Re: Base of riser on placards

2016-07-08 Thread Brad Casterline
Sorry, I just wanted to add one more thing-- Personally, I would be skiddish drawing too many conclusions from calc placards. As-Builts and Main Drain Tests is what I would want. I would call BOR the Riser Gauge. That would also be the Test Node, since I would measure the MD pipe, fittings and valv

Re: Base of riser on placards

2016-07-08 Thread Brad Casterline
Maybe it was 1972 Edition. It's been a year and a half since I knew for sure. b On Jul 8, 2016 2:30 PM, "Timothy W Goins" wrote: > Main drain testing should only be compared to other main drain testing. > The usual Venturi effect on the supply/system gauges do not give you an > accurate pressure

Re: Base of riser on placards

2016-07-08 Thread Timothy W Goins
Main drain testing should only be compared to other main drain testing. The usual Venturi effect on the supply/system gauges do not give you an accurate pressure reading when reading the residual pressure as the water passes by on its way to the drain. "For I am not ashamed of the gospel, becau

RE: Base of riser on placards

2016-07-08 Thread Brad Casterline
Main Drain tags are usually legible though, even on pipe scheduled systems. What was "Base of Riser" before 1975? (the year the Density/Area Curves made their first appearance if I'm not mistaken). Brad _ From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org

RE: Base of riser on placards

2016-07-08 Thread Todd Williams
I've also seen placards that are total crap, but that's another issue... Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2] On Fri, Jul 8, 2016 at 3:09 P

RE: Base of riser on placards

2016-07-08 Thread Scott Futrell
This is a fun discussion to watch (read). Plays right into the relevancy (or not) of NFPA 25. Placards are generally not legible when I need to look at them because 1) someone wants to revise their system, 2) someone wants me to analyze their system, 3) we are doing risk management at a facilit

Re: Base of riser on placards

2016-07-08 Thread Todd Williams
A main drain test is for comparison to previous main drain tests only. There should be one done when the system in put in service. Any deviation from that means a change in available water but not any hydraulic analysis Sent using CloudMagic Email [https://cloudmagic.com/k/d/mailapp?ct=pi&cv=7.

Re: Base of riser on placards

2016-07-08 Thread rongreenman .
Different test. Full flow test is to ensure the back flow device fully opens (the question is what is a full test mean and I believe has been determined to be the system demand rather than how much water push through the pipes). The main drain test is to verify that the originally recorded residual

RE: Base of riser on placards

2016-07-08 Thread Ryan Labrie
A 2” main drain is not sufficient in all situations. You must be able to a full forward flow of the backflow including system demand and hose streams (#13 2010 10.10.2.5.2). I have installed a test header with 2½” hose valves at the riser to do this in the past. Ryan Labrie Fire Protection Desi

Re: Base of riser on placards

2016-07-08 Thread rongreenman .
Good. That is a good rationale for that particular piece of information being readily available. I have had that problem before myself, but the anomaly was easily noticed as the provided and collected data defied physics so I knew something was wrong before I stated anything. On Fri, Jul 8, 2016 a

RE: Base of riser on placards

2016-07-08 Thread Steve Leyton
I’ve always looked at it as a red-flag benchmark. The residual demand at BOR takes static lift and friction loss to the remote area into account, so if I do a main drain test and I look at the calc’ card and read that the demand is … whatever, 63.5 PSI @ 331.7 GPM. And then I look at the gau

Re: Base of riser on placards

2016-07-08 Thread rongreenman .
So I have the total demand at the BOR and the expected pressure loss from static with the entire design area flowing. How does a main drain test simulate this? My understanding of the main drain test is a comparative analysis of pressure drop as recorded at acceptance from the Contractor's Above Gr

RE: Base of riser on placards

2016-07-08 Thread Steve Leyton
The information of value at least once a year when you do the main drain test. Maybe you could add both BOR and Source demands, but I don’t agree with posting Source data in lieu of BOR. SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd William

RE: Base of riser on placards

2016-07-08 Thread Todd Williams
I'll ask the unthinkable question, is the BoR demand on the placard worthwhile? Hydraulic calculations are done back to the effective point of the flow test. The underground losses, hose demand and sometimes backflow preventer losses are taken before the BoR. Consequently you cannot compare the

Re: Dwelling Unit Sprinkler Calc

2016-07-08 Thread wmenster
In response to the original question, is it just me or are we over-thinking this? NFPA 13 says that when using residential heads, you calculate the 4 heads that produce the greatest hydraulic demand.  No mention of units, rated walls, corridors, type of construction, etc.   I didn't know Geor

RE: Base of riser on placards

2016-07-08 Thread Ed Kramer
I’ve asked this question in the past and the answers have been all over the board. I tend to think the BOR location needs to be consistent from project to project, whether it’s a single system riser or multiple system risers. In our part of the universe, most (but not all) backflow preven