*From:* Ray Walters [mailto:r...@solarray.com]
*Sent:* Friday, October 26, 2012 10:28 PM
*To:* glenn.b...@glbcc.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Enphase and Romex
** **
So if the Romex is loaded with THHN/THWN (damp/wet rated), and no where
does the outer covering
mailto:r...@solarray.com]
*Sent:* Friday, October 26, 2012 10:28 PM
*To:* glenn.b...@glbcc.com mailto:glenn.b...@glbcc.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Enphase and Romex
So if the Romex is loaded with THHN/THWN (damp/wet rated), and no
where does the outer covering
]
Sent: Friday, October 26, 2012 10:28 PM
To: glenn.b...@glbcc.com; RE-wrenches
Subject: Re: [RE-wrenches] Enphase and Romex
So if the Romex is loaded with THHN/THWN (damp/wet rated), and no where does
the outer covering of the Romex itself get exposed to the wet location, that
should
...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, October 25, 2012 9:13 AM
To: RE-wrenches
Subject: [RE-wrenches] Enphase and Romex
I'm sure this has been covered, but I could not find it in the archives.
We are considering using Romex in the attic for the first time. My
-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Friday, October 26, 2012 3:10 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase and Romex
Thanks Benn, I've also never seen anyone switch to UF, just to wire to an
exterior
Ditto Ray.
Sent from Samsung tabletRay Walters r...@solarray.com wrote:Thanks Benn, I've
also never seen anyone switch to UF, just to wire to
an exterior outlet mounted directly on an exterior wall of a home.
Further, the box is usually indoor rated(if it's in the wall) and only
the
*To:* RE-wrenches
*Subject:* [RE-wrenches] Enphase and Romex
** **
I'm sure this has been covered, but I could not find it in the archives.**
**
** **
We are considering using Romex in the attic for the first time. My plan
was to use the new Enphase coupler to connect the trunk cable
Beach, Ca. 92660
760-403-6810
From: benn kilburn b...@daystarsolar.ca
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Friday, October 26, 2012 11:02 AM
Subject: Re: [RE-wrenches] Enphase and Romex
Glenn/Jason,
So you wouldn't use romex to feed
: Thursday, October 25, 2012 9:13 AM
To: RE-wrenches
Subject: [RE-wrenches] Enphase and Romex
I'm sure this has been covered, but I could not find it in the archives.
We are considering using Romex in the attic for the first time. My plan was to
use the new Enphase coupler to connect the trunk
in wet locations
*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *benn
kilburn
*Sent:* Friday, October 26, 2012 2:03 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Enphase and Romex
Glenn/Jason,
So you wouldn't use romex to feed
I'm sure this has been covered, but I could not find it in the archives.
We are considering using Romex in the attic for the first time. My plan was
to use the new Enphase coupler to connect the trunk cable to Type TC-ER,
enter a Soladeck passthrough box on the roof into a junction box in the
Jason:
You can run a 6 or 8 bare in the attic (don't have the book handy) alongside
your romex.
690.47 has an exception exempting the supplementary electrode if the DC load is
within the array, which is the case.
William
On Oct 25, 2012, at 6:12 AM, Jason Szumlanski ja...@fafcosolar.com
Jason:
If bare copper can be subject to damage in the attic, the same would be
true of NMC. Is your inspector willing to shut down every residential
wiring project in his/her jurisdiction? I don't think so...
William
At 07:41 AM 10/25/2012, you wrote:
William,
Regarding the bare CU in
Jason,
Why don't you transition to romex in the Soladeck, eliminating the need for a
junction box in the attic?
I abide by the CE Code (Canadian) and run a #6green from the roof to the dist
pnl.
benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and
typos.
On
Subject: [RE-wrenches] Enphase and Romex
I'm sure this has been covered, but I could not find it in the archives.
We are considering using Romex in the attic for the first time. My plan was
to use the new Enphase coupler to connect the trunk cable to Type TC-ER,
enter a Soladeck passthrough
, October 25, 2012 9:13 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Enphase and Romex
** **
I'm sure this has been covered, but I could not find it in the archives.**
**
** **
We are considering using Romex in the attic for the first time. My plan
was to use the new Enphase coupler
, October 25, 2012 8:37 AM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] Enphase and Romex
Soladeck on the rooftop places it in an environment that is considered
‘wet’.
I don’t think Romex is listed for use in a wet environment.
This would force you to use the proposed jbox in the attic