2009-03-01 Thread Arnaud Quette
bonsoir Vianney, 2009/3/1 Vianney Lejeune > Hello, > >I encounter a problem using the UPS MGE Evolution 850 VA USB with > Debian Etch and the nut package available for this version. I got this > error: > hey, Lenny is out. come on! ;-p > > ==syslog== > Can't connect to UPS [MGE850VA]

Re: [Nut-upsuser] driver for HP/Compaq T750 ?

2009-02-27 Thread Arnaud Quette
2009/2/27 KP Kirchdoerfer > Am Donnerstag, 26. Februar 2009 20:37:56 schrieben Sie: > > Citeren KP Kirchdoerfer : > > > > [...] > > > > > And the upshid-ups driver ends with: > > > No matching HID UPS found > > > Driver failed to start (exit status=1) > > > > Try this driver again, but make sure

[Nut-upsuser] Mustek PowerMust 424 / 636 / 848 (USB) compatibility

2009-02-27 Thread Arnaud Quette
Hi Vitaly, 2009/2/26 Vitaly Polyakov > Hello. > > You are the site administrator Project Network UPS Tools, are not you? I > think? it is a good idea to add information about the compatibility the > NUT with a Mustek PowerMust 424/636/848 USB. These UPS are using > modified protocol, and therefo

[Nut-upsuser] support for APC Matrix 5000, vintage 12/00 (was: NUT apcsmart driver - firmware addition)

2009-02-27 Thread Arnaud Quette
Hey Jarett, 2009/2/24 > After upgrading to the 2.4.1 version, I wasn't able to read as many > variables from my UPS. After a bit of experimentation, I determined that > the firmware on my UPS was different than what is currently in the > apcsmart driver, though it had worked before. I located

Re: [Nut-upsuser] early shutdown of VMware VMs

2009-02-26 Thread Arnaud Quette
Hi David, just a forward to the list since others might be interested in that info. 2009/2/25 David Newman > On 2/17/09 5:26 AM, Arnaud Quette wrote: > > > > I've appended a script excerpt I've once made to address the guest > > shutdown from the host. > >

Re: [Nut-upsuser] driver for HP/Compaq T750 ?

2009-02-26 Thread Arnaud Quette
2009/2/26 Charles Lepple > On Wed, Feb 25, 2009 at 1:54 PM, KP Kirchdoerfer > wrote: > > Hi, > > > > I own a UPS HP T750. > > > > Is there a driver for this UPS (either serial or USB)? > > As you may have already seen, we don't have an entry for this UPS in > data/drivers.list yet. > > However,

[Nut-upsuser] Opensource bits from EATON

2009-02-23 Thread Arnaud Quette
Dear users and developers, just a small mail to inform you that: * EATON protocols library is now mostly complete! UPSCode II has been published for some time now. I've just released this morning a full set for the XCP protocol (Powerware), including the general information, and Alarm / Meters ma

Re: [Nut-upsuser] megatec_usb vs Mustek NetGuard / Ippon SmartWinner problem

2009-02-20 Thread Arnaud Quette
2009/2/20 Alexander I. Gordeev > Hi Oleg, > > On Friday 20 February 2009 01:21:25 Oleg Pshenychnyy wrote: > > Greetings Gentlemen, > > > > I have Mustek NetGuard 1000 UPS which is equivalent to Ippon SmartWinner > > 1000. > > I have tried to run several latest builds of NUT, but run megatec_usb >

Re: [Nut-upsuser] NUT 2.4.1 crashes on FreeBSD - additional info

2009-02-20 Thread Arnaud Quette
Hi Joerg, 2009/2/19 Joerg Pulz > -BEGIN PGP SIGNED MESSAGE- > Hash: SHA1 > > > On Thu, 19 Feb 2009, Arnaud Quette wrote: > > Hi Volker, >> >> I forward your request to the user list since I don't currently have much >> time to process it

Re: [Nut-upsuser] NUT 2.4.1 crashes on FreeBSD - additional info

2009-02-19 Thread Arnaud Quette
Hi Volker, I forward your request to the user list since I don't currently have much time to process it. quickly testing 2.4.1, I wasn't able to reproduce it. a question: was it working with the exact same context/config with 2.2.2? cheers, Arnaud -- Linux / Unix Expert R&D - Eaton - http://www

Re: [Nut-upsuser] Recommended UPS brand (OffTopic sort of)

2009-02-17 Thread Arnaud Quette
p;D - Eaton - http://www.eaton.com/mgeops >> Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ >> Debian Developer - >> http://people.debian.org/~aquette/<http://people.debian.org/%7Eaquette/> >> Free Software Developer - http://arnaud.quette.free.fr/

Re: [Nut-upsuser] early shutdown of VMware VMs

2009-02-17 Thread Arnaud Quette
I've appended a script excerpt I've once made to address the guest shutdown from the host. it was for ESX, and at that time, I was really surprised to not see anything to address automagically an ordered shutdown (of the VMs)... hope this helps. Arnaud -- Linux / Unix Expert R&D - Eaton - http://

Re: [Nut-upsuser] Network UPS Tools version 2.4.1 released

2009-02-17 Thread Arnaud Quette
Hi Scott and Rob, 2009/2/17 Rob MacGregor > On Tue, Feb 17, 2009 at 10:12, Scott Evans > wrote: > > Hi Arnaud... > > > > Will this update be made available as .deb file ??? I'm using Ubuntu, I > > prefer to use files from the repositories over compiling, > > That is going to be largely in the h

