Re: 165 Halsey recurring power issues

2023-10-31 Thread Joe Maimon
Willing to bet that there was slicing on both sides of that conversation and this is what I will now refer to as the expected and resulting razor burn. Babak Pasdar wrote: Thanks James, At signup we asked for N+1 power, two circuits to different UPS units. I think they sliced it thin by

Re: 165 Halsey recurring power issues

2023-10-31 Thread Joe Maimon
The building itself got into the action and their goal was to make a top notch facility focusing on central patch panel fiber cross connects. They started with half of the 9th floor originally called MMR-2 and continued with multiple spaces each bigger as it was quite successful. No raised

Re: 165 Halsey recurring power issues

2023-10-23 Thread Eric Kuhnke
At which point one starts looking at the risk factors, if your whole facility is "redundant", is the power feed coming in from two geographically diverse substations, via diverse duct banks, into diverse entry vaults, and diverse risers? Doesn't eliminate the possibility of the entire building

Re: 165 Halsey recurring power issues

2023-10-23 Thread Eric Kuhnke
I didn't say that I have sympathy for it but that unfortunately this is considered acceptable practice within many low-budget "hosting" companies and probably has been for 15 years. It's a known risk when you're buying a $50/month "server". Same general category of problem as the OVH datacenter

Re: 165 Halsey recurring power issues

2023-10-23 Thread Jay Hennigan
On 10/23/23 15:56, Eric Kuhnke wrote: In this case their use of the incorrectly-described A/B was probably exclusively to handle the (not extremely rare) instances of rackmount server power supply failures, to give each 1U or 2U size machine, or rack of blades, two live power supplies with

Re: 165 Halsey recurring power issues

2023-10-23 Thread William Herrin
On Mon, Oct 23, 2023 at 3:56 PM Eric Kuhnke wrote: > Bulk/high-volume hosting companies, dedicated server companies/small > rack unit count colocation operate on very thin margins. Unless a > customer is paying a LOT more per month they're not economically > going to be connected to true diverse

Re: 165 Halsey recurring power issues

2023-10-23 Thread Eric Kuhnke
Bulk/high-volume hosting companies, dedicated server companies/small rack unit count colocation operate on very thin margins. Unless a customer is paying a LOT more per month they're not economically going to be connected to true diverse A/B power. In this case their use of the

Re: 165 Halsey recurring power issues

2023-10-23 Thread Aaron Wendel
I toured The Planet years ago in Dallas and was told by the sales rep that A+B power was two circuits from the same PDU. :) I consider A+B power to be two distinct feeds, separate utility entrances, separate generators, separate UPS', PDU's, etc.  Past that I consider things like firewall

RE: 165 Halsey recurring power issues

2023-10-23 Thread Tony Wicks
is utterly irrelevant. This DC provider is, in my opinion is very much out of step with reality if they think this is some sort of normal practice. -Original Message- From: NANOG On Behalf Of Babak Pasdar Sent: Tuesday, October 24, 2023 8:31 AM To: James Jun Cc: nanog@nanog.org Subject: Re:

Re: 165 Halsey recurring power issues

2023-10-23 Thread William Herrin
On Mon, Oct 23, 2023 at 7:38 AM Babak Pasdar wrote: > A few months ago, 165 Halsey took us down for several hours. They > claimed that a UPS failed causing this issue. Our natural reaction was > that we have A/B redundant power so a failed UPS on the A circuit should > not take down the cabinet.

Re: 165 Halsey recurring power issues

2023-10-23 Thread Sean Donelan
On Mon, 23 Oct 2023, James Jun wrote: "2N" generally means you're connected to completely different UPS system/complex and corresponding distribution systems for each of your circuit. This is ideal configuration for most critical loads. If you are in a single facility, even one with 2N+2

Re: 165 Halsey recurring power issues

2023-10-23 Thread James Jun
On Mon, Oct 23, 2023 at 03:31:21PM -0400, Babak Pasdar wrote: > > Is the UPS the battery or the battery and controller combined? "N+1" nominally means you're connected to the same UPS system/complex, but each of your feed is on a different module. Your other leg will be diverse from a failure

Re: 165 Halsey recurring power issues

2023-10-23 Thread Babak Pasdar
Thanks James, At signup we asked for N+1 power, two circuits to different UPS units. I think they sliced it thin by connecting us to two battery packs on the same UPS. When the UPS controller crashed both battery packs went down.  Which now raises the question -- is it reasonable to have to

Re: 165 Halsey recurring power issues

2023-10-23 Thread James Jun
On Mon, Oct 23, 2023 at 10:38:09AM -0400, Babak Pasdar wrote: > I wanted to get some feedback as to what is considered standard A/B > power setup when data centers sell redundant power.?? It has always been > my understanding that A/B power means individually unique and preferably > alternate

Re: 165 Halsey recurring power issues

2023-10-23 Thread Sean Donelan
165 Halsey (and most of its tenant) data centers is an older facility. Data center practices have changed over the decades, and terminlogy wasn't standardized until recently. The biggest FUBAR in telco and data centers is the difference between "redundancy" and "diversity." Redundant