Re: [RE-wrenches] Aquion troubleshooting

2021-07-24 Thread don
-0600 From: Mac Lewis <maclew...@gmail.com> To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Aquion troubleshooting Message-ID: <CAOABG49o=uqnxre4qgzz5qi_9cnvfpkk6ebyom1dgd-ptng...@mail.gmail.com> Content-Type: text/plain; charset="utf-8" Hey

Re: [RE-wrenches] Aquion troubleshooting

2021-07-24 Thread Glenn Burt
typos and spelling errors.-- Original message--From: Mac LewisDate: Sat, Jul 24, 2021 1:03 PMTo: RE-wrenches;Cc: Subject:[RE-wrenches] Aquion troubleshootingHey wrenches,Does anyone have any advice for troubleshooting Aquion batteries? This particular stack is an Aspen 48M-25.9

Re: [RE-wrenches] Aquion troubleshooting

2021-07-24 Thread Jerry Shafer
Wrenches Personnelly l would replace the stack, rather than them loosing a charge there might just not be any charge to begin with. Once the batteries settle they just are dead. You can isolate and load test if that makes the customer feel better. Jerry On Sat, Jul 24, 2021, 10:03 AM Mac Lewis

[RE-wrenches] Aquion troubleshooting

2021-07-24 Thread Mac Lewis
Hey wrenches, Does anyone have any advice for troubleshooting Aquion batteries? This particular stack is an Aspen 48M-25.9. They are losing power on a nightly basis. I'm not seeing much technical literature out there and I'm not familiar with these batteries. Are there any common failures? How

Re: [RE-wrenches] Aquion

2020-08-06 Thread Chris Sparadeo
Hi Drake, About a year ago I inherited two different off-grid customers with existing/ failing Aquion battery banks. Higher discharge rate seemed to be the prognosis. One system had 12 batteries and only 4 could hold under load. Both battery banks eventually had to be replaced with LFP batteries

Re: [RE-wrenches] Aquion

2020-08-05 Thread Jay
Hi Drake, Unfortunately yes this is becoming a common problem And worse there is really nothing you can do. Company is gone The new company that formed from the remains of Aquion has a new different battery which is different enough I’ve been told they are not compatible. And they are not

[RE-wrenches] Aquion

2020-08-05 Thread drake . chamberlin
Hello Wrenches, A bank of Aquion batteries has 5 out of 8 that can not carry any load without dropping down to a couple of volts. One battery is leaking. Three batteries seem to be working. Has anyone experienced this before? Is massive failure common to Aquion battery banks? Thank you,

[RE-wrenches] Aquion

2020-08-05 Thread Marco Mangelsdorf
Hi all, Does anyone know whether Aquion is still around and producing product with that unique saltwater electrolyte after being purchased for cheap cheap by Chinese investors three years ago? Thanks, marco Rebellion logo --- This email has been checked for viruses by Avast

Re: [RE-wrenches] Aquion - Mix and Matching Layers

2019-05-12 Thread Drake
e a big loss both to our reputation and financial health. I recommend discussing the issues and replacing the entire bank. Sent from my Verizon LG Smartphone -- Original message-- From: Lou Russo Date: Thu, May 9, 2019 11:53 AM To: RE-wrenches; Cc: Subject:[RE-wrenches] Aquion - Mix

Re: [RE-wrenches] Aquion - Mix and Matching Layers

2019-05-10 Thread Tom Duffy
o:t...@solar-biz.com> MAIN TOLL FREE: 888-826-0939 DIRECT: 888-503-6772 International: 001-575-539-2111 PANAMA: 507-836-5588 X 122 FAX: 520-844-8442 www.thesolarbiz.com From: RE-wrenches On Behalf Of Bradley Bassett Sent: Thursday, May 9, 2019 2:36 PM To: RE-wrenches Subject: Re: [RE-wrenches]

Re: [RE-wrenches] Aquion - Mix and Matching Layers

2019-05-09 Thread Bradley Bassett
sso > *Date: *Thu, May 9, 2019 11:53 AM > *To: *RE-wrenches; > *Cc: * > *Subject:*[RE-wrenches] Aquion - Mix and Matching Layers > > Wrenches, > > I am getting more and more call about orphaned Aquion systems that have > gone bad. Many of the systems have one or two "

