> Bottom line, in my opinion, sprinkler and standpipe piping can run into
> and out-of the enclosure as many times as required with
> through-penetration protection, but, not through.
I am confused. Happens very easily.
if we are allowed to make single penetrations of the [exit enclosure]
as man
http://www.charlestonbusiness.com/news/34288-s-c-senate-votes-to-delay-sprinkler-mandate-for-new-homes-until-2014
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerfo
If the AHJ determines that you cannot pass through the stair, you can always
provide a rated enclosure (1 hr or 2 hr) around your piping so that the piping
is not "in" the stair enclosure. This is often done with other utility risers.
Duane Johnson, PE
Program Manager
Division of the Fire Marsha
You need to tread carefully on this one. 2006 IBC 1020.1.2 states
"Penetrations into and OPENINGS THROUGH ...". Peel back to 1020.1 which
states "Interior exit stairways and interior exit ramps shall be
enclosed with fire barriers constructed in accordance with Section 706".
Peel back to 706.6
Forest-
It's my understanding that the 3 times rule only applies to structural
members when dealing with light hazard (8.6.5.2.1.4) I believe my situation
would fall under 8.6.5.1.2
Brian Harris
FDFP INC.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:spri
Brian,
I wouldn't jump to that conclusion... It does say "required" in the IBC
verbiage below which I assume applies to the whole list of exceptions. One
could argue that the only "required" sprinkler piping in the stair enclosure is
the pipe feeding a sprinkler or sprinklers in the stairway.
email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
__ Information from ESET NOD32 Antivirus, version of virus
signature database 5124 (20100518) __
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
__ Informat
ubscribe in the subject field)
__ Information from ESET NOD32 Antivirus, version of virus
signature database 5124 (20100518) __
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
__ Information from ESET NOD32 Antivirus, version of virus
signature database 5124 (2010
Standpipe risers in stairs are common, but pipes just passing through the stair
are often disallowed.
Better make sure you know what the local AHJ's perspective is on the matter
because there can be great inconsistency on this issue.
Craig L. Prahl, CET
Fire Protection Specialist
Mechanica
Be careful with this one, in Seattle the Building Official does not allow
sprinkler pipe penetrations of stairways unless is strictly to serve a
sprinkler in the space (eg: no pass through arrangements).
Rich Richardson
Seattle Fire Department
-Original Message-
From: sprinklerforum-bou
Based on language in NFPA 13-8.6.5.2.1.1 and 8.6.5.2.1.2, the light would be
considered an obstruction. This appears to be clarified in the commentary,
A-8.6.5.2.1.4.
But, why do you need 24"? Using the three times rule, for a light 5" deep,
you would need to be 15" away.
The options could be: (A)
You'll still need to remember to protect any penetrations with fire stopping
details equal to the rating of the stairwell shaft rating.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message
Reed-
So if it's a single stairway I can pass my sprinkler pipe straight through,
awesome. I've always routed the pipe out and around a stairway. Thanks for
the info.
Brian Harris
FDFP INC.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...
I just had an architect send me this since we were running a dry riser thru
a stair shaft to feed attic; technically sounded like he was right, I called
AHJ and he blessed my galv steel pipe running in there, along with the FDC
line and wet system that did service the stairs.
Having server/email/i
In the Vertical Exit Enclosures section (1020) of IBC 2006 it says that
penetrations are prohibited except for ...sprinkler piping
1020.1.2 Penetrations. Penetrations into and openings through an exit enclosure
are prohibited except for required exit doors, equipment and ductwork necessary
The degree in this post is temp, not angle
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Tuesday, May 18, 2010 9:18 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Dry Pendent Sprinklers at 45 Degree Area
Unless it's been removed in the editions from thi
Unless it's been removed in the editions from this decade (I haven't
had need to look since the early nineties) there is/was an
illustration in 13 showing this arrangement for loading docks and
eaves when the throw is within the rules.
On Tue, May 18, 2010 at 4:54 AM, Tom Duross wrote:
> I've act
Thanks Rich. The builders loved it, the fire guys hated it. Nice to be
speaking in the past tense about it. It joins the other Haighisms on
the trash heap along with life safety systems (Seattle version), Class
I manual dry standpipes in high rises, etc.). What a wonderful world
it must have been.
Forum,
I've always been taught that you cannot pass a pipe through a stairway, can
someone point me to that section in the code book and or give me your
thoughts on it?
Regards,
bh
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
htt
Chris-,
Thanks for your input, I'll definitely bring it up with the AHJ.
Brian Harris
FDFP INC.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Tuesday, May 18, 2010 9:45 AM
To: sprinkler
There is certainly some judgment to use. Is a light really a solid
continuous obstruction? String the lights end to end over a bunch of heads
and I'm with you. One light judgment time. OK it's the only head in the
room so all the heads are obstructed so maybe it is a solid continuous
obstruction
Cleaning out the stuffing box drains, every pump room should have one.
TD
Thank you, Tom.
What is the coat hanger for?
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
Chris-
8.6.5.2.1.2 (07) seems to apply to any "solid continuous" obstruction...
Brian Harris
FDFP INC.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Tuesday, May 18, 2010 9:10 AM
To: sp
For the record, the allowance to which Ron speaks in Seattle is on the way out
now that NFPA 13R became more explicit in the 2010 edition. And I might add,
that allowance came well before my time here, I just try to clean up the messes.
Rich Richardson
Seattle Fire Depatrtment
-Original Me
>From NFPA 13 '02 - 8.6.5.2.1.4 For light hazard and ordinary hazard
occupancies, structural members only shall be considered when applying the
requirements of 8.6.5.2.1.3.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: chr...@sent
Thank you, Tom.
What is the coat hanger for?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Saturday, May 15, 2010 7:21 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Strainer for a Ci
Point out if he wanted it to look nice, he wouldn't be using surface mounted
lights. If he wants recessed or concealed sprinks, change the light!
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Se
I have a project that is using surface mounted lights that are approx. 5"
deep. One of the rooms (Lobby) is very small but still has a 2x4 light, per
Table 8.6.5.1.2 I need to be at least 24" away from this light in order to
avoid obstruction. The problem is the room is so small I can't get 24" awa
I've actually seen standard pendents on a 45 degree pitched branchline on a
dry system. There are a bunch of metal butler buildings up in Gloucester,
MA the fishermen use, unheated and old. I replaced a couple of drum drips
about 10 years ago and these were scheduled systems with regular pendents
29 matches
Mail list logo