So I have the total demand at the BOR and the expected pressure loss from
static with the entire design area flowing. How does a main drain test
simulate this? My understanding of the main drain test is a comparative
analysis of pressure drop as recorded at acceptance from the Contractor's
Above Ground Materials and Test Certificate with the pressure drop at the
time of the test. I presume that original data is what is noted under the
area of the placard for "Supply Data" and is irrelevant regarding the
calculations.



On Fri, Jul 8, 2016 at 10:16 AM, Steve Leyton <[email protected]>
wrote:

> The information of value at least once a year when you do the main drain
> test.   Maybe you could add both BOR and Source demands, but I don’t agree
> with posting Source data in lieu of BOR.
>
>
>
> SL
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Todd
> Williams
> *Sent:* Friday, July 08, 2016 10:15 AM
> *To:* [email protected]
> *Subject:* RE: Base of riser on placards
>
>
>
> I'll ask the unthinkable question, is the BoR demand on the placard
> worthwhile? Hydraulic calculations are done back to the effective point of
> the flow test. The underground losses, hose demand and sometimes backflow
> preventer losses are taken before the BoR. Consequently you cannot compare
> the BoR demand to a new public water test and make a valid conclusion
> without a full set of original plans and calculations. Wouldn't it make
> more sense to put the demand at the water source on the placard?
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-608-4559 (cell)
>
>
>
> Sent using CloudMagic
> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>
>
>
> On Fri, Jul 8, 2016 at 10:21 AM, Ed Kramer <[email protected]> wrote:
>
> I’ve asked this question in the past and the answers have been all over
> the board.
>
>
>
> I tend to think the BOR location needs to be consistent from project to
> project, whether it’s a single system riser or multiple system risers. In
> our part of the universe, most (but not all) backflow preventers are
> located inside the building immediately downstream of the underground
> flange. I locate the BOR at the underground flange on all systems. By
> placing data from that location on the Hydraulic Design Placard, it makes
> it easier for someone else to compare the sprinkler system demand to water
> supply data.
>
>
>
> I believe the intent is to include the combined hose allowance, but got
> nothing from the standard to back that up. With a strong water supply (lots
> of volume), available pressure while flowing the sprinkler plus hose demand
> is going to be virtually the same as pressure available while flowing only
> sprinkler demand. But many of the water supplies we work with are marginal.
> Removing 100, 250 or 500 gpm combined hose allowance from the water supply
> can make a very significant difference in available pressure. So when
> comparing sprinkler demand to water supply data, knowing the combined hose
> allowance is very helpful.
>
>
>
> Respectfully,
>
> Ed Kramer
>
> Bamford Fire Sprinkler
>
>
>
>
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Ben Young
> *Sent:* Thursday, July 07, 2016 3:06 PM
> *To:* [email protected]
> *Subject:* Base of riser on placards
>
>
>
> What's the general consensus on the location of the 'base of riser' for
> hydraulic placards that everyone uses? See Figure A 24.5 in the 2010
> Edition of 13 and/or 24.5.2
>
> I feel its supposed to be at the base of each sprinkler riser (where you
> have multiple systems) where it ties into a common header.
>
> Others in my office think its where the incoming flange comes into the
> riser room.
>
> If you have a vertical riser with a vertical backflow, then these two
> points would be the same with either method in my line of thinking.
>
> Also, is the hose indicated on the placards supposed to be inside hose
> only, or combined in and out?  I just realized after reading this today
> that it could only be referring to inside hose, but I've always put the
> combined hose there...
>
> Thanks,
>
>
> Benjamin Young
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)