[Nut-upsuser] Network UPS Tools version 2.4.1 released

2009-02-17 Thread Arnaud Quette
Network UPS Tools version 2.4.1 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.4/nut-2.4.1.tar.gz - News: http://www.networkupstools.org/source/2.4/new-2.4.1.txt - ChangeLog: http://www.networkupstools.org/source/2.4/ChangeLo

Re: [Nut-upsuser] Recommended UPS brand (OffTopic sort of)

2009-02-17 Thread Arnaud Quette
p;D - Eaton - http://www.eaton.com/mgeops Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ Debian Developer - http://people.debian.org/~aquette/ Free Software Developer - http://arnaud.quette.free.fr/ > On Mon, Feb 16, 2009 at 9:13 AM, Arnaud Quette wrote: >

Re: [Nut-upsuser] Recommended UPS brand (OffTopic sort of)

2009-02-16 Thread Arnaud Quette
2009/2/13 Douglas Parsons > Arnaud, > > Cool. Found the unit. Looks like they renamed it as I had a Pulsar EX 2200 > and it is now the Pulsar M 2200. The EX line only goes to 1500 now. Sent > the link to the reseller. > not that easy again ;-) the various ranges are under renaming between MGE a

Re: [Nut-upsuser] Recommended UPS brand (OffTopic sort of)

2009-02-13 Thread Arnaud Quette
2009/2/13 Douglas Parsons > Hello, > Hi Doug, > I am looking for a compatible brand for nut. I currently have both APC and > MGE units in house. I liked the MGE units and had switched to them after > several bad experiences with the APC line. We ordered 13 APC Rack mount > units and the qualit

Re: [Nut-upsuser] Solution for SOLA-330 UPS !!!

2009-02-13 Thread Arnaud Quette
2009/2/12 Scott Evans > Hi Arnaud... > Hi Scott, > I've attached a simple graphic for the pin-out of the SOLA-330 UPS cable > thanks. I've updated the page: http://test.networkupstools.org/Support/Cables/SOLA cheers, Arnaud ___ Nut-upsuser mailing

Re: [Nut-upsuser] Solution for SOLA-330 UPS !!!

2009-02-12 Thread Arnaud Quette
2009/1/29 Scott Evans > Hi To all on this list... > > I emailed the EATON (the company that has bought out SOLA) > and that sponsors NUT ;-) > to request some information about the pin-out for this model UPS and I got > a reply today! > > The answer is really simple! this model UPS just uses

[Nut-upsuser] Build issue with 2.4.0

2009-02-12 Thread Arnaud Quette
Hey Alexey, I just realized that you sent this mail privately! 2009/2/5 Alexey Rytchkov > Hi, > > It seems /make clean/ do extra work when it removes scripts/hal/ > ups-nut-device.fdi.in and scripts/udev/nut-usbups.rules.in. > Configure fails not finding this files. > Your can reproduce that by

[Nut-upsuser] Network UPS Tools version 2.4.0 released

2009-01-28 Thread Arnaud Quette
Network UPS Tools version 2.4.0 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.4/nut-2.4.0.tar.gz - News: http://www.networkupstools.org/source/2.4/new-2.4.0.txt - ChangeLog: http://www.networkupstools.org/source/2.4/ChangeLo

Re: [Nut-upsuser] FreeBSD usbhid-ups problem

2009-01-27 Thread Arnaud Quette
Hi Daniel, 2009/1/27 Daniel O'Connor > On Thursday 25 September 2008 17:56:43 Daniel O'Connor wrote: > > > you might want to have libusb debug trace also, to see more low level > > > things. use "export USB_DEBUG=3" before launching usbhid-ups. > > > you might also have a look at your kernel out

[Nut-upsuser] Network UPS Tools version 2.4.0-pre2 released

2009-01-21 Thread Arnaud Quette
Network UPS Tools version 2.4.0-pre2 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.4/testing/nut-2.4.0-pre2.tar.gz - News: http://www.networkupstools.org/source/2.4/testing/new-2.4.0-pre2.txt - ChangeLog: http://www.networku

Re: [Nut-upsuser] powerware 5110 and openbsd

2009-01-05 Thread Arnaud Quette
2009/1/4 Charles Lepple > On Fri, Jan 2, 2009 at 3:27 PM, Hannu Vuolasaho wrote: > > > >> > >> We are still in the process of collecting all the NUT/USB/*BSD > >> documentation from various emails, but have you also checked > >> /dev/usb0? I believe that libusb on BSD requires permissions on > >

[Nut-upsuser] Christmas mail

2008-12-30 Thread Arnaud Quette
Dear NUT users and developers, A bit later than usual, here is the traditional end of the year mail to sum up the past year, think about the future and make some announcements. Those of you who have followed closely the project already know: 2008 has been a harder year than ever. And the UPS worl

Re: [Nut-upsuser] Exide NetUPS SE (aka Powerware 5119 etc)

2008-12-24 Thread Arnaud Quette
Hi Johan, just a quick note to say that I saw your mail and will process it soon. sorry for not having answered earlier, but the Christmas mail I'm preparing will complete your mail.. cheers, Arnaud -- Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops Network UPS Tools (NUT) Project

[Nut-upsuser] Network UPS Tools version 2.4.0-pre1 released

2008-12-24 Thread Arnaud Quette
Network UPS Tools version 2.4.0-pre1 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.4/testing/nut-2.4.0-pre1.tar.gz - News: http://www.networkupstools.org/source/2.4/testing/new-2.4.0-pre1.txt - ChangeLog: http://www.networ

