Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Darryl Thayer
Jay has a real strong point. If you are near low voltage low state of charge. Two or 4 hrs from a 4kw array is only 8 to 16 kwh nowhere near 46 kwh. Given the recomended max charge rate is C/5 you would have to be charging for days On Fri, Apr 19, 2019, 10:20 PM John Blittersdorf <

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread John Blittersdorf
Mac, If there is a TriMetric or charge controllers, you can get min/max voltages each day or since last reset. I have found that is very useful info when large, short duration loads hit. ie well pump. I would find on one of my 24 v systems that an 18 or 19 v min would indicate that the well

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Glenn Burt
Hi Larry, I am curious why you would use the 100Hr rate for this approximation and not the 20 or 24Hr one, since that is the period in which Mac is reporting the anomaly. Happy to learn the details! Thanks, Glenn From: RE-wrenches On Behalf Of Starlight Solar Power Systems Sent:

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Jay
Hi Mac I don’t know if this is pertinent, but it could be the SOC /fndc getting out of calibration. I’ve seen this happen if % SOC charge termination is on ( default). Kinda goes into a negative loop. The other thought is that 2 hr absorb is pretty short for that size bank, but maybe that

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Starlight Solar Power Systems
Mac, Only removing 6kWh from 46kWh of storage should not be able to produce the voltage sag to trigger AGS. That’s only about 13% at a 100Hr rate. Voltage should be no where near that point. Have you verified actual voltage when the AGS is triggered? Loose wiring or terminal corrosion can

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Howard Arey
Might want to confirm that the FNDC Relay is off and just the AGS relay is set from the Mate menu. Seems I went through this one time before and excellent Outback support quickly surmised the issue for me. Scot Arey Solar CenTex From: RE-wrenches On Behalf Of Mac Lewis Sent: Friday,

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Mac Lewis
Good question. Voltage slowly drops in a fairly linear fashion through out the night. If it is a sudden short duration load, it is short enough that Optics can't pick it up, or it get's averaged out. When I've been on site, I didn't observe any loads that caused concern. On Fri, Apr 19, 2019

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Roy Rakobitsch
Using Optics, can you equate the voltage sag/ gen start command with a particular load? Or is the voltage dropping quite evenly over the course of the night? They could actually be degraded if there is no indication of a sudden load/ voltage drop. A simple load test when on site can also help

[RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Mac Lewis
Hello Wrenches, We recently inherited an Outback system that I've been keeping an eye on via Optics. Its a dual stack 3648 VFXR, with about 4kW of PV with a single string of EnergyCell 1100RE battery bank (reported to be ~6 months old) ~.46 kWh at C20. I have been observing how the system

Re: [RE-wrenches] 1000 volt

2019-04-19 Thread Harry Mahon
Bill – A couple items: 1. The 3TL-US (along with all the STP TL-US line) has been discontinued, and I believe this particular model has been completely sold out. Some Distributors may have stock remaining or you may have already obtained the unit. As Blake noted, if you use this

[RE-wrenches] REC 290 TP

2019-04-19 Thread drake . chamberlin
Does anyone have 4, REC 290 TP modules? Please contact me off the list if you do. Thank you, Drake ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: