston Churchill
'90 300D, '87 300SDL, '81 240D, '78 450SLC, '97 Ply Grand Voyager



Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread Jim Cathey

That doesn't sound like it's working right - my APC 2200 unit handles
everything the power company dishes out (or doesn't dish out) just
fine. Two PCs, printer, all the network gear, amateur radio, sound
system, all run without a hiccup while the lights are flickering off,
going off for half an hour, etc. Wind induced power events are
common here.


I'd been impressed with it up 'til that point.  The load bar was
only on 2 or 3 out of 6 at that time, though there were four
computers on, with monitors, and the network gear.

-- Jim




Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread John M McIntosh
A while back I picked up a 2Kwa and 1Kwa HP powerwise UPS. These fine  
UPS made by
HP before that division was bought out by APC run the UPS side fully  
isolated from the line via the inverter,
so no surprises, because the system is always running via the  
batteries, which is why I picked them up
from a hospital for $100 because the batteries were dead. I think the  
purchase cost was  $3000


With the optional extra battery pack they required 24 gell batteries  
to restore.


On Dec 17, 2006, at 10:01 PM, Jim Cathey wrote:



You may find that all your gear runs just fine 'unprotected'.

I use an APC 2kW smart-UPS on the computer bank.  Got it at  
auction for
$35 with another 400W back-UPS.  Both obviously in need of  
batteries.





John
1983 300TDt  374k Kilometers (mobil 1 Delvac)
1990's 300TDt  174k Kilometers (mobil 1 Delvac)
1993 500SEL 184k Kilometers (mobil 1 Delvac)





Re: [MBZ] OT: Generator voltage spikes

2006-12-18 Thread David Brodbeck
John M McIntosh wrote:
 A while back I picked up a 2Kwa and 1Kwa HP powerwise UPS. These fine  
 UPS made by
 HP before that division was bought out by APC run the UPS side fully  
 isolated from the line via the inverter...

Those are the ultimate in power stability.  I've heard that type of unit
referred to as an on-line UPS.  No spikes from the line side get
through, and there are no switchover transients when going on battery. 
They do tend to be noisier, though.  I had one for a while (different
brand, not HP) but got rid of it because I didn't like the constant
noise from the inverter and fan.




Re: [MBZ] OT: Generator voltage spikes

2006-12-17 Thread Van Cleve


Message: 17
Date: Sat, 16 Dec 2006 14:35:21 -0800
From: David Brodbeck [EMAIL PROTECTED]
Subject: Re: [MBZ] OT: Generator voltage spikes
To: Mercedes Discussion List mercedes@okiebenz.com
Message-ID: [EMAIL PROTECTED]
Content-Type: text/plain; charset=ISO-8859-1

Zeitgeist wrote:
 I'm presently without power, and may be for some time, due to recent wind
 storm activity.  My generator blew up my surge protector, so I'm running my
 DSL modem off of the battery from my van, and using our laptop w/wireless.
 I strongly suspect our generator is malfunctioning and pumping an
 unregulated voltage supply, which unfortunately blows stuff up.  Is there an
 external voltage rectifying unit I can purchase which will avoid this
 situation so it doesn't keep happening every time I fire up the generator?

The power just came on up here on Marrowstone.  This is what I was looking at

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=LE1200#




Re: [MBZ] OT: Generator voltage spikes

2006-12-17 Thread Craig McCluskey
On Sat, 16 Dec 2006 16:51:44 -0800 Van Cleve [EMAIL PROTECTED] wrote:

 Zeitgeist wrote:
   I'm presently without power, and may be for some time, due to recent
   wind storm activity.  My generator blew up my surge protector, so I'm
   running my DSL modem off of the battery from my van, and using our
   laptop w/wireless. I strongly suspect our generator is malfunctioning
   and pumping an unregulated voltage supply, which unfortunately blows
   stuff up.  Is there an external voltage rectifying unit I can
   purchase which will avoid this situation so it doesn't keep happening
   every time I fire up the generator?
  
 The power just came on up here on Marrowstone.  This is what I was
 looking at
 
 http://www.apc.com/resource/include/techspec_index.cfm?base_sku=LE1200#

Lots of interesting specs, but they're missing the important ones. Like,
what input voltage range gives what output voltage range?