Re: [Nut-upsuser] MGE Evolution and programmable outlets configuration

2008-12-19 Thread Arnaud Quette
Hi Marco, just a (very) quick followup... the support being overloaded (so do I but), I'll answer to your questions to speed up the process ;-) Le mercredi 10 décembre 2008 à 21:52 +0100, Marco Chiappero a écrit : > Arnaud Quette ha scritto: > > [a quick walk through the ml, stil

Re: [Nut-upsuser] MGE Evolution and programmable outlets configuration

2008-12-17 Thread Arnaud Quette
2/10 Marco Chiappero : > Arnaud Quette ha scritto: >> >> [a quick walk through the ml, still from the UDS/Googleplex...] >> >> Hi Marco, > > Hi Arnaud, good to read you! > >>> A digression about the fan: it's really annoying not just because it&#x

Re: [Nut-upsuser] MGE Evolution and programmable outlets configuration

2008-12-09 Thread Arnaud Quette
[a quick walk through the ml, still from the UDS/Googleplex...] Hi Marco, 2008/12/7 Marco Chiappero <[EMAIL PROTECTED]>: > Arjen de Korte ha scritto: > >> Regarding this, the fan is indeed annoying, but I don't agree with the >> other arguments you're raising here. MGE officially supports NUT, yo

Re: [Nut-upsuser] MGE Pulsar EX over serial problem (FreeBSD)

2008-11-20 Thread Arnaud Quette
Hi Daniel, 2008/11/18 Daniel O'Connor <[EMAIL PROTECTED]>: > On Tuesday 18 November 2008 19:57:23 Arnaud Quette wrote >> a small update... sorry for the delay! > > No problem :) thanks for your kindness >> > Yes I got the sorry tale from our wholesaler wh

Re: [Nut-upsuser] MGE Pulsar EX over serial problem (FreeBSD)

2008-11-18 Thread Arnaud Quette
2008/11/18 Rob MacGregor <[EMAIL PROTECTED]>: > On Tue, Nov 18, 2008 at 09:27, Arnaud Quette <[EMAIL PROTECTED]> wrote: >> I've installed a FreeBSD into VirtualBox, but haven't yet completed >> this install (what's the right command to install nut bt

Re: [Nut-upsuser] I Need help configuring my UPS- Noobie.

2008-11-18 Thread Arnaud Quette
Hi John, 2008/11/16 John @ BER Ltd <[EMAIL PROTECTED]>: > Hi, > I'm at my wits end and need help regarding my UPS. I am a newbie to Linux > (10 months) and need help with trying to configure my UPS to my Linux SME > server. > I have little or no experience with Bash and am finding it overwhelming

Re: [Nut-upsuser] MGE Pulsar EX over serial problem (FreeBSD)

2008-11-18 Thread Arnaud Quette
Hi Daniel, a small update... sorry for the delay! 2008/11/6 Daniel O'Connor <[EMAIL PROTECTED]>: > On Tuesday 04 November 2008 02:08:50 Arnaud Quette wrote: >> still on my stack. I've discussed a bit with our QA team, and we are >> checking to setup something to t

Re: [Nut-upsuser] Mustek PowerMust 600 USB configuration

2008-11-12 Thread Arnaud Quette
hey there, 2008/11/11 <[EMAIL PROTECTED]>: > On Tue, Nov 11, 2008 at 12:13:38AM +0200, Janeks Kamerovskis wrote: >> > > >> > > I have no /dev/bus/... >> Sorry, I was wrong it is! >> >> > >> > This is strange... >> > Ok, waiting for the output of megatec_usb with -D... >> ??? >> > > I asked yo

Re: [Nut-upsuser] MGE Pulsar EX over serial problem (FreeBSD)

2008-11-03 Thread Arnaud Quette
Hi Daniel, 2008/11/3 Daniel O'Connor <[EMAIL PROTECTED]>: > On Tuesday 28 October 2008 20:30:29 Daniel O'Connor wrote: >> On Tuesday 28 October 2008 19:36:25 Arnaud Quette wrote: >> > > Looking at the above, you're probably using the newmge-shut driver,

Re: [Nut-upsuser] [Bug 278495] Re: megatec_usb does'nt detect ups

2008-10-30 Thread Arnaud Quette
2008/10/30 Alexander I. Gordeev <[EMAIL PROTECTED]>: > Hi Arnaud, > > On Thursday 30 October 2008 13:25:20 you wrote: >> Hi Alexander and Chuck, >> >> ok, the situation is now clear to me. >> So the mentioned patch hasn't been reconducted for 2.2.2! >> thanks for having recalled me everything (I'm

Re: [Nut-upsuser] [Bug 278495] Re: megatec_usb does'nt detect ups

2008-10-30 Thread Arnaud Quette
Hi Alexander and Chuck, 2008/10/29 <[EMAIL PROTECTED]>: > Arnaud, > > On Wed, Oct 29, 2008 at 03:17:45PM +0100, Arnaud Quette wrote: >> 2008/10/29 <[EMAIL PROTECTED]>: >> > Hi Arnaud, >> >> Hi Alexander, >> >> thanks for your sum up.

