Stairways

2010-05-18 Thread å . . . . . . .
> Bottom line, in my opinion, sprinkler and standpipe piping can run into > and out-of the enclosure as many times as required with > through-penetration protection, but, not through. I am confused. Happens very easily. if we are allowed to make single penetrations of the [exit enclosure] as man

SC sprinkler requirement delay

2010-05-18 Thread Todd Williams
http://www.charlestonbusiness.com/news/34288-s-c-senate-votes-to-delay-sprinkler-mandate-for-new-homes-until-2014 Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com ___ Sprinklerforum mailing list Sprinklerfo

RE: Stairways

2010-05-18 Thread Johnson, Duane (NIH/OD/ORS) [C]
If the AHJ determines that you cannot pass through the stair, you can always provide a rated enclosure (1 hr or 2 hr) around your piping so that the piping is not "in" the stair enclosure. This is often done with other utility risers. Duane Johnson, PE Program Manager Division of the Fire Marsha

Stairways

2010-05-18 Thread plansappr+djkarch.com
You need to tread carefully on this one. 2006 IBC 1020.1.2 states "Penetrations into and OPENINGS THROUGH ...". Peel back to 1020.1 which states "Interior exit stairways and interior exit ramps shall be enclosed with fire barriers constructed in accordance with Section 706". Peel back to 706.6

RE: Obstruction to Discharge

2010-05-18 Thread Brian Harris
Forest- It's my understanding that the 3 times rule only applies to structural members when dealing with light hazard (8.6.5.2.1.4) I believe my situation would fall under 8.6.5.1.2 Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:spri

RE: Stairways

2010-05-18 Thread Reed Roisum
Brian, I wouldn't jump to that conclusion... It does say "required" in the IBC verbiage below which I assume applies to the whole list of exceptions. One could argue that the only "required" sprinkler piping in the stair enclosure is the pipe feeding a sprinkler or sprinklers in the stairway.

RE: Stairways

2010-05-18 Thread Richardson, R
email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 5124 (20100518) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __ Informat

RE: Stairways

2010-05-18 Thread Steve Leyton
ubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 5124 (20100518) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __ Information from ESET NOD32 Antivirus, version of virus signature database 5124 (2010

RE: Stairways

2010-05-18 Thread Craig.Prahl
Standpipe risers in stairs are common, but pipes just passing through the stair are often disallowed. Better make sure you know what the local AHJ's perspective is on the matter because there can be great inconsistency on this issue. Craig L. Prahl, CET Fire Protection Specialist Mechanica

RE: Stairways

2010-05-18 Thread Richardson, R
Be careful with this one, in Seattle the Building Official does not allow sprinkler pipe penetrations of stairways unless is strictly to serve a sprinkler in the space (eg: no pass through arrangements). Rich Richardson Seattle Fire Department -Original Message- From: sprinklerforum-bou

RE: Obstruction to Discharge

2010-05-18 Thread Forest Wilson
Based on language in NFPA 13-8.6.5.2.1.1 and 8.6.5.2.1.2, the light would be considered an obstruction. This appears to be clarified in the commentary, A-8.6.5.2.1.4. But, why do you need 24"? Using the three times rule, for a light 5" deep, you would need to be 15" away. The options could be: (A)

RE: Stairways

2010-05-18 Thread Thom McMahon
You'll still need to remember to protect any penetrations with fire stopping details equal to the rating of the stairwell shaft rating. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message

RE: Stairways

2010-05-18 Thread Brian Harris
Reed- So if it's a single stairway I can pass my sprinkler pipe straight through, awesome. I've always routed the pipe out and around a stairway. Thanks for the info. Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...