The idea is a good one, though.


Craig



Re: [MBZ] OT: Generator voltage spikes

2006-12-17 Thread David Brodbeck
Craig McCluskey wrote:
 http://www.apc.com/resource/include/techspec_index.cfm?base_sku=LE1200#
 

 Lots of interesting specs, but they're missing the important ones. Like,
 what input voltage range gives what output voltage range?
   

It sort of does here:
http://sturgeon.apcc.com/techref.nsf/partnum/990-1286A/$FILE/990-1286A_EN_REV01.pdf




Re: [MBZ] OT: Generator voltage spikes

2006-12-17 Thread Craig McCluskey
On Sat, 16 Dec 2006 20:31:26 -0800 David Brodbeck [EMAIL PROTECTED] wrote:

 Craig McCluskey wrote:
 
 http://www.apc.com/resource/include/techspec_index.cfm?base_sku=LE1200#
 
 
  Lots of interesting specs, but they're missing the important ones.
  Like, what input voltage range gives what output voltage range?

 
 It sort of does here:
 http://sturgeon.apcc.com/techref.nsf/partnum/990-1286A/$FILE/990-1286A_EN_REV01.pdf

Well, so it does:

===
Input Voltage Range 80 - 130V (Selector Switch set to 110V)
85 - 140V (Selector Switch set to 120V)
90 - 150V (Selector Switch set to 127V)

Maximum Input Voltage 250V

Output Regulation +6 to -12%
===

These sound pretty good. Something indeed worth looking at.


Craig



Re: [MBZ] OT: Generator voltage spikes

2006-12-17 Thread Mitch Haley


kevin kraly wrote:
 
 
 My wife has one of these UPS systems with bad batteries, so it's a good
 thing we're still hangin' onto it.  It looks like the unit will have to be
 split to get to the batteries.

Look for #1 or #2 phillips head screws in the bottom of the case. 
Some of the APCs even have battery doors. 
If it's twelve volt, you can just put a spare group 49 from your mbz
next to it and wire it up. That'll really extend your runtime. 
Mitch.




Re: [MBZ] OT: Generator voltage spikes

2006-12-17 Thread Van Cleve
My apologies for no signature, I must have been overwhelmed with joy 
to be shutting the generator down:-)
Google turned up several of those units and that was one of the least 
expensive. I wanted one without the UPS, just something too make sure 
the power is cleaned up before getting to my transfer switch.


Regards
Steve
85 Euro 240D, 5 spd manual, 110K
79 240D, 5 spd manual, 20K on eng rebuild
94 Dodge/Cummins PU, 100K
64 VW Bug
65 D15, AC tractor


Message: 12
Date: Sat, 16 Dec 2006 20:54:38 -0700
From: Craig McCluskey [EMAIL PROTECTED]
Subject: Re: [MBZ] OT: Generator voltage spikes
To: Mercedes Discussion List mercedes@okiebenz.com
Message-ID: [EMAIL PROTECTED]
Content-Type: text/plain; charset=US-ASCII

On Sat, 16 Dec 2006 16:51:44 -0800 Van Cleve [EMAIL PROTECTED] wrote:

 Zeitgeist wrote:
   I'm presently without power, and may be for some time, due to recent
   wind storm activity.  My generator blew up my surge protector, so I'm
   running my DSL modem off of the battery from my van, and using our
   laptop w/wireless. I strongly suspect our generator is malfunctioning
   and pumping an unregulated voltage supply, which unfortunately blows
   stuff up.  Is there an external voltage rectifying unit I can
   purchase which will avoid this situation so it doesn't keep happening
   every time I fire up the generator?
  
 The power just came on up here on Marrowstone.  This is what I was
 looking at

 http://www.apc.com/resource/include/techspec_index.cfm?base_sku=LE1200#

Lots of interesting specs, but they're missing the important ones. Like,
what input voltage range gives what output voltage range?

The idea is a good one, though.


Craig






[MBZ] OT: Generator voltage spikes

2006-12-16 Thread Zeitgeist

I'm presently without power, and may be for some time, due to recent wind
storm activity.  My generator blew up my surge protector, so I'm running my
DSL modem off of the battery from my van, and using our laptop w/wireless.
I strongly suspect our generator is malfunctioning and pumping an
unregulated voltage supply, which unfortunately blows stuff up.  Is there an
external voltage rectifying unit I can purchase which will avoid this
situation so it doesn't keep happening every time I fire up the generator?