Re: [Nut-upsuser] [Bug 278495] Re: megatec_usb does'nt detect ups

2008-10-29 Thread Arnaud Quette
2008/10/29 <[EMAIL PROTECTED]>: > Hi Arnaud, Hi Alexander, thanks for your sum up. > On Mon, Oct 27, 2008 at 04:30:20PM +0100, Arnaud Quette wrote: >> 2008/10/27 Chuck Short <[EMAIL PROTECTED]>: >> > Arnaud, >> > >> > Any thought about this

Re: [Nut-upsuser] MGE Pulsar EX over serial problem (FreeBSD)

2008-10-28 Thread Arnaud Quette
2008/10/28 Arjen de Korte <[EMAIL PROTECTED]>: > Citeren Daniel O'Connor <[EMAIL PROTECTED]>: > >> When it loses comms I see stuff like this.. >> entering shut_get_report(id: 2f, len: 1800) >> shut_wait_ack(): ACK received >> entering shut_get_report(id: 20, len: 1800) >> shut_wait_ack(): ACK recei

Re: [Nut-upsuser] ups question from your web site

2008-10-28 Thread Arnaud Quette
OS (generally in the halt script) to be the UPS shutoff / poweroff. this part is one of those handled by the package. so next time, come back with the answers to the questions I've asked! -- Arnaud > ------ > From: "Arnaud Quette&qu

Re: [Nut-upsuser] Cyberpower/powerpanel error: Data stale

2008-10-27 Thread Arnaud Quette
> ... > If I use the powerpanel driver, it either dies, or fails to start. this is the important part. please, start the driver in debug mode (powerpanel -DDD -a ...) and send us back the output for analysis. as Kjell told prev., powerpanel is set to replace cyberpower. so we have to hunt your is

Re: [Nut-upsuser] ups question from your web site

2008-10-27 Thread Arnaud Quette
Hi Nick, Peter is retired from the project for excellent reason. if you need support, use the Network UPS Tools mailing list. we will be happy to help. as Peter told, we don't work for APC (not at all, and proud!!). we are friendly and won't pull your teeth ;-) checking the below thread, your req

Re: [Nut-upsuser] [Bug 278495] Re: megatec_usb does'nt detect ups

2008-10-27 Thread Arnaud Quette
2008/10/27 Artin <[EMAIL PROTECTED]>: > Arnaud > > I have already posted the debug output of 2.2.1 : > http://launchpadlibrarian.net/18231851/debug2.txt uh, right. I was off doing another update for Lenny... looking a bit at the trunk's changelog, I would guess this is a regression. not dug much

Re: [Nut-upsuser] [Bug 278495] Re: megatec_usb does'nt detect ups

2008-10-27 Thread Arnaud Quette
2008/10/27 Chuck Short <[EMAIL PROTECTED]>: > Arnaud, > > Any thought about this? Its a regression from 2.2.1. not yet! @Alex: any idea on your side (change of the default driver or something alike) this seems to be a timing or reading problem according to the "short read" msg Artin, can you also

Re: [Nut-upsuser] upsc does not dig connection from other hosts

2008-10-14 Thread Arnaud Quette
2008/10/14 Han Boetes <[EMAIL PROTECTED]>: > Arnauds, > > It does work! I just had to completely stop upsd to make it reload > the configuration file. > > Looks like two things don't work like one would expect reading > from the documentation. > > 1) "upsd -c reload" does not reread the configurat

Re: [Nut-upsuser] upsc does not dig connection from other hosts

2008-10-13 Thread Arnaud Quette
Hi Hans, 2008/10/13 Han Boetes <[EMAIL PROTECTED]>: > I got a bunch of configfiles that look like this: > mgmt-dev:/etc/nut# grep -v 'niets' * > ups.conf:[ups] > ups.conf:driver=newhidups > ups.conf:port=auto > upsd.conf:ACL all 0.0.0.0/0 > upsd.conf:ACL localhost 127.0.0.1/32 > upsd.conf:ACL remo

Re: [Nut-upsuser] FreeBSD usbhid-ups problem

2008-09-02 Thread Arnaud Quette
Hey there, 2008/8/25 Daniel O'Connor <[EMAIL PROTECTED]>: > On Sat, 23 Aug 2008, Arjen de Korte wrote: >> >> Are the 'usbhid-ups' (driver) and 'upsd' (server) also running as >> >> 'nutmon'? We recommend that they run as a different user than the >> >> 'upsmon' (client). >> > >> > They are running

Re: [Nut-upsuser] MGE Ellipse 500 cable config

2008-09-02 Thread Arnaud Quette
Hi Harri, 2008/8/9 Harri Järvi <[EMAIL PROTECTED]>: > I have trouble in getting communication work with MGE Ellipse 500. I > bought it second hand and I don't have the cable for it. > > How do I know if it's the Serial or USB model? The serial number of the > unit is: 769B16015. I suspect it is th

[Nut-upsuser] NUT in the press

2008-08-07 Thread Arnaud Quette
As I've stated some time ago, NUT is more and more embedded in appliances, such as the Synology x07 NAS models and Opengear network units. I'm working for some time with these two manufacturers to see how NUT can be improved for a better user experience. There was a small article on Linux Devices

[Nut-upsuser] possible regression in genericups with Tripplite UPS

2008-08-06 Thread Arnaud Quette
reported through launchpad: https://bugs.launchpad.net/bugs/253999 the possible regression is between nut 2.0.1 (sarge) and 2.2.1 (confirmed Jamie?) @Arjen: it may be related to some of your changes there... @Jamie: we'll need some debug output from the drivers (-DDD) Arnaud

