RE: system modification hydro test

2018-11-15 Thread Pete Schwab
There was some attempt to rewrite these testing procedures during the 2019 process. Some for wet and some for dry. It didn’t really go anywhere but there definitely was a desire to see it changed based on conversations exactly like this. NFPA 13 is open for Public Inputs so fire away!! From: S

Re: system modification hydro test

2018-11-15 Thread Phillips, Mark
Yes An AHJ can ask for anything. We produce a letter outlining NFPA testing requirements to the GC and dissolve us of any libilaty due to testing existing system and we dont test until they agree and sign. Just SOP Sent from my cell phone. Please excuse spelling etc. Mark Phillips Vice Pr

RE: system modification hydro test

2018-11-15 Thread MFP Design, LLC
That’s funny. I believe that statement has been in the standard since before flex drops were even available. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com

RE: system modification hydro test

2018-11-15 Thread bjnewlin
Yes.  We were told that the only instance where isolated drops that numbered greater than 20 would not require hydrostatic testing at 200 psi was if they were existing flex drops that were relocated within the original radius of the flex drop and they weren't removed from the existing system.   The

system modification hydro test

2018-11-15 Thread Matt Grise
We had a situation where a TI modification involved adding over 20 mechanical t's to a system (office area layout change). NFPA 13 2013ed 25.2.1.6 says "modifications that cannot be isolated, such as relocated drops, shall not require testing in excess of system working pressure" The mechanica

Re: Tracpipe commodity class

2018-11-15 Thread Bruce Verhei
I’ve had good luck if you getting back to manufacturer. If they don’t have the right person I have them refer me to their insurer. Often at that point, especially if it’s FM, you are within 2-3 calls. It may be they are more helpful if you are the fire department. Best. Bruce Verhei > On N

Re: Tracpipe commodity class

2018-11-15 Thread Ben Young
Sorry I meant E84 not 82. On Thu, Nov 15, 2018 at 11:06 AM Ben Young wrote: > Does anyone know the commodity classification for Tracpipe counterstrike > gas line? > Its SS flex with a polyethylene jacket that includes a flame retardant. > It comes on wooden spools. > > Apparently this place is t

Tracpipe commodity class

2018-11-15 Thread Ben Young
Does anyone know the commodity classification for Tracpipe counterstrike gas line? Its SS flex with a polyethylene jacket that includes a flame retardant. It comes on wooden spools. Apparently this place is the only one that stores this stuff. Is there someplace where UL or FM or anyone else keep