Re: [RE-wrenches] Classic 150 100 amp utput breaker tripping?????

2015-10-28 Thread Daniel Tittmann
An update on this issue: On my initial visit to diagnose this problem I changed the AGS settings higher volt start and % state of charge start. The report from the client is that this has fixed the AGS issue. So now I am just dealing with the 100 amp breaker tripping. The trip time from the

Re: [RE-wrenches] Classic 150 100 amp utput breaker tripping?????

2015-10-28 Thread Starlight Solar Power Systems
Bizarre, Daniel. I can not imagine that the breaker will open with the tiny PV current available at first light then handles full current all day without a problem. Wild guess here... could it be the Classic transition from open circuit voltage to operation is creating a momentary short that

[RE-wrenches] Classic 150 100 amp utput breaker tripping?????

2015-10-26 Thread Daniel Tittmann
Hive mind- hoping you all can help me solve this mystery issue. System: Magnum double panel with Parallel stacked 2x4448 pae inverters. Classic 150 charge controller wired with an NMEPV 50 (din rail) and NMEPV100 18 - 245 watt solar modules (6x3). (not over powered) Issue: every morning the 100

Re: [RE-wrenches] Classic 150 100 amp utput breaker tripping?????

2015-10-26 Thread Mac Lewis
Hi Daniel, Do you know what the error is on the AGS? What are the start set points that you have? Jay could be on to something if the battery voltage is collapsing before the generator can start, the cc current could be high. Do you know specifically what time of day the breaker is tripping? I'd

Re: [RE-wrenches] Classic 150 100 amp utput breaker tripping?????

2015-10-26 Thread b...@midnitesolar.com
Daniel... This one is kind of unusual... Especially tripping only in the morning. Temperature ? Something moving or shaking the breaker box ? Have you tried changing the circuit breaker ? What is the approximate maximum current output from the Classic in the morning ? You can access

Re: [RE-wrenches] Classic 150 100 amp utput breaker tripping?????

2015-10-26 Thread Jay
Hi Daniel Is this a new classic with OCP? Or maybe they don't have it anymore? What it sure sounds like like is a big load on the batteries, it hits faster than the AGS can start, and the caps in the classic are dumping into the super low battery voltage. If this is happening in the AM,