Re: [Nut-upsuser] mgeops psp has now an ebuild

2008-07-25 Thread Arnaud Quette
Hi Jimmy, 2008/7/24 <[EMAIL PROTECTED]>: > Hello, > > FYI, I left an ebuild for mgeops in Gentoo Bugzilla under the number > 232855. thanks for this info. do you have a direct pointer please? have you used the one embedded in the source (packaging/ directory)? FYI, I'm thinking of a complete r

Re: [Nut-upsuser] Nut-cgi error

2008-07-24 Thread Arnaud Quette
2008/7/24 Charles Lepple <[EMAIL PROTECTED]>: > On Thu, Jul 24, 2008 at 11:00 AM, Arnaud Quette <[EMAIL PROTECTED]> > wrote: > > > > I guess you missed the dir itself: > > as per /usr/share/doc/nut-cgi/README.Debian > > > chmod 766 /etc/nut >

Re: [Nut-upsuser] Nut-cgi error

2008-07-24 Thread Arnaud Quette
Hi 2008/7/24 Georgy <[EMAIL PROTECTED]>: > Hello all, > I have succefully configure a trust 1200v ups with nut-2.2.2 on an > ubuntu 6.06 LTS by follow this instructions : > http://www.networkupstools.org/doc/2.2.0/INSTALL.html > > I have the nut-cgi 2.0.3-4 from the ubuntu repos installed > Now,

Re: [Nut-upsuser] MGE Pulsar EX1500 RT comms problem

2008-07-22 Thread Arnaud Quette
Hi Daniel, - increase MAXAGE in upsd.conf - increase DEADTIME in upsmon.conf - possibly increase the UPS polling interval (pollinterval in ups.conf) which is set to 2 seconds currently, to lower the communication load on the UPS. the exact values depends on what you see in your log. ie, if your U

Re: [Nut-upsuser] Old APC SmartUPS 1250, Nut 2.2.2 Fedora 9

2008-07-10 Thread Arnaud Quette
2008/7/10 Arjen de Korte <[EMAIL PROTECTED]>: >>> I've modified the apcsmart driver source & briefly tested against >>> the 1250 with no issues noted yet. >>> >>> I've attached a patchfile for apcsmart.c & apcsmart.h with the >>> extra bits I've added. >> >> thanks for testing that. I just committe

Re: [Nut-upsuser] NUT with PowerWalker vi 400 se (usb).

2008-07-07 Thread Arnaud Quette
Hi Thierry, could you give Nick some help on his below issue? thanks, Arnaud 2008/7/7 Никита Шишков <[EMAIL PROTECTED]>: > Здравствуйте, Charles. > > Вы писали 4 июля 2008 г., 0:07:56: > >> [Please keep the list CC'd. Thanks.] > >> On Jul 3, 2008, at 2:36 PM, Никита Шишков wrote: > >>> Здравствуй

Re: [Nut-upsuser] Cyberpower Value 600E UPS (unlisted) working

2008-07-03 Thread Arnaud Quette
Hi Thomas, Le mercredi 02 juillet 2008 à 18:52 +0200, Thomas Backman a écrit : > Hey! I just bought my first UPS, a Cyberpower Value 600E, and set it > up using NUT 2.2.x (on Gentoo x86_64). Everything is working great, > using the usbhid-ups driver, and the UPS isn't on the compatibility >

Re: [Nut-upsuser] Trying to build opensuse 11.0 64-bit rpm for nut-2.2.2

2008-07-02 Thread Arnaud Quette
2008/7/2 Arjen de Korte <[EMAIL PROTECTED]>: >> quite right about the outdated packages links. >> wouldn't this one be more useful for nut: >> http://packages.opensuse-community.org/index.jsp?searchTerm=nut > > I don't think so. It is much more convenient to add the OSS repository > (the link can b

Re: [Nut-upsuser] Trying to build opensuse 11.0 64-bit rpm for nut-2.2.2

2008-07-02 Thread Arnaud Quette
2008/7/2 Arjen de Korte <[EMAIL PROTECTED]>: >>> > I am trying to build an rpm for nut-2.2.2 on 64 bit opensuse 11.0. >>> Why? >> I didn't dare hope that opensuse would include nut-2.2.2, so I visited >> http://networkupstools.org/packages.html where "SuSE RPMs" goes nowhere. >> Perhaps it would be

[Nut-upsuser] Megatec and Belkin F6H550-UPS

2008-06-27 Thread Arnaud Quette
Hi Jayson, I forward your request to the right place. Carlos (or some other) will have an answer, or at least some questions for you. -- Arnaud 2008/6/27 Jayson Anderson <[EMAIL PROTECTED]>: > Greetings Arnaud, > > I wrote you some time ago about whether NUT would support the Belkin > F6H550-UPS

Re: [Nut-upsuser] iBall UPS support?

