Re: [RE-wrenches] weak voltage

2012-10-15 Thread William Miller
Mac: We had a similar problem with a large bank of IBE 2 volt cells. The batteries had to be removed the same day they were installed and then reinstalled the next day. They sat outside for one night. The flags acquired an invisible but insidious corrosion that caused problems getting and

Re: [RE-wrenches] AC (only) Diversion

2012-10-15 Thread Drake
You could use Morning Star relay driver to control the AC dump load. I have one for my system, but have not yet installed it, but have programmed it on my computer. If it works as designed, it should be perfect in conjunction with a relay. At 04:42 AM 10/14/2012, you wrote: Hi there, Is

[RE-wrenches] 500A bussing

2012-10-15 Thread mac Lewis
Hi Wrenches, I am looking for a 500A DC rated DC bussing, one with a built in shunt and one without. I'll need at least 4 terminals/bussbar that will bolt on or land 4 ott cable. Does anyone know where I can find something like this? Thanks -- Mac Lewis * Yo solo sé que no sé nada.

Re: [RE-wrenches] weak voltage

2012-10-15 Thread mac Lewis
Hmmm, This had factory installed bussing. I will pull it off and clean it up. Thanks. I suppose that something like this be invisible to an Amp hr meter. On Sun, Oct 14, 2012 at 11:01 PM, William Miller will...@millersolar.comwrote: Mac: We had a similar problem with a large bank of IBE 2

[RE-wrenches] weak voltage

2012-10-15 Thread Mick Abraham
Hello, Wrenchies~ Mac Lewis wrote about battery strangeness on the Sunny Island system for his clients. Here is a theory to consider, Mac. I once bought a 48v string of famous brand two volt cells in which one cell had been loaded backwards into its case. When hooked up according to the +/-

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Bill Loesch
Mick, Thanks for sharing. Outstanding troubleshooting (particularly when done remotely). Bill Loesch Solar 1 - Saint Louis Solar On 15-Oct-12 8:24 AM, Mick Abraham wrote: Hello, Wrenchies~ Mac Lewis wrote about battery strangeness on the Sunny Island system for his clients. Here is a

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Chris Mason
You should see a voltage drop across the connections if they are faulty. On Mon, Oct 15, 2012 at 8:54 AM, mac Lewis maclew...@gmail.com wrote: Hmmm, This had factory installed bussing. I will pull it off and clean it up. Thanks. I suppose that something like this be invisible to an Amp hr

Re: [RE-wrenches] weak voltage

2012-10-15 Thread mac Lewis
How much voltage drop indicates a problem? On Mon, Oct 15, 2012 at 8:13 AM, Chris Mason cometenergysyst...@gmail.comwrote: You should see a voltage drop across the connections if they are faulty. On Mon, Oct 15, 2012 at 8:54 AM, mac Lewis maclew...@gmail.com wrote: Hmmm, This had factory

[RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread William Dorsett
What brand recommendations do the group have for an battery charger to be plugged into a genset? Used to be Todd but at some point they lost favor. Thanks all. Bill Dorsett Sunwrights 1715 Leavenworth Manhattan, KS 785/539-1956 Home/Office

Re: [RE-wrenches] 500A bussing

2012-10-15 Thread jay peltz
Hi Mac Check out midnight they have exactly what you need Jay Peltz power Sent from my iPad On Oct 15, 2012, at 5:24 AM, mac Lewis maclew...@gmail.com wrote: Hi Wrenches, I am looking for a 500A DC rated DC bussing, one with a built in shunt and one without. I'll need at least 4

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Aaron Mandelkorn
Check out Iota. Aaron Mandelkorn NABCEP Certified PV Installer Renewable Energy Outfitters Box 65 Salida, CO. 81201 (970)596-3744 reoso...@gmail.com www.reosolar.com On Oct 15, 2012, at 9:14 AM, William Dorsett wrote: What brand recommendations do the group have for an battery

