I have always had a problem when I saw thin wall AL flex being used with
twist-in-insert type fittings.
Mark Frye
On 11/9/2012 5:44 AM, Dave Click wrote:
Nick, what the AHJ is telling you may actually
Exactly,
Another fine example of how the Code works. Anyone out there have the
definition of special permission.
Any changes have to go back to the NFPA? Really the buck stops at the
quasi-judicial authority of the head of the building department.
Inspectors are the bearers of that
thoughts?
Mark Frye
Berkeley Solar Electric Systems
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http
find
references in the Code to support this.
Mark Frye
Berkeley Solar Electric Systems
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re
1 - What is the AC output rating of the PV inverter?
2 - What is the size of the feeder conductors?
3 - Does the sub panel at the garage have a main breaker of it's own?
4 - Does your AHJ or utility require anAC disconnect or not?
Mark Frye
Berkeley Solar Electric Systems
On 4/11/2012 7:09 AM
Also,
Was a ground conductor run with the feeder?
Mark Frye
On 4/11/2012 7:09 AM, Aladdin Solar wrote:
Wrenches:
There's probably an obvious answer but please help me think this
through. Here's the situation--comes up all the time: The PV array and
grid-tied inverter will be located
Not necessarily. NEC 2008, 250.32 (B), Exception allows you to use the
neutral conductor for existing structure so long as several requirements
are met.
Check it out.
On 4/11/2012 8:41 AM, Aladdin Solar wrote:
I meant the question largely to be a generic one but I can give you an
example:
*
Rooftop solar installation sparks fires in Trenton, New Jersey*
28.03.2012: According to local news portal NJ.com, a rooftop solar
system has triggered several small fires at a recycling center in
Trenton, New Jersey. The article reports that a major malfunction in
the rooftop solar
Is there a Standard to which a battery enclosure can be tested such that
it can be listed and marked as conforming to the requirements of
performance that a battery enclosure must conform to in order for that
battery enclosure to be used as a battery enclosure?
Is the inspector looking at the
Still, if you put 2 x 4's on the ground between the batteries and the
floor, wouldn't the 2x4's have to be UL listed?
On 3/22/2012 3:53 PM, Brian Teitelbaum wrote:
Jeremy,
Sometimes the best enclosure is a locked room. Is it possible in
this case to wall off the space and provide a locked
for
things like monitoring equipment, it is reasonable that the above remain
unchanged so long as there is permanent marking stating that no additional
load circuits can be added (only supported by Code to the extent AHJ's can
make determination of acceptability.)
Mark Frye
Berkeley Solar Electric Systems
as the service,
then the dedicated load center can be main lug without main breaker. If the
dedicated load center is located on a buidling remote from the the service,
then it will need a main breaker rated at 125A.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530
? Why did they include the language
capable of supplying multiple branch if their intent was other than to
allow the use of dedicated load centers?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
Rich,
If you have an archive of Wrenches email, also see thread on this subject
dating on and about March 29, 2011.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re
?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Tuesday, January 17, 2012 8
OK,
But let's assume only one string, how important is it to develop a higher
bulk charge current?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
Todd,
I thought you were totally off-grid.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
Rebekah,
If you knew only the power and voltage, then you would use the root of 3 to
determine the amps. But since you know the amps, you don't need to use the
root.
The second equation would be the correct one.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA
.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
you store the acid dry for ten years?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
I see. So there is a big difference between using the DC generator. With an
AC unit I can run it into the inverter/charger and it will give me three
stage charging. With the DC unit, I can really only us it to bulk charge.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City
How would you integrate a dc generator like to Polar Power into a standard
inverter/charge-battery-pv charge controller system?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
breaker in the
existing main panel. Move the existing 30A breaker into the new subpanel and
install the new 15A breaker into the same.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
.
I think this is a much better interpretation and method that preserves a
clean and functional load side connection topology. I think most reasonable
inspectors would agree as well.
Good Luck.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
of the
frame brings it into square and on we go.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
Lumeta around this?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
electrode shall
be permitted to be used for both systems...
Review this article and share it with your inspector in order to determine
what is motivating him.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
be either a diversi9on
load or a contactor that disconnects the grid tied inverters all together.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun
Folks,
Has anyone talked with PGE about needing (or not needing) a new
Interconnection Agreement when changing out inverter make and model without
increasing the size of the PV generator (number of modules) on a system that
is already interconnected?