Re: [RE-wrenches] Aquion - Mix and Matching Layers

2019-05-09 Thread Glenn Burt
the entire bank.Sent from my Verizon LG Smartphone-- Original message--From: Lou RussoDate: Thu, May 9, 2019 11:53 AMTo: RE-wrenches;Cc: Subject:[RE-wrenches] Aquion - Mix and Matching LayersWrenches,I am getting more and more call about orphaned Aquion systems that have gone bad. Many

[RE-wrenches] Aquion - Mix and Matching Layers

2019-05-09 Thread Lou Russo
Wrenches, I am getting more and more call about orphaned Aquion systems that have gone bad. Many of the systems have one or two "layers" that have gone bad. Voltage spikes up to the 14-15V range while charging and cratering to zero if even the tiniest load is put on it (e.g. turning on a charge

Re: [RE-wrenches] Aquion Batteries

2019-01-24 Thread Jason Andrade
ote: > > Message: 1 > Date: Wed, 23 Jan 2019 16:08:55 -0600 > From: Darryl Thayer > To: offgridso...@sti.net, newrewrenches > > Subject: Re: [RE-wrenches] Aquion Batteries > Message-ID: > > Content-Type: text/plain; charset="utf-8" > > I have used Si

Re: [RE-wrenches] Aquion Batteries

2019-01-23 Thread jerrysgarage01
smartphone Original message From: Darryl Thayer Date: 1/23/19 2:08 PM (GMT-08:00) To: offgridso...@sti.net, newrewrenches Subject: Re: [RE-wrenches] Aquion Batteries I have used Simphiphy.  Had a problem  over time nearly 2 years the cells were what appears to be out of balance.  I think

Re: [RE-wrenches] Aquion Batteries

2019-01-23 Thread Darryl Thayer
I have used Simphiphy. Had a problem over time nearly 2 years the cells were what appears to be out of balance. I think i balanced them by setting the charge voltage higher than recomended. I think the factory has it wrong On Wed, Jan 23, 2019, 1:39 PM Dave Angelini Offgrid Solar <

[RE-wrenches] Aquion Batteries

2019-01-22 Thread John Blittersdorf
Awhile back, it was mentioned that missmatched cell voltages could be corrected with a 6 volt charger attached to each low layer. I tried this on one and it worked. I have several stacks that have mostly even voltages with one cell over charged. Often 8 to 25 volts. Some showed the high

Re: [RE-wrenches] Aquion Testing

2018-12-24 Thread Bradley Bassett
gt; *www.thesolarbiz.com <http://www.thesolarbiz.com>* > > > > *From:* RE-wrenches *On > Behalf Of *John Blittersdorf > *Sent:* Saturday, November 10, 2018 6:48 PM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Aquion Testing > > > > Lou, I recently disc

Re: [RE-wrenches] Aquion Testing

2018-12-24 Thread Tom Duffy
A: 507-836-5588 X 122 FAX: 520-844-8442 www.thesolarbiz.com From: RE-wrenches On Behalf Of John Blittersdorf Sent: Saturday, November 10, 2018 6:48 PM To: RE-wrenches Subject: Re: [RE-wrenches] Aquion Testing Lou, I recently discovered that each layer can be checked for voltage. I had one b

Re: [RE-wrenches] Aquion Testing

2018-11-10 Thread John Blittersdorf
Lou, I recently discovered that each layer can be checked for voltage. I had one battery test lower than the rest. Looking at the battery closer, I found that my meter probe could get the voltage of each layer indivually. Through an opening in the case. The top layer had the reduced voltage

[RE-wrenches] Aquion Testing

2018-11-10 Thread Lou Russo
Aloha Wrenches, I have a orphaned system with 6 - Aquion Aspen 48Ss that is running out of energy nightly. This is a off-grid system with a Outback FP1. The logs from the Mate 3 do not show excess usage. Beyond testing the voltages of the individual stacks is there any way to check if a battery

Re: [RE-wrenches] Aquion disposal

2018-08-01 Thread Tom Duffy
We had some random 6 volt tray failures from 48 volt Aspens as well, (making the whole stack look bad, but it was bad MC4 connections. So we just charged the low trays (6 volts) individually and brought them up. There does however seem to be poor series connections in the stacks and occasional

Re: [RE-wrenches] Aquion tech support

2017-04-26 Thread Tump
Hate to be an ass, but look in the mirror! There is NONE! The battery set point voltage w/ the SMA Aquion BM200 is ~57.5V UNLIKE all the other inverter manu’s suggestions of 59.8 V. Contact me off list if you want additional thoughts. TUMP > On Apr 26, 2017, at 12:31 PM,