Re: [RE-wrenches] Two NEC questions

2012-10-15 Thread Steve Jefferson
Morning, The AFCI units are shipping now. There are a few AHJ that are working off 2011 code (including most of Alaska). The TL (240 VAC) with integrated AFCI should be shipping when the new -22 (3k - 5k) come. These are the units with the EPS module. Thanks SMA America, LLC Steve Jefferson

Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-15 Thread Ray Walters
I've run a 3 HP well pump off a pair of Outbacks, but make sure you have plenty of battery behind it. We had shut downs from low voltage, when the batteries were at 50% charge from the starting surge. My experience with Magnum has been good, and they have even more surge current than the

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread jay peltz
You might also check Power Source Jay Peltz power Sent from my iPad On Oct 15, 2012, at 8:32 AM, Dan Fink danbo...@gmail.com wrote: We have had great luck with Iota. More reasonably priced than Xantrex, too, but not as many flashy lights. They also work great as 12VDC power supplies for

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Chris Mason
Anything more than a few millivolts. On 10/15/12, mac Lewis maclew...@gmail.com wrote: How much voltage drop indicates a problem? On Mon, Oct 15, 2012 at 8:13 AM, Chris Mason cometenergysyst...@gmail.comwrote: You should see a voltage drop across the connections if they are faulty. On

Re: [RE-wrenches] weak voltage

2012-10-15 Thread mark
I had one wholepallet of "famous brand" that were charged backwards. The positive post (as charged) WAS painted red, but the plastic case "+" and "-" markings were by the wrong posts. Before I realized the error, I installed 8 of these at a customer, going by the red painted post, not noticing

Re: [RE-wrenches] 500A bussing

2012-10-15 Thread Ray Walters
You will need to get a 1000 amp 100 mV shunt. I did just what you're wanting to do on a 4 SW4048 inverter system once. I built my own buss out of copper bar, but you might be able to double up the Midnite buss on to the bigger shunt. I then used paralleled 4/0 cables for the battery side of

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Allan Sindelar
Funny, happened to us, too, some years back... six sets of 2V cell pairs in a 24V bank, with one case showing 0.05 volts DC, the difference in resting voltage between the two cells. We opened up the cover (the case was red, as I recall, Mick), disconnected the

[RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread August Goers
Hi Wrenches, Here is yet another 120% rule question as it relates to center fed main panels. 2011 NEC 705.12 deals with inverter point of connection and 705.12(D)(7) reads: *Inverter Output Connection.* Unless the panelboard is rated not less than the sum of the ampere ratings of all

Re: [RE-wrenches] 500A bussing

2012-10-15 Thread Allan Sindelar
Mac, Well, maybe not yet. If you expect to run consistently high current, you will want a shunt larger than 500A, as according to Ralph Heisey at Bogart Engineering, most shunts can handle about 2/3 of their rated capacity for extended duration,

[RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Mick Abraham
Hi, Mechanix~ Bill Dorsett polled the group about recommended battery chargers for connection to a generator. Iota brand is the successor to Todd brand; I believe Iota bought the designs, tooling, etc. and these have appeal because of the relatively low cost per rated amp. They seem generator

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread William Dorsett
Thanks Aaron, but I need one that goes to 15.5 or 16V for equalizing the bank. Just got this back from Iota: Iota does not make any chargers that go to 15 volts output for equalizing. Thank you Iota Engineering Xantrex TruCharge 20 at least has an equalize setting, though I don't know

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Dave Palumbo
There is a potentiometer on the board of the IOTA chargers that used to be assessable through a hole in the cover. I adjusted a new one two weeks ago and had to open it up to get at the pot. Adjusts up 15.6VDC with plug in and 14.8 with the jumper plug out. Some of the older models would adjust

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread boB
How about an off grid inverter/charger that most off-griders would normally have ?? Almost any of the typical off grid I/C would do a much better job at charging. I would think that any el-cheap-o 12V inverter would balk at seeing much over 15V anyway. boB On 10/15/2012 11:27 AM,