RE: Stairways

2010-05-18 Thread George Church
I just had an architect send me this since we were running a dry riser thru a stair shaft to feed attic; technically sounded like he was right, I called AHJ and he blessed my galv steel pipe running in there, along with the FDC line and wet system that did service the stairs. Having server/email/i

RE: Stairways

2010-05-18 Thread Reed Roisum
In the Vertical Exit Enclosures section (1020) of IBC 2006 it says that penetrations are prohibited except for ...sprinkler piping 1020.1.2 Penetrations. Penetrations into and openings through an exit enclosure are prohibited except for required exit doors, equipment and ductwork necessary

RE: Dry Pendent Sprinklers at 45 Degree Area

2010-05-18 Thread Brad
The degree in this post is temp, not angle -Original Message- From: Ron Greenman [mailto:rongreen...@gmail.com] Sent: Tuesday, May 18, 2010 9:18 AM To: sprinklerforum@firesprinkler.org Subject: Re: Dry Pendent Sprinklers at 45 Degree Area Unless it's been removed in the editions from thi

Re: Dry Pendent Sprinklers at 45 Degree Area

2010-05-18 Thread Ron Greenman
Unless it's been removed in the editions from this decade (I haven't had need to look since the early nineties) there is/was an illustration in 13 showing this arrangement for loading docks and eaves when the throw is within the rules. On Tue, May 18, 2010 at 4:54 AM, Tom Duross wrote: > I've act

Re: Residential Building

2010-05-18 Thread Ron Greenman
Thanks Rich. The builders loved it, the fire guys hated it. Nice to be speaking in the past tense about it. It joins the other Haighisms on the trash heap along with life safety systems (Seattle version), Class I manual dry standpipes in high rises, etc.). What a wonderful world it must have been.

Stairways

2010-05-18 Thread Brian Harris
Forum, I've always been taught that you cannot pass a pipe through a stairway, can someone point me to that section in the code book and or give me your thoughts on it? Regards, bh ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org htt

RE: Obstruction to Discharge

2010-05-18 Thread Brian Harris
Chris-, Thanks for your input, I'll definitely bring it up with the AHJ. Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Tuesday, May 18, 2010 9:45 AM To: sprinkler

RE: Obstruction to Discharge

2010-05-18 Thread Chris Cahill
There is certainly some judgment to use. Is a light really a solid continuous obstruction? String the lights end to end over a bunch of heads and I'm with you. One light judgment time. OK it's the only head in the room so all the heads are obstructed so maybe it is a solid continuous obstruction

RE: Strainer for a Circulating Relief Valve?

2010-05-18 Thread Tom Duross
Cleaning out the stuffing box drains, every pump room should have one. TD Thank you, Tom. What is the coat hanger for? ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

RE: Obstruction to Discharge

2010-05-18 Thread Brian Harris
Chris- 8.6.5.2.1.2 (07) seems to apply to any "solid continuous" obstruction... Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Tuesday, May 18, 2010 9:10 AM To: sp

RE: Residential Building

2010-05-18 Thread Richardson, R
For the record, the allowance to which Ron speaks in Seattle is on the way out now that NFPA 13R became more explicit in the 2010 edition. And I might add, that allowance came well before my time here, I just try to clean up the messes. Rich Richardson Seattle Fire Depatrtment -Original Me

RE: Obstruction to Discharge

2010-05-18 Thread Chris Cahill
>From NFPA 13 '02 - 8.6.5.2.1.4 For light hazard and ordinary hazard occupancies, structural members only shall be considered when applying the requirements of 8.6.5.2.1.3. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: chr...@sent

RE: Strainer for a Circulating Relief Valve?

2010-05-18 Thread Bobby McCullough
Thank you, Tom. What is the coat hanger for? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross Sent: Saturday, May 15, 2010 7:21 AM To: sprinklerforum@firesprinkler.org Subject: RE: Strainer for a Ci

RE: Obstruction to Discharge

2010-05-18 Thread George Church
Point out if he wanted it to look nice, he wouldn't be using surface mounted lights. If he wants recessed or concealed sprinks, change the light! -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris Se

Obstruction to Discharge

2010-05-18 Thread Brian Harris
I have a project that is using surface mounted lights that are approx. 5" deep. One of the rooms (Lobby) is very small but still has a 2x4 light, per Table 8.6.5.1.2 I need to be at least 24" away from this light in order to avoid obstruction. The problem is the room is so small I can't get 24" awa

RE: Dry Pendent Sprinklers at 45 Degree Area

2010-05-18 Thread Tom Duross
I've actually seen standard pendents on a 45 degree pitched branchline on a dry system. There are a bunch of metal butler buildings up in Gloucester, MA the fishermen use, unheated and old. I replaced a couple of drum drips about 10 years ago and these were scheduled systems with regular pendents