2008-06-24 Thread Arnaud Quette
Le lundi 23 juin 2008 à 21:16 +0530, John Kennedy a écrit : > Salut! bonjour > I have an iBall Nirantar UPS-630 UPS > (http://iball.co.in/inner/show_product_details2.asp?catid=25) and am > interested in hooking it up to my Ubuntu box. Problem - it only comes > with WinPower Windows driver... Alas

Re: [Nut-upsuser] Multiple ups/Belkin 1500VA no serial number

2008-06-06 Thread Arnaud Quette
2008/6/6 Arjen de Korte <[EMAIL PROTECTED] <[EMAIL PROTECTED]>>: > >> > Am I missing something in the logic, or do I just have an unusual > >> case? > >> Neither. These devices are just not suitable for use with NUT as long as > >> the libusb library doesn't expose the physical ports the UPS is at

Re: [Nut-upsuser] Multiple ups/Belkin 1500VA no serial number

2008-06-06 Thread Arnaud Quette
2008/6/6 Arjen de Korte <[EMAIL PROTECTED] <[EMAIL PROTECTED]>>: > > I hadn't previously looked into libusb, but is there a reason why the > > filename > > member of usb_device is't matched on? On linux, they may not be unique > or > > deterministic in theory --- but in practice they are, particu

Re: [Nut-upsuser] MGE Ellipse Max 1100 configuration question

2008-06-02 Thread Arnaud Quette
2008/6/1 Chris Cohen <[EMAIL PROTECTED]>: > Sorry for the delay. > > On Friday 30 May 2008 09:30:45 you wrote: > > Hi Chris, > > > > > > I just booted into a non-xen kernel (linux-image-2.6.24-17-server). > > > Ran /lib/nut/usbhid-ups -a mgeups. > > > The UPS shut down again and so did my entire n

Re: [Nut-upsuser] MGE Ellipse Max 1100 configuration question

2008-05-30 Thread Arnaud Quette
Hi Chris, 2008/5/22 Chris Cohen <[EMAIL PROTECTED]>: > On Thursday 22 May 2008 16:07:08 you wrote: > > >> Weird. This is not something the driver can do, unless you > > >> specifically tell it to kill the power (-k). I see that you're > > >> using Linux 2.6.24-17-xen. > > > > > > I do. (Running U

[Nut-upsuser] Re : MGE Ellipse Max 1100 configuration question

2008-05-21 Thread Arnaud Quette
2008/5/21, Chris Cohen <[EMAIL PROTECTED]>: > Hi, Hi Chris, > I bought an Ellipse MAX 1100 a few months ago. excellent choice ;-) > First I attached it to my > desktop and installed mge's personal solution pac. (a graphical > interface which uses nut). It works. But I want to attach the ups to

Re: [Nut-upsuser] upstart configuration for nut

2008-05-15 Thread Arnaud Quette
Hi Udo, 2008/5/14 Udo van den Heuvel <[EMAIL PROTECTED]>: > Hello, > > I'm just migrating my boxes to fedora 9 which brings us to the upstart > mechanism instead of SystemV, etc.The distro as it is delivered does not > have configuration which supports powerfail events. > > What can I put in /etc/

Re: [Nut-upsuser] addition to "nut" compatibility list

2008-05-15 Thread Arnaud Quette
Hi Kristian, Le mercredi 14 mai 2008 à 14:34 +0200, Kristian Wiklund a écrit : > > hi, > > first, thanks for the excellent work with "nut". > > "Trust 1300VA Management UPS PW-4130M" works fine with the stable > release (built for solaris x86, using serial port communication). > "megatec" pr

Re: [Nut-upsuser] Network UPS Tools version 2.2.2 released

2008-05-14 Thread Arnaud Quette
2008/5/14 Arjen de Korte <[EMAIL PROTECTED]>: > > So yes, you're welcome to register a demo link, but using the freshly > > created http://demo.networkupstools.org/ > > I've pointed your page, and just regenerated the DNS entries. So it > > will take a few more days to propagate. > > Provided y

Re: [Nut-upsuser] Network UPS Tools version 2.2.2 released

2008-05-14 Thread Arnaud Quette
2008/5/14 Jean Delvare <[EMAIL PROTECTED]>: > Hi Arnaud, Hi Jean, > On Tue, 13 May 2008 13:10:23 +0200, Arnaud Quette wrote: > > 2008/5/13 Jean Delvare <[EMAIL PROTECTED]>: > > > > I'd like to accept but I doubt that my tight schedule will let me do

Re: [Nut-upsuser] upssched

2008-05-13 Thread Arnaud Quette
Bonjour Alain, Le 13 mai 2008 15:16, Alain Le Thomas <[EMAIL PROTECTED]> a écrit : > Hello, > (Saddened for my bad English) > I have just created a script to install NUT > I manage the events with UPSSCHED and I would like to know how to launch > this command via /etc/nut/upssched-cmd every 5 m

Re: [Nut-upsuser] Network UPS Tools version 2.2.2 released

2008-05-13 Thread Arnaud Quette
2008/5/13 Jean Delvare <[EMAIL PROTECTED]>: > On Tue, 13 May 2008 10:14:36 +0200, Arnaud Quette wrote: > > 2008/5/8 Jean Delvare <[EMAIL PROTECTED]>: > > > > On Wed, 7 May 2008 12:52:21 +0200, Arnaud Quette wrote: > > > > Netw

Re: [Nut-upsuser] Network UPS Tools version 2.2.2 released

2008-05-13 Thread Arnaud Quette
2008/5/8 Jean Delvare <[EMAIL PROTECTED]>: > Hi Arnaud, Hi Jean, > On Wed, 7 May 2008 12:52:21 +0200, Arnaud Quette wrote: > > Network UPS Tools version 2.2.2 has been released. > > Installed, works perfectly for me. Thanks a lot for the excellent work! > > This

Re: [Nut-upsuser] NUT for laptop

2008-05-07 Thread Arnaud Quette
2008/5/2 Emard <[EMAIL PROTECTED]>: > On Fri, May 02, 2008 at 09:29:28AM +0200, Arnaud Quette wrote: > > Hi Emard, > > > > 2008/5/2 Emard <[EMAIL PROTECTED]>: > > > HI all > > > > > > How to setup nut to use and monitor lap

[Nut-upsuser] validating ambient.temperature from APC IEM (AP9618, AP9619) patch

2008-05-07 Thread Arnaud Quette
Hi Dmitry and the list, would you (or anyone owning such a device) be able to validate the below patch: https://alioth.debian.org/tracker/index.php?func=detail&aid=310613&group_id=30602&atid=411542 Most notably, it's about the paths changes: -#define APCC_OID_IEM_TEMP ".1.3.6.1.4.1.318.1.1.

