We use this 3M wire numbering dispenser.  They don't stick as well as I'd like, but it can solve some very weird problems later. 3M STD Wire Marker Dispenser with #0-9 H-5223 - Uline I'm also a fiend for color coding, and have had numerous discussion here on the list about the need to color

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-23 Thread Jason Szumlanski
What made this installation (again, by others) a bit more complicated was that all branch circuit line conductors were black. I make it a point on my installations to require black for L1 and red for L2 up to #6 wire size. It's not a failsafe by any means but does reduce risk. On Thu, Jan 23,

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-23 Thread August Goers
Jason - Thanks for sharing - this is a good lesson for all Wrenches. Years ago we had a dual string inverter installation where the DC positives and negatives were mixed between the two interters. String 1 positive went to inverter 1, string 1 negative went to inverter 2 and vice versa. The

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-22 Thread Blake Gleason
Thanks for sharing, Jason. That's an excellent cautionary tale... On Wed, Jan 22, 2020 at 2:58 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > I discovered the issue I believe, so I thought I'd update all of you who > gave me ideas on what to look for (thank you). > > And this

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-22 Thread Jason Szumlanski
I discovered the issue I believe, so I thought I'd update all of you who gave me ideas on what to look for (thank you). And this is something that I stress the importance of all the time... The branch circuit pairs were not properly paired up! All of the L1 conductors went to L1 on the bus and

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Ray
Almost every meltdown I've looked at was not due to lightning, but heat from a high resistance connection.  A lug not torqued can cause surrounding plastic to melt.  If the wrong breakers are used with the buss bar, they might snap on and work, but not be able to take the current over time. 

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Jerry Shafer
Wrenches Cant tell anymore but l had a buss failure due to water getting on buss and pealing the tin off the buss and the aluminum base will light up real quick. Jerry On Tue, Jan 21, 2020, 9:10 AM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > (System installed by another

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Jason Szumlanski
I just remembered this... There was a tripping breaker here almost immediately after installation. We investigated the string and found no issues, including checking the termination cap (on all strings). We reset the breaker a few times and it would run for days without issue, then trip. Then we

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Jason Szumlanski
Yes - It's only 56A total inverter output rating on a 125A bus. Max string is 13A inverter output rating on 20A OCPD. On Tue, Jan 21, 2020 at 12:58 PM Chris Sparadeo wrote: > Jason, > > Have you calculated your back-fed amapacity allowance to confirm it > complies with the 120% busbar rule

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Chris Sparadeo
Jason, Have you calculated your back-fed amapacity allowance to confirm it complies with the 120% busbar rule as per 705.12? Best, Chris On Tue, Jan 21, 2020 at 12:40 PM August Goers wrote: > Hi Jason - > > It certainly appears that there was some sort of surge or short. We've had > a few

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Dave Tedeyan
Hi Jason, I have had an experience servicing other's arrays where they used PVC on the roof. The LB cover does not hold up over time and then water and snow were getting into the conduit, which came straight down into the top of that same kind of Eaton panel. Corrosion caused at least one breaker

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread August Goers