TIA

--
Casey
Olympia, WA
Biodiesel: I drive in a persistent vegetative state
'87 300TD intercooler/propane #22 0-60mph 7.3sec (220k)
'84 300D (218k)
Gashuffer:
'89 Vanagon Wolfsburg Edition (187K)
http://users.zhonka.net/zeitgeist/Misc/IMG_0171.JPG


Re: [MBZ] OT: Generator voltage spikes

2006-12-16 Thread David Brodbeck
Zeitgeist wrote:
 I'm presently without power, and may be for some time, due to recent wind
 storm activity.  My generator blew up my surge protector, so I'm running my
 DSL modem off of the battery from my van, and using our laptop w/wireless.
 I strongly suspect our generator is malfunctioning and pumping an
 unregulated voltage supply, which unfortunately blows stuff up.  Is there an
 external voltage rectifying unit I can purchase which will avoid this
 situation so it doesn't keep happening every time I fire up the generator?
   

Higher-end computer UPS units will do it.  Look for one with
buck/boost capability.  APC's SmartUPS line has this, for example, but
their cheaper BackUPS line does not.  A UPS would also let you keep
loads running while you shut the generator down to refuel.

Used or surplus UPSs are often a good deal because a lot of people
discard them when the batteries fail.  The batteries are usually
easy-to-replace, standard-size gel cells.  I recently picked up three
APC BackUPS units for $1 each at a computer surplus place, and all of
them just needed new batteries.



Re: [MBZ] OT: Generator voltage spikes

2006-12-16 Thread Craig McCluskey
On Sat, 16 Dec 2006 14:29:27 -0800 Zeitgeist [EMAIL PROTECTED] wrote:

 I'm presently without power, and may be for some time, due to recent
 wind storm activity.  My generator blew up my surge protector, so I'm
 running my DSL modem off of the battery from my van, and using our
 laptop w/wireless. I strongly suspect our generator is malfunctioning
 and pumping an unregulated voltage supply, which unfortunately blows
 stuff up.  Is there an external voltage rectifying unit I can purchase
 which will avoid this situation so it doesn't keep happening every time
 I fire up the generator?

You want a real UPS, something that will even out voltage levels. I think
the Smart-UPS line from American Power Conversion is quite good. Take a
look at,

http://www.apc.com/products/configure/index.cfm?base_sku=SUA750full_sku=SUA750totalwatts=50lid=order_options_link_SUA750;

If that's a little too expensive, try the Back-UPS choices offered at,

http://www.apc.com/products/category.cfm?id=13subid=5


Craig



Re: [MBZ] OT: Generator voltage spikes

2006-12-16 Thread Werner Fehlauer
Casey - I would try and tame the generator, assuming that it and its 
governor are working properly.  Make sure the load you're trying to carry 
does not exceed the generator capacity, and even preferably stays under 80% 
of that.  Don't dump a big load on it all at once; also, don't run it 
unloaded.  You can put a few lights on it to give it some work to do, then 
drop off the lights as you add other loads.
What drives a small genset crazy is going from no load to 150% load (the 
surge of a motor, pump, etc) - unless there's a lot of super fast electronic 
regulation, there will be all kinds of surges.  I'm not so sure that a UPS 
can handle that, as it also is susceptible to big spikes.

Good luck in dealing with the elements!
Werner

- Original Message - 
From: Zeitgeist [EMAIL PROTECTED]

To: Mercedes Discussion List Mercedes@okiebenz.com
Sent: Saturday, December 16, 2006 5:29 PM
Subject: [MBZ] OT: Generator voltage spikes



I'm presently without power, and may be for some time, due to recent wind
storm activity.  My generator blew up my surge protector, so I'm running 
my

DSL modem off of the battery from my van, and using our laptop w/wireless.
I strongly suspect our generator is malfunctioning and pumping an
unregulated voltage supply, which unfortunately blows stuff up.  Is there 
an

external voltage rectifying unit I can purchase which will avoid this
situation so it doesn't keep happening every time I fire up the generator?

TIA

--
Casey
Olympia, WA