Re: [RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread Kent Osterberg
If you back feed at the end of the bus bar where the main is connected to the middle of the bus bar, the back fed breaker cannot overload the bus bar between the main and the back fed breaker, but it would be possible to overload the other side of the bus bar - it's being fed by both the main

Re: [RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread August Goers
Kent, Brian, It still seems like a grey area to me. I think that from a conservative point of view that we cannot apply the 120% rule to a center fed panel. In my experience, AHJs around the Bay Area know a little about the 120% rule but haven't thought about it to this level of detail. In

Re: [RE-wrenches] Fwd: Charge control question

2012-10-15 Thread Allan Sindelar
Dan, I checked out the Tigo website, and found nothing there to suggest that these were intended for off grid battery charging applications. A round-the-world sailboat is off grid. Are you suggesting that these will work in battery charging applications? If

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Bill Brooks
boB, The limit of 80-volts was to make an exception for single module devices like micro-inverters and for 48-volt battery systems and smaller. A change controller operating above 80V would be required to have an AFCI whether on or off grid if the array is mounted on a building. Bill.

Re: [RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread Bill Brooks
August, I'm not really worried about residential center fed buswork since the 120% exception only applied residential prior to the 2008 NEC and the location of the OCPD was not specified. The location of the OCPD was specified in the 2008 NEC to address commercial panelboards that are run

Re: [RE-wrenches] Fwd: Charge control question

2012-10-15 Thread Jay Peltz
Hi Allan I have a client who did indeed install Tigo with a outback CC and it all works well I don't recommend it for the boat. Too much to go wrong. Jay Peltz power Sent from my iPhone On Oct 15, 2012, at 12:46 PM, Allan Sindelar al...@positiveenergysolar.com wrote: Dan, I checked out

Re: [RE-wrenches] Fwd: Charge control question

2012-10-15 Thread Jesse Dahl
I was wondering about battery charging using Tigos. I have a few spare Tigos and modules for them lying around and was thinking of using them with a magnum to run my radon fan and chest freezer. Since the Tigos have MPPT built in, would the use of a MPPTing charge controller be unnecessary?

Re: [RE-wrenches] Fwd: Charge control question 2

2012-10-15 Thread dan
Hey Alan, I checked in with Tigo tech support to reconfirm. they assure me yes, this generation of optimizer (Basically a module level MPPT DC to DC converter) does work with MPPT controllers for battery charging. I pressed them for a cut sheet or statement outlining their performance in battery

Re: [RE-wrenches] Fwd: Charge control question 2

2012-10-15 Thread Allan Sindelar
Dan, Starting around 1999 with the successful introduction of the RV Power Products (long since renamed Blue Sky Energy) Solar Boost 50, we did lots of controller upgrades, as that 15-20% winter boost was a cheap and effective upgrade. For a few years we

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Larry Crutcher, Starlight Solar Power Systems
Hi MIck, I often see your explanation for absorption charge phase. Consider this: While charging, current is applied without voltage regulation (CC). At the charge set point, PWM control (CV) takes place to regulate voltage. There is no control over current as the battery internal resistance

Re: [RE-wrenches] Fwd: Charge control question 2

2012-10-15 Thread Jesse Dahl
When I get home I will send you the link to my Tigo system on my home. I just installed it, but the few times I fired it up, I saw increased production. (230W from 210W modules.) I have the inverter monitored as well, so I'm thinking of running the tigos for a year and then run the system

[RE-wrenches] FW: AC (only) Diversion

2012-10-15 Thread Carl Emerson
Hi there, Just to clarify, we are talking about a battery-less grid tie system. We want to have the choice to divert the AC available for export to an AC load for example a pump or a thermal store. The reason for this is that the tariff for export may be only 10c and the unit cost to

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread William Dorsett