Mark Frye
Berkeley Solar Electric Systems
303
customers:
- Buy the refurbished units w/ 1 year warranty
- Buy new replacement units with 10 or 20 year warrranties
- Buy entirely new equipment such as Enphase or SolarEdge
What are other folks experiencing as we move well past the 5 year warranty
horizon for many of our earlier customers?
Mark Frye
based on their online
configuration tool, and also well in line the the SMA white paper of many
years ago suggesting a 120% mod/inv ratio as optimal.
And yet, the first unit failed in 4 years and the refurb failed in 2 year.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada
, 75%? Would I have avoided most of my inverter failures
if I had?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
? If not, it is
possible that the coil taps are connected in a manner that is not efficient.
That being said, 15.6 A @ 120V sound like an awefully large number. Perhaps
you have a bad connection at one of your pull boxes.
I would be happy to stop by and take a look at the xfrm spec etc. with you.
Mark
the
internal face gasket.
I really haven't looked into it much further but I wonder if the water you
observed entered through an incomplete connector mate, along the conductors,
into the inverter enclosure?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530
The question is not well addressed without knowing the nominal dc system
voltage.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re
was behaving the same as to old dics meters.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay
closely have you looked at this? It looks like the Tigo is already about
1/4 the cost of an Enphase. So how close are you to moving from an optimizer
/ inverter combination to a microinverter?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http
, with high
voltage (over 250V) DC wiring, and doubling DC connector count.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE
system yield
.0.0013%.
I am not complaining, just musing over this interesting evolution.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List
Thanks Phil,
I have already swapped the module to confim that the problem follows the
module, not the inverter.
I am currently working within channels with my distributor for warranty
replacement having just requested an RMA.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada
is
inherent in microinverters as well.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
Bob,
I think you are talking about Cougar Paws:
http://www.cougarpaws.com/
I love them and buy a pair for anyone who works for me.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
Jason,
My guess is that this will work just fine.
My comment is that according to my conversations with Enphase, they would
consider this an off-grid application for which they do not warranty their
product.
If this is the case, it is something your customer should understand
upfront.
Mark
of these three is electrically identical and
solidly connected inside the inverter. But, I don't know.
The folks at Enphase tech support will not tell me whether or not this is
true.
Anyone out there have any ideas about this?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City
..except..there wasn't any rubber there anymore...all rotted out.
Back in the day I went for a custom rolled cone flashings that I could caulk
into the post and slide a rubber counter-flashing over the whole thing.
Overkillperhaps.
Best of Luck.
Mark Frye
Berkeley Solar Electric Systems
Generally, in order to develope the full tensil strength of the bolt, it
should be engaged by a minimum of 5 threads.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re
Manager
Southwest Technology Development Institute, New Mexico State University
575-646-6105 575-646-3841 (FAX)
http://www.nmsu.edu/~tdi/Photovoltaics/Codes-Stds/Codes-Stds.html
SWTDI/NMSU
3705 Research Drive
Box 30001/MSC 3 SOLAR
Las Cruces, NM 88003-8001
Mark Frye
Berkeley Solar Electric
Folks,
I have a couple of new SunExtender AGM batteries that I will be using in a
UPS application.
My understanding is that I should cycle them before floating them out for
standby service.
Am I getting this right?
How many cycles - to what DOD?
Mark Frye
Berkeley Solar Electric Systems
303
my merry way?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick
the groundingstem of
multiple seperately derived systems, but could we construe a utility service
to one dwelling as a seperately derived system relative to another dwelling
with it's own service? Where can one find the definition of a seperately
derived system in the Code?
Mark Frye
Berkeley Solar
in this case because each building
has it's own service and therefore cannot be considered as a seperately
derived system. So where does the Code speak to this.
My sense is that it is a big no-no, but can exactly explain why.
Anyone else out there agree or disagree?
Mark Frye
Berkeley Solar
I have not yet visited the site to see, but I would guess that they are feed
from the same transformer.
If they were, how would that make it OK?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana
Sent: Monday
Or another way to illustrate this problem:
There is nothing in the Code that would stop me from hauling out the old #6
and bonding my GEC to my next door neighbors GEC, if I wanted to?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http
it. Otherwise
it's onward and upward.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
Folks,
I did send the question to John Wiles and he was gracious enough to reply.
Here is his response:
Mark:
Better ask the utility involved. Probably depends if they are on a common
transformer or not.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
I have a customer who has two separate buildings, a home and a shop. Each
dwelling has it's own service.
He wants to put in two pv systems, one for each service, but wants all the
PV modules to be on the shop roof.
Why is mind going clunk when I try to deside if this is allowed by Code?