[RE-wrenches] Aquion tech support

2017-04-26 Thread garyh
I am scheduled to be going out to a site in a couple of weeks that is experiencing frequent shutdowns and I've offered to investigate why the shutdowns are occurring. The site is 208 3 phase with six Sunny Islands and Aquion batteries. I've got SMA tech support aware in case I need to talk

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread Andrew Truitt
FYI, Aquion just went BK . - Andrew "Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to fission. And it just so happens that there's an enormous

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread William Miller
8-5600 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Tump *Sent:* Wednesday, March 08, 2017 1:13 PM *To:* findso...@herzfeld.org; RE-wrenches *Subject:* Re: [RE-wrenches] Aquion Batteries I have dual Sunny Islands & dual SB 4000TL22US w/ 20 st

[RE-wrenches] Aquion BANKRUPT

2017-03-08 Thread Tump
As of today at ~ 3PM Aquion has closed up shop! Another reason NOT to use them! > t...@swnl.net > > www.SWNL.net > >

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread Starlight Solar Power Systems
Hi Tump, If you recall, this is EXACTLY what I was calling into question on this list back on November 11th, 2014 and again on Jan 29th, 2016. It looks like you have confirmed my suspicion. The battery can not possible provide the rated capacity. I hope others that have tested these batteries

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread Tump
I have dual Sunny Islands & dual SB 4000TL22US w/ 20 stack on one and another site w/ the Aspen 48M w/ Schneider. I will say this; cost per amp hour of storage sucks w/ the Aquion batteries. Both my client and I feel, that the batteries, despite there size have very little capacity. The

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread John Blittersdorf
Drake, I just did my first Aquion Install on an off-grid second home. It is a 24V single VFX3524. 10 Aspen 24 volt stacks. No one has been living there since I installed it but at least the generator stopped running 2 or 3 times a day just to maintain the heating system. The generator

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread Martin Herzfeld
Has anyone worked with them with a Sunny Island? Space is not an issue for this client. Martin Herzfeld, IREC Certified Master Trainer ™ for PV Installation Professional #IREC 10037 California Solar Contractor License #00833782 C46, D56, D31, C-7 Solar, Trenching, Pole Installation &

Re: [RE-wrenches] Aquion Batteries

2016-07-20 Thread Jerry Shafer
We had a customer request them but once we found out how many it would take, he decided on the deka unigee instead. l dont like running my OB's at such a low voltage as they seem to get hotter due to the higher current. Some of our other product lines don't even reccomend aquions due to that low

Re: [RE-wrenches] Aquion Batteries

2016-02-18 Thread Michael Welch
Hi folks. Tim Wood of Aquion asked me to post this on his behalf. Early versions of the Aquion battery had substantially lower continuous and peak power ratings.  Very few made their way out into the field however some did and we believe the concerns expressed on the board are related to those

[RE-wrenches] Aquion Batteries

2016-01-31 Thread William Dorsett
Our utility wanted to add a new capacity and demand charge to all solar customers' bills. And the new California Public Utilities Commission decision on net metering included a mandate for new solar installs to join Time of Use pricing by 2019. This seems to be the trend that many grid connected

Re: [RE-wrenches] Aquion Batteries

2016-01-29 Thread Starlight Solar Power Systems
I too am interested in anyone that has installed these. I had some concerns back on Nov 10, 2014. Here is a copy/past from that conversation: Something does not add up to me. The cell has a voltage discharge curve way outside that of RE equipment, 1.75 Vpc down to 0.5Vpc. I can't see how this

Re: [RE-wrenches] Aquion Batteries, Was LiFePO4

2016-01-29 Thread Chris Schaefer
To All, Great insight on the lithium movement. I do am looking for anyone dealing with the new Aquion batteries. I’ve got a couple of potential clients that have inquired about them. Saw them at a NABCEP training session last spring and while the idea is moving I wasn’t impressed.

