-boun...@lists.re-wrenches.org] *On Behalf Of *Rebekah Hren *Sent:* Tuesday, July 20, 2021 6:20 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Snap-n-rack bonding certification Minor update, I got word from Snapnrack that: "The new protocol established with UL eliminates the need to in

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread jay
Can WEEBS be used instead? jay peltz power > On Jul 20, 2021, at 4:37 PM, Rebekah Hren wrote: > > Hi William > > Groan, I don't see that precise model in the series 100 installation manual > > on pg

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread Rebekah Hren
Minor update, I got word from Snapnrack that: "The new protocol established with UL eliminates the need to include the wattage ranges for each module type" Still a pain and the manufacturer/model should be on the rack manufacturer list - but not down to the precise wattage - so slightly less of a

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread Rebekah Hren
Hi William Groan, I don't see that precise model in the series 100 installation manual on pg 74 which is the bonding evaluation list of modules I hope for your sake Snapnrack will send an email the AHJ will

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread Sam Haraldson
The SnapNrack UL 2703 document highlights it's UL listing when used with Type 1 and Type 2 modules. https://snapnrack.com/wp-content/uploads/2019/05/SnapNrack_Fire_Classification_Tech_Bulletin_v.2-1.pdf *SnapNrack Series 100, Ultra Rail and RL systems have been Certified for a Class A fire

[RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread William Miller
Friends: I received the following correction noticed from a hired plan-checker: *Please provide the technical listing for the support rail system documenting that the supports have been tested with the PERC 60 panels. The UL 2703 listing requires the two to be tested/listed together for the