Mark
the DC diversion side
solution if you have someplace to put the power instead of just the
batteries, although that might be generally less commonly available for
retrofits into existing on-grid households.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401
high. Once the voltage drops the contactor can close and bring the Fronius
back on line and then the 5-minute start up delay before it is feeding the
line again.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
caps using the gravity feed.
I don't have any idea what is going on with the distribution of the product
from Europe.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
, so better safe than
sorry.
So now I see, I have to do what I have to do if I want to be even half as
good an electrican as my NABCEP certification says I am.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
not exceed
the allowance for the feeder or the sub-panel. Still, if you do have loads
in the subpanel, you have to up sizes the sub-panel, but not the feeder
conductor.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
an over current
condition in any of that equipment.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
we
need more to concern ourselves with continuous overload conditions and not
so much with short-circuit/ground fault conditions?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
wiring.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Al
I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
Opps!
My bad, I was thinking of a single phase system, not the three phase system
shown in the article.
For the three phase system Kent is correct in counting 180A of supply per
bar.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http
will see the same 480A of supply breakers as the
conductors and busbar of the 400A load center. Here is where I am taking
leap of faith that the AHJ will agree with me that the same 120% allowance
given to the conductors and load center will be given to ATS itself.
Mark Frye
Berkeley Solar Electric
Ken,
In the situation you show in your drawing, what was the rating of the
transfer switch?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun
agreed with me that this was an undesirable
constraint on the operation of an otherwise reliable grid-tied system and it
was not clear that this would satify the warranty issue.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http
) 519-1470
f: (604) 422-2756
Only have one of these puppies in the field, no problems yet.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
derived system and would not require it's own system ground. At
that point, would the AC side of the inverter still be considered a
separately derived system or would the need for system grounding go away?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401
disipators
DC power supplies
Standby generators
??
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
the complexity in wiring?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent
with current capacities would be a problem. It seems like the
frequency would be more of a problem for some devices.
Anyone have experience with deliberately adjusting generator frequency away
from 60 hertz as described above?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City
it in the wings to address voltage faults if they
occur.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
their time faulting and
resetting during daily peaks.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re
Aaron,
Can you give a bit more information? Is this a situation where the meter and
the main disconnect are located on the outside of the building, with a
feeder running to a load center in the garage? Does the utility at this
location require a external lockable disconnect?
Mark Frye
Does anyone here have the 2011 Code available on CD in a searchable format?
Know where to get it?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
Thanks August,
NFPA says there are giving away a softcover copy of 2011 to folks who take a
years subscription to NECPLUS before February something.
Seems like a good value.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
Al,
Are the inverters located inside on the 8th floor with the MLP panel or are
they located on the roof?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches
.
I assume that the fused disconnect is co-located in the basement with the
service equipment?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun
Has any information become available about this fire?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
I am pretty sure you can get it from Multi-Contact USA.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches
with grease etc.?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Get three electricians in the room
It 6'-7 from the center of the grip of the operating handle...when in
highest position.
Happy Holidays.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
by a
positive static charge which restores the module
performance.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
generator
situation. Of course I push the question up past first tier support to the
supervisor.
I bet that if you ask them to put it in writing they will decline.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com
the project at all? All you folks who are
putting Enphase on the load side of grid-tied, battery based inverters need
to ask yourself the same question. It appears that Nick already has his
answer.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
points
for not servicing the warranty? Any claw back of CSI funds on projects that
don't meet projected yields due to unfulfilled warranty claims?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
be steel chain link fence.
Hell we have a pool here at our condo and we need a 5 foot metal fence with
self closing gate to keep kids out. The County would laugh at me if I went
and asked if I could replace it with a wood lattice fence.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada
over to a PV array and put my hand
on a piece of double insulated PV wire with 10A of 30VDC running on it.
I don't get it.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun
talking about on one hand the detailed requirements of a UL1741
inverter and on the other the use of garden supply material as requirements
for ensuring the safety of the system we build.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
It doesn't sound like you have a supply side connection. It sounds like
you have a load side connection which is upstream of the transfer switch
but still downstream of the service disconnect.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
switch equipment.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
do they cross over into a daily-cycle off-grid situation with
moderate daily DOD?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
Thanks Bill,
I am learning more every second.
:-)
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
this scenario?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options settings:
http
are
bonding jumpers that are not required to be continuous.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http://www.berkeleysolar.com/ www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
and may be
located anywhere on the premise. The remainder of the circuit is then
provided by the EGC as it runs back to the service enterance and then the
GEC to the GES. Correct?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
http
101 - 200 of 258 matches
Mail list logo