Re: [RE-wrenches] Aquion Batteries, Was LiFePO4

2016-01-29 Thread Jerry Shafer
Wrenches We were looking at these “Aquion batteries” but once we compared the power, voltage operating range and storage of the Unigy vs the Aquion we went with the Unigy brand the volt range worked normally no changes to the LBCO setings. I have Unigy applications going back close to 15 years

Re: [RE-wrenches] Aquion Batteries

2016-01-29 Thread Dan Fink
I second Larry's concerns about Aquion's SOC/voltage curves and tripping LVD at only 40% DOD with standard PV equipment, tied in with not being able to handle high discharge C-rates and surge loads. I did some math on running a typical off-grid home with a well pump on Aquions, and it wasn't

Re: [RE-wrenches] Aquion Energy

2015-07-16 Thread Dana
the environment before printing this email. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye Sent: Thursday, July 16, 2015 6:20 AM To: RE-wrenches Subject: [RE-wrenches] Aquion Energy Does anyone have any thoughts/experience

[RE-wrenches] Aquion Energy

2015-07-16 Thread Mark Frye
Does anyone have any thoughts/experience with the Aquion Energy battery? Mark Frye Berkeley Solar Electric Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings:

Re: [RE-wrenches] Aquion Energy

2015-07-16 Thread Starlight Solar Power Systems
Hi Mark, There was some discussion back in November 2014 on this list. They claim 100% DoD but I can’t see how you can use the full capacity of the battery due to the broad operating voltage. Larry Crutcher Starlight Solar Power Systems On Jul 16, 2015, at 5:20 AM, Mark Frye

Re: [RE-wrenches] Aquion Energy

2015-07-16 Thread Roland Shackelford
Aloha All, We have been integrating Aquion Energy batteries into select Off Grid homes for just over a year now, with great success. The key is designing them for what they are, and not as if they were a lead acid battery. The biggest added design criteria is taking into consideration their power

Re: [RE-wrenches] Aquion Energy

2015-07-16 Thread Jarmo . Venalainen
Gilmore Way, Burnaby, BC V5G4M1 *** Please consider the environment before printing this e-mail From: Mark Frye ma...@berkeleysolar.com To: RE-wrenches re-wrenches@lists.re-wrenches.org, Date: 07/16/2015 05:20 AM Subject: [RE-wrenches] Aquion Energy Sent by: RE-wrenches re-wrenches

Re: [RE-wrenches] Aquion Energy

2015-07-16 Thread Jerry Shafer
Wrenches We did research on this battery going back close to two years, we found that there was an unusable part of the battery capacity that was to far out of range to consider refer to the charts from Aquion, also look at the mass or space required. I do like the idea but the cupcake holder has

Re: [RE-wrenches] Aquion batteries - batteries in general

2015-02-18 Thread Greg
Bill Jerry, Thanks for the updated intel on lead acid battery recycling. I hope the Aquions turn out to be an awesome product. If I ever get a set installed I'll report back : ). Cheers, Greg Egan Remote Power Inc. NABCEP Solar Installation Professional Alaska #00106064 Journeyman

Re: [RE-wrenches] Aquion batteries - batteries in general

2015-02-18 Thread Jerry Shafer
installer PA contractor #44411 www.berkssolar.com -- *From:* Greg g...@remotepowerinc.com *To:* re-wrenches@lists.re-wrenches.org *Sent:* Tuesday, February 17, 2015 1:56 PM *Subject:* [RE-wrenches] Aquion batteries - batteries in general Marco and all wrenches

[RE-wrenches] Aquion batteries - batteries in general

2015-02-17 Thread Greg
Marco and all wrenches, Thanks for the cost /benefit comparison on batteries. We need batteries that won't freeze easily. Even if the cost was the same we'd need to know more about the Aquions before we could risk installing them in the North. I need a fact check from someone on Lead

Re: [RE-wrenches] Aquion batteries - batteries in general

2015-02-17 Thread Bill Hennessy
Centennial Rd Mertztown, PA 19539 o 610 682 4300 c 484 560 4666 NABCEP certified installer PA contractor #44411 www.berkssolar.com From: Greg g...@remotepowerinc.com To: re-wrenches@lists.re-wrenches.org Sent: Tuesday, February 17, 2015 1:56 PM Subject: [RE-wrenches] Aquion batteries

[RE-wrenches] Aquion Energy Batteries.

2015-02-16 Thread Marco Mangelsdorf
Hey Kirpal, I have one of their ~ 22 kWh stacks in my warehouse….looking for a good home. It cost $12,000, including shipping, to get it from PA. to Hawaii. On paper, it looks quite impressive; 3,000 cycles @ 100 percent DOD, which assumes that whatever inverter is used has the DC