RE: Misc. Gas Storage

2018-05-17 Thread Thomas Reinhardt
Depending on what codes you have adopted check out the following: International Fire Code chapters : 50,53,63, and 61. The chapters will reference NFPA 58 and other codes. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin Sent: Wednesday, May 16

Re: Dry Barrel Sprinklers

2018-05-17 Thread Richard Mote
I don't know, I started in the business in Sept. 1978, and it was in the book then, -Original Message- From: Mark Eckard To: sprinklerforum Sent: Thu, May 17, 2018 3:34 pm Subject: RE: Dry Barrel Sprinklers As an option if return bends cannot be installed in a heated space. Tha

RE: Dry Barrel Sprinklers

2018-05-17 Thread Mark Eckard
As an option if return bends cannot be installed in a heated space. Thank You *Mark E. Eckard SET* *Fire Protection Services, LLC* 2126 US Hwy. 41 North Perry, GA 31069 Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta) Mobile: 478-244-6653 SYL-216 *From:* Sprinklerforum

RE: Dry Barrel Sprinklers

2018-05-17 Thread Matt Grise
Can you clarify? Do you mean when they first came in as an option? Matt From: Sprinklerforum On Behalf Of Mark Eckard Sent: Thursday, May 17, 2018 2:30 PM To: sprinklerforum@lists.firesprinkler.org Subject: Dry Barrel Sprinklers Does anyone know what year the requirement to install Dry Barrel

Dry Barrel Sprinklers

2018-05-17 Thread Mark Eckard
Does anyone know what year the requirement to install Dry Barrel pendent sprinklers appeared in NFPA-13? -- *Mark E. Eckard SET* *Fire Protection Services, LLC* 2126 US Hwy 41 Perry, GA 31069 Office: (478) 987-7319 or (404) 445-0798 Cell: (478) 244-6653 meck...@fireprotectionservicesllc.com ___

RE: Misc Rack Storage

2018-05-17 Thread Larry Keeping
Just a word of caution. When you are using 23.4.4.1.1.4, you also have to have additional flow added in, as per the corresponding 23.4.4.1.1.5 (see A.23.4.4.1.1.4). Larry Keeping From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin Sent: May-17-1

RE: Misc Rack Storage

2018-05-17 Thread John Irwin
Thanks everyone. John Irwin DynaFire Inc. – “*Same Day – Next Day*” *From:* Sprinklerforum *On Behalf Of *Steve Leyton *Sent:* Thursday, May 17, 2018 11:36 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* RE: Misc Rack Storage What Craig and Travis said. From a performance per

RE: Misc Rack Storage

2018-05-17 Thread Steve Leyton
What Craig and Travis said. From a performance perspective, I always liked the “double density” approach where you prove the required density for the hazard that mostly characterizes the use and then a smaller hot spot for the more hazardous aberration. So EH2 per Chapter 11, and also a .6/900

RE: Misc Rack Storage

2018-05-17 Thread Art Tiroly
Two rows of in-rack sprinklers may solve the rack problem. Art Tiroly From: Sprinklerforum On Behalf Of John Irwin Sent: Thursday, May 17, 2018 11:23 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Misc Rack Storage Regardless of the trailers, do I need to provide .6/2000 f

RE: Misc Rack Storage

2018-05-17 Thread John Irwin
We have a winner. Thanks. 23.4.4.1.14 – uhg Is this even English? John Irwin DynaFire Inc. – “*Same Day – Next Day*” *From:* Sprinklerforum *On Behalf Of *MFP Design, LLC *Sent:* Thursday, May 17, 2018 11:29 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* RE: Misc Rack Stor

RE: Misc Rack Storage

2018-05-17 Thread MFP Design, LLC
When you have mixed criteria areas, you need to extend the higher density into the lower density area for 15’. Reference NFPA 13: 12.3 for that requirement. Also, don’t forget the issue of complying with 23.4.4.1.1.4. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298

RE: [EXTERNAL] RE: Misc Rack Storage

2018-05-17 Thread Prahl, Craig/GVL
Not necessarily, you could use the provision of dissimilar adjacent hazards where you extend the more demanding design criteria 15 ft beyond the limit of that area per 12.3 (1) (2016 NFPA 13). Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jaco

RE: Misc Rack Storage

2018-05-17 Thread Steve Leyton
One single rack? Seems to me that it makes sense to lower the storage and spread it out. Look at the definition of miscellaneous storage – if one fixture doesn’t characterize the occupancy, then it’s miscellaneous storage. But 24’ of plastics is a serious fire load, so diluting it makes sens

RE: Misc Rack Storage

2018-05-17 Thread John Irwin
Regardless of the trailers, do I need to provide .6/2000 for the racks? If so, do I need to do that for the entire 5,000 sqft area? Seems excessive. John Irwin DynaFire Inc. – “*Same Day – Next Day*” *From:* Sprinklerforum *On Behalf Of *Steve Leyton *Sent:* Thursday, May 17, 2018 11:19

Re: Weight of water filled pipe

2018-05-17 Thread Fpdcdesign
The table description states “... for Determining Horizontal Loads” and it is under the section for Earthquake Bracing. The question came up do these apply to vertical loads for regular hangers. Maybe this table should be A.9.1.1.2 instead. Todd G Williams, PE Fire Pro

RE: Misc Rack Storage

2018-05-17 Thread Steve Leyton
I tend to agree – trailers potentially shielding fire load within from sprinklers above (5.4.2). SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fpdcdesign Sent: Thursday, May 17, 2018 7:06 AM To: Sprinklerforum Subject: Re: Misc Rack Storage Wouldn

Re: Weight of water filled pipe

2018-05-17 Thread cw bamford
well the answer is weight is weight ... horizontal or vertical using a 2013 edtion NFPA 13 Table A.9.3.5.9 has pipe weight foot then 9.2.5 Support of Risers 9.2.5.5support every <25' Figure A.9.1.2.3(1) & Exhibit 9.14 show some Vertical Loads. I think we are getting into Physic

RE: Weight of water filled pipe

2018-05-17 Thread Matt Grise
Is there a reason that the weight would be different? Matt From: Sprinklerforum On Behalf Of Fpdcdesign Sent: Thursday, May 17, 2018 9:03 AM To: Sprinklerforum Subject: Weight of water filled pipe Is there a reliable table for the weight of water filled pipe for vertical loading (as in a st

Re: Misc Rack Storage

2018-05-17 Thread Fpdcdesign
Wouldn’t the trailer storage bring it up to EH2? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On May 17, 2018 at 9:47 AM, mailto:john.ir...@dynafire.com)>

Weight of water filled pipe

2018-05-17 Thread Fpdcdesign
Is there a reliable table for the weight of water filled pipe for vertical loading (as in a straight hanger)? Table A.9.3.5.6 is for determining horizontal loading, per the heading. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 8

Misc Rack Storage

2018-05-17 Thread John Irwin
Here’s the situation … I have a 5,000 sqft, (currently) ordinary hazard mixed use space. The new tenant intends to store two emergency disaster management trailers in this space. However, along two walls, they want to put a 3-teir rack with storage up to 20’ in height. TOS in the center of the unit