Re: Residential Heads under Soffit

2009-03-09 Thread Justin Reid
8.10.4.1 of the 2002 edition says that residential heads are to be no more than four inches from the ceiling unless the listing allows more.Check the listing. If there is nothing in there that allows the deflector distance to be down to 11" then you will need sprinklers in the higher pocket

sprinkler save

2009-03-09 Thread Scott A. Futrell
Not your everyday sprinkler save if all is true in the attached story http://www.ocregister.com/articles/fire-sabol-firefighters-2329243-cloth es-residents Scott A. Futrell ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mai

Residential Heads under Soffit

2009-03-09 Thread George Medina Jr
I have a 500 sq. ft. room which has a soffit around the perimeter that sticks out 12" and is 11" from the ceiling. My boss seems to think that I can put a sprinkler under the soffit on each side of the room and since the soffits are 12'-6" apart (on each side of the wall) we do not have to add s

Re: Test/Drain at the Riser

2009-03-09 Thread ParsleyConsulting
Rodney, Some of this was addressed in the ROP and ROC on NFPA-13, and there are some revisions coming to 7.1.2.1 and 7.1.3 that will require 1/2" pressure relief valves on all wet pipe systems, and for a manual or automatic air venting valve to be installed on all wet pipe systems. The discus

RE: Test/Drain at the Riser

2009-03-09 Thread Steve Leyton
Rodney: Welcome to Standards Land, the newest attraction in the non-reality based theme park called Sprinkler World. Note well that the language you cite conspicuously used the term, "should", which has been a long-overlooked shortcoming of this particular section of the standard.The NFPA man

RE: Test/Drain at the Riser

2009-03-09 Thread Rodney Hamm
I am writing this response on behalf of any forum members who do not completely understand some of these issues, not as a direct response to Mark. The following two paragraphs are from NFPA 13 (2002): 8.16.4.2.1 An alarm test connection not less than 1 in. (25.4 mm) in diameter, terminating in

Re: Test/Drain at the Riser

2009-03-09 Thread Ron Greenman
Timothy, You're right about testing the single head flow but on a wet system this can be done from anywhere since the water is equal everywhere. It does not need to be timed at the most remote point because it is already there. Timing is in this case to note the time from beginning of flow to alar

RE: Test/Drain at the Riser

2009-03-09 Thread David de Vries
Of course it is important to have the ITC at the furthest remote location for a dry system, since you do want to know the longest time it takes to get water on the fire, but as Ron pointed out, in a wet system the volumetric flow rates are the same, no matter where (elevation being equal) in the

RE: Test/Drain at the Riser

2009-03-09 Thread Michael Fitz
hsupp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET Smart Security, version of virus signature database 3921 (20090309) __ The message was checked by ESET Smart

RE: Open Grating

2009-03-09 Thread Chris Cahill
That's my point what sprinkler work? Code 50% open they claim 50% open. We can review the details and make sure it's 50.1% open to cover the more than part. They have full control over maintaining flues. I'm not judging whether this is a good idea or not just reading the code and comparing

RE: Test/Drain at the Riser

2009-03-09 Thread Timothy W Goins
I respectfully disagree. The purpose is to test the alarm device during a one head fire flow. Since we have to time the device, putting it at the most remote area makes more since, since we are simulating a fire at the most remote area and timing the activation of the alarm device. The alarm devic

RE: Test/Drain at the Riser

2009-03-09 Thread Steve Leyton
And I just as respectfully re-disagree. The purpose of the ITC is to test each waterflow alarm device, and to be sure that an audible alarm sounds within 5 minutes - see 6.9.1 and 8.17.4.2 (2007 ed.). That's it - the standard even contains a new disclaimer regarding this issue - see A.8.17.4.2

RE: Open Grating

2009-03-09 Thread George Church
Until they pay more for this than plywood only to have us tell em thanks, here's the cost of the sprinkler work anyway.. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Monday, Marc

RE: Test/Drain at the Riser

2009-03-09 Thread Steve Leyton
Hear, hear! Theoretically, one would need multiple air relief locations if purging were the issue. The issues of surging and pressure swell/packing can be mitigated with a pressure relief valve, which can be at the test/drain (obviously, several are sold with this feature) or at a more remote o

RE: Open Grating

2009-03-09 Thread Chris Cahill
Except for the fact the definition of solid shelving seems to support the case. '02 - 3.10.10...Shelves of wiremesh...more than 50% open and where the flue spaces are maintained shall be defined as open rack. They are not advertising to us. They are advertising to people who have warehouses and

RE: Open Grating

2009-03-09 Thread Craig.Prahl
So it lets sprinkler discharge through as opposed to a solid shelf. They think this is special? It makes no difference when the rack is loaded with products, the sprinkler discharge is still obstructed. Who builds racks and puts nothing on them? It's a dumb advertising feature. Craig L. Pr

RE: Open Grating

2009-03-09 Thread George Church
No, but its only 50% open, and I believe it needs to be 70% open to be considered acceptable waterflow. Now maybe a sharp guy could specify an increase in density to overcome this, and confirm interruption of spray pattern to droplets coming thru their deck. But its tough to design for boxes or

Open Grating

2009-03-09 Thread Matthew J. Willis
http://www.punchdeck.com/index.html I found this advertised in the current issue of a major magazine. It seems like it is mostly designed for in rack, but under applications it speaks of archive storage over large area. It also seems the key selling point to this is the ability to allow sprinkl

RE: Test/Drain at the Riser

2009-03-09 Thread Mark Sornsin
Pardon me if this is ground that was already covered- I specify the Inspector's test Connection to be located at the sprinkler riser. This is NOT something that is new to NFPA-13 either. E.g., the 1996 edition (4-15.4.2) does not require the location to be at the riser - it doesn't specify any

RE: relief valve on gridded system

2009-03-09 Thread George Church
There's been other threads defining systems, but in this case the SF defines you have two, so two PRVs are reqd. If this bothes you as stupid, console yourself that when the one clogs up, you have installed a redundant one ready to take over. Unless you're using the larger claval we'd use on a pump