Something else you might want to keep in mind is the idea of AS-BUILT
CALCULATIONS. Say you calc an Ord. Haz. II at 104 SF/head because the heads
are 6'-6 from one wall and 4'-0 from another. But there is a conduit at
4'-0. The fitter knows 130 SF max for standard coverage heads in Ord. Haz.,
so
the last time I looked there was no such restriction. You may be
thinking of Electrical VAULTS which does have that restriction. You
can identify these by the high voltage 10,000 or 12,000 voltage
entering the vault and the 3 or 4 hour fire rated construction
segregating it form the
Why would different voltages, or the addition of an elevator motor make a
difference whether a pipe can go in and out or not? If a pipe that enters a
room is going to leak, why is the leak different if it stops in the room or
passes through?
Ed
-Original Message-
From:
In all seriousness, I find submission of AsBuilts in this industry as the
exception rather than the rule, and the likelihood of AsBuilt Calcs even more
remote, absent a contractual obligation and an engineer either smart enough or
PIA enough to followup.
Not saying they aren't a great idea
Hello Ed.Tambini,
I know here that anything that enters the elevator room can not exit the room
unless it goes directly into the shaft. Had a building that had been here 20
years, Got a new owner who did the typical paint/wallpaper make over. When the
elevator inspector came out the sprinkler
We've had similar experiences, but when questioned, no one can produce a code
reference to back it up.
Ed
Aero Automatic Sprinkler
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Charles Thurston
Sent:
All true George, and maybe I worry a little too much, but when Gerzayn
mentioned Best Practice, the idea of not all heads ending up exactly as
planned occurred to me. I left out the part about calcing all sched. 40 and
figuring total pressure at all flowing outlets, not just a few! Have you
ever
Pain in ...
Similar to badge heavy in this usage.
George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE 570-837-6335 fax
g...@rowesprinkler.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Brian Harris
FDFP Inc.
_
From: Brian Harris [mailto:br...@firstdefensefire.com]
Sent: Tuesday, March 01, 2011 11:32 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Pre-Action
Quick question,
What is the reasoning for pitching a pre-action system like you would a dry
To get the water out of the pipes.
Why are you putting a preaction in a heated area?
Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com
Craig-
Customer request, I know it's to drain the pipes but why the need to
completely drain them if it's heated? Corrosion?
Brian Harris
FDFP Inc.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Any room with contents sensitive to water? Electrical equipment rooms, come to
mind. As far as pitching the pipe, it is required by code, but all the code
language suggests it's predicated on the assumption the system will be used in
an area subject to freezing. If it's an issue you could
Please check the following book; ASME A17.1/CSA B44-2004;Safety Code for
Elevators and Escalators; Section 2.8.2.; Pipes , Ducts, Tanks ,and
Sprinklers.; Diagram 2.8.1.;Machine Room Pipe,etc.,Separation ;. 2.8.2.3.
.the ASME Code A17 Committee could not blindly prohibit sprinklers in
Ok, why? What's his concern?
If he wants PA because he scared of accidental sprinkler discharge then any
water in the pipes could leak on his stuff. So drain it.
But regardless, if you don't need to drain it, he doesn't need a PA system.
Give us some specifics.
Craig L. Prahl, CET
Fire
The code reference is from the ASME Code for Elevators A17.1 2004 edition as
referenced by the 2006 IBC
Jim Davidson
Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500 Fax:302-234-1781
-Original Message-
From:
FOR THOSE WHO MAY NOT HAVE A17.1 HANDY.. AND THAT REFERENCE STATES
???
Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
ASME A17.12007
2.8.3 Pipes, Ducts, Tanks, and Sprinklers
2.8.3.1 Steam and hot‐water pipes shall be permitted to be installed in
hoistways, machinery spaces, machine rooms,
control spaces, and control rooms for the purpose of heating these areas only,
subject to 2.8.3.1.1 through 2.8.3.1.3.
Since the PA system is filled with compressed air, minimizing the water in
it helps minimize corrosion and/or MIC. Won't stop it, but should give the
system a longer life.
Ed Kramer
Littleton, CO
Quick question,
What is the reasoning for pitching a pre-action system like you would a
dry
Just a follow up on AS Built drawings, won't they become Common practice
as NFPA 3 Commissioning becomes more common???
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Thursday, March 03,
Pitch to drain the water out to minimize air water interface.
Provide N2 cylinders or generator for air supply, or a GAP dry Air Pak, to
minimize corrosion.
Speaking of corrosion, we were looking at a job where 13 year old Sch 10 galv
has had 3 pinholes surface in last week.
Pitched right,
WHEN? IF….
On Thu, Mar 3, 2011 at 12:35 PM, Thom tmcma...@firetechinc.com wrote:
Just a follow up on AS Built drawings, won't they become Common practice
as NFPA 3 Commissioning becomes more common???
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Thank you all for your help, it is much appreciated
Ed
Aero
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joe Burtell
Sent: Thursday, March 03, 2011 1:16 PM
To: sprinklerforum@firesprinkler.org
Subject:
While Cx is on the front page of all the cutting edge magazines, most of us
know BIM is a generation away from realizing half its potential, and most of
what BIM or Revit are used for, from what I've heard, is that it's a collision
checker- that's it.
The vast majority of work in our industry
Understand still no LEED points for sprinklers and we haven't released the RP
for Cx and Integrated Testing yet.
So without points and without a procedure to follow, I think we're talking
infancy.
However, I live in the sticks- but I do get out occasionally ;) and
occasionally communicate
CX?
Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Craig,
My guess is 'Commissioning'.
Cliff Whitfield, SET
President
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Ph: 850-526-1886
Fx: 850-526-1884
cl...@fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Folks,
The Commissioning Industry is gaining BIG ground as real BIM approaches. Cx is
easier to implement than the total BIM process and so it will gain ground
faster than BIM, and you can see how quickly the idea of having BIM is growing.
Everyone is using the catch phrase BIM when we are
Commissioning per NFPA 3, but what's that? I see it on a list with Easter
Bunny, Tooth Fairy and Great Pumpkin.
SML
Sent from my Verizon Wireless BlackBerry
-Original Message-
From: Cliff Whitfield cl...@fire-design.com
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Thu,
Dude,
Ya gotta add to THAT list:
Commissioning per NFPA 3, but what's that? I see it on a list with Easter
Bunny, Tooth Fairy and Great Pumpkin, GSA, US NAVY, HARVARD.
Hey, would ya look at that?!?! Yer right, they go together. :-)
SprinklerGEEK
Subject: Re:
Add USACE on certain projects (Not necessarily per NFPA 3 but full
commissioning with REAL BIM).
Rod DiBona
Rapid Fire
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sprinkler
Academy - C Bilbo
Sent:
Many Gov. agency's (GSA) and other are now Revit only, and BIM is really
making headway with smart metering and building control systems.
Maybe not as long as we dinosaurs would like?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org