[Nut-upsuser] Network UPS Tools version 2.2.2 released

2008-05-07 Thread Arnaud Quette
Network UPS Tools version 2.2.2 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.2/nut-2.2.2.tar.gz - News: http://www.networkupstools.org/source/2.2/new-2.2.2.txt - ChangeLog: http://www.networkupstools.org/source/2.2/ChangeLo

Re: [Nut-upsuser] NUT for laptop

2008-05-02 Thread Arnaud Quette
Hi Emard, 2008/5/2 Emard <[EMAIL PROTECTED]>: > HI all > > How to setup nut to use and monitor laptop battery on linux? > (/proc/acpi/battery/BAT0/state) why would you do so? there is nothing to gain doing so (no master/slave conf possible). there are already many PM tools suite in the field, a

[Nut-upsuser] Network UPS Tools version 2.2.2-pre3 released

2008-04-25 Thread Arnaud Quette
Network UPS Tools version 2.2.2-pre3 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.2/testing/nut-2.2.2-pre3.tar.gz - News: http://www.networkupstools.org/source/2.2/testing/new-2.2.2-pre3.txt - ChangeLog: http://www.network

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre2 released

2008-04-23 Thread Arnaud Quette
Hi Arjen, 2008/4/22, Arjen de Korte <[EMAIL PROTECTED]>: > Arnaud Quette wrote: > > > > > > In the mean time, I have divided the main 'nut' package in the > > > following sub packages: > > > > > > - nut (client applicati

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre2 released

2008-04-22 Thread Arnaud Quette
2008/4/22, Arjen de Korte <[EMAIL PROTECTED]>: > > well, that's the biggest problematic of packaging. > > none of the solutions are perfect, and both have big pros and cons. > > there are still many rooms for improvement there... > > > Indeed. In the mean time, I have divided the main 'nut' packa

Re: [Nut-upsuser] 2.2.2-pre2 64 bit rpm tested on openSUSE 10.3

2008-04-22 Thread Arnaud Quette
2008/4/21, Arjen de Korte <[EMAIL PROTECTED]>: > Arnaud Quette wrote: > > > > > > > There is no /var/state in openSUSE 10.3, so I changed PIPEFN and > LOCKFN to > > > > /var/run and defined directory /var/run/ups. > > > > > > >

Re: [Nut-upsuser] 2.2.2-pre2 64 bit rpm tested on openSUSE 10.3

2008-04-22 Thread Arnaud Quette
Hi Roger 2008/4/21, Roger Price <[EMAIL PROTECTED]>: > On Mon, 21 Apr 2008, Roger Price wrote: > > On Mon, 21 Apr 2008, Arnaud Quette wrote: > > > > > > A source RPM for SuSE is also available, but I'm not sure it's x64 ready! > > > http://op

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre2 released

2008-04-22 Thread Arnaud Quette
2008/4/21, Arjen de Korte <[EMAIL PROTECTED]>: > Arnaud Quette wrote: > > > > > > No, and that's because I doubt that openSUSE will follow this approach. > > > Historically, there hasn't been too much interest in splitting packages, > > >

Re: [Nut-upsuser] 2.2.2-pre2 64 bit rpm tested on openSUSE 10.3

2008-04-21 Thread Arnaud Quette
2008/4/20, Arjen de Korte <[EMAIL PROTECTED]>: > Roger Price wrote: > ... > >> As you are using a usb ups, you may use this instead of the nut package. > >> If you install it, the ups gets hotplugged by udev hal and would show up > as a > >> battery in the power monitor in Gnome. (should be th

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre2 released

2008-04-21 Thread Arnaud Quette
2008/4/21, Arjen de Korte <[EMAIL PROTECTED]>: > Arnaud Quette wrote: > > > I previously splitted the Debian packages in nut, nut-usb, nut-cgi, > > nut-snmp, nut-dev, nut-doc (empty ATM) and now nut-hal-drivers. I've > > then re-integrated the USB part into the c

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre2 released

2008-04-21 Thread Arnaud Quette
2008/4/20, Arjen de Korte <[EMAIL PROTECTED]>: > > >> I'll try them tomorrow; meanwhile, another n00bie question : What does > >> nut-hal do? Do I need it? > > > > The nut-hal package is a package that contains the hal drivers and fdi > > file udev rules. > > > > As you are using a usb ups,

[Nut-upsuser] Network UPS Tools version 2.2.2-pre2 released

2008-04-15 Thread Arnaud Quette
Network UPS Tools version 2.2.2-pre2 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.2/testing/nut-2.2.2-pre2.tar.gz - News: http://www.networkupstools.org/source/2.2/testing/new-2.2.2-pre2.txt - ChangeLog: http://www.network

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre1 released

2008-04-14 Thread Arnaud Quette
2008/4/8, Jean Delvare <[EMAIL PROTECTED]>: > On Tue, 8 Apr 2008 11:23:33 +0200, Arnaud Quette wrote: > > 2008/4/4, Jean Delvare <[EMAIL PROTECTED]>: > > > > * battery.temperature changed from 28 degrees C to 29.2 degrees C. Note > > > that I am a bit

Re: [Nut-upsuser] [Bug 215389] [NEW] No battery charge percentage on belkin usb avr

2008-04-11 Thread Arnaud Quette
2008/4/10, David Erosa <[EMAIL PROTECTED]>: > Public bug reported: > > Binary package hint: nut > > After updating to last nut package (2.2.1-2.1ubuntu6), the megatec_usb > driver seems to be working, except for the charge percentage: > > $ /lib/nut/megatec_usb -D -a SAI > ... > Checking

Re: [Nut-upsuser] Network UPS Tools version 2.2.2-pre1 released

2008-04-08 Thread Arnaud Quette
Bonjour Jean, 2008/4/4, Jean Delvare <[EMAIL PROTECTED]>: > Salut Arnaud, > > > On Wed, 2 Apr 2008 16:31:36 +0200, Arnaud Quette wrote: > > Network UPS Tools version 2.2.2-pre1 has been released. > > > > http://www.networkupstools.org/ > > &g

Re: [Nut-upsuser] [Bug 209001] [NEW] Nut no longer functions with belkin usb avr

2008-04-07 Thread Arnaud Quette
Hi Alex and Carlos, 2008/4/5, Alexander I. Gordeev <[EMAIL PROTECTED]>: > On Sat, 05 Apr 2008 16:38:15 +0400, Carlos Rodrigues > <[EMAIL PROTECTED]> wrote: > > > > On Fri, Apr 4, 2008 at 8:46 PM, Alexander I. Gordeev > > <[EMAIL PROTECTED]> wrote: > > > > > > thanks for these info, and good luck

Re: [Nut-upsuser] [Bug 209001] [NEW] Nut no longer functions with belkin usb avr

2008-04-04 Thread Arnaud Quette
Hi Carlos, 2008/4/3, Carlos Rodrigues <[EMAIL PROTECTED]>: > On Thu, Apr 3, 2008 at 8:11 AM, Arnaud Quette <[EMAIL PROTECTED]> wrote: > > @Carlos, Andrey, Alexander, Jon: can one of you take care of > > backporting this to Testing for -pre2? > > > With all

Re: [Nut-upsuser] [Bug 209001] [NEW] Nut no longer functions with belkin usb avr

2008-04-04 Thread Arnaud Quette
Hi Alex, 2008/4/3, Alexander I. Gordeev <[EMAIL PROTECTED]>: > On Thu, 03 Apr 2008 10:59:34 +0400, Arjen de Korte <[EMAIL PROTECTED]> > wrote: > > > > > > > so there are chances that this has been backported in Testing / > > > 2.2.2-pre1 (released today). > > > > > > > No, it hasn't been backporte

Re: [Nut-upsuser] nut with hal on Fedora 8

2008-04-03 Thread Arnaud Quette
Hi, please keep the list cc'ed for info... 2008/4/3, Amadeus W. M. <[EMAIL PROTECTED]>: > Thanks for the very informative answers. Please see below though. > > > > > 1) How do I actually check that my setup is working? > > > > when you plug your unit, you should see the hald-addon-usbhid-ups

Re: [Nut-upsuser] [Bug 209001] [NEW] Nut no longer functions with belkin usb avr

2008-04-03 Thread Arnaud Quette
2008/4/3, Arjen de Korte <[EMAIL PROTECTED]>: > > so there are chances that this has been backported in Testing / > > 2.2.2-pre1 (released today). > > > No, it hasn't been backported as far as I can see, so this is something > that needs to be done for nut-2.2.2-pre2. Since we have active maintai

Re: [Nut-upsuser] [Bug 209001] [NEW] Nut no longer functions with belkin usb avr

2008-04-02 Thread Arnaud Quette
thanks for this update Arjen. so there are chances that this has been backported in Testing / 2.2.2-pre1 (released today). Can you (the bug reporters) grab this, call configure as per the packaging/debian/rules, make and test from the build dir? -- Arnaud ___

Re: [Nut-upsuser] [Bug 209001] [NEW] Nut no longer functions with belkin usb avr

2008-04-02 Thread Arnaud Quette
Carlos, is this bug a known regression of 2.2.1 vs 2.2.0? I can't find much in the ChangeLog. https://bugs.launchpad.net/bugs/209001 thanks, -- Arnaud ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mail

[Nut-upsuser] Network UPS Tools version 2.2.2-pre1 released

2008-04-02 Thread Arnaud Quette
Network UPS Tools version 2.2.2-pre1 has been released. http://www.networkupstools.org/ Direct access: - Download: http://www.networkupstools.org/source/2.2/testing/nut-2.2.2-pre1.tar.gz - News: http://www.networkupstools.org/source/2.2/testing/new-2.2.2-pre1.txt - ChangeLog: http://www.network

Re: [Nut-upsuser] nut with hal on Fedora 8

2008-04-02 Thread Arnaud Quette
2008/3/31, Amadeus W. M. <[EMAIL PROTECTED]>: > I bought a new CyberPower CP850AVRLCD ups, connected it to a usb port > and I'm trying to use it with hal. I installed > > [EMAIL PROTECTED] ~]# rpm -q nut nut-client > nut-2.2.0-6.1.fc8 > nut-client-2.2.0-6.1.fc8 > > lsusb sees it: